Does anyone know what / if there are any guidelines for use of Breakers / RCDs on electrical equipment on construction sites. We have a number of electrically powered tools (drills, hammers etc) on site, not all of which are connected up to an RCD etc. Is there any guidance on this?
|
|
|
|
Rank: Guest
|
Posted By Martyn Hendrie
At what voltage do these power tools operate?
|
|
|
|
Rank: Guest
|
Posted By steven bentham
You should have a big push for low voltage particular in wet or outdoors.
|
|
|
|
Rank: Guest
|
Posted By Ian Gardner
The IEE CoP for In-Service Inspection & Testing of Electrical Equipment has a bit in it that relates.
Table 1 (which details suggested initial frequency of inspection & testing of equipment):
For moveable, portable and hand-held equipment types, 110V, used on Construction sites, there is a note against, saying: "110V earthed centre tapped supply. 230V portable or hand-held equipment must be supplied via a 30mA RCD and inspections and tests carried out more frequently."
So I would interpret this as if the equipment is 110V, it must be from an earthed centre tapped supply, but no RCD required. If it is 230V, you must have a 30mA RCD in circuit.
I've only got the 2nd edition IEE CoP to hand at the moment, so I don't know if the new 3rd edition has any more to say on the matter.
|
|
|
|
Rank: Guest
|
Posted By mark gough2
I would agree with previous postings the hierarchy is quite clear:-
Battery operated
110volt centre tapped to earth
Both of which virtually eliminate the risk of fatal electrical shock burn injuries. Neither require an RCD and the maintenance schedule can be quite relaxed.
The use of mains 230volt equipment on construction sites is "an unacceptable risk of death or serious injury"
Unless it is RCD protected etc etc etc..the controls required run to three pages in HSG141 Electrical safety on construction sites.
In my experience there is no need to have 230 volt tools on construction sites.
Site cabins should be RCD protected and equipment such as hoists etc which cannot be sourced at 110 volt should be rcd protected.
Remember an RCD only provides supplementary protection and should never be used as a primary source of protection. They should be tested daily by push button and monthly by trained electrician.
|
|
|
|
Rank: Guest
|
Posted By anon1234
Agree with the above - use battery or 110V equipment and avoid the need for RCD
|
|
|
|