Rank: Guest
|
Posted By Richard Beevers I need some real expert advice from someone electrically competent.
Please dont refer me to HSG85, EIS 35-38 or the EAWR, or BS EN 60529.
When is a live adjacent conductor "suitably covered with insulating material so as to prevent danger"? Can is be thought of in terms of IP ratings?
All of our switchboards are at least IP2 rated for their internal curcuits, and most have perspex screens as well.
Some of our electrical staff work with adjacent circuits live. Some are insistant that the whole of a pabel / swichboard must be isolated and racked out before working on any circuit within in.
If there is any caselaw on this I'd really appreciate it. Am getting grief from both sides, each of whom thinks the other is to risk averse / risk taking.
Regards, Al.
|
|
|
|
Rank: Guest
|
Posted By Larry If a competent fitter is not happy to work under those conditions, who are the others to tell them otherwise?
We all have rights and we all have different opinions.
It's the fitters life and if s/he is not happy working in a manner which they perceive as dangerous, they have the right to request additional control measures. No one should be putting pressure on them to work in a manner which they feel is unsafe.
|
|
|
|
Rank: Guest
|
Posted By Rich E Hi Richard,
I'm not sure I can give you a definitive answer, but as it happens I have been considering this kind of issue from a manufacturers perspective today after a customer asked a similar question.
Switchgear made to meet IP2X or IPXXB is subject to a test with a 'standard' 12mm finger approaching from the front. It usually means that conductors are protected only against accidental contact, and not if you start poking fingers in to things.
The danger tends to be when working, stray wires, tools, etc can accidentally touch live parts. For example I've seen flashovers caused by armour strands poking round barriers.
Unless a panel is constructed strictly to form 4, for example, adjacent circuits may be accessible, albeit via very narrow gaps.
We have always worked on the acceptability that IP2X is suitable for working on adjacent circuits live, but many customers are beginning to require supplementary solid insulation (polycarbonate screens) to prevent the above problems.
BS7671 suggests IP2X is satisfactory, again this is not infallible and only provides protection against accidental contact. Anyone working on such equipment should be aware of the dangers and we consider a ‘competent’ person should be able to safely work.
Some customers are happy working live on equipment which has minimal shrouding, where others still isolate the entire unit on fully shrouded kit.
As usual it is a matter of risk assessment and whether isolation can reasonably be carried out, this is the eternal question. From my experience total shrouding is possible, but would be prohibitively expensive for most commercial equipment.
Hope this helps, but I may have more guidance if needed.
Rich
|
|
|
|
Rank: Guest
|
Posted By Paul Skyrme Richard, I take it that you are referring to low voltage installations?
DNO personnel regularly work live. I gather that HSE accept this as it is impractical often to isolate large areas of the low voltage national grid for minor works! Also there are robust safe systems of work in place and a great level of experience in such matters. However, there are certain precautions. Lone live working in a panel is almost certainly a no-no? I would suggest that it is down to the individual risk assessment for the task taking into account the competence of the operative. IF the operative is not happy working live then the panel should be fully isolated as the person will be nervous and perhaps more prone to mistakes? If the operative has a "gung ho" attitude then perhaps the panel should be fully isolated as they may be tempted to take too many risks?
A little more description of the systems may be useful e.g. machine control panels, distribution boards etc.?
Any use? Paul.
|
|
|
|