Posted By Peter Younger As part of a review of my fire safety management, myself and a work colleague attended a refresher course on fire safety management run by a well renowned national provider. During the days training, the course instructor ( an ex brigade fire safety officer) stated that AFFF where a far more efficient extinguisher for electrical fires, and where tested and safe on voltages up to 35000 volts. This immediately drew my interest, as I could then use the same kind of extinguishers right across the business, without the confusion of what puts out what! Having then run it past the fire safety officer at my local station, he stated he preferred the use of CO2 on electrical fires, but confessed that he was not sure. Opinions and suggestions, would be much appreciated
|
|
|
|
Rank: Guest
|
Posted By tony fog I've heard this too and do recommend both options to clients, many companies are now using this single type as it covers a variety of situations.
However after educating staff for years on co2, you may find it a hard sell to you staff.
Good luck, but you trainer was right
|
|
|
|
Rank: Guest
|
Posted By David Bruce I may be wrong but I thought there was a possiblity that the foam could conduct electricity and therefore cause electric shock. Additionally, in the event of small electrical fire, would C02 not cause signficant less damage to the building finishes and surrounding equipment than foam?
|
|
|
|
Rank: Guest
|
Posted By Kevin Ray Hi all,
I'm now confused. I too have just recently (17/05/07) attended a fire safety course (1 Day Fire warden training) where the advice was not to use foam on electrical fires as it is water based therefore significantly increases the chance of electrocution to the operator? Has the information that has been given to myself and other colleagues incorrect? If so where could i get hold of the correct or most current information to take back to the course provider?
Kev Ray
|
|
|
|
Rank: Guest
|
Posted By Peter Younger To continue with the debate. My course instructor stated that it was the suppliers of extinguishers that stick by the rule that CO2 is only suitable for electrical fires, thereby selling more extinguishers. Foam is apparently non conducting
|
|
|
|
Rank: Guest
|
Posted By David Whaley Peter,
I understand that some foam is resistant to conducting electricity when used from the extinguisher. But, if it pools on the floor, being water based, is likely to conduct electricity. Just a thought. Unless someone knows better.
David
|
|
|
|
Rank: Guest
|
Posted By WTaylor AFFF is essentially water with an additive. I agree that it's foreseeable that the water will pool on the floor and possibly conduct the electricity to the user. It may be a good idea to check with your extinguisher manufacturer and get the technical data on the conductivity!
Also, you should consider the difficulty you may have when using a foam extinguisher on electrical applicances. If the fire is contained inside of a closed unit or box, it helps if the extinguishing agent actually penetrates the casing to the fire inside. A CO2 would be far more effective as it can be fired through gaps in the casing or through ventilation panels.
And let's not forget that the first thing you should do with an electrical fire is turn off the electricity. That will stop the fire 9 times out of 10 (as long as you catch it early enough). A CO2 extinguisher may put it out temporarily, but if you leave the power on the fire will just start again!
Kind regards,
Will
|
|
|
|
Rank: Guest
|
Posted By John Murgatroyd Foam Fire Extinguisher - 2 litre
A refillable extinguisher designed for use in vehicles, boats, and for industrial and commercial applications. Requires regular maintenance (at least once a year). Warranty: 5 years Fire Rating: 8A/55B Conformance Standard: Third party Certified to BS EN3 - 1996. Manufactured under Strict Quality Management System to BS EN ISO 9002 - 1994. Extinguishant: Water based extinguishing medium using a multi purpose Aqueous Film Forming Foam (AFFF) concentrate with water and stored under pressure using dry Nitrogen. Uses: A and B class fires containing carbonaceous materials like paper, wood, straw or textile. Also for fires involving flammable liquids, leaded or unleaded petrol, diesel, oil, and fat. Not suitable for use involving live electrical equipment.
|
|
|
|
Rank: Guest
|
Posted By Rob Hughes I have heard that you could use a foam extinguisher on an electrical fire and the reason in some cases it has passed the test is due to the electricity not passing up the stream coming from the extinguisher to the user as the foam is aspirated via the nozel. However, as mentioned in previous posts this does not stop it pooling on the floor and potentially reaching the user. Also I think you could be on sticky ground if the extinguisher was clear on what it can be used for and specifically if electrical fires are not covered. The extinguishers in place must relate to the potential fire risks and remember that it is now a specific legal requirement to undertake training on fire.
|
|
|
|
Rank: Guest
|
Posted By Merv Newman Let it burn. One life is worth more than a million pound building
Merv
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever I cannot believe we are having this debate!
