I am interested in the opinions on the following:
A door set is located at the base of a stairwell. The door set comprises of hardwood framed double leaf doors, with 6mm polished georgian wired glazing positioned at the upper and lower area of the doors. The frame is some 50mm thick, with approx 250mm timber depth surrounding the glazing panels.
The frame surrounding the doors is provided with 2 x 10mm intumescent seals, while the doors are provided with a brush smoke strip between the door mating faces, a gap of 3mm is present at the top of both doors, while a gap of 2mm is present between the door mating faces.
The doors are hung using 3 x 100mm steel hinges per door and a door closer is present at both leaves. The hinges intersect one of the two intumescent seals.
The door frame is surrounded by the same georgian wired glass in the form of side and top panels.
No visible fire door cert or marking is present.
Discuss.
|
|
|
|
Rank: Forum user
|
Sounds like a lovely door.
Do you think I could get one for my living room?
|
|
|
|
Rank: Super forum user
|
Fantastic input there Alex, bet you are mustard when it comes to FRA
|
|
|
|
Rank: Super forum user
|
My original post was made on the back of a critical review of a number of FRA's made by what should be credible organisations. In particular, I have recently carried out a scope of work where I ahve been asked to provide a second opinion/appraise the findings of a FRA.
I have not seen any evidence thus far, that individuals carrying out FRA take into account the impact on the result of the FRA due to defects associated with fire doors.
|
|
|
|
Rank: Super forum user
|
Alex, I see you are a member of the Fire Risk Management Group.
Based on your reply, why dont you answer my question and calculate the leakage of ambient smoke through labyrinthian gaps between fire/smoke door sets and frames and enlighten us as to how you incorporate this information into your fire risk assessments.
Similarly, perhaps you could expand on your comments and provide us with your philosophy concerning radiant heat flux through georgian wired glazing and the calculated effect and failure rate on the glazing beading.
Based on your response, clearly we all have a lot to learn from your wisdom.
|
|
|
|
Rank: Super forum user
|
|
|
|
|
Rank: Super forum user
|
Bleve - can you confirm that this door is supposed to be acting as a fire/smoke door on an escape route in this particular situation?
Where exactly in the building is the stairwell (between which floors) and is it the only means of escape? What type of building is this?
I have also come across the "not marked, rated, or documented" fire door and realising that it's not practical to condemn just on this basis, have been faced with the "how to classify the adequacy of the door" question. I sympathise with the problem!
|
|
|
|
Rank: Super forum user
|
Heather, Unfortunately, although it may not be practical to condemn such doors, it is not possible to demonstrate to a client that such a door is capable of fulfilling its intended function of fire resistance, integrity and smoke control.
In the context of my posting, I have had to offer a second opinion and condemn 200 plus double leaf doors based on the calculated level of heat flux through the gwg and calculated transmision of ambiant smoke in excess of 3m^3/M/hr.
|
|
|
|
Rank: Super forum user
|
I see your dilemma! Obviously I haven't seen the doors but your description ticks many of the right boxes for a 30 min fire door - correct hinges, fairly small gaps, seals in place, self-closers, etc, etc. However without either door markings (surprising how many people don't know about those or where to find them!) or documentary evidence of the provenance of the doorsets then it is very difficult to give any guarantee of performance in a fire.
Is it practical for you to have a doorset removed and actually tested? Replacement of 200 sets is going to cost a few bob!
|
|
|
|
Rank: Super forum user
|
It will cost a few bob, that why I have recomended full fire test of a sample door set.
My main area of interest is where this has been overlooked by others offering FRA
|
|
|
|
Rank: Super forum user
|
Of course I could flog a few to Alex for his front room LOL
|
|
|
|
Rank: Super forum user
|
of course where the glazing exceeds 50% of door area and 0.65 m^2 unless glazing has insulative properties it will fail.
As I have stated, am interested where this has been captured by the great and the good of FRA.
To be honest would drive anappliance through the majority of FRA that I have seen.
