Construction work beneath overhead power lines
Rank: Guest
|
Posted By Malcolm Hogarth I am looking for advice please on the safe distances for carrying out construction work beneath overhead power lines. I have already got some information including such things as disconnecting the power, consulting with the line owner etc but am looking for specific distances.It is not possible to move either the proposed construction or the power lines.
Figures that I have found so far include:
No closer than 15m from overhead lines suspended from steel towers or 9m from overhead lines supported on wooden poles.
And:
•275 or 400 kV Minimum clearance 7m •132 kV Minimum clearance 6.7m •33kV,11kV and low voltage 5.2m
Can anybody add anything to this? Many thanks,
Malcolm.
|
|
|
|
Rank: Guest
|
Posted By Delwynne Usually the electric company responsible for the line will tell you how far away you need to be from the particular line in question so in a 'specific' stiuation I would refer back to them. If you're looking for 'general guidance' the HSE has quite a good section on all aspects of electrical safety at work including overhead lines. http://www.hse.gov.uk/electricity/index.htm
|
|
|
|
Rank: Guest
|
Posted By Safetynut i have emailed you direct some info which may be of some use to you
|
|
|
|
Rank: Guest
|
Posted By Davelfc Malcolm,
Consult GS6 this gives general guidance.
As earlier the power company will come out and meet on site, you need to have information on what machines you will use make model and dimensions etc.
they will advise on height of goal posts etc.
Regards Dave
|
|
|
|
Rank: Guest
|
Posted By Malcolm Hogarth Many thanks for all the replies. I did get on to both the National Grid and EDF Energy for advice on this. Would you believe that they would not give advice on the telephone but wanted between 20 days and 6 weeks notice!I did try to explain that I wanted general advice on the guidance for safe distances but they were still not forthcoming.
Malcolm
|
|
|
|
Rank: Guest
|
Posted By Paul Bellis The vertical figures I work to are:-
Up to 11kV 8'6" 2.6 m
>33kV-66kV 9'10" 3.0m
>66kV-132kV 12'2" 3.7m
275 kV 15'0" 4.6m
400 kV 18'0" 5.5m The clearances quoted in the table are taken from Engineering Recommendation D,1975 (Electricity Council) for voltages up to and including 132kV and other guidance,
Paul
|
|
|
|
IOSH forums home
»
Our public forums
»
OSH discussion forum
»
Construction work beneath overhead power lines
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.