Estates do all of the damper maintenance
see also this alert, this should have been signed off by the trust find out who did it and ensure maintenace is carried out under article 17 of the RRO
here is link to alert which also helps on compartmentation
https://www.iheem.org.uk/write/EFA_2014_003_Fire_Dampers.pdf
HTM 03.01 b
4.13 All fire dampers should be tested as part of the annual verification
you should ensure all maintenance is carried out on
Emergency generators
Emergency Lighting
Portable fire fighting appliances
Portable fire fighting extinguishers
Private fire hydrant testing
Private fire hydrant bypass valve testing
Dry/Wet fire main riser testing
Inert gas systems
Fire warning systems
Cause and effect for horizontal evacuation
Fire smoke and ventilation system damper tests BS9999:2017
Fire door condition, calso note cold seals and intumescent strips
Liquid oxygen storage and tanjk maintenance
Lightning conductors
Fixed electrical installations
Portable appliance testing
Gas installations
Cooking ductwork and filters
then there is quality assurance for
Hot works certificates
compartmentation breeches
Contractors induction
your staff training
information provided for employees
Fire policy
fire procedures
Etc etc etc
it becomes more complicated with PFI or the new long arm within the NHS companies at the end of the day you must provide evidence that you comply with outcome 10a of the care quality commission document
PM me your NHS email and i will provide you with the documentation i use
Edited by user 03 April 2018 10:58:45(UTC)