#1 Posted : 30 January 2002 20:34:00(UTC)
Rank: Guest
Admin

Posted By Graham Sargeant I'm sure everyones aware of the requirement to test portable appliances, I work with a tool hire company and we test equipment every hire, the grey area we have is with flash testing as part of the appliance test. I cannot find a reference that states we must flash test every time, so we've adopted a policy of testing earth bond and insulation every hire (along with the usual visual checks) and flash test every 3 months, is this acceptable or are we in breach of any duty/regulations. Thanks for your responses.
Admin  
#2 Posted : 05 February 2002 23:21:00(UTC)
Rank: Guest
Admin

Posted By John Bennett Graham, Firstly I am not expert on flash testing and I am passing some information that was given to me about two-years ago when I attended a PAT course at Robin (yes the PAT test equipment manufacturer). When I asked a question about flash testing and the high voltages that are involved the instructor replied to me that this process must be undertaken with extreme caution. This was for two reasons A)The risk to the employee from the high voltages used and B) he stated that that the flash test wears down the insulation. As stated previously, this information was passed on to me after asking a question about flash testing which is not carried out in our organisation as I feel the IT Dept would have a fit (mind u I might get a computer that actually works, understands the UK dictionary and works without crashing). Regards, John
Admin  
#3 Posted : 06 February 2002 09:36:00(UTC)
Rank: Guest
Admin

Posted By Jim Walker Dielectric strength tests, flash test to you, can indeed over stress circuits. Anything that contains semiconductor devices including IT equipment is unlikely to survive repeated flash testing. I once witnessed someone destroy the control room of a major UK oil refinery with indiscriminate flash tests Generally the test is only done following a repair or if you suspect the machine is unsafe. This is why a competent person (ie not a PAT tester button presser) is required to carry out inspection and testing. Personally I think too much emphasis is placed on electrical results and not enough on what a suitably competent person would see and deduce. Note also that done incorrectly the flash test can be hazardous to the test operative. This is particularly so with Class 2 double insulated equipment. I work in an electrical manufacturing environment where all equipment needs flash testing and our controls are very strict because of this. You say you are a hire shop as a rule of the thumb I would flash test anything with an electric motor every three months possibly more if the machine has had some stick. If you contact Megger or Seward they will send you some very helpful booklets. See also HSG107 (essential reading) and INDG236 both from HSE books
Admin  
#4 Posted : 06 February 2002 21:39:00(UTC)
Rank: Guest
Admin

Posted By Graham Sargeant Thanks for your responses to my query, Graham
Admin  
#5 Posted : 15 February 2002 00:18:00(UTC)
Rank: Guest
Admin

Posted By Nigel Singleton BSc The 'Code of Practice for In-service Inspection and Testing of Electrical Equipment' produced by the Institution of Electrical Engineers states in section 10.4 (in bold text) Dielectric strength testing is not normally carried out during in-service testing. On the PAT course that I attended, the instructor informed us that 'flash testing' was no longer 'in vogue' and should only be conducted in extreme circumstances, as it invariably damages or weakens the appliance being tested. In many cases it leads to complete destruction. The electricity at work Regs, do not require PAT testing to be conducted at all, they state that electrical equipment must be maintained in an efficient manner. PAT testing is only one means of checking the efficient manner.
Admin  
#6 Posted : 19 February 2002 14:23:00(UTC)
Rank: Guest
Admin

Posted By Kevin Minton Graham There's a lot that can be written about this subject, but I have tried to summarize my views on the main points. The duty on hire companies is under s6 HSWA - which is to carry out examinations and tests to ensure that the equipment is safe SFAIRP. Proper inspection would catch 19 out of 20 problems - and must not be over looked or diminished in favour of a test. However, the duty is SFAIRP - and flash tests are RP on most "tools" normally available from a tool hire company. The duty is analogous to that of manufacturers; trade association recommended tests are therefore based on routine tests under EN50144 - including a "flash test" at 2500v. Equivalent tests exist for equipment outside EN50144. The test is carried out between each hire (= SFAIRP). Provided it is done in accordance with the test device instructions, no significant damage or deterioration occurs. Hundreds of hire companies have been applying this regime to their tools without problems since 1974. There are similar duties under consumer protection law. Trading Standards Officers will use EN routine tests to determine compliance with the Consumer Protection Act, etc. There are items of equipment for which regular application of a flash test is not reasonably practical, or not useful. IT equipment may come into this class. A regime to fulfil s6 duties which does not apply inspections and tests between every hire should be supported by proper records and justification that the interval between "full" tests is appropriate and does not allow deterioration to an unsafe condition. The IEE COP does not encompass equipment supplied by hire (see 1. Scope). INDG236 does not encompass s6 duties, HSG107 refers to this issue; particularly paragraphs 1, 39 and 41. Safety test machines for this application have the test current limited normally to 5mA to control and minimize risk to test operators. In addition to Robin, Megger and Seaward, Clare Instruments can give good advice on hire industry applications. I hope this is useful. Perhaps not surprisingly, the principal trade association for the hire industry has very similar views. Regards Kevin
Admin  
#7 Posted : 24 February 2002 16:11:00(UTC)
Rank: Guest
Admin

