Rank: Guest
|
Posted By Stephen A
I have noted an increase in Evacuations of residential areas of late due to the Fire Brigade recommendations when a Fire takes place within the vicinity of Acetylene cylinders.
I understand the reasons why this is done, but I do not fully understand how Enforcing Authorities Manage and 'Police' such companies who use these cylinders.
In a fire situation the cylinders are treated like an unexploded bomb, thus 100's possibly 1000's of people are evacuated for periods of up to 48 hours.
I suggest people look to local Papers just to see how often such incidences occur.
It would be interesting to see how large this issue is in the UK.
Like everything, there is a financial cost to such instances, but what of the psychological damage to residents who live adjacent to where such cylinder are used.
Do members have a view if alternative methods of welding take place and it be mandated in Law so as to take Acetylene out of use?
|
|
|
|
|
|
Rank: Guest
|
|
|
|
|
|
|
Rank: Guest
|
Posted By David Bannister
Ian, just been thinking after looking at your link (always a dangerous occupation) - if there is such a large volume of experience and published data on the risks of explosion, what potential liability is there on a company who stores these cylinders?
As I understand it, fire is assumed to be an accidental occurrence (unless proved otherwise) and any spread also accidental. Consequently there is no automatic liability for fire spread. However, if we know that acetylene is particularly hazardous and can require a 200 metre, 24 hour post-fire evacuation zone, does this change the legal framework? Can a garage owner be sued for compensation for the effects of an enforced evacuation?
Any knowledgeable legals or insurance specialists out there with an opinion?
|
|
|
|
|
|
Rank: Guest
|
Posted By Merv Newman
Any compressed flammable/oxygenating gas in a "fire" situation is extremely dangerous. First to the firemen and next to local residents. I think most people will accept that an oxygen, acetylene or hydrogen cylinder can go off in random directions and land anywhere. And I have no idea on what radius they can cover.
Best practice is to have all such weapons stored outside of the building at night. Somewhere securely locked but accessible to the fire brigade so that they can get them away from the fire.
The usual solid masonry wall between oxygen and flammables. But I have had to accept over the years that for welding trolleys, while they may be stored outside over night, the welders will not separate the bottles.
Risk assessment ? Low.
Merv
|
|
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever
What's even worse is that some schools have acetylene cylinders but they are not recognising this in their fra's. Either they are not carrying out their fra's or not realising that the whole community may be affected/evacuated.
|
|
|
|
|
|
Rank: Guest
|
Posted By John Murgatroyd
Explain why a dissolved acetylene cylinder is a higher risk than, for instance, a 30kg propane tank ?
Or a 230 BAR hydrogen cyclinder ?
Is it more likely to explode ?
No.
The risk of explosion is low.
Even if heated in a fire, the risk is still low. The things have a LEAD plug in the bottom, they are low-pressure cyclinders, 15 BAR(ish) (depending on temperature)
The Oxygen cylinder, however, is a high risk in a fire...
Apart from acetylene instability at pressures higher than 25 PSI, what else ?
Over the 100 years of acetylene use it has propved itself a safe way to store a fuel gas....and it is hotter than propane, which is why it is still used for flame cutting...
http://www.aga.com/web/w...ages/History_Acetylene_1
I sometimes worry about the endless waste of time spent trying to invent the wheel again.
I've used oxy/acetylene for flame cutting for 40 years, never had a problem, not ONE.
Compare it with the storage of petrol and other flammable liquids.....like anything else, let an idiot loose near it and you've got trouble. The problem is with the idiot.
|
|
|
|
|
|
Rank: Guest
|
|
|
|
|
|
|
Rank: Guest
|
Posted By Phil Grace
I work for an insurer (so know soemthing of insurance but am I an insurance expert?) not am I an expert on acetylene.
But I recently attended London Brigade launch of their campaign on acetylene. Too much to reproduce in full but would comment:
Acetylene cylinders do NOT have a fusible (lead) plug
Fire Brigades are uncomfortable having to set up exclusion zones but are worried about consequences of not doing so (being sued?). They're also under pressure from councils/politicians etc about effects of this disruption.
Research by HSL reveals that the acetylene cylinders become dangerously unstable when subjected to heat. Decomposition of the acetylene takes place with generation of considerable heat and over pressure. Whilst decomp can be slowed by cooling any release of pressure e.g. by cracking the valve (traditional practice) can cause it to resume with "explosive" consequences.
As for liability for spread of fire: Any claim for consequences of fire must firstly pass test of negligence - in essence - was there negligence? did fire start because of negligence of site "owner/operator"? If not no liability.
