#1 Posted : 02 October 2009 17:03:00(UTC)
Rank: Guest
Admin

Posted By Nigel
Although I know official guidance states extinguishers should be located on escape routes, at exits from rooms or floors & at FINAL EXITS I've always been puzzled ... why at final exits? Surely once you've reached the final exit you're going to be more interested in going through it than picking up an extinguisher ... and to do what with it in any case? If they're intended to aid your escape through the final exit then having them located right next to it (that seems to be standard practice) probably means you'd have to be standing in the fire that's blocking your escape in order to reach them. I don't get it.

Can anyone please enlighten me?
Admin  
#2 Posted : 02 October 2009 17:24:00(UTC)
Rank: Guest
Admin

Posted By Crim
The theory is you are on the way out and once you reach the exit and the extinguisher you can then decide whether to use the extinguisher to attack the fire or just keep on keeping on.

If the extinguisher is located inside the building there is a chance you would have to enter the building to reach the extinguisher, thus taking you into a dangerous situation.

There will be times when extinguishers are located inside buildings but this would be to protect a particular machine, or due to excessive travel distances.

Hope this satisfies.
Admin  
#3 Posted : 02 October 2009 18:24:00(UTC)
Rank: Guest
Admin

Posted By D H
It also gives you something to fight fire with if your escape is hindered by fire- also useful for breaking glass etc to aid escape.

Dave
Admin  
#4 Posted : 02 October 2009 18:52:00(UTC)
Rank: Guest
Admin

Posted By Phil Rose
It's Friday and I am feeling mischievous. Isn't it so that they can be used to hold the doors open :-)
Admin  
#5 Posted : 04 October 2009 11:24:00(UTC)
Rank: Guest
Admin

Posted By FAH
Hi Nigel

This is an issue that has been revisited so many times on this forum.

In the UK there are NO rules as to where FEs must be placed; so, those doing the FRA are required to identify exactly where the FEs should be placed. Most of those who decide to place them at only exits are, in my opinion, not thinking about the real issues at all!

Regardless of where you are in the world; with regard to selection & placing of FEs, the first criteria MUST be to identify any area [using the FRA] within the premises that could be difficult to escape from if a fire occurred between that place and the exit [normally termed "dead-end" conditions]- the most appropriate FE should then selected and placed within that dead-end to facilitate the escape of any persons who may be there when a fire occurs.

The nonsense that is frequently given about the FE being at the exit to facilitate going back into the fire to attack it is patently a direct contradiction of the UK workplace fire safety legislation that requires all those affected to leave without delay AND for the premises controller to ensure that no-one returns to the premises until informed that it is safe to do so [normally by the Fire Service].

Given the above, I'm entirely with you here - just why do people put FEs at exits if that exit is going to take the occupants out to a place of safety? In my opinion, it's because even now, a substantial majority of premises controllers either copy what others do 'cos it's easier than doing a proper FRA, or rely far to much on the advice of those selling/hiring the FEs [who don't even realise that they then have a liability for their advice as to which type & where it should go] and who naturally have a vested interest in getting the premises controller to take as many units as possible! More FEs = more money!!!

Another nonsense frequently given is that the Fire Service will use them as they go in to the fire. Given that UK firefighters have an incredibly deep distrust of anything that they don't absolutely know is not going to put their lives at greater risk; this doesn't stand up; I don't know of any competent UK firefighter who would even consider using a FE found on the premises that they're attending as even a third choice.

There, that should get a few people going!

I'm off to lunch now.

Frank Hallett
Admin  
#6 Posted : 04 October 2009 12:35:00(UTC)
Rank: Guest
Admin

Posted By Crim
Hi Frank,

You certainly poo poo the idea idea of extinguishers at exits so just where would you put them?

On this forum there often are people like you making negative comments withiout really offering the requested guidance or advice.

Further, the suggestion of using them to break glass is a definate no no - I don't know where some people get their ideas from.

Try thowing a 9l water extinguisher at a double glazed unit and see what happens?

I do agree, however that placing them at exits should not be the rule everytime - for instance my recent fire risk assessment in a city centre betting shop led me to recommend some being positioned behind the staff counter at the rear of the shop, which is permanently manned. If they were placed at the main exit there is a great possibility of vandalsm or theft. This way the staff can use them to escape from a fire if necessary.

Risk assessment will decide!

