Metheringham17703  
#1 Posted : 15 December 2009 16:35:27(UTC)
Rank: Forum user
Metheringham17703

I am currently trying to convince poeple that PAT testing should be carried out 3 monthly instead of 6 monthly for on site equipment (construction site) . I am coming up against the old "thats just guidance not law" argument. (head, brick wall, bang bang bang). Can anyone point me in the direction of some case law relating to not following guidance, particularly if it relates to failure to PAT test equipment at the reccomended frequency. Hopefully this might get a response.
paul.skyrme  
#2 Posted : 15 December 2009 16:51:59(UTC)
Rank: Super forum user
paul.skyrme

Hi, I am just wondering why you want to go to 3 months? Are you getting a lot of failures after 6 months? Are you getting a lot of equipment fail on user checks? Are you getting a lot of reliability failures or damage? Is the equipment that heavily abused that it requires formal inspection & testing that often? If so I would think about it not being fit for purpose. Otherwise the users need serious retraining! User checks should be at least daily and they should pick up any obvious damage or deficiencies. It is just guidance not law, there is NO LAW that requires PAT. The requirement is under EAWR, HASAWA & PUWER. That is for adequate maintenance and safe equipment. Spoke to one HSE Electrical Specialist who openly admitted that the guidance was a bit over zealous! The persons inspecting your equipment if competent should be able to give you a definitive answer on this one as they are the persons signing the equipment off. They should know that you have 6 monthly intervals and should be advising/acting accordingly. If you want a legal aspect I suggest that the deficiencies/failures in your written PAT report are used as ammunition to prove that equipment was unsafe/dangerous immediately prior to formal inspection/test and was thus removed from service. This could illustrate the faults and failure modes and how these could be lethal. Remember however, that most of these tools will be suplied by extra low voltage supplies and now more often than not the supplies may well be protected by residual current devices. Probably does not help I know. Sorry Paul.
Metheringham17703  
#3 Posted : 15 December 2009 17:04:36(UTC)
Rank: Forum user
Metheringham17703

Paul, thank you for your comments. 6 months is a long time for an extension lead to be used on a construction site. i believe that the environment means that there is a real risk of damage leading to electrocution. 3 month testing reduces that period and therefore the risk. Also the guidance may be over zealous, but it is guidance none the less and would likely be used in court if an accident occured. I am aware that there is no law requiring PAT testing, but bearing in mind the requirements of HASWA and PUWER, i believe that a 6 monthly test would not be sufficient, given the environment in which the equipment is being used. Even if no failures occured in the past on PAT tests the risk remains and in mind is foreseeable. (by the way we do have failures) Some opinions on this would be appreciated
jwk  
#4 Posted : 15 December 2009 17:16:11(UTC)
Rank: Super forum user
jwk

Agree with Paul to an extent, it is indeed EAWR and PUWER. EAWR have the effect that electrical equipment must be safe and free from danger; PUWER requires employers to risk assess their equipment to ensure that it is safe and fit for purpose, SFARP applies under PUWER, not under EAWR. So it sounds to me like you have done your RA and have decided that portable electric appliances used outdoors by a shifting and ever-changing number of people need a three-month PAT; sounds reasonable to me. If you have a high rate of failures after 6 months then you have a reasonable argument for reducing the frequency, John
teh_boy  
#5 Posted : 15 December 2009 17:20:19(UTC)
Rank: Super forum user
teh_boy

http://www.hse.gov.uk/pubns/books/hsg107.htm Try this document - I think it has a list of recomended inspection periods.
jwk  
#6 Posted : 15 December 2009 17:30:09(UTC)
Rank: Super forum user
jwk