Posted By Colin Brayshaw.LicCIPD Hi Graham Sorry about the delay in responing! Information on Flash Testing The flash test, also referred to as “HI PoT”, “Dielectric Strength” or “Insulation Breakdown” test is intended to verify that creepage distances, clearance distances and insulation levels around live parts, are sufficient to prevent excessive leakage currents causing hazards to the user. As another “core” electrical safety test, this is also a requirement of many National, European and international standards. In application, live parts refer to both the line (Phase) and Neutral supply paths. For test purposes these are joined together to form one test point, with the other test point being the Earth (Protective Conductor) for class 1 products, or the outer surface of class 2 products. Any function switches on the product should be switched on to include all parts of the supply path. Typical “Type Test” requirements are for a test voltage of between 1,000Volts and 1,500 volts, for class 1 products and (2,500 to 4,200Volts) for class 2 products, to be applied for 1-minute period and for the product to withstand a leakage current level of up to 100mA. For Production line testing, where high throughput is a major consideration, the test period can be reduced to a few seconds by increasing voltage levels by 10%, and at the same time lowering the acceptable leakage current to less than 5mA. This has the added benefit that it makes the test safer for the operator. Most flash tests requirements stipulate that the test voltage should be from an a.c. source, with a substantially sinusoidal waveform. With the increase in sensitive components within many of today’s products, alterative methods are sometimes called for: These can range from the application of d.c. Voltages (Usually 1.4 times the stated a.c. voltage) to the soft-start. Advantages offered by more sophisticated testers that use programmable ramp profiles for raising and lowering the test voltage. This minimises the rapid rates of potential change that are the main cause of sensitive component failures, not the actual high voltage. It is important to remember that flash testing can be hazardous if improperly applied. And common sense precautions should be taken, such as the use of safety enclosures, well defined test areas and adequate operator training. To test or not? The view that flash testing is a destructive test is often raised in discussion. This largely originates from its use in Type testing laboratories where high voltages are sometimes applied for long durations, with the intention of testing products to destruction. However, in terms of production and routine in-service testing applications, there is little or no evidence to suggest that the short period flash test degrades a product, even after repeated testing. There are many reasons for flash failures, most of which lead back to such things as manufacturing errors, inappropriate materials and designs that fall short of the exacting standards required in today’s safety conscious environment. The flash test doesn’t cause the problems; it merely provides the means to find them. So within the Hire industry you would be wise to Flash test all apropriate appliances. Colin
Admin  
#8 Posted : 24 February 2002 22:28:00(UTC)
Rank: Guest
Admin

Posted By David J Bristow Hi Graham Jim is right in that the term to use is dielectric testing however; he refers to this not being a job for a “PAT Testing button presser”, I would agree in the sense of, I think not all PAT testers with the City & Guilds qualification are competent to do so – let me explain! I undertook my PAT testing course at a college in HULL, the course delivered over 6 hours including all paperwork and breaks (instead of the 9 hours required by C&G) did not give me the confidence to go out and PAT test to feel both confident and competent. As those that have undertaken the course will verify the test/exam is an "open book" (the first I have ever undertaken) and what I found alarming is that qualified and competent electricians cannot attempt PAT testing until they have taken the exam and passed – whilst people like myself who are able to take in the delivery of the course, go away and read the book with no prior knowledge of electrics can then sit and pass the exam. I think this is one course the City & Guilds has got totally wrong and needs an urgent review so that a “PAT testing qualification” means more than the piece of paper it is written on. Lastly I take nothing away from those "non electrical" colleagues who have taken, passed and are competent at “PAT Testing”. Regards David B