Some foam extinguishgers, specifically spray foam extinguishers, are safe if accidentally discharged onto electrical fires up to 35kV.
If you know what you are doing, you can even use water for tackling electrical fires. Firefighters are trained at the fire service college in using water to extinguish electrical fires, but only in specific circumstances and only if correctly applied as a spray.
I would not recommend the use of water based extinguishers as the norm for tackling electrical fires particularly where the user is unlikely to be trained to the same standard as professional firefighters.
Use dry powder or CO2 but not water or foam.
|
|
|
|
Rank: Guest
|
Posted By Ashley Wood You are correct that a lot of confusion surrounds fire extinguishers (of all types). The test for a foam extinguisher is for conductivity whilst discharging and does not cover the pool of liquid that the user may be standing in. I have seen other types of extinguishers put in the wrong place. For example kitchens. I have seen hundreds of powder extinguishers used when this is inappropriate. In a modern kitchen (communal not domestic) all appliances are electrical, no body cooks with an open fryer. Powder has little effect on electrics and is very dirty to use. It can also cause breathing problems when discharged in small spaces. The reason people keep using it is because it states on the cylinder 'suitable for use on electrical fires'. This is a statement that implies it is the best thing to use but in fact refers to the conductivity test and not its best performance.
Then I have seen Co2 used in gas boiler rooms when powder would be better. The problem with Co2 is that it could blow out the nice gas flame that you get if a gas boiler catches fire. this then goes from a fire to an explosion risk!
The reason the fire officer stated foam for use on electrical is probably more to do with what burns when an item of electrical equipment catches fire. Plastics, rubber, circuit boards etc. Co2 will not cool burning plastic to any great effect and as it burns little pockets of air become trapped and this enable the fire to reignite. Foam would cool, due to the water content, and remove the oxygen by coating the effected material in foam. So I can see where the fire officer is coming from.
|
|
|
|
Rank: Guest
|
Posted By Robert K Lewis You will find that foam is more effective in the open air than powder or CO2 for electrical fires but as Ashley states the problem is the secondary materials involved thus CO2 and powder abilities to extinguish are stretched to the limit. Electricity without combustible materials will not provide a stable fire - only an electrical discharge. Neither CO2 nor powder have significant cooling effect - they merely reduces the O2 level at the fire point and thus rely on confinement to be fully effective.
In general terms AFFF, please distinguish this from chemical foam as they are not the same thing, has many advantages - They are 1/3rd smaller for the same fire rating and thus easier to manage weight wise. They will also not conduct electrical power through the spray. As an all round extinguisher they are thus much to be preferred and are much better than water alone. This does not mean CO2 is defunct - if you have electrical equipment that catches fire and the air movement is low then they have a role to play. My choice always rests on these two with occasional placement of Powder in open situations external to the building.
Bob
|
|
|
|
Rank: Guest
|
Posted By Steve Cartwright You can always turn off the power supply, then you can use water, foam, co2.
Best thing to do though is leave the building.