And the thing about guidance is that you can't be prosecuted for breaching guidance; it does have some legal status, and could be taken into account, but unless it's in the Regulations you can't be prosecuted for it. ACOPs have more force. And yes, you already know all this, but have a look at the Corporate Manslaughter & Guidance thread, there's an interesting spin on an old story in there, John
Clairel  
#7 Posted : 15 December 2009 17:51:53(UTC)
Rank: Super forum user
Clairel

jwk You can't be prosecuted for failing to follow established guidance. But you can be prosecuted for breaching legislation. As legislation is usually written in quite woolly terms how you comply with that legislation is set out in ACOP's, COP's and guidance. So technically someone may be prosected for breaching (for example)the Electricity at Work Regulations but it is the failing to follow the guidance that is relied upon to win the case in court. I did so successfully on many occasions (but I hasten to add not in relation to PAT). Personally I always tell clients that the whole ACOP, guidance thing is misleading becuase although you can't be prosecuted for failing to follow guidance the standard set out in the guidance will stand up in a court of law when being prosecuted for breach of the Regulations (unless you can demonstrate that you achieved the same equally effective measure (which I never saw happen). When it comes to PAT I think far too many companies rely on PAT instead of understandiung that it is just one of a range of measures that need to be in place. I've lost count of how many extension cables or pieces of equipment I've seen which were PAT tested recently but had damaged cables.
paul.skyrme  
#8 Posted : 15 December 2009 18:07:04(UTC)
Rank: Super forum user
paul.skyrme

clairel wrote:
jwk When it comes to PAT I think far too many companies rely on PAT instead of understandiung that it is just one of a range of measures that need to be in place. I've lost count of how many extension cables or pieces of equipment I've seen which were PAT tested recently but had damaged cables.
Yes quite, a PAT is simply a snapshot in time, just like the MOT on a car. Only really valid at the split second the sticker is fitted. Also it has no value with most customers with regard to its status etc. Being sold to the lowest bidder often undertaken by staff who are barely trained and don't really understand the equipment or the principles behind the tasks they are undertaking. Many companies are doing 60-70 recordings, inspections, tests & labelling per hour at 60p per test. I know what is supposed to be done, having done it. OK you get better with practice, quicker and more able to spot problems but under 60 seconds to identify & record the equipment, inspect, check fuse and undertake the required tests for the item in question! The comment above, just confirms the situation really? Anyway, soap box away. Paul. p.s. doing this on my pc at home, have Google toolbar installed, spell checker works fine :-)
firesafety101  
#9 Posted : 15 December 2009 19:08:42(UTC)
Rank: Super forum user
firesafety101

I'll share some of my experiences here if I may? A few months ago I attended a meeting with HSE inspectors who were giving a "ticking off" to one of my clients, a shopfitting contractor who's standards were below the expected. One area was PAT and the HSE recommended three monthly tests/inspections. I asked if this was required and the answer was "Yes"! Good enough for me! I carry out safety inspections on construction sites and see problems in getting PAT carried out on lots of sites. Those that have PAT are usually over the three month, sometimes over one year since previous tests, other equipment no record at all. This usually applies to individual worker's tools i.e. hammer drills, saws etc. Most of the contractors are now hiring in the site electrical equipment and this comes with records of testing that is quite up to date. My advice to contractors is to use rechargeable hand tools, the chargers do not create a problem and can be used in the hotel room overnight, otherwise hire the tools and always ask for records of up to date testing.
paul.skyrme  
#10 Posted : 15 December 2009 19:53:00(UTC)
Rank: Super forum user
paul.skyrme

ChrisBurns wrote:
I'll share some of my experiences here if I may? A few months ago I attended a meeting with HSE inspectors who were giving a "ticking off" to one of my clients, a shopfitting contractor who's standards were below the expected. One area was PAT and the HSE recommended three monthly tests/inspections. I asked if this was required and the answer was "Yes"! Good enough for me! I carry out safety inspections on construction sites and see problems in getting PAT carried out on lots of sites. Those that have PAT are usually over the three month, sometimes over one year since previous tests, other equipment no record at all. This usually applies to individual worker's tools i.e. hammer drills, saws etc. Most of the contractors are now hiring in the site electrical equipment and this comes with records of testing that is quite up to date. My advice to contractors is to use rechargeable hand tools, the chargers do not create a problem and can be used in the hotel room overnight, otherwise hire the tools and always ask for records of up to date testing.
Chris, I remember "the meeting"! Regional variation in inspections. Your guy said 3m, the senior electrical inspector I talked to said that the guidance was a little "over zealous". Mind no exact figures! Hire tools IIRC must be provided with test certs? Not sure if this is a legal thing or a Hire Equipment "Association" thing? As you say personal tools must be treated with the same level of inspection as company stuff. I don't feel that in ALL circumstances 3m is essential, but 12m is excessive. It is site specific. If you have mainly sparks, they should not need any doing! ;-)))) Rechargeable are great, what about hand drills, no electric, back to the bit & brace. I jest not, RSI aspects apart. Surely the, I was going to put Project Sup' not any more! Surely the Principal Contractor should keep tabs on this, as should individual subbies? I don't PAT any of our equipment. I have trained my users to inspect every time before use, any smallest defect must be reported in writing, woe betide them if they don't! I will inspect & test as I feel fit & undertake random audits to check condition of our equipment and how it is being used. Notwithstanding any of the previous posts, Chris has 1st hand knowledge of HSE advice which "contradicts" that I was given, though mine was not formal, (IEE (IET) meeting). First and foremost, user checks are the most important. Visual and user checks pick up the most defects IF carried out correctly. Fact. How about our old friend the toolbox talk to increase awareness? Informal is best, especially if you have any wannabee sparks! HTH Paul.
Canopener  
#11 Posted : 15 December 2009 20:43:20(UTC)
Rank: Super forum user
Canopener

