Rank: Guest
|
Posted By Diane Thomason
Can anyone give an approximate figure for an oxygen concentration that would constitute a dangerous level of oxygen enrichment?
I know there isn't an exact figure, but would like to know of any references, examples, industry precedents or norms, or the experience of "confined space" safety experts.
The purpose is to advise users of oxygen cylinders when they should (after risk assessment and putting control measures into place etc) consider installing oxygen monitors - i.e. something like "if the O2 in the room could exceed X if all the O2 in your cylinder leaks out suddenly, then O2 monitoring is needed".
Would be grateful for the advice of anyone who has relevant experience.
|
|
|
|
Rank: Guest
|
Posted By Philip McAleenan
Diane,
23.5%. Gas detectors calibrated for oxygen will alarm at this level,
Philip
|
|
|
|
Rank: Guest
|
Posted By Diane Thomason
Sorry all, ignore me. Have found some material on the BCGA website where I should have looked to start with!
EIGA suggests 23% as dangerously enriched so that's good enough for me.
Cheers, Diane
|
|
|
|
Rank: Guest
|
Posted By Diane Thomason
Thanks Philip, and just out of interest what would you normally set oxygen depletion alarms at? 19%, 18% or "other"? (have heard a lot of arguments sbout this.)
D
|
|
|
|
Rank: Guest
|
Posted By Philip McAleenan
Diane,
the following notes may be useful:
Oxygen deficiency relates to atmospheres where the air content has an oxygen concentration below 19.5%.
§ Levels of oxygen between 14% and 17% will cause impaired judgement, breathing difficulty and fatigue.
§ Oxygen concentrations below 14% will cause loss of consciousness and if endured even for a short period could cause brain damage or death.
§ At concentrations at 8% and lower immediate death is inevitable.
Note: It is an accepted industry norm that any atmosphere with less than 19.5% oxygen should NOT be entered without an approved self-contained breathing apparatus (SCBA).
Philip
|
|
|
|
Rank: Guest
|
Posted By Diane Thomason
Philip
Aha!
It's the 18-19% range I'm interested in. I have heard lots of discussion on this, with much opinion being that 19% does not warrant evacuation.
Can you tell me where the 19.5% industry norm comes from? Is there a reference to a document somewhere?
|
|
|
|
Rank: Guest
|
Posted By John Webster
If my memory serves me right, all the portable multi gas detectors (methane/H2S/O2) that I used in the oil & gas sector were calibrated to alarm at 23%Hi and 19%Lo Oxygen.
John
|
|
|
|
Rank: Guest
|
Posted By Philip McAleenan
Diane,
If the oxygen content drops from 21% to 19.5% it indicates that it is being replaced by something not conducive to breathing, and that it is likely to continue to drop. AT 19.5% it is breathable and people in that environment are stiull capable of unimpaired judgement. However to wait any longer before evacuation may put them into a situation whereby their judgement is so unoimpaired that they are not capable of makinga decision to evacuate at all.
In addition, with the drop in oxygen content, the unknown factors are
1) the source of the contamination is unlikely to be known, and it may be possible that the oxygen content between the worker and the exit may be much less that 19.5%.
2) the rate of decrease in oxygen content is unknown and may continue rapidly, causing the workers to be overcome if they delay.
The alarm sounds at 19.5% giving the workers a small window of opportunity to don their SCBA and evacuate. This must be done immediately. If the margin was any less, they would have no time to evacuate.
A statistic to note is that on average if anything goes wrong in a confined spaces there is a 1 in 10 likelihood that it will result in a fatality, and when that happens there is a 50:50 chance of multiple fatalities.
Philip
|
|
|
|
Rank: Guest
|
Posted By Diane Thomason
Thanks John and Philip
Diane
|
|
|
|
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.