| 
Rank: Forum user   | 
            
	      
                Hi, I have looked at approved document B and it only seems to refer to the internal of a Building. Our insurers have advised we removed a part of the Building at the side that used to house an oil storage tank many years ago before we rented the property.  The reason being is that approx 15 feet away from our final exit the external route becomes narrow to 559 milimetres to which I have on multiple occasions safely passed through. There are other fire exits to the front of the Building and would most likely only have a maximum of 1 person passing through in an event of emergency althought unlikely. Can anyone advise if there is a rule on measurements on this please I am now under scrutiny from the Business. Edited by user 15 August 2024 14:28:26(UTC)
 | Reason: Not specified | 
    | 
             | 
            
         | 
    |  | 
        
        
        
            
        
            
            
    | 
Rank: Super forum user   | 
            
	      
                Advise what?  You haven't asked a question - you've made a series of statements, and it's not clear to me (at least) what advice you are looking for. | 
    | 
              1 user thanked achrn for this useful post. |  | 
    |  | 
        
        
        
    
        
            
            
    | 
Rank: Super forum user   | 
            
	      
                When you rented the building it's use was likely changed. Redundant fuel storage removal would be prudent in eliminating environmental risks in the future and controlling costs to todays values. As to the final exit being 559mm beware of using yourself as a standard measure - would a fire & rescue worker in full kit be able to readily pass? Too often we only observe the world in terms of how we fit rather than how others do  | 
    | 
              2 users thanked Roundtuit for this useful post. | 
            Kate on 15/08/2024(UTC), Kate  on 15/08/2024(UTC)
         | 
    |  | 
        
        
        
            
        
            
            
    | 
Rank: Super forum user   | 
            
	      
                When you rented the building it's use was likely changed. Redundant fuel storage removal would be prudent in eliminating environmental risks in the future and controlling costs to todays values. As to the final exit being 559mm beware of using yourself as a standard measure - would a fire & rescue worker in full kit be able to readily pass? Too often we only observe the world in terms of how we fit rather than how others do  | 
    | 
              2 users thanked Roundtuit for this useful post. | 
            Kate on 15/08/2024(UTC), Kate  on 15/08/2024(UTC)
         | 
    |  | 
        
        
        
    
        
            
            
    | 
Rank: Super forum user   | 
            
	      
                Let's be clear, ADB only really applies to new builds or where significant changes to the building are proposed. There are 1000s of buildings where ADB and BS999 guidance cannot be strictly applied- for example historic premises. The exit routes for your premises are down to you to establish via a (suitable & sufficient) fire risk assessment. To be fair, ADB, BS999 and other guidance is really useful at setting benchmarks, but try applying it to a medieval church with a tiny arched entrance door or an overheight Victorian single staircase building in a city centre ADB does state escape widths "May be reduced to 530mm for gangways between fixed storage racking, other than in public areas of ‘shop and commercial’ (purpose group 4) buildings."(Table 2.1 on page 19)
 
 Thats a useful benchmark which sets an absolute minimum escape width for minimal numbers of staff only. However to apply this to an external final exit would need to most careful consideration to justify and could only be done in exceptional circumstances (sse the last paragraph re Grandfather rights)
 
 Reducing down to less that 600mm would be hugely difficult to justify at any time and especially where: the public are present, if there are say more than 10 staff expected to use the route, if you could reasonably expect disabled persons to be in the premises, if you have conditions where a rapidly developing fire may occur or if you use anything less than a Cat L2 fire detection system to assist a simultaneous evacuation
 
 But the big advantage you have is grandfather rights.  If you have used this exit for many years and have documented evidence of successful fire drills and you havent made any significant changes to your business (other than not using oil!), that certainly helps your case
 
 Can I ask why are the insurance company getting involved?
 | 
    | 
             | 
            
         | 
    |  | 
        
        
        
            
        