If you are really determined to find some case law, I suggest you start with the HSE prosecutions database and drill down on the EAWR - don't envy you trawling through that though to find a case specific to PAT. I can't recall one I have to say, but guess there are some! Good luck and let us know.
firesafety101  
#12 Posted : 15 December 2009 21:28:11(UTC)
Rank: Super forum user
firesafety101

Paul, just to agree with one of your points - I audit the PC on behalf of the client. My report goes to the client with a copy to the PC. Any audit exception is directed at the PC including PAT. I look at all site tools and equipment and seek records as proof of inspection and test. If records are available then at least something is being done even if out of date (whatever that date is)? The fact that you do not have a regular frequency for testing is OK because you have random audit checks, with I assume records kept? That would satisfy any HSE inspector. Don't forget - we usually only fall foul if something goes wrong. With electrical equipment that is potentially fatal!
jwk  
#13 Posted : 16 December 2009 09:39:53(UTC)
Rank: Super forum user
jwk

Claire, I believe that's what I said; you can only be prosecuted for breaking the law. Although I agree that as far as your clients are concerned the difference between ACOPs and Guidance is not very important. What matters is that they don't break the law. Guidance can be used in prosecutions arising from the Corporate Manslaughter & Corporate Homicide Act by the Jury in their deliberations. The Act defines guidance so as to include ACOPs, Guidance and practically anything else any government body has ever said about H&S. OK, this Act should only result in a handful of prosecutions per year, and in HSE's terms the difference between ACOP and guidance is still clear cut. However, if you are arguing with an employer who is using the 'that's only guidance' bit, as in the OP, it could help to point out that perhaps the scariest law employers face gives guidance rather more weight than we are used to. Also it's worth bearing in mind the idea people have about guidance; it's very often confused with the notion of guidelines, or jolly good ideas. It's not, and maybe an explanation of the technical definition of guidance could be helpful. Chris though hits the nail on the head; low voltage tools reduce the risk at source and meet the principles of prevention in Annexe 1 of the Management Regs; if there is little risk of a fatl shock it really doesn't matter what this or that HSE Inspector said, really, John
jwk  
#14 Posted : 16 December 2009 09:43:40(UTC)
Rank: Super forum user
jwk

And Claire, I can't agree that legislation is written in woolly terms in general (poor legislation is). It is written usually in very precise technically defined language (it shall be the duty of every employer; suitable and sufficient assessment of the risk). ACOPs and guidance exist to explain that condensed, precise language in terms which are closer to the vernacular, and to add some necessary detail. It's the guidance that's woolly, though ACOPs are usually fairly precise, John
firesafety101  
#15 Posted : 16 December 2009 13:16:05(UTC)
Rank: Super forum user
firesafety101

The following link may just answer the question. http://www.pat-testing.info/legal.htm Not sure if it states frequency of testing but there are lots of places to go.
ianm69  
#16 Posted : 16 December 2009 13:59:38(UTC)
Rank: Forum user
ianm69