I cannot wait until these are examoned in a court of law
|
|
|
|
Rank: Super forum user
|
Alex Whats Scots Gaelic for langer?
|
|
|
|
Rank: New forum user
|
The fire risk associated with the door will need to be considered as part of the buildings assessment - i.e what is the ocupancy, what fire detection is present, what is the level of management available, where is the door located, waht is the fire load in the area it protects and how important it is in preventing smoke and heat into the area it closes does it require to fulfil a com[artment pretection role above 60 mins etc. - this door would appear to meet a E20 or even E 30 standard- if in doubt put a class O panel on either side of and ensure the frame is tight to with in 3mm of door
|
|
|
|
Rank: Super forum user
|
Hi BLEVE - you certainly ask a good question, I also saw your topic the other day re all those doors you condemned.
Is the door set meant to be Fire Resisting - have you checked the original requirement, an original drawing may help?
This door you describe certainly sounds like a fire door especially with the measurements to provide but are there any relevant BS EN markings on the associated equipment? You do not mention if there are any.
In my experience if something looks good it usually is good, perhaps this is an exception to that rule?
I have a few questions for you:
How old are the premises? More than a good few years and it may have suited older Regs?
Was this door set installed as a fire door according to the build requirements? If it should have been BS EN etc. the person responsible for the premises may have a good claim against the installer?
Is this a sleeping risk? If so then you are correct to be concerned, if not and it looks like the door set will hold long enough for an evacuation to take place then not so urgent, otherwise it looks like you need it testing/replacing.
There begs a question - those of us that do fire risk assessment according to the fsrro guide may not be as particular as you, but when we do discover something like this how much power do we have to get things sorted in accordance with requirements?
In my situation I would write a report and issue it to the Client, as far as I am concerned as long as I issue the "Main findings" to the RP who employed me and discuss the recommendations with him/her that's it until the review date.
|
|
|
|
Rank: Super forum user
|
Chris, Door set is installed at Residential premises.
Although the doors were installed many years ago and would have been acceptable at that time, in the context of modern day FRA, it is impossible to comply with recent performance requirements.
Consider that the polished Georgian wired glazing exceeds max permitted area of non insulating glass, as a result the fire integrity of the beading holding the glass in place may also be compromised due to thermal flux likely to result in the non-piloted ignition of the beading.
My biggest concern, relates to the apparent lack of understanding or knowledge from many fire risk assessors relating to the function of intumescent seals or cold smoke seals. More often than not, it is a case that seals are in place and move on. Rarely, is consideration given to the leakage value being exceeded by even a 1mm gap.
I am of the opinion that many individuals are carrying out FRA without realising that they don’t know what they don’t know.
|
|
|
|
Rank: Super forum user
|
You just said what I say - you don't know what you don't know!
So is it sleeping accommodation? If yes you should seek an improvement even though it is an old door set. Life safety comes before cost etc.
Regarding the lack of knowledge and understanding it takes a good quality training course to input the knowledge but those courses are not mandatory so anyone can set up as a fire risk assessor, all they need is a copy of the guidance document.
A colleague of mine recently attended a one day fire risk assessment course at the fire service college, he went away after being told he can now carry out fire risk assessments at small premises.
How does someone like him get experience and understanding, he thinks he has the knowledge now.
|
|
|
|
Rank: Super forum user
|
BLEVE Whilst what you say may be correct the type of questions you have asked with regards to the integraty of a fire door can only be determined by having at least two of the door sets tested in a fire situation to the relevent British Standard, one as is and the other with any necessart inprovements required. One thing quite often over looked with fire doors is the standard of installation, does this meet the relevent requirements and BS. I would recomend any one who carries out FRA attend a one day seminair given by Chilten Fire that shows a live fire door test on one fitted correctly and the other with minor fitting faults - a 60 minute fire rated door set lasted all of 15 minutes. There are so many ifs and buts with regard to FRA's carried out in older buildings and the standards of some FRA's can be somewhat dubious. Lets not critisise each other with sarcastic comments but make constructive recomendations. As an ex Firefighter I have seen both good and bad installation and the consequences of the bad. So as Safety Professionals, involved in Fire Safety lets strive to make this world a safer place for every body - Lifes too short to be bitchy
|
|
|
|
Rank: Super forum user
|
No one is being bitchy, In my experience and professional opinion the vast majority of FRAs are not worth the paper they are written on.
