Welcome Guest! The IOSH forums are a free resource to both members and non-members. Login or register to use them

Postings made by forum users are personal opinions. IOSH is not responsible for the content or accuracy of any of the information contained in forum postings. Please carefully consider any advice you receive.

Notification

Icon
Error

Options
Go to last post Go to first unread
Admin  
#1 Posted : 03 December 2003 14:54:00(UTC)
Rank: Guest
Admin

Posted By Sarah Bessey Our maintenance guys carry out Arc/MIG welding operations (stainless/mild steel only) about once evey two months, for a duration of about 10 mins max. Their workshop is reasonably well ventilated although it has no windows which open to the outside and is probably about 19ft square. Do you think that portable extraction is a necessity or a nice to have considering the infrequent operation and short duration?
Admin  
#2 Posted : 03 December 2003 16:35:00(UTC)
Rank: Guest
Admin

Posted By Robin V Boughton You should undertake an assessment under the COSHH Regulations and assess the risks to health in a systematic manner. Welding fumes are hazardous to health and can cause drowsiness etc if personel are not properly protected.A seat of the pants approach is not wise. Some form of RPE may be appropriate rather than portable extraction equipment.
Admin  
#3 Posted : 03 December 2003 16:55:00(UTC)
Rank: Guest
Admin

Posted By Jane Blunt With MIG welding it is probable that levels of nuisance particulate and carbon monoxide exceed the occupational exposure limits. When welding stainless steel, it is probable that the chromium and nickel fume levels exceed the exposure limits. To help you, you should consult the manufacturer's MSDS for the welding consumable - they usually give typical fume analyses. Jane
Admin  
#4 Posted : 03 December 2003 19:41:00(UTC)
Rank: Guest
Admin

Posted By John Murgatroyd The guys should wear Rpe, since they are welding stainless as well. The rpe should be of the type that supplies clean filtered air to the headshield. If the type with a separate air pump is used then the filter fitted should be capable of filtering particulates of respirable size. I say stainless especially, because of the risk from hexavalent chromium. As for extraction, if welding in a small room with no forced extraction and welding operations being carried out, then there is also a visibility risk as well as the fume risk. Depending on the shield gas being used the risk from carbon dioxide/monoxide may not be great, but there is also the risk of asphyxiation since the shield gas will be composed of from 80% to 95% argon. When mig welding stainless the shield gas will be 100% high purity argon. There are also the risks from surface contamination of whatever is being welded. If contaminated with various hydrocarbons then there will also be a fire and/or explosion risk. I would say: RPE, minimum air fed. With extraction as well or better ventilation. A typical analysis of weld fume recently carried out, using the mig/mag process on mild steel with good ventilation and no extraction, with measuring equipment at the welders face was: Iron oxide 8.13 mg/cuM Manganese 1.39 mg/cuM Chromium3 0.139 mg/cuM Copper 0.107 mg/cuM The tests were of 2 hour duration and the results extrapolated for an 8 hour work period. the results exceeded the specified OEL for total welding fume and exceeded the limit for iron oxide in the welding fume calculation. These results can be considered typical !! You should also consider that the iron oxide level was also exceeded by another operative 30 feet away and NOT welding.
Admin  
#5 Posted : 03 December 2003 20:19:00(UTC)
Rank: Guest
Admin

Admin  
#6 Posted : 04 December 2003 08:02:00(UTC)
Rank: Guest
Admin

Posted By Jane Blunt In MIG welding most of the chromium is released in the trivalent state, which is less hazardous. In manual metal arc welding most of the chromium is in the hexavalent state. Don't forget that extraction is higher up the hierarchy of controls than RPE. You can also vary the fume emission rate by changing the mode of transfer in MIG. The highest rates occur with spray transfer, and dip transfer the lowest. A full gas bottle contains approximately 10 cubic metres of gas (in round figures) so you can estimate what effect this would have on the total quantity of oxygen in your room. Calculate the volume of your room, subtract 10 cubic metres, and calculate 21% of the result - this, in a very simple model is how much oxygen you have. Take this figure and divide by the volume of the room. If the result is less than 18% you could have a problem if the contents of the whole bottle was released. If it isn't, your risk of asphyxiation is not significant. You give your room dimension as 19 foot square. Thus, if your room is 70 cubic metres, the above calculation reveals that you could have 18% oxygen left if the WHOLE gas bottle emptied itself into the room and there was no replacement of air in that time. Note that the portable extraction units only filter the air - which is ideal for particulate fume. They won't help with the argon, but the calculation above suggests that it is not likely to be a problem in any event. Jane
Admin  
#7 Posted : 04 December 2003 20:03:00(UTC)
Rank: Guest
Admin

Posted By John Murgatroyd Assuming that 100% argon is used. Calc for 80% Ar and 20% CO2. Take into account the human consumption of oxygen and the amount of CO2 released welding and human CO2 from respiration. Factor into account the effect of higher CO2 on the metabolism. Note the heat output and the fume output from the consumables and from any surface contamination. Bear in mind that many employers will not bother with any of this. Many will not have a risk assessment for any welding problems likely to occur. I work as a welder fabricator. 19x19x8 rooms just DON'T get welded in by me without precautions being taken BUT my employer won't like the time and bother taken for any of it.
Admin  
#8 Posted : 04 December 2003 20:42:00(UTC)
Rank: Guest
Admin

Posted By John Murgatroyd And the fume from mma welding stainless steel (used more often than mig, because the shield gas for mig is more expensive and many workplaces don't stock either high purity argon or the 1.5% Ar/O2 or stainshield gases) contains up to 8% chromium and significant amounts as hex chromium. Please read this webpage.... Until you've tried welding in confined spaces you won't know the effects. The fume in such an area will be considerable, especially welding mma stainless steel. Note that many consumables use higher levels of chromium/nickel than the workpieces being welded. Note also the ozone presence. http://www.twi.co.uk/j32...otected/band_3/jk31.html
Users browsing this topic
Guest (2)
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.