I'm positive PAT comes under PUWER and not EAWR. You can check, but I 'guess' that most cases would probably of been tried under PUWER and MGMTR. PAT testing is the recognised way for finding faults, visual inspections are another (if you got records that is). If you've got nothing in place currently, then your probably going to get stung big-time and it may hurt But, if you have something in place currently and its evidence points to increasing frequency for tests then it is self-explanatory evidence you can use. You can advise, cudjule (spelling error me thinks) and motivate, but if the management are not going to do it....suggest you need to try and put temporary measures to protect your people meanwhile - worksite inspections, additional staff training (on identifying faults)
martinw  
#17 Posted : 16 December 2009 14:06:15(UTC)
Rank: Super forum user
martinw

This is interesting in that EWR is the breached regs, but the case notes apparently are backed up by reference to no PAT testing haven taken place: B&S Engineering (Cradley) Ltd Fined £1,500 under EWR 1989. Injured by 415v electric shock. Failure to maintain 3 phase twin and earth extension cable which had a visible split in insulation. No PAT testing. HSE Prosecution Case F120000473 (20/6/03) Cannot find the case on the HSE prosecutions database to double check if no PAT testing was just a side note or whether it was used as an aggravating factor.
jwk  
#18 Posted : 16 December 2009 14:18:28(UTC)
Rank: Super forum user
jwk

Ian, If you follow the link Chris has put up you will see that PAT is, as has been said already on this thread, based on several different sets of regulations; PUWER and EAWR are the two most relevant but the Management Regs and HASAWA itself also have relevance. The link posted by Chris also mentions the Workplace Regs but I would have thought that was more relevant to the fixed installation. PUWER requires work equipment to be maintained in a safe and efficient state, EAWR requires electrical circuits and equipment to be safe and free from danger. PAT is a recognised way of demonstrating reasonably practicable efforts to discharge the duty. The issue for the OP isn't whether or not to test, it's how often, John
Grizzly  
#19 Posted : 16 December 2009 14:20:08(UTC)
Rank: Forum user
Grizzly

ChrisBurns wrote:
The following link may just answer the question. http://www.pat-testing.info/legal.htm Not sure if it states frequency of testing but there are lots of places to go.
Chris, The text on that website is lifted wholesale from the 2nd edition of the IEE Code of Practice. Very cheeky. A much more extensive explaination can be found in Chapter 3 ('The law') of the 3rd edition of the IEE CoP (http://www.theiet.org/publishing/books/wir-reg/cop.cfm).
ianm69  
#20 Posted : 16 December 2009 14:29:57(UTC)
Rank: Forum user
ianm69

Grand! I stand corrected. PAT tests easy to figure out, you do it or dont - we do. So, if evidence dictates that 6 months is not identifying problems then it can stay at that point. Otherwise he would need to pull it in to earlier tests. I wonder which laws the (courts) would prosecute anyone under then? A side issue then; Fixed electrical tests (yes, the painful one). Most companies I know dont do it. We did and it blew a few systems.
Clairel  
#21 Posted : 16 December 2009 15:30:09(UTC)
Rank: Super forum user
Clairel

Just a point, HSE guidance on maintenance of electrical equipment only refers to duties under the EAW Regs. Not PUWER nor the MHSWR. Please please please remember that PAT is not enough in it's own right. There has to be a range of measures (formal visual inspections and user checks as well) otherwise it's not enough. Also just because one inspector says one thing it doesn't make it 'fact'. So unless you have what they said in writing from them it will hold no legal weight. Even then they will use the argument that the circumstances were somehow different. Can I also clarify that I said Regs are 'woolly' (in my opinion) because they are too broad. For example EAW says that all electrical systems have to be safe at ALL times. That in itself is unachieveable. The guidance is what sets out the standards for what is reasonably practicable etc in achieving that. That's all I was trying to get across..
jwk  
#22 Posted : 16 December 2009 15:46:11(UTC)
Rank: Super forum user
jwk

Afternon Claire, Good points about the need for a complete PPM for electrical appliances and the fact that one Inspector's word is not law. On the point about guidance though Appendix 1 of HSG107 refers explicitly to PUWER & MHSWR as being relevant to the guidance on electrical safety, as they set out general duties, John
Clairel  
#23 Posted : 16 December 2009 16:06:09(UTC)
Rank: Super forum user
Clairel