They could of course use then to prop open some doors as somebody else has suggested, or even to hang their coats on. No laughs here as it's serious business!

Admin  
#7 Posted : 04 October 2009 13:14:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Portable fire fighting equipment is provided so as to enable a trained user to extinguish an incipient stage fire, it is nonsense to suggest that this equipment is provided to aid a means of emergency egress from a location with a single means of escape.

A probable explanation for positioning at a final exit is that there is an increased probability of activating a manual call point prior to use of extinguisher. That is not to say that this equipment should not be provided at the likely point of hazard or within a reasonable travel distance.

Admin  
#8 Posted : 04 October 2009 16:10:00(UTC)
Rank: Guest
Admin

Posted By FAH
Many thanks for your views Crim & Dave.

Crim, I did provide some positive guidance as well as attempting to get those reading to actually think for themselves about this.

There is absolutely nothing in the FSO or FSA [Scotland] that requires anyone to attack a fire - but why are you so defensive about my comments anyway?

Frank Hallett
Admin  
#9 Posted : 04 October 2009 16:26:00(UTC)
Rank: Guest
Admin

Posted By D H
Mr Hilton - not its intended use I agree, but if you needed to break out of somewhere would a fire extinguisher - full or empty not be a useful tool?

Dave
Admin  
#10 Posted : 04 October 2009 16:57:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Consider the travel distances and passive fire protection set out within AD B. Then consider that the distances to means of egress as specified decrease in cases where fire risk increases.


Admin  
#11 Posted : 04 October 2009 17:04:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
FAH
The main reason that Fire Service personnel would be less likely to use a portable extinguisher is typically due to a fire being at pre or at flashover on their arrival and so the PFE would be of no tactical use.

Admin  
#12 Posted : 04 October 2009 17:49:00(UTC)
Rank: Guest
Admin

Posted By FAH
D Hilton - I dislike being so formal but I not sure that "D" would suit.

It's obvious that you're basing your comments on a great deal of practical front-line fire safety & firefighting experience.

I have no arguement with your observations generally, they're perfectly valid.

However, it is my experience that even in the best planned & managed premises, it isn't always possible to have absolutely no "dead-end" conditions. It is these conditions and the fact that users of such spaces may need to get past a fire that is not otherwise segregated that I'm considering.

Frank Hallett
Admin  
#13 Posted : 04 October 2009 19:22:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Frank
Surely that would be the exception rather than the rule. If it was conceivable that ignition and fire growth would occur so as to trap the occupants in a non domestic dead end scenario, the travel from the extreme of the dead end could not exceed 9 meters until the choice of alternative means of escape.

Moreover, in the event that such accelerated fire growth is anticipated, it is more likely that the dead end scenario would have been removed at planning stage.

If portable fire fighting equipment was intended to be provided as a means to aid emergency egress then the provision and positioning would be considerably more prescriptive and would be included within AD B.

I am not saying an individual is prohibited from using this equipment as a means to aid egress I am stating that this was not the intent of providing this equipment.

In addition, if the HRR was to such an extent as to prevent egress, it would be most unlikely that the use of a fire extinguisher would reduce the thermal radiation to an extent as to allow safe passage or egress through the fire.

Regards
Darren
Admin  
#14 Posted : 04 October 2009 19:25:00(UTC)
Rank: Guest
Admin

Posted By Crim
When I was in the fire brigade I was always tought never to use anything that was not fire brigade equipment, especially builder's ladders as they cannot be relied upon.

I would never have imagined using a fire extinguisher as there was always lots of other available equipment on on the fire appliance. The hose reel was always ready, charged with an unlimited supply of water and so quick to get to work.

I did however use a foam fire extinguisher once, on a chip shop range well alight.

Outside the brigade I once tackled a car fire in a car park using extinguishers from various shops. I had assistance from other members of the public but the fire was still burning when the brigade arrived. As I remember we used two water, one foam and one carbon dioxide, to no avail.
Admin  
#15 Posted : 04 October 2009 19:30:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
crim
I dont know many builders with a 135

Admin  
#16 Posted : 04 October 2009 19:32:00(UTC)
Rank: Guest
Admin

Posted By Crim
Fire safety risk assessment offices and shops guidance document, page 58 states:

Where the fire risk is not confined to a particular location eg class A fires, the fire extinguishers should be positioned on escape routes, close to the exit from the room or floor, or the final exit from the building.

