#1 Posted : 03 March 2010 08:33:40(UTC)
Rank: New forum user
steve1973

On a safety tour of a vessel I'm working on I discovered someone doing spark generating hot work in a room where co2 cylinders for fire fighting are stored. The sparks were going directly onto the cylinders at the shoulder of the cylinder. I stopped the job and tried to explain my concerns (language barrier) but I did not receive a positive response.

I would consider this to be a very dangerous activity. Am I over reacting?
RayRapp  
#2 Posted : 03 March 2010 09:47:57(UTC)
Rank: Super forum user
RayRapp

Steve

Whilst I'm not a fire expert I suspect you are going a bit OTT. The CO2 extinguishers are designed to withstand certain types of external hazards and indeed are used in conjunction with 'hot works'. I am not aware of any guidance which dictates that CO2 extinguishers should be isolated from hot works or minimum distances, they are not deemed explosive to my best knowledge. Happy to be corrected by someone who knows better.
Steve Sedgwick  
#3 Posted : 03 March 2010 09:58:56(UTC)
Rank: Super forum user
Steve Sedgwick

I agree with ray. But my main concern would be to ensure that the CO2 system was isolated / immobilised to prevent accidental release into the room which would have the potential to be fatal.

Steve
steve1973  
#4 Posted : 03 March 2010 10:04:29(UTC)
Rank: New forum user
steve1973

Well I was unsure in all honesty so I did a bit of browsing and found this:

http://www.airproducts.c...fb0c2/0/safetygram18.pdf

on page 5 of 6 point 9.

the cylinders are not connected to the system but i'm unsusre whther the system is isolated
ianm69  
#5 Posted : 03 March 2010 10:32:05(UTC)
Rank: Forum user
ianm69

Thats actually a very good sheet on CO2. I'm keeping it for use later!
Firesafetybod  
#6 Posted : 03 March 2010 11:40:51(UTC)
Rank: Forum user
Firesafetybod

Steve
Here,s an MDS Date sheet,u may find useful.

http://www.energas.co.uk/downloads/009.pdf

See Storage (item 3)
Squash  
#7 Posted : 03 March 2010 12:30:17(UTC)
Rank: Forum user
Squash

It is not clear to me whether we are talking about some (small) self contained portable CO2 fire extinguishers for use against small fires, or potentially larger cylinders for connection to or already connected to a fire system. Without the full picture it is hard to see a safety issue of the sparks ( although poor practice)

My immediate concern would be whether the cylinders and work activity turn the vessel into a confined space (potential for loss of consciousness due to lack of oxygen).
colinreeves  
#8 Posted : 03 March 2010 13:58:05(UTC)
Rank: Super forum user
colinreeves

Steve sedgwick wrote:
I agree with ray. But my main concern would be to ensure that the CO2 system was isolated / immobilised to prevent accidental release into the room which would have the potential to be fatal.

Steve


If the original poster meant by "vessel" a ship, then the CO2 would likley be the main fire extinguishing system for machinery spaces. The design is not to release CO2 into the space where the cylinders are but to be piped to the appropriate space. The only problem with CO2 within the space is if there is a fault in the system - a person should be able to enter the CO2 room at all times.

However, I agree that welding sparks onto the upper end of the cylinders is not good - both from the effect on the cylinders themselves, but primarily on the valves and actuating linkages. However a fiireproof blanket would have been sufficient protection.

Colin
firesafety101  
#9 Posted : 03 March 2010 19:08:41(UTC)
Rank: Super forum user
firesafety101

Should not be a problem if covered, especially the valve groups and any hoses.

Recommend hot work permit system, permit to be requested prior to starting hot work, this should resolve any issues.
Steve Sedgwick  
#10 Posted : 03 March 2010 19:58:06(UTC)
Rank: Super forum user
Steve Sedgwick

Colin
"a person should be able to enter the CO2 room at all times"
I may have mis-understood your meaning here. So for clarification for the readers:-

Automatic CO2 Fire Systems are designed for non-manned areas ie areas where people only go infrequently. Before anyone enters an area with such a system then that system must securly isolated and immobilised so that it cannot be activated while persons are in the room.