I have seen too many FRA's written by people who have not got a clue, mostly they follow a check list approach PAS 79 etc without considering what is actualy present within the building they are assesing, hence they do not know what they dont know.
Unfortunately, these individuals will avoid prosecution as they are not defined as the RP more is the pity.
There are people on this forum who think that they can carry out a FRA based on
Fire service history
participation on a FRA couse of 1-5 days
NONSENSE
|
|
|
|
Rank: Forum user
|
Bleve by name----bleve by nature!
|
|
|
|
Rank: Super forum user
|
I'm struggling to see the question here. The OP ends with an invitation to discuss and then appears to be irritated when somebody makes a flippant contribution.
|
|
|
|
Rank: Super forum user
|
It sounds to me by the tone of this whole thread that the OP had his own agenda from the word go. That agenda being that in his opinion most people who conduct FRAs are not competent to do so or maybe I have misunderstood him. Maybe if he had been a bit clearer about what he wanted from the thread instead of just writing "discuss" like some sort of frustrated exam invigilator he may have had a more serious reply. I'm with Alex, it does sound like a lovely door. My advice is be a bit more up front about what you want, instead of laying a trap and waiting to pounce on anyone who wanders near or doesn't meet your obviously superior standards
|
|
|
|
Rank: Super forum user
|
By the way, I have conducted FRAs for 3 major employers with large premises over the past 5 years and I have never gone to the lengths of calculating smoke leakage etc. All of these FRAs have been audited on several occasions by the Lancashire Fire Service without any concerns being raised at any time as to the quality of the FRAs.
|
|
|
|
Rank: Moderator
|
Please could I remind you all of the forum rules, an extract of which is copied below, which are designed to keep proceedings relatively friendly and welcoming to others:
2. You mustn’t antagonise other users or post any information that could be considered defamatory, obscene, abusive, offensive, inflammatory, unlawful or creates a risk to a person’s safety or health.
3. You mustn’t indulge in bullying, aggressive, discriminatory or nuisance behaviour. Please be respectful towards other guests, IOSH members, moderators and IOSH staff. Please remember, our forums are used by guests who might not have a background in occupational safety and health. Inappropriate postings made towards guests aren’t tolerated. If you’re an IOSH member, bear in mind the Code of Conduct, in particular:
"Members shall not behave in a way which may be considered inappropriate to other members or staff of the Institution." (Paragraph 10)
Please also try not to stray too much from the original topic Jane
|
|
|
|
Rank: Super forum user
|
Hi bleve, it sure looks like you've upset someone!
I don't think your question is about integrity of fire doors - more about integrity of the fire risk assessor?
We agree that you don't know what you don't know but we also don't remember what we used to know but have now forgotten.
The guide to fire risk assessment does not require a comprehensive knowledge of smoke leakage etc. it does however allow us to assume that if a smoke seal in in place that it will work and stop the required quantity of smoke. Only a well read, experienced and qualified fire engineer would be able to recognise potential failings in such matters.
I do not rely on what I have learned in the past and do take certain reference documents with me when carrying out fra's, and I do refer to those docs when coming across something out of the ordinary, that helps me to "know what I don't" and to "remember what I have forgotten".
The spirit of the regs is in the guidance book and it allows a certain quality of assessment that is perhaps not up to your own personal standard.
|
|
|
|
Rank: Super forum user
|
Chris I do not see it that guidance accepts or condones a lesser standard of FRA.Are we saying that because a smoke seal is in place that it is effective? these are subject to errors of fitting and wear! How many people have not recognised that a gap of circa 0.75 - 1mm may result in the limit of smoke transmission being exceeded. Similarly, how many people have looked at a fire door c/w gwg and thought nothing of an absence of insulative properties, heat flux and likely modes of failure.
