Posted By BeSafe Hi, Bit of a basic question, but can anyone advise the testing frequency for self contained emergency lighting units and where this is documented? I thought it was monthly check of lamps and units functioning and quarterly check leaving them on battery for an hour, but may be wrong! Thanks in advance.
Admin  
#2 Posted : 02 October 2006 12:16:00(UTC)
Rank: Guest
Admin

Posted By Steven The guidance for emergency lighting related to the RR(FS)O states: Typically, testing would include: • a daily visual check of any central controls; • a monthly function test by operating the test facility for a period sufficient to ensure that each emergency lamp illuminates; and • an annual full discharge test. Hope this helps Steve