Where there are manned areas that requires a gaseous extinguishing system "Control Rooms or Pulpits" then the gas used is not CO2 but a safer substitute such as FM200 or Inergen

Steve
bleve  
#11 Posted : 03 March 2010 20:20:11(UTC)
Rank: Super forum user
bleve

Steve 1973 has stated the CO2 cylinders were not connected, provided a hot work permit was in place and other combustible materials were not in the vicinity of the CO2, then I would suggest that it was an over reaction.

With regard to FM 200 and Inergen being a safer alternative to CO2 ????????

They are also both asphyxiants!!!!
Steve Sedgwick  
#12 Posted : 04 March 2010 08:48:50(UTC)
Rank: Super forum user
Steve Sedgwick

bleve
I agree that they are asphyxiants at high concentrations but there is no doubt that they are a much safer substitute to CO2.

The Inergen and FM 200 are designed to release their gas into the room to produce a 12 = 15% concentration which will suppress any fire but not have any significant effect to those who may have been in there at the time

The concentration at which CO2 extinguishs fire is life threatening

Steve
firesafety101  
#13 Posted : 04 March 2010 09:23:56(UTC)
Rank: Super forum user
firesafety101

Many many many many years ago the Liverpool Fire Brigade Chief Fire Officer entered a Russian ship on fire at the Liverpool docks. A while after he came of the ship he collapsed with carbon monoxide poisoning - and recovered.

I wonder if anyone has died as a result of total flooding a compartment with CO2? Or whatever is used nowadays.

Jane Blunt  
#14 Posted : 04 March 2010 10:28:55(UTC)
Rank: Super forum user
Jane Blunt

The point that Steve is making is that carbon dioxide is toxic.

The vital statistics are:
Exposure limit 0.5%
Level at which it is evidently toxic, approx 4%
Level at which it can be lethal, approx 7%

jimbo the jet set  
#15 Posted : 04 March 2010 11:01:41(UTC)
Rank: New forum user
jimbo the jet set

Hi there, why not cover the area that is to be welded in a Habitat this would then contain the sparks. Make sure that the area is well ventilated. Your task should have been well risk assessed before starting the task. There should also be a someone there to act as a fire watcher.
jimbo the jet set  
#16 Posted : 04 March 2010 11:06:00(UTC)
Rank: New forum user
jimbo the jet set

You should be congratulated on STOPPING THE JOB. It will allow the task to be re assesed.
bleve  
#17 Posted : 04 March 2010 11:18:32(UTC)
Rank: Super forum user
bleve

Steve
I disagree with the view that Inergen & FM 200 (HFC 227 ea) are a MUCH safer substitute for Co2.
I will however agree that HFC 227 ea is a more efficient fire suppressant.

Ultimately, there are hazards associated with all three agents viz Cardiac sensitization in the case of FM 200 and Asphyxiation in respect of CO2 and Inergen. The overall risk is dependent on the duration of exposure and concentration of suppressant within an occupied space.

Provided that an effective alarm/warning of activation/discharge is available and that suitable means of emergency egress is provided taking into account the volume of the room, discharge rate and NOEL value, then the three suppressants present a similar degree of hazard.

In the case of Inergen, inert gas extinguishing data from VDS, Cologne, Germany, provides evidence that a concentration of between 28-43.8% is required for effective suppression of various fuels when compared to 16-28% CO2.

When considering FM 200, the concentration required for suppression is largely fuel dependant. In addition, acute exposure limits derived from (PBPK) Physiologically based pharmacokinetic modelling for HFC 227 ea, show that exposure duration at 12% concentration should not exceed 29.4 seconds.