By the same token, how many "Fire Risk Assessors" take cogniscence of fire load, rate of burning, smoke evolution, time to restriction of visibility, location and positioning of signage t/ic visibility etc.
I agree with the many training organisations when after 1-5 days training, they advise individuals to stick to the FRA of simple and low risk premises.
To others that say they have never taken the time or trouble of calculating such matters, or that A member of the fire survace has carried out a vague review of your FRA, that does not equate to the FRA being suitable or sufficient, only the courts can decide on that matter.
Any individual that carries out any risk assessment and ignores or misses an aspect later considered as contributing to a loss, then the RA will be judged as being deficient. To those Fire Risk Assessors out there, reflect where you have not given due consideration to matters outside your checklists and maybe start to worry. Although, to be fare the legislation provides a nice little get out of jail clause and places any responsibility on the shoulders of the responsible person.
|
|
|
|
Rank: Super forum user
|
By the way, I have no difficulty in causing upset to anyone who thinks they are capable of carrying out an fra. Its a pity that there is too much moderation on this site as I would have liked to have seen the removed responses. To those in question, feel free to PM me.
|
|
|
|
Rank: Super forum user
|
PL53, I have spent 20 plus years carrying out FRA for thousands of organisations, so what.
|
|
|
|
Rank: Forum user
|
Talk about FRA - looks like I lit a touchpaper!
|
|
|
|
Rank: Forum user
|
I guess we shouldn't raise issues such as assessing linings, fire resistant abilities of compartment walls, inspecting voids.
|
|
|
|
Rank: Super forum user
|
Bleve, you clearly have a high level of technical competence re fire safety and I have no wish to challenge that. What I would like to ask you is where do you see the line between design risk assessment for fire safety systems and general fire risk assessment? Indeed do you see them as the same thing or not?
The general guidance and codes are clearly written as if they are different aspects and thus allow a more general approach. I suspect this is based on an assumption that building regs approval and other design controls should ensure a safe design for fire precautions leaving the end user to rely upon that design in their risk assessment. Is there a place for pragmatism here or not? As an example, I doubt that many of those who complete day to day workplace risk assessment would have a detailed engineering knowledge of machinery safety and yet can produce s&s assessments through relying upon the safe design and subsequent mtce and ops provided by the suppliers. Is there a parallel in FRA?
p48
|
|
|
|
Rank: Super forum user
|
What I would like to ask you is where do you see the line between design risk assessment for fire safety systems and general fire risk assessment? Indeed do you see them as the same thing or not?
Pete, A lot of my work involves design r/a & documentation of fire safety strategy, where it is necessary to carry out detailed evaluation and r/a by calculation and modelling. I am a bit confused with the use of the term general fire risk assessment and more so by the interpretation that “the general guidance and codes are clearly written as if they are different aspects and thus allow a more general approach”
To my mind the RR (Fire Safety) Order is very clear:
Risk assessment 9. —(1) The responsible person must make a suitable and sufficient assessment of the risks to which relevant persons are exposed for the purpose of identifying the general fire precautions he needs to take.
Meaning of "general fire precautions" 4. —(1) In this Order "general fire precautions" in relation to premises means—
(a) measures to reduce the risk of fire on the premises and the risk of the spread of fire on the premises;
(b) measures in relation to the means of escape from the premises;
(c) measures for securing that, at all material times, the means of escape can be safely and effectively used;
(d) measures in relation to the means for fighting fires on the premises;
(e) measures in relation to the means for detecting fire on the premises and giving warning in case of fire on the premises; and
(f) measures in relation to the arrangements for action to be taken in the event of fire on the premises, including—
(i) measures relating to the instruction and training of employees; and
(ii) measures to mitigate the effects of the fire.
I suspect this is based on an assumption that building regs approval and other design controls should ensure a safe design for fire precautions leaving the end user to rely upon that design in their risk assessment.
The difficulty in this is that design can be flawed, installation may not have been up to the requirements of the design, passive and active precautions may have been modified or not maintained, etc. Many fire precautions have a finite working life.