Yes, I know but paragraph 10 says that the use and maintenance of electrical equipment is contained within EAW. So I guess I've taken that as being the direction to take. Certainly when I was trained internally by the HSE all the emphasis was on EAW. The regs are 'woolly' (lol) enough to make any deficiency successful in court as a breach of EAW.
Metheringham17703  
#24 Posted : 16 December 2009 16:14:11(UTC)
Rank: Forum user
Metheringham17703

Thank you all for your responses, wasn't expecting to get such a response! Interesting to hear everybodies points of view. I still believe that 3 monthly testing is required for equipment used outside on a site. I agree it only provides a snapshot, but think that that snapshot should be taken quite regularly. I also agree that PAT is only part of a range of measures, including visual user checks and formal inspections, which i am introducing along with the PAT testing. Just one final point on the HSE inspectors comments mentioned previously, i believe the HSE take a different view on things after an incident than they do before one. Just an opinion.
paul.skyrme  
#25 Posted : 16 December 2009 19:14:25(UTC)
Rank: Super forum user
paul.skyrme

ianmilne69 wrote:
A side issue then; Fixed electrical tests (yes, the painful one). Most companies I know dont do it. We did and it blew a few systems.
The requirement for fixed electrical tests is “almost” as enshrined in legislation as is PAT. I don't have my copy of the IET, CoP for PAT, BS7671, or GN3 with me at the moment, however they all include a reference to maintenance, inspection & testing in some form to ensure that equipment/systems are safe. As does EAWR, PUWER & MHSWR(? Don’t have this to hand), CDM, HSR25 & HSG107, INDG372, INDG354, L22, L114, some of the EIS series, and I could go on, & a host of other quasi-legal documents apart from the obvious legislation. Remember, fixed electrical installations come under CDM. Ian, did your company undertake the Periodic Inspection yourselves, or did you utilise an external provider? I'm sorry to say that there can be no doubt, the "persons" undertaking the inspection were not competent to do so if damage resulted, FULL STOP. There is no technical reason for damage to be caused during a Periodic Inspection of a fixed electrical installation. To do so is incompetent, end of. Periodic Inspections should NOT be "The Painful One" IF all work is carried out correctly and PIR's are undertaken according to guidance. The "Pain" arrises due to cost cutting and not getting the correct documentation for electrical changes etc. undertaken between PIR's or when electrical installations are undertaken by competent persons. IF all certification is present and all works are correctly undertaken then a PIR should be a painless exercise. Chris has, along with others mentioned visual inspections, well these form part of a PAT regime, as do user checks. It is NOT just about a so called "qualified" person coming alone once in a blue moon and putting stickers on appliances. Coz thats invariably what happens! I have yet to see a full PAT system correctly implemented according to IET guidance by anyone where external contractors are used. Keeping costs to a minimum is just too much to overcome. PAT is seen as a commodity just like buying bread or milk in the supermarket. You go in to buy these at a particular shop because they are cheap, so you browse for more, expecting these to be cheap too. With many companies it is a loss leader or barely trained operatives are utilised who do not fully understand the ramifications of the system hoping that they will be able to generate additional work from the situation. I came across one from a large supposedly reputable national testing co. the other day that failed a kettle on functional test. The item did not even have a fuse fitted. He did not inspect the item, nor check the fuse rating, no other tests, he just plugged into his tester and did a functional on it and failed it! The problem is that there are very few people out there doing these sorts of work that actually UNDERSTAND what they are doing and WHY they are doing it. This is NOT to meet legislation. It is to save lives and prevent injuries by ensuring that the items/systems are safe and correctly maintained. How many companies get an adequate written report from their PAT provider? How many reports contain a reference to the fixed installation? This requirement is contained in the IET CoP. How many persons who demand PAT, buy on price, and actually realise that no matter how good the earth on the portable appliance, extension lead, etc. is, that IF the earthing in the fixed installation is inadequate and a fault occurs where the case of a Class I appliance becomes live it can still KILL, even IF the appliance was PAT tested on that day and passed and is actually still safe and in the same situation as it was. Please refer to my previous comments on extension leads and 4 gang leads etc. Do you check that persons doing your PAT & PIR's have Professional Indemnity insurance? Why, because they are providing an intangible professional opinion on the condition of your appliances/systems. If they are wrong, someone could die and your employer/you could be prosecuted! Regina Vs Octel anyone? (IIRC) I am willing to discuss this further and explain myself and my comments and give background, if anyone wishes, please PM, as I am a little cautious about the public forums. Sorry. Rant over, but these are real issues that I really have seen and continue to day to day and boy does it wind me up! Paul
RayRapp  
#26 Posted : 16 December 2009 19:28:26(UTC)
Rank: Super forum user
RayRapp

