Perhaps a bit technical, but I've been trying to solve a psychrometrics problem for quite a while now.
It concerns a dryer in which a substance is dryed by air. The substance is added and removed continuously. The air is cooled between states 2-3 and heated between 1-3. The drying chamber is between 1-2, and is considered adiabatic.
State 1: T1 (dry bulb) = 65C
State 2: relative humidity = 85%
State 3: T3 (dry bulb) = 2C, relative humidity = 100%
Pressure is constant at 1 bar, airflow is 10kg/s and circulates in a closed process.
I'm trying to sketch the process in a Mollier-diagram; Any tips/ideas on how to determine the temperature at state 2?
Thanks!
Kan
|
|
|
|
Rank: Guest
|
Posted By Keith32
Assuming this is not one of the usual wind up questions...
But you state the process/air is cooled between states 2 -3 and then heated between 1 - 3.
Therefore doesn't 1 - 3 cover stages 2 -3?
That's how I read the question, therefore overall the process is being heated....
|
|
|
|
Rank: Guest
|
Posted By Kan
Thanks for the reply.
The problem is to determine state 2 in a psychrometrics chart.. I think a solution is to consider the enthalpy to be constant from 1-2. The process line follows the lines of constant enthalpy until it reaches the .85 saturation.
Hope this is a good enough approx.
Kan
|
|
|
|
Rank: Guest
|
Posted By Keith32
I never did Mollier diagrams/air conditioning design calculation in my engineering studies.
I did expansion/compression of gasses in compressors/combustion chambers and expansion across turbines - as used in jet engines - tends not too be too much moisture inside such engines.
Do you not need to consider Boyle's Gas Equations P1 V1/T1 = P2 V2/T2 or whatever it is.
What about the other thermodynamic laws/formula which slip my memory now that the grey matter is fading away.
|
|
|
|
Rank: Guest
|
Posted By Psycho
Kam
Try this
CDB RH CWB CDP W H ALT POINT
[degC] [%] [degC] [degC] [kg_WV/kg_DA] [kJ/kg_DA] [m]
2.0 100.0 2.00 2.000 0.00438 12.989 0 3
65.0 2.8 25.50 2.000 0.00438 76.870 0 1
27.5 85.0 25.50 24.796 0.01992 78.528 0 2
DESCRIPTION OF PROCESSES IN THE CYCLE
3-1 SENSIBLE HEATING OF COLD AIR OFF OF COOLING APPARATUS AT POINT 3. CONSTANT HUMIDITY RATIO
1-2 COUNTERFLOW OF AIR AND PRODUCT IN PRODUCT DRYING TUNNEL. THIS IS AN EVAPORATIVE COOLING PROCESS AT CONSTANT WET-BULB TEMPERATURE
2-3 COOLING AND DEHUMIDIFYING AIR AS IT PASSES ACROSS A COOLING COIL
STEPS IN SOLVING THE PROBLEM
DESCRIBE THE PROBLEM COMPLETELY AND IN ITS ENTIRETY
• START FROM KNOWN POINT 3 AND HEAT AT CONSTANT HUMIDITY RATIO TO KNOWN 65°C. THIS STATE POINT IS NOW KNOWN FROM CDB, W AND PBAR
• FOR THE ADIABATIC EVAPORATIVE COOLING PROCESS PROCEED FROM POINT 1 UP THE 25.50°CWB LINE TO 85% RH. THIS STATEPOINT IS NOW KNOWN FROM CWB, RH AND PBAR
• THE AIR IS NOW COOLED AND DEHUMIDIFIED FROM POINT 2 TO POINT 1 AND CYCLE IS COMPLETE
CHECK YOUR WORK. DOES IT MAKE SENSE? ARE THE ANSWERS REASONABLE?
(from author of ASHRAE's Understanding Psychrometrics.
|
|
|
|
Rank: Guest
|
Posted By Psycho
Kam
The table did not paste well
It is a 5 row 8 column table. The last 3 rows are for state points 3, 1, and 2 in that order
|
|
|
|
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.