Posted By JJF Good Afternoon. Can anyone advise on the frequency of water system sterilisation or where guidance can be sought on this? The water is from the mains supply - stored in holding tanks and supplies toilets and taps in an office environment (but is not drinking water).
Admin  
#2 Posted : 13 September 2005 16:32:00(UTC)
Rank: Guest
Admin

Posted By Peter Taylor14 The HSE guidance booklet THE CONTROL OF LEGIONELLA BACTERIA IN WATER SYSTEMS gives all the info you need
Admin  
#3 Posted : 14 September 2005 10:23:00(UTC)
Rank: Guest
Admin

Posted By JJF Thank you Peter
Admin  
#4 Posted : 14 September 2005 12:09:00(UTC)
Rank: Guest
Admin

Posted By Jeff Watt JJF Chartered Institute of building services engineers (CIBSE) have a good Technical Memoranda on legionella and how to check your water sysyem. I think it is titled "legionairres disease" and was published in 2002. I have an old photocopy, sorry about the sketchy info. The guide goes into greater detail than this but basically says that your cold tap should be below 20 degrees celcius after letting it run for 2minutes. This should keep legionella at a low risk of multiplication. Your warm tank should be able to maintain a temperature of at least 55degrees celcius at all your warm taps. Storage tanks should be clean have a lid to prevent vermin/debris entering the water and in some cases insulated to prevent heat transfer. I would read this first before getting into an expensive disinfection routine which would have it's own risks re COSHH. All the best Jeff
Admin  
#5 Posted : 15 September 2005 14:32:00(UTC)
Rank: Guest
Admin

Posted By Jeff Watt Technical error in my last post re hot water temps. Your calorifier should be at 55 degrees celcius and able to maintain at least 46 degrees celcius at the taps. CIBSE TM13 Minimising the risk of legionairre's disease.
Admin  
#6 Posted : 15 September 2005 15:26:00(UTC)
Rank: Guest
Admin

Posted By JJF Thanks for that Jeff.