'Just one final point on the HSE inspectors comments mentioned previously, i believe the HSE take a different view on things after an incident than they do before one. Just an opinion.' Can't believe you are implying that the HSE are reactive! Sticking with the thread, we PAT cert our electrical items every 6 months. In terms of usefulness probably one of the biggest waste of time and effort in the industry - but there you go. Ray
barnaby  
#27 Posted : 16 December 2009 20:51:07(UTC)
Rank: Guest
Guest

clairel wrote:
For example EAW says that all electrical systems have to be safe at ALL times.
Well, sort of. Isn't it actually "All systems shall at all times be of such construction as to prevent, so far as is reasonably practicable, danger", which is surely achievable?
paul.skyrme  
#28 Posted : 16 December 2009 20:52:54(UTC)
Rank: Super forum user
paul.skyrme

Barnaby wrote:
clairel wrote:
For example EAW says that all electrical systems have to be safe at ALL times.
Well, sort of. Isn't it actually "All systems shall at all times be of such construction as to prevent, so far as is reasonably practicable, danger", which is surely achievable?
Barnaby, That really depends on who works on them and the checks done on them! Paul
paul.skyrme  
#29 Posted : 16 December 2009 22:27:36(UTC)
Rank: Super forum user
paul.skyrme

FWIW, This may over rule my advice earlier with regard to test periods based on condition? http://www.hse.gov.uk/el...ctricequip.htm#condition Paul
paul.skyrme  
#30 Posted : 16 December 2009 22:29:52(UTC)
Rank: Super forum user
paul.skyrme

You could also look at this? http://esc.org.uk/busine...ce-for/construction.html Paul
barnaby  
#31 Posted : 16 December 2009 23:39:26(UTC)
Rank: Guest
Guest

paul.skyrme wrote:
Barnaby wrote:
clairel wrote:
For example EAW says that all electrical systems have to be safe at ALL times.
Well, sort of. Isn't it actually "All systems shall at all times be of such construction as to prevent, so far as is reasonably practicable, danger", which is surely achievable?
Barnaby, That really depends on who works on them and the checks done on them! Paul
Yes, but even if something is only achievable under certain circumstances or with certain people it is still achievable.
toe  
#32 Posted : 16 December 2009 23:56:56(UTC)
Rank: Super forum user
toe

Please do not shoot me down in flames (not that you would) if I have missed something in one of the previous posts, but.... as I read the original post it is asking on guidance for PAT on electrical equipment used on construction sites. On a majority of the sites I have been involved with (not many) only 110V equipment was allowed on site which will only give a belt of 55 Volts if a fault arises. Therefore only the transformers require to be tested and therefore 6 months testing would be sufficient for these. If the site uses 240V equipment then save the money for conducting more frequent testing and convert to 110 Volt systems. REF Section 6 EAWR where it states protection of electrical equipment used in adverse or hazardous environments. IMHO I would not expect that not PAT electrical equipment would be cited in case Law as not complying with the legal requirements because as discussed previously you cannot be prosecuted for not PAT equipment because it is only guidance, therefore not testing is not breaking the law. Also if someone was to be electrocuted or receive an electric shock then a prosecution would come under the EAWR because the equipment gave rise to danger. However if the equipment was PAT this will show that some reasonable steps were taken to reduce the risk of such danger. What I am saying is that I believe PAT can be used as a defence of good practice but not used in the prosecution as not complying as it is only guidance, in the event of an accident happening.
firesafety101  
#33 Posted : 17 December 2009 00:23:58(UTC)
Rank: Super forum user
firesafety101

paul.skyrme wrote:
FWIW, This may over rule my advice earlier with regard to test periods based on condition? http://www.hse.gov.uk/el...ctricequip.htm#condition Paul
Paul. well done and top marks to you, this is something I was looking for earlier but failed to find. Now that I know where it is it will be in my favourites, how sad is that? I will add that anything the HSE have on their web site they look upon as serious stuff. Fail to take note at your peril!
firesafety101  
#34 Posted : 17 December 2009 00:26:58(UTC)
Rank: Super forum user
firesafety101