A safer alternative to the above would be a fine water mist suppression system.

Regards

Bleve
colinreeves  
#18 Posted : 04 March 2010 14:02:14(UTC)
Rank: Super forum user
colinreeves

Steve

On board ships (totally differing regulations) the traditional and very common method of fire-fighting in machinery spaces is by CO2. This is NOT an automatic system but is manuially activated from outside the space. However, the CO2 storage room must always be accessable and always is, so long as there is no fault.

Therefore, whilst your comments may be true for shore-side automated systems, the original post was about ships, a different system.

In fact, apart from water fog systems as a secondary method, CO2 is the norm on manned machinery spaces - the old halon systems having now been replaced, most commonly by CO2.
Steve Sedgwick  
#19 Posted : 05 March 2010 09:46:02(UTC)
Rank: Super forum user
Steve Sedgwick

Bleve
in my last post on this I wrote "much" not "MUCH". I am not able to quantify how "mUcH". The point I make is that there are safer substitutes to CO2 and I accept that inert gas and halocarbon systems can kill too, but the risks between the 2 are not comparable.

You state “Physiologically based pharmacokinetic modelling for HFC 227 ea, show that exposure duration at 12% concentration should not exceed 29.4 seconds.”
Anyone one in an environment with 12% CO2 would be dead within a couple of seconds, this is far more serious than “12 % HFC 227 should not exceed 29.4 seconds”

A report on these systems was done in 2003 that I would point the readers of this post to "REVIEW OF THE USE OF CARBON DIOXIDE TOTAL FLOODING FIRE EXTINGUISHING SYSTEMS" http://www.epa.gov/ozone.../fire/co2/co2report2.pdf

I realise that these CO2 systems are predominent in the Marine industry and that they are Manually Operated which are much safer than the automatically that can be accidentally discharged.
Steve
bleve  
#20 Posted : 05 March 2010 10:00:38(UTC)
Rank: Super forum user
bleve

Anyone one in an environment with 12% CO2 would be dead within a couple of seconds

Bit of an exageration there Steve. 12% concentration @ > 1 minute results in dizziness and possible unconciousness.


jay  
#21 Posted : 05 March 2010 11:15:18(UTC)
Rank: Super forum user
jay

steve1973 wrote:
Well I was unsure in all honesty so I did a bit of browsing and found this:

http://www.airproducts.c...fb0c2/0/safetygram18.pdf

on page 5 of 6 point 9.

the cylinders are not connected to the system but i'm unsusre whther the system is isolated



The original question was regarding sparks from a hot work activity impinging upon the shoulder of CO2 cylinders "STORED" in a vessel without any information regarding the risk assessment carried out and any permit to work system --so we are all speculating! Steve1973 has informed that the cylinders are not connected. Therefore, the cylinders ( and also other equipment etc) can be protected from sparks by means of screens /fire blankets!

The question to ask would have been does this type of work come inder
jay  
#22 Posted : 05 March 2010 11:17:42(UTC)
Rank: Super forum user
jay

My understanding is that in context of classification & MSDS information, CO2 is not toxic, but an asphyxiant.

Refer to:-

https://apdirect.airprod...playPDF.aspx?docid=68725
Steve Sedgwick  
#23 Posted : 05 March 2010 18:22:02(UTC)
Rank: Super forum user
Steve Sedgwick

Jay
here this is a different MSDS for CO2 gas that mentions the toxic effects of CO2
http://www.energas.co.uk/downloads/009.pdf
This is the link I gave above to a study that was was made into the toxic effects of CO2 http://www.epa.gov/ozone.../fire/co2/co2report2.pdf
Steve
leadbelly  
#24 Posted : 05 March 2010 20:07:59(UTC)
Rank: Super forum user
leadbelly

But Steve, the Energas information states that it is non-toxic. Toxicity implies to me that a substance is poisonous. Carbon dioxide is not poisonous; it kills by asphyxiation.