BS9999:2008 recommends for fire doors with cold smoke control that the threshold gap should be either less than 3mm in height or should be fitted with a threshold seal.
I work in a relatively new office buiding that has internal fire doors (with cold smoke seals), and the gaps under the doors range from 5mm to 10mm. Im aware that BS are not a legal requirement but if the fire service were to make a visit would they insist upon remedial to reduce the gaps.
The fire risk in the office is relatively low, fire detection in place, travel distances are short... Thanks in advance
|
|
|
|
Rank: Super forum user
|
Are you sure that is what it states, I have asked this in the past as I thought the BS required 2 to 4mm on sides and top (so set to 3), and I’m sure I was told 10mm at bottom was ok, to actually allow the air / smoke under ( there is no seal at the bottom) Chris
|
|
|
|
Rank: Super forum user
|
BS 9999:2017 does not seem to specify a gap just reference to the principles of BS 8214:2016 I would task the question back to the designer
|
2 users thanked Roundtuit for this useful post.
|
|
|
Rank: Super forum user
|
BS 9999:2017 does not seem to specify a gap just reference to the principles of BS 8214:2016 I would task the question back to the designer
|
2 users thanked Roundtuit for this useful post.
|
|
|
Rank: Forum user
|
For general fire doors (eg FD30) it's generally accepted that a threshold gap of up to 8mm is acceptable, but I would contact the door manufacturer to to see what their recommended threshold gap is for that particular design of door.
|
|
|
|
Rank: Super forum user
|
Sorry that should have been 8mm, However it seems things have changed and you can get either FD30s or FD30 where it sems the S is if you need cold smoke seal. I was under the impression that the gap under the door allowed fresh air to flow under, feeding the fire and would keep the smoke back, so no seal needed. It seems that this is something that can now be specified as required. In this case yes should be 3mm if required. I don't know what circumstances would or would not make it a requirement.
|
|
|
|