Hopefully someone can point me in the right direction to obtain the correct info.
I'm currently in discussions with a building contractor about the number of exits required in a CAT 3 lab. I'm of the opinion there should be two exits, the building contractors says not.
Any guidance other than building regs?
Thanks
Andy
|
|
|
|
Rank: Super forum user
|
All the cat 3 labs I have seen have always had a main exit/entrance and a fire/evacuation only exit, which was sealed behind a pull out plastic cover
|
|
|
|
Rank: Forum user
|
Thank you.
Any idea if there is a British Standard? Fire regs say Ideally have two exits.
|
|
|
|
Rank: Forum user
|
Hi Scrumpyman
I have a feeling that the "Cat 3" issue is a bit of a red herring on an assumption that you're referring to either biological or radiological hazards.
Bio Cat 3 is enforced via COSHH and there is nothing within this that states any additional controls are required, thus refer to Building Regs and relevant industry codes of practice.
Rad is covered via IRR and your RPA will be able to advise but suggest that Building Regs would still be applicable.
Unless you're referring to something else?
Hope tha this helps
Pete
|
|
|
|
Rank: Forum user
|
Thanks Pete.
Its as I thought really. Its Biological so will come under CoSHH. Just cant find anything other than the building regs which say Section b1.v there should be alternative means of escape.
At the moment the plan is to build the cat 3 lab with one exit and no other means of escape. My argument is there should be an alternative means of escape. The other point is the lab will be in a basement with only one way in and out of the basement. I don't want to sign this off without getting the alternative escape route.
|
|
|
|
Rank: Super forum user
|
Have you had a chance to consult with a fire engineer? Being a basement adds a level of hazard - they will ask what is adjacent / outside? how far are the travel distances? what are the lab dimensions? Is it a place of special hazard (thus generating a 9m travel distance) or a 'normal' risk?
If you engage a fire engineer you would get an informed opinion - whether you agree with it or not.
S
|
|
|
|
Rank: Super forum user
|
Why the objection to a single travel distance?
Unless the lab is working using materials which may develop a rapid spread of fire, I am not sure what the issue is? I think we used ADB in ours, but the work carried on is low fire risk.
I have also seen the sealed escape doors (in this case, 600mm x 600mm escape hatches under benches!) that A Kurdziel talks about in a lab built in the last few years.
We installed aspirating SD in the rooms and in the air gap around the rooms for early detection, and had MCPs installed in all labs so that staff could operate them quickly without going through air locks
It was the air locks that posed the biggest issues. Building control made a fuss as they said they formed inner/inner/inner rooms, whilst I argued they were lobbies. Plus the MOE through the air locks did slow down the MOE as staff had to pass through them unless conditions in the space were untenable.
I am still not 100% happy with the set up, but unannounced fire drills show that they work!
|
|
|
|
Rank: Forum user
|
Its not so much that there is only one exit. Its an exit into another room, then into another room then onto a staircase that leads to a place of relative safety, then on to a place of absolute safety.
The Cat 3 lab will be in a basement which reduces the maximum travel distances and it could be argued as there will be flammable substances in the lab that it is a place of special fire hazard.
mssy your opinion is greatly valued as you obviously have first hand experience with this.
|
|
|
|
Rank: Super forum user
|
Unfortunately my experience was with a low/non combustible process, so perhaps not comparable with this trickier one
Your layout of course is an inner/inner room which so often freaks out building control and fire safety folk alike. However, I try not to get myself too excited about this concept.
The travel distance through each room, plus the nature of activity in those access rooms is critical when assessing this risk. EG: If there's a long travel distance through an access room where flammable substances are being stored or used, you have a problem
The coverage of AFD and type of heads are critical to achieve an early detection of fire, and the door fixings from the high risk area may need to be panic bolts/pads to help with a rapid movement.
Lastly the management of the housekeeping in the access rooms and circulation space needs to be controlled to avoid combustibles and ignition sources
Can you help fill in any of those details? (although I am doubtful I can give anywhere near a definitive answer to your questions being blind as it were)
|
|
|
|
Rank: Super forum user
|
It’s not the fact that that you might be working with flammable materials in the CL3 lab that is the issue but having it in basement is bit scary if, for example, a fire was to break out upstairs and there was no other way out. The last two CL3 labs I was involved with we decided that they had to be sited in a separate building.
Locating in an existing building can be interesting when you are trying to install the dedicated air handling systems. How are you going to fumigate the lab? if you use traditional formaldehyde then you will need to be able to purge the lab after fumigation (itself a minor fire risk) and that gas will need to go somewhere; all the way from the basement to the roof.
Sounds like fun
|
|
|
|
Rank: Forum user
|
We have 2 cat 3 rooms on 2 sites, Both are single travel, less than 9 meters with a fume cupboard at the bottom one comes into a lab with 2 way travel, the other exits into acorridor with 2 way travel, both have in date certification and built to standard. You do not need 2 way into such a small room
negative air pressure is more important
|
|
|
|
Rank: Forum user
|
That's all very interesting, thank you very much.
The lab is in a basement which is a problem in itself.
|
|
|
|