Posted By James Putman
Hello All,
I have been asked to fit fire safety document cabinets within the common parts of residential buildings.
The client has requested that these cabinets are fitted to the back of the doors to the electrical intake room within each block.
The screws for these cabinets are around 2cm, thick, and the cabinets themselves are quite lightweight.
Can anyone confirm whether this is accetpable, or whether it is likely that an inspecting fire officer would advise against it, due to a potential breach of the fire resistance of the door.
Are there any specific standards for the dimensions of any screws etc which may be fitted to fire doors?
|
|
|
|
Rank: Guest
|
Posted By Bob Youel
if you breach the mechanical integrity of a fire door you are probably breaching the T&C's of your insurance policy and and manufactures/ suppliers guarantees
|
|
|
|
Rank: Guest
|
Posted By martinw
'Most other items of building hardware
on the door perform a function not directly associated with its fire
performance ("non-essential"), but they must in no way impede or
reduce the door's ability to withstand fire attack for the specified
time. This also requires careful selection. Too often, holes are drilled
through timber fire doors, and large metal components are attached,
with no thought as to the consequences.'
The above is from
http://firecode.org.uk/C...ire_and_escape_doors.pdf
which is referred to specifically as a source of information in Approved Document B.
It is a big document and does not specify what can and cannot be used. It says that whatever you do must not cause less fire resistance performance. Difficult to see how drilling holes, using metal screws which are conductant, will not reduce performance. Might also invalidate the fire resistance certification which came with the door until it is re-tested(may need to be - have to speak to a competent person to find out if it is required) following the fitting any of any non-essential devices being fitted.
The document gives all the British and European Standards you should need.
Martin
|
|
|
|
Rank: Guest
|
Posted By martinw
Forgot this on the previous post, but dependant on other factors has an asbestos survey been carried out? Often used substance in fire doors of a certain age...
|
|
|
|
Rank: Guest
|
Posted By James Putman
Thank you very much for your help.
We will be requesting Asbestos Surveys prior to any works commencing. However, after giving this some thought I think an alternative location will be more appropriate.
One other question:
Does anyone know the fire resistance standard to which communal doors within council blocks of flats were built to if they were constructed around the 1960's? Was it still 30 minutes fire resistant?
Thanks in advance
|
|
|
|
Rank: Guest
|
Posted By martinw
Can't find it anywhere. Not an expert - but the GLC had requirements for means of escape at the time, the first building regulations really came in formalised in about 1966, national requirements sometimes differed from London specific legislation. Muddled, so it will require a H&S historian to help.
But have a look at the original architect plans for the building in Camberwell which caught fire recently. Gives an idea of what the standards were without being specific.
http://www.architectsjou...ng-study/5204667.article
Martin
|
|
|
|