Then there is the issue of whether someone who was simply evacuated from their premises due to Fire Brigade exclusion zone suffered any physical loss. Most Public Liability policies exclude what we in the insurance world call "economic/financial loss". If the neighbours property was damaged by spreading fire then there is a valid basis for a claim. If they were just evacuated on Fire Brigade orders - tough luck. They could claim but there would be no insurance, no deep pocket, so they could end up driving their neighbour into bankruptcy and getting next to nothing.
|
|
|
|
|
|
Rank: Guest
|
Posted By Dean Harris
This is what im taught:With dealing with acetylene cylinders the fire service require and demand a 200 metre cordned off area, no one is allowed into these areas unless wearing a full BA set,for example on some occasions a snatch rescue may be required the cylinders are classed as ticking bombs from a fire service point of view, in most circumstance these cylinders will have water jets poured on them to cool them down,monitored with a thermal imaging camera, the fire service will also try and protect any buildings, with other jets that are close to the cylinders,environmental services will be called in on depending how many cylinders in use and damage
|
|
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever
John Murgatroyd
the risk of an acetylene cylinder explosion are far greater than propane or hydrogen. The chemical bonds between the carbon and hydrogen atoms in acetylene are single bonds whereas in propane they are triple bonds. This makes the acetylene gase far more unstable. Mechanical shock or heat can cause decomposition within the gas cylinder with associated increase in the internl pressure which make s the cylinder more likely to rupture. As the flammability range of acetylene in air lies between 2.5% and 80% (very broad) it means that on contact with air their is likely to be an almost instantneous explosion. The flammability range for propane lies in the region of 6% - 15% (or is that methane?), the band is much, much lower. The ignition energy required for acetylene is far less than for propane or other flammable gases.
Take my word for it acetylene is an extremely dangerous gas by comparison to other gases.
|
|
|
|
|
|
Rank: Guest
|
Posted By Jane Blunt
Shaun, you have some errors in the chemical explanation.
All the bonds in propane (both between carbon atoms and between carbon and hydrogen atoms) are single bonds.
In acetylene you have single bonds between carbon and hydrogen atoms and a triple bond between the two carbon atoms.
Jane
|
|
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever
Thanks Jane, I knew my chemistry was a little rusty but I still think I am correct that the bonding between the atoms is the principle reason why acetylene is so unstable.
|
|
|
|
|
|
Rank: Guest
|
Posted By Robert.
Shaun,
I think John M is correct.
The muzzle velocity of an SA80 is exactly the same whether used by a trained individual (who knows and is aware of the "risks",) or an idiot!
|
|
|
|
|
|
Rank: Guest
|
Posted By Jane Blunt
Yes, the bonding is the reason for the reactivity. However, chemical bonding is responsible for most things in life, the universe and almost everything! ;o)
My two-penn'orth on this topic is that the key difference between acetylene and other compressed/stored gases/LPG or whatever is that the risk from acetylene persists for a period after the fire because the material may still be reacting inside its cylinder. Other cylinders will either fail during the fire or, once the fire is extinguished, the risk subsides.
The key danger inside the 200 metres cordon is projectiles from failed cylinders, unless you can be shielded by a substantial piece of masonry.
|
|
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever
John M is right as far as the idiot thing goes but he questions why acetylene is any worse than other gases. Hopefully I have given him an answer albeit I got my chemistry mixed up.
I don't know why an oxygen cylinder would be any worse than the others. Oxygen supports combustion and will promote rapid fire spread but does not in itself burn. It does not explode.
|
|
|
|
|
|
Rank: Guest
|
Posted By Jane Blunt
We have strayed off topic. Acetylene cannot be replaced by another fuel gas for most of the welding applications for which it is used. It has unique properties.
There may be some applications for which it could be substituted, but we have to guard against getting into a situation where we need to have two fuel gases in the workshop because we have decided that for some applications we can use another gas.
Jane
|
|
|
|
|
|
Rank: Guest
|
Posted By John Murgatroyd
I am very well aware of the inherent instability of actylene, which is why the output pressure of the gas should not exceed 15psi. that is also why the gas is dissolved in a porous material. With the gas stored in the proper cylinder, under the proper conditions, with the right equipment and used by trained operators, it is no more dangerous than many other fuel gases.
Let any untrained idiot near anything with the potential to be dangerous and you've got problems, not matter what you're using.
Trained users.
Correct equipment.
Bottle stored and used upright.
Transported using a proper bottle trolley with restraint.
Trained users will know that equipment cannot be substituted. IE: if the pipes become damaged you don't "fix" them, you replace them.
They also know that no copper fittings are used on acetylene.
Nothing more than good H&S management.
And please don't assume that I'm an idiot, I really don't like being preached to about things I learnt in school over 40 years ago. I have used acetylene for longer than many of you have been alive. I must be good at it, I've never had any problems yet.
****trained users****
Surely the basis of any H&S routine !
|
|
|
|
|
|
Rank: Guest
|
Posted By Pete48
John, but what if the untrained idiot is not yours but starts the fire that causes the issue with your cylinders?
