Welcome Guest! The IOSH forums are a free resource to both members and non-members. Login or register to use them

Postings made by forum users are personal opinions. IOSH is not responsible for the content or accuracy of any of the information contained in forum postings. Please carefully consider any advice you receive.

Notification

Icon
Error

Options
Go to last post Go to first unread
Admin  
#1 Posted : 11 November 2008 16:43:00(UTC)
Rank: Guest
Admin

Posted By Jason McQueen Whats the best way of calculating the number of air changes that a room has? I guess its a case of working out the volume of the room and then dividing this by the air speed per hour but whats the best way of determining the air speed for a standard, non forced/mechanically vented room? Is it a case of standing there with an anemometer?
Admin  
#2 Posted : 11 November 2008 16:48:00(UTC)
Rank: Guest
Admin

Posted By Tony abc jprhdnMurphy Leakage, Infiltration, Size of room, extract system? All info you need
Admin  
#3 Posted : 11 November 2008 16:50:00(UTC)
Rank: Guest
Admin

Posted By Bossa nova Jason, If you haven't got forced ventillation you will have nothing to measure. Are you checking for compliance or because there is a problem? Crossover
Admin  
#4 Posted : 11 November 2008 16:52:00(UTC)
Rank: Guest
Admin

Posted By Jason McQueen Its as a result of a DSEAR assessment. We need to ensure that one of the rooms in which we stored flammable liquids has six changes of atmosphere per hour. The room is vented via natural draught ventilation but nothing else. We therefore need to calculate if this is sufficient to generate the six changes and if not, look at forced ventilation.
Admin  
#5 Posted : 11 November 2008 16:56:00(UTC)
Rank: Guest
Admin

Posted By Bossa nova A little quick to hit the send button earlier. If you have a flow to measure, assuming this is continuous for the purposes you state! The you measure the velocity multiply this by the open inlet area and this gives you your volumetric flow, divide the room volume by this and hey presto.
Admin  
#6 Posted : 11 November 2008 17:07:00(UTC)
Rank: Guest
Admin

Posted By Guderian Buried somewhere deep in the text of one of the DSEAR guidance books, there is some guidance on the size of ventilation louvres etc. From memory if the area is 1.5% of the wall size, then ventilation is likely to be ok. If you consult BS60079-10, there is a formula in there for calculating air flow rates and air changes. Sorry can't send you a copy, its a copy right document. Also consider the existing/proposed layout, check that there are no stagnant areas.
Admin  
#7 Posted : 12 November 2008 09:30:00(UTC)
Rank: Guest
Admin

Posted By Guderian Slight correction to my earlier post. The percentage area of ventilation vents is given in the following publication: The Storage of Flammable Liquids in Containers ISBN 071761479 (1998 Ed) Para 61 Recommends 5 x air changes per hour The area of the vents should be between 1-3% of the total roof and wall area. The building/vents should not be obstructed from external winds etc.
Admin  
#8 Posted : 12 November 2008 09:38:00(UTC)
Rank: Guest
Admin

Posted By Bossa nova A little more involved than a straight 1-3% I would suggest you getting a copy of HSG51, a nominal investment considering the task you are undertaking. Blowover
Admin  
#9 Posted : 12 November 2008 10:26:00(UTC)
Rank: Guest
Admin

Posted By Guderian The info in my last post is taken from HSG 51. Your advice is not too specific, to help the original poster of the query they had.
Admin  
#10 Posted : 12 November 2008 10:38:00(UTC)
Rank: Guest
Admin

Posted By Paul Leadbetter Jason Have you considered trying to measure the air change rate? Paul
Admin  
#11 Posted : 12 November 2008 10:48:00(UTC)
Rank: Guest
Admin

Posted By Guderian In practice it is quite difficult to measure natural ventilation rates - the air flow velocities are usually too small to get accurate measurements. Anemometers/turbine flow meters requires probably in excess of 0.5-1m/s wind speed to give anything like an accurate reading. In which case if you have these speeds, then the ventilation is probably ok. Not to mention other inaccuracies caused by draughts around doors/windows etc. Its not so much the amount of air flow (although still important), as to where the air flow goes. High flow rates can sometimes mask leaks/build up of vapours. Hence my earlier comment about giving consideration to areas where stagnant air/vapours might gather.
Admin  
#12 Posted : 12 November 2008 10:53:00(UTC)
Rank: Guest
Admin

Posted By Paul Leadbetter It is out of print now but the method in MDHS 73 was pretty straightforward. Paul
Users browsing this topic
Guest
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.