            
            
    | 
Rank: Forum user   | 
            
	      
                Originally Posted by: Messey  Let's be clear, ADB only really applies to new builds or where significant changes to the building are proposed. There are 1000s of buildings where ADB and BS999 guidance cannot be strictly applied- for example historic premises. The exit routes for your premises are down to you to establish via a (suitable & sufficient) fire risk assessment. To be fair, ADB, BS999 and other guidance is really useful at setting benchmarks, but try applying it to a medieval church with a tiny arched entrance door or an overheight Victorian single staircase building in a city centre ADB does state escape widths "May be reduced to 530mm for gangways between fixed storage racking, other than in public areas of ‘shop and commercial’ (purpose group 4) buildings."(Table 2.1 on page 19)
 
 Thats a useful benchmark which sets an absolute minimum escape width for minimal numbers of staff only. However to apply this to an external final exit would need to most careful consideration to justify and could only be done in exceptional circumstances (sse the last paragraph re Grandfather rights)
 
 Reducing down to less that 600mm would be hugely difficult to justify at any time and especially where: the public are present, if there are say more than 10 staff expected to use the route, if you could reasonably expect disabled persons to be in the premises, if you have conditions where a rapidly developing fire may occur or if you use anything less than a Cat L2 fire detection system to assist a simultaneous evacuation
 
 But the big advantage you have is grandfather rights.  If you have used this exit for many years and have documented evidence of successful fire drills and you havent made any significant changes to your business (other than not using oil!), that certainly helps your case
 
 Can I ask why are the insurance company getting involved?
 Hi thanks for the response. The insurers pick a site to use as a sample as we have hundreds for our annual tender. They dont normally look at specifics to an individual site but on this occasion have. | 
    | 
             | 
            
         | 
    |  | 
        
        
        
    
        
            
            
    | 
Rank: Forum user   | 
            
	      
                This is why a Fire Risk Assessment is called an FRA! Some FRAs are simply a compliance check against standards. When everything meets the standard, the job is easy. But the competence of the assessor comes into play when the current standards are not met, that's when the risk assessment bit of the title truly kicks in. The assessor has to consider all the factors, including additional mitigation controls that may 'compensate' for the shortfall against a standard. There are some recognised allowances that can be applied which are straightforward, but in many cases, professional judgement may need be used. Questions I would ask include "Does this need to be an escape exit and why?"; "How many other escape routes are needed and/or available?"; "How many people does it need to be wide enough to handle?"; "Likely to be used by wheelchair users?'; etc. Your FRA should have considered all these matters. If your FRA was undertaken by a competent assessor, it should have recognised the narrow exit and then commented on why they deemed it as acceptable (if they did of course). Having said that, insurance companies often require controls over and above basic legal compliance. It can be hard to argue with them :(.  Hope it helps, Tony. | 
    | 
             | 
            
         | 
    |  | 
        
        
        
            
        
            
            
    | 
Rank: Super forum user   | 
            
	      
                Originally Posted by: antbruce001  This is why a Fire Risk Assessment is called an FRA! Some FRAs are simply a compliance check against standards. When everything meets the standard, the job is easy. But the competence of the assessor comes into play when the current standards are not met, that's when the risk assessment bit of the title truly kicks in. The assessor has to consider all the factors, including additional mitigation controls that may 'compensate' for the shortfall against a standard. There are some recognised allowances that can be applied which are straightforward, but in many cases, professional judgement may need be used.
 This is what separated The Fire Precautions Act and the Fire Safety Order 
 
 The former involved applying strict rules like a robot with no opportunity for flexibility or even common sense. The latter allows creativity and professional judgement - but sadly it appears that many hang on to advice as if it were a legal requirement. That's a pity
 
 I always loved these sort of difficult jobs, which was just as well as I worked in an industry where there were often challenges where no guides of SOPs could be applied so some kind of lateral thinking would be required
 | 
    | 
              1 user thanked Messey for this useful post. |  | 
    |  | 
        
        
        
    
                           
    You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.