You clearly have a lifetime of experience of working with industrial gases so, in the original context of this thread, I would be interested to hear your view of the appropriate level of emergency response if your "safe" cylinders were involved in an emergency caused by someone else's idiot?
|
|
|
|
|
|
Rank: Guest
|
Posted By Stephen A
Out of interest, try Google news and type Acetylene cylinders- and see how often this is happening.
Clearly we have an issue that must be looked at with closer scrutiny
|
|
|
|
|
|
Rank: Guest
|
Posted By Aidan Toner
As we speak, the main dual carriage way between Belfast and Dublin is closed (with no small impact on traffic flow)and will not be opened until midday tomorrow (Thursday)- All due to fire in roadside metal workshop and hence related acetylene concerns.
Local cinema closed 6 weeks ago due to fire in 'nearby'?? foundry and once again acetylene concerns.
Certainly appears that acetylene has been given a raised profile in terms of 'extended' safety cordon.
|
|
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever
John I don't understand why you think anyone has suggested you are an idiot and I don't see why you think anyone anyone is preaching to you. I suspect your comments are directed at me. All I have done is try to offer an answer to a question you posed.
|
|
|
|
|
|
Rank: Guest
|
Posted By Tabs
We are looking at alternatives here in the City based on the fact that the Brigade has a clear and non-changeable policy of 200m cordon evacuation, from 24 to 48 hours.
Incidents involving acetylene is running at more than one per month.
Regardless of the chemistry, the advantages or disadvantages, being denied access to our buildings because of a cordon is very expensive. This is the primary incentive to change.
|
|
|
|
|
|
Rank: Guest
|
Posted By Jeffrey Watt
On the subject of silly use of Acetylene...
In Peter Gurney's book "Braver men walk away" a biography of a bomb disposal expert, he tells of a garage owner in Palestine who was getting so enraged with people stealing his cylinders he started to weld a brass name plate to the trolly...but never finished the job, the job finished him.
Kind regards
Jeff
|
|
|
|
|
|
Rank: Guest
|
Posted By Geoff Parkinson
The fundamental difference between acetylene and other gases is this:
When heated, the contens of the cyliner expands - very dangerous. However, when cooled the gases (with the EXCEPTION of acetylene) contract and the risk goes away. Acetylene has the unpleasant capability to thermally decompose after heat has been removed. This 'self-sustaining' decomposition will continue to pressurise the vessel until it is either subjected to cooling or, in the worst scenario, ruptures the container.
My first Watch Officer (old firefighter!) told me that if a propane cylinder hasn't ruptured by the time you start cooling it, it won't. As the temperature is reduced, so is the internal pressure. Something to do with the Gas Laws.
I attended many 'cylinders involved' incidents over the years and always found his rule of thumb to be correct.
To prevent the thermal decomposition, the brigade applies water for 24 hours (this timescale is NOT set by the fire service, they are guided by others on the matter).
Ignoring the damage the cylinder might produce, imagine the water damage that will be produced by the cooling jets! 24 hours is a lot of water!!!! Anyone got major flooding in their risk assessment?
|
|
|
|
|
|
Rank: Guest
|
Posted By John Murgatroyd
If I remember right, and it was a few years ago, the majority of events with acetylene cylinders occur in the "back-street" industry. The type that "buys" its cylinders from other businesses.
BOC and I suspect the other suppliers, don't supply cylinders to one-man band businesses.
In the business I'm in, everyone is trained in the use and maintenance of gases and cylinders.
It would be interesting to see the results of a ban. No gas welding for a start, acetylene is the gas of choice for that....propane burns too cold. There would be a large increase in sales of plasma cutters....propane is a right dog for manual cutting....with a large increase in the operators of same dying early from respiratory disease in about 20+ years, not to mention the increase in fires (I don't do plasma cutting, I researched the dust and fume from same and then researched the masks and filters as well, the results scared the ****out of me....)
Not to worry.....Oh, in case you didn't know, the HSE and DoH is doing research into the increase in COPD in non smokers....apparently from 15-30% could be caused by exposure to dust and fume at work.
More litigation soon....
|
|
|
|
|
|
Rank: Guest
|
Posted By Crim
When I was a young firefighter in the 60's we would make a dam, fill it with water and carry the affected acetylene cylinder and place it in the water. The extra PPE we had at the time to deal with such incident was an asbestos (yes asbestos) hood and asbestos gloves (to protect from a flash burn), these were worn with our basic fire fighting uniform.
We also fought fires in prefabricated bungalows made with asbestos cement without wearing breathing apparatus, and tackled chimney fires from the roof tops in freezing weather without any fall protection.
Then there was the rescue of persons from upper floors of buildings by hook ladder?
Ah the good old days!
Nowadays fire services pay a lot of heed to health and safety in an effort to protect firefighters from harm, and why should'nt they. They are employees just like us and deserve the same protection.
They are getting a lot of bad press regarding this exclusion zone issue but it's all in the interest of safety.
|
|
|
|
|
|