Posted By Paul Bibby
Hi Barrie,
Getting back to your original questions:
1. Anything from 1 to 2 m/s at the tip will be sufficient to move solder fumes. Problem is most LEV systems (Nederman systems for example) generate face velocities much higher than that, which can interfere with the soldering process (reduces tip temperatures). One recent study (http://www.hse.gov.uk/research/hsl_pdf/2005/hsl0519.pdf) found tip extraction systems generating face velocities of between 5 and 100+ m/s depending up on the cross-sectional area of the aperture. Much higher than necessary and almost guaranteed to annoy the solderer.
All properly designed metal fume LEV systems work on the principle of 'high velocity-low volume' and this requires the LEV aperture to be small and as close to the solder tip as possible. A significant issue, therefore, is the fact that these systems rely heavily on the operator using them properly. In my judgement this is a hit and miss affair and other complimentary steps should be taken to improve overall control.
Lead-free solders are not hazard free - many contain Silver, Antimony, Bismuth, Copper, Zinc, and Indium in various quantities - all are hazardous in fume form, some arguably more so than Lead. Antimony, for instance. MSD sheets do not tell the whole story but they do help move things forward. Check this one for instance
http://www.kester.com/MS...%20Free%20Solder%20US%20(24Mar06).pdf
If you are using rosin/colophony free solders and can tolerate the higher melting points of lead free solder then I would recommend using these as a matter of course. You will still require a suitable LEV system that the operator is correctly trained and instructed to use but its proper use is less critical than with Lead solder. It is essential to monitor the operator to ensure he uses the LEV correctly. I assume the flux your guys use is rosin free too.
Once you have an LEV in place you are legally obligated to keep it maintained - this includes making sure it is working correctly i.e. maintaining the adequate velocity at the tip.
The best off the shelf systems I have recommended are produced by Nederman. They are not tip extraction systems, which are the best overall, but they are good for small volume work such as yours.
2. Epoxy resin vapours require 'high volume-low velocity' extraction and will not be removed by the Solder Tip LEV system. A face velocity of 0.5 m/s will be sufficient to remove the vapours. The critical issue is the design of the LEV.
As I don't have sufficent info on the quantities involved I will assume the worse - using a few litres or more of resin daily. My recommendations may be grander than is necessary but the principles remain the same for smaller quantities.
The adhesive work should be done at the very least in a partially enclosed system. The air should be drawn from the front of the bench towards the LEV duct at the rear of the bench. The design would partially enclose the bench at the sides, rear and above the bench. The operator would work by reaching into the enclosure to do the work but not putting his head in it, for obvious reasons. The open front of the enclosure forms the face of the LEV where the face velocity if measured. 0.5 m/s is sufficient to move the vapours away from the operative. Ideally, the contaminated air should be passed through a suitable filter (i.e. activated charcoal) before it is exhausted to atmosphere.
regards,
Paul