Toe are you really suggesting that 110 v equipment is not dangerous? If so I will not need to shoot you down in flames, you've done that to yourself.
ianm69  
#35 Posted : 17 December 2009 00:31:40(UTC)
Rank: Forum user
ianm69

True. Lots of answers throughout which gives a mixed impression of who is / is not right. Like the HSE always say, its only provable in court and by then its a bit too late for someone, and the publicity would probably cripple the person/company. What the HSE do say though is; this is the guidance that you dont have to follow. You just have to prove that you have implemented somethin just as good. So, summary. What I gather is that PAT tests are not mandatory but 'integrity' must be proved. And these are only effective when used with other 'mitigations'. But I dont see many doing them or even aware of them despite being mentioned in several regs (equipment must be safe etc). 'Recommeded' electrical tests of fixed systems (the 240v behind the walls) is not mandatory but again, we must ensure the electrical systems are safe. We have not records of any equipment failing due to electrical faults, no system overloads, nothing and therefore no indication that the fixed systems are unsafe. Therefore, where would we stand. And fixed electrical testing (5 years for business, 10 years recommendedfor domestic houses) is also rarely done. Okay, I'll check again for an answer later tomorrow. Thanks
ianm69  
#36 Posted : 17 December 2009 00:33:06(UTC)
Rank: Forum user
ianm69

Oh and metheringham...hope you got the answer you needed.
firesafety101  
#37 Posted : 17 December 2009 10:23:48(UTC)
Rank: Super forum user
firesafety101

ianm69 wrote:
True. Lots of answers throughout which gives a mixed impression of who is / is not right. Like the HSE always say, its only provable in court and by then its a bit too late for someone, and the publicity would probably cripple the person/company. What the HSE do say though is; this is the guidance that you dont have to follow. You just have to prove that you have implemented somethin just as good. So, summary. What I gather is that PAT tests are not mandatory but 'integrity' must be proved. And these are only effective when used with other 'mitigations'. But I dont see many doing them or even aware of them despite being mentioned in several regs (equipment must be safe etc). 'Recommeded' electrical tests of fixed systems (the 240v behind the walls) is not mandatory but again, we must ensure the electrical systems are safe. We have not records of any equipment failing due to electrical faults, no system overloads, nothing and therefore no indication that the fixed systems are unsafe. Therefore, where would we stand. And fixed electrical testing (5 years for business, 10 years recommendedfor domestic houses) is also rarely done. Okay, I'll check again for an answer later tomorrow. Thanks
Ian, your second paragraph here is not quite right? The HSE comment at the front of their ACOPs usually goes on to say something like, "but if you do follow this guidance you are usually doing enough" or words to that effect. That, to me, says that if I do follow the guidance I should be OK?
toe  
#38 Posted : 18 December 2009 00:21:53(UTC)
Rank: Super forum user
toe

Chris, Please point out where I have stated that 110V is not dangerous?
firesafety101  
#39 Posted : 18 December 2009 00:59:00(UTC)
Rank: Super forum user
firesafety101

Toe wrote:
Chris, Please point out where I have stated that 110V is not dangerous?
Toe, you don't actually say it's not dengerous but it's the way you say "On a majority of the sites I have been involved with (not many) only 110V equipment was allowed on site which will only give a belt of 55 Volts if a fault arises. Therefore only the transformers require to be tested and therefore 6 months testing would be sufficient for these." It just appears a bit casual as if you think the hazad/risk is very small if non existant. 110 v tools on construction site should be tested 3 monthly, in my opinion, and also according to the opinion of the HSE inspector that visited a site managed by one of my "ex" clients.
ahoskins  
#40 Posted : 18 December 2009 11:44:18(UTC)
Rank: Super forum user
ahoskins

Hadn't seen the table linked to by Paul before, but have seen similar ones. However - it is rather confusing to my mind (and I haven't had a Christmas drink yet today) as it purports to list test requirements by business, but goes on to list types of equipment... And what of user checks in a light industrial setting? 'Yes' is not particularly helpul here is it? Also, cables plugs and extension leads have their own entry in the table, apparently irrespective of the industry in which they are being used! Is it me??? A