It goes on further about specific risks and more than that, but I think this answers the original question.
Admin  
#17 Posted : 04 October 2009 19:36:00(UTC)
Rank: Guest
Admin

Posted By Crim
Darren fire fighters do not always use 135 ladders, in fact not very often, more likely to be short ex. Step ladders are often found in buildings and these were not to be relied upon. Anyway when I first started in the brigade we had 50 ft wheeled escapes, I never saw one of those on a construction site unless we brought it in, ha ha
Admin  
#18 Posted : 04 October 2009 19:57:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Crim
I know it would be more usual to slip & pitch a 105
Admin  
#19 Posted : 04 October 2009 20:30:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Quick calculation tells us that 9 litre water extinguisher could remove 20700 kJ of heat on complete vapourisation (more likely 13000 kJ at 55% efficiency).

This heat of combustion is the equivalent of 720g of cellulose.

unlikely to prevent escape.

Admin  
#20 Posted : 04 October 2009 20:32:00(UTC)
Rank: Guest
Admin

Posted By Crim
Darren, now you're being clever!

Do you remember the 30' ajax. A wooden ladder that was still in use on the Green goddess during the 1977 strike. Splinters and string friction burns - ouch!
Admin  
#21 Posted : 04 October 2009 20:33:00(UTC)
Rank: Guest
Admin

Posted By Crim
Unlikely to prevent escape?
Admin  
#22 Posted : 04 October 2009 20:49:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Meaning that if a fire prevented an individual from passing in order to reach comparative or ultimate safety, then the use of an extinguisher is not going to improve the situation and Franks argument is flawed.

Admin  
#23 Posted : 04 October 2009 21:18:00(UTC)
Rank: Guest
Admin

Posted By martinw
oh, get a room
Admin  
#24 Posted : 04 October 2009 21:19:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Put another way

Threshold of pain of human skin is 5 kW/m^2 over 10 seconds.

If fire scenario is above this level escape from Franks dead end is unlikely.

Assume the fuel source at Franks dead end is timber/wood with Heat of Combustion of 15 kJ/g, also assume fantastic burn rate of 200g/second.

200.15 = 3000 kJ/sec = 3000 kW

Lets assume some 40% is radiated out from the fire, 55% convected, 5% not released due to incomplete combustion.

Lets also assume that the heat is radiated out equally in all directions (isotropic) and that an individual must pass within a distance of 1.5 m in order to escape.

A hypothetical sphere centred on the fire has an area of (4 . Pi . 1.5^2 = 28.26 m2)


In this case the fraction of heat flux impinging on 1 m^2 is calculated :

1/28.26 = 0.35 kW/m^2

well below 5 kW/m^2



Admin  
#25 Posted : 04 October 2009 21:29:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Any one spot the deliberate error LOL

Scrub that.

Lets also assume that the heat is radiated out equally in all directions (isotropic) and that an individual must pass within a distance of 1.5 m in order to escape.

A hypothetical sphere centred on the fire has an area of (4 . Pi . 1.5^2 = 28.26 m2)

In this case the fraction of heat flux impinging on 1 m^2 is calculated :

1200/28.26 = 42.46 kW/m^2

So individual would be well crispy !!!!

note to self (check calcs and less speckled hen before posting)

Burn rate would need to be 20 g/sec to result in successful escape.

In any event well beyond the capabilities of the fire extinguisher.



Admin  
#26 Posted : 04 October 2009 21:30:00(UTC)
Rank: Guest
Admin

Posted By D. Hilton
Watcha
Martin
Admin  
#27 Posted : 04 October 2009 21:40:00(UTC)
Rank: Guest
Admin

Posted By martinw
indeed Darren
is there a specialist FF forum by any chance to which I do not have access? If so, can you and Crim cage fight in there? :-) Love you all really
Admin  
#28 Posted : 04 October 2009 21:41:00(UTC)
Rank: Guest
Admin

Posted By Crim
I just got this from Wikepedia, it could just end this argument?

A fire extinguisher is an active fire protection device used to extinguish or control small fires, often in emergency situations. It is not intended for use on an out-of-control fire, such as one which has reached the ceiling, endangers the user (i.e. no escape route, smoke, explosion hazard, etc.), or otherwise requires the expertise of a fire department.

Goodnight all Zzzzzzzzzzzzzzzzzzzzzzzzzzzzzzzzz