Steve
|
|
|
|
Rank: Guest
|
Posted By Richie Wilson If only B.C.F. wre still about CO2 is one of the most overated media ever. Check your foams carefully as there are several to choose from ie, FFFP, AFFP, AFFF Protien and alchohol based foams and generaly there is no mention of the foam type used in the extinguishers.
|
|
|
|
Rank: Guest
|
Posted By Ken Taylor A problem is that many people will not recognise the difference between AFFF and other foams. Another is that being safe to use on electrics does not mean that it's necessarily the best option to deal with a fire. CO2 will penetrate into electrical equipment whereas AFFF tends to remain on the external and to some extent relies upon forming an enclosing foam 'blanket'. Another issue is that providing only one AFFF at a fire point may leave you without any 'cover' until a replacement is obtained after discharge or damage. There's a lot still to be said for the 'water (or foam) plus CO2' approach in many situations but each area will need to have whatever is judged to be the most appropriate fire cover by the responsible and competent person.
The 'just get out and leave it' approach touched upon by others above may be OK in terms of personal safety (although escape itself may sometimes need the use of an extinguisher) but the consequences of a fire-trained person leaving a small and safe to tackle fire (eg the size of a waste bin) to develop into a building and job devouring inferno before the FRS arrive may be something of a poor choice. 8 or 9 out of every 10 fires are believed to be extinguished without the intervention of the FRS. I wonder what the built environment and employment situation would be like if we all simply left them to burn.
|
|
|
|
Rank: Guest
|
Posted By Andrew Joule Land
I thought that the term "electrical Fire" had been defunct for years. There are fires that involve electrical energy source. and if this is the case as far as is practicable this energy source should have been removed by a safety device e.g. fuse RCD Etc. If it is thought that through neglect or and unsafe act that has taken place to defeat safety devices ISOLATE EQUIPMENT FROM ALL ENERGY SOURCES BEFORE YOU TACKLE A FIRE - Then at no risk to yourself attack the fire IF YOU HAVE BEEN TRAINED TO DO SO if not raise the alarm by the company recognised method evacuate to a designated safe place making sure you shut doors etc behind you to limit the spread of fire the leave it to the professionals.
The use of inert gas drenching is preferred by engineers to enable salvage of equipment. Dry powder is great for knocking FIRE out but used internally you have the problem of dust Clouding. CO2 knocks out flame but is not to good at cooling down the fire source so there is a risk of re ignition. There are the other risks with CO2 The Person who attacks the fire may try and open cabinet or other covers to enable them to reach the fire source - backflash - injuries thus making the situation worse becase now you have a casualty. DONT BECOME PART OF THE PROBLEM Attachments can be procured for extinguishers and electrical energy sourced equipment so that you can inject the inert gas into cabinets etc. without having to open them up. but again this would be operated by specially trained staff.
There are to many dead and maimed heroes already.
I don't consider the advice given by the fire trainer very good for average staff who would normally only be expected to deal with minor fires - I think he fell into the trap of many instructors from a "profession" in the assumption that their students are already "semi professional"
as always - Personal View.
|
|
|
|
Rank: Guest
|
Posted By shaun mckeever Richie I'm not sure if CO2 is over rated. My first experience of CO2 for fire fighting was when a main coolant pump on a nuclear powered submarine caught fire. The main coolant pump serves cooling water to the reactor. A failure would result in melt down. Yes there was a back up but since the fire was next to the first pump it is possible the fire may have taken them both out. So over rated? Nah - saved a polaris submarine!
|
|
|
|
Rank: Guest
|
Posted By Ken Taylor As far as portable extinguishers go, CO2 gets into the electrical works and puts the fire out rather well. OK, so there is the issue with very confined spaces where O2 is displaced - but the fire is also depleting the O2 at a pace in addition to producing toxic combustion products. I'd like to be very sure of complete electrical isolation before applying water from a portable!
|
|
|
|
Rank: Guest
|
Posted By Jeepster Any water based product has the potential to conduct electricity particularly if you are standing in it. Co2 has no potential to conduct electricity. The choice therefore is easy, also most foams have a shelf life and some are even made up of animal proteins etc, which will degrade and affect their efficiency.
Alternatively try the Darwin Award approach and try it and let us know if you live. If there is the slightest doubt then you know it is not the right choice.
Always remember not every electrical circuit is protected by MCB, or RCD so it is possible for equipment to be still live.
I personally am of the opinion that extinguishers are there to aide escape.
|
|
|
|