#1 Posted : 10 December 2002 18:50:00(UTC)
Rank: Guest
Admin

Posted By Andrew J Blair Can anyone tell me the required frequency for the electrical testing of temporary site accommodation (ie Site Portacabins)on a construction site. I think it is every 6 months? Also, can anyone direct me to the specific piece of legislation or guidance which states or suggests the frequency the site accommodation electrical installation must be tested.
Admin  
#2 Posted : 11 December 2002 14:39:00(UTC)
Rank: Guest
Admin

Posted By Maurice Bolland Andrew Under BS7671:2001 Requirements for Electrical Installations the recommended period between inspections is 3 months. The guidance differentiates between 'Routine checks' and 'Inspection and Testing' both of which should be done every 3 months and of course at the initial installation. Hope this helps.
Admin  
#3 Posted : 30 December 2002 14:11:00(UTC)
Rank: Guest
Admin

Posted By Renny Thomson Consideration should also be given to ensure that the installation is suitably "earthed". We have recently come across situatiuons where temporary accomodation is only at a site for 2-3 weeks, powered by an independent generator and not bonded to earth.
Admin  
#4 Posted : 03 January 2003 16:09:00(UTC)
Rank: Guest
Admin

Posted By Ian Laber I can't lay my nands on a copy at the moment, but I believe that HS(G)141 Electrical Safety on Construction Sites also gives the recommendation of 3 monthly testing.
Admin  
#5 Posted : 06 January 2003 08:28:00(UTC)
Rank: Guest
Admin

Posted By Andy Beveridge HS(G) 141: Section 77. Electrical distribution systems on construction sites (excluding those within site offices) should be retested every 3 months or more often as experience dictates. (Snip) Installations in site offices experience more harsh conditions than office installations in a non-construction environment. They should be tested more regularly - a period of no more than 12 months is recommended, as well as each time the office is moved. Hope this helps. Best regards Andy