Posted By TomP Just want to check my sanity before I approach the already stressed MD. Bottles of hydrogen gas fixed to the wall outside, in a cage, piped in to labs through copper piping for use in lab equipment. It all looks well managed but should this fall under DSEA regs? If the specification in L138 is correct then it does if all the safety checks and controls were to fail. 'Zone 2: A place in which an explosive atmosphere consisting of a mixture with air of dangerous substances in the form of gas, vapour or mist is not likely to occur in normal operation but, if it does occur, will persist for a short period only.' Comments?
Admin  
#2 Posted : 19 April 2006 12:12:00(UTC)
Rank: Guest
Admin

Posted By TomP May have just answered my own question: 'where it can be ensured that the gas or dust is present in a concentration below the lower flammable limit, the atmosphere is not explosive, and regulations 7, 11 and 17 do notapply.' So how to ensure this doesn't happen is now the trick.
Admin  
#3 Posted : 19 April 2006 12:43:00(UTC)
Rank: Guest
Admin

Posted By Frank Hallett Spot on Tom. Ventilation, process controls and and restricted access are going to be key issues for you. Frank Hallett
Admin  
#4 Posted : 19 April 2006 13:38:00(UTC)
Rank: Guest
Admin

Posted By Ian Waldram For such an application you should have, outside the lab: regulator plus relief valve sized for the regulator-failure case (regulators have small RV's, but designed to protect the pressure gauge, not any downstream equipment). That ensures any releases inside the lab will be small-scale. Inside the lab you should have no pipework joints up to the point of use, or else tested HP joints even though it's LP piping. Good practice would be to have the lab equipment inside a fume cupboard, with ventilation alarm and regular ventilation flow measurement. You can check that a worst-case leak won't exceed LEL at the design ventilation rate. If you do have any joints or potential leak points inside the lab, then there will be Zone 2's around these.
Admin  
#5 Posted : 19 April 2006 13:45:00(UTC)
Rank: Guest
Admin

Posted By Descarte Pressure regs could apply as well to your valves, safety devices, manifolds and pipelins where applicable