As an example, I doubt that many of those who complete day to day workplace risk assessment would have a detailed engineering knowledge of machinery safety and yet can produce s&s assessments through relying upon the safe design and subsequent mtce and ops provided by the suppliers.
How many machinery risk assessments have we seen that are not S&S, indeed as you know well very few would accept that CE marking equates to safe design and I would suggest that carrying out a machinery based risk assessment to the requirements of Directive specific EHSR’s or PUWER is again a specialist area.
Ultimately, in order to complete a S&S FRA, it must be necessary to take into account the fire integrity, insulation, fire loading, fire spread, occupancy, smoke build up/obscuration, evacuation time based on these factors. Only in this context can a FRA be viewed as being S&S.
Let’s assume we carry out a FRA, consider a situation whereby fire glazing installed on an escape route in a premises constructed some 30 years ago. The risk assessor examines the door and records that a GWG fire door is provided. There is no possible way that the risk assessor can guarantee that the door in question actually provides 30 minutes integrity and in actual fact would have no insulating properties. Similarly, Joe risk assessor looks at a cold smoke seal and 1 mm gap between door and frame (or possibly not). Does he take notice of the impact of cold smoke spread and possible impact on the escape route?
|
|
|
|
Rank: Super forum user
|
Bleve Your original question on existing fire doors seems to have gone by the way. Several people, including yourself suggested you have a door set(s) tested to BS 476. You seem to think that most FRA are not suitable and sufficient, may be true. You have managed to upset quite a few professional colleagues with your opinion, you are entitled to your opinions so are other people. You mention Design Risk Assessments for Fire safety, what is required under the current Building Regulations Part B Documents is for the Designer to provide a Suitable Fire Stratergy for the building with all relevent information to enable the end user (Client or tennant) to produce the FRA. Under CDM Regulations the Designer is required to Design out hazards not produce a risk assessment, this goes for the fire statergy as well, design out the hazard and where not possible ensure the hazard is recorded and controlable by various means. I am open to new ideas and bow to expert knowledge when it is given in a professional way.
|
|
|
|
Rank: Super forum user
|
Bleve, thanks for the reply. I do empathise with your technical standpoint even though I cannot comment upon it directly as I am not competent to do so. I do have a remaining doubt though. If I read the various guidance documents (from communities.gov.uk) as a non-fire safety specialist, I find references such as: "This guide is for all employers, managers, occupiers and owners of factories and warehouses"...."helps you to carry out a fire risk assessment and identify the general fire precautions you need to have in place."
It also clearly states "Where the building has been recently constructed or significantly altered, the fire detection and warning arrangements, escape routes and facilities for the fire and rescue service should have been designed, constructed and installed in accordance with current building regulations. In such cases, it is likely that these measures will be satisfactory as long as they are being properly maintained and no significant increase in risk has been introduced."
Later in the guide it has under recommended monthly checks "Check that all fire doors are in good working order and closing correctly and that the frames and seals are intact."
So, from where I sit, I can complete a general fire risk assessment which follows the guidance and includes checks on detailed arrangements for things like monthly checks on fire doors. If in place, completed by staff trained in what to check for, recorded etc then OK. If not in place I then recommend we might need to talk to someone like you. Is that perfect? Maybe not in some situations but it is practicable for the vast majority and I might be persuaded to argue such in a court if required--- but, of course, hope I never have to!
|
|
|
|
Rank: Super forum user
|
MEDen, it may be me that introduced the term "design risk assessment" into this thread. I meant that part of the process where the hazards arising from the project are assessed and appropriate design controls identified. Which is I think what you are also referring to in designers duties? Sorry if I confused anything
p48
|
|
|
|
Rank: Super forum user
|
Pete
As you have noticed:
"Where the building has been recently constructed or significantly altered, the fire detection and warning arrangements, escape routes and facilities for the fire and rescue service SHOULD have been designed, constructed and installed in accordance with current building regulations. In such cases, it is LIKELY that these measures will be satisfactory as long as they are being properly maintained and no significant increase in risk has been introduced."
My concern is that within the numerous FRA that I have examined, these issues are subject to nothing more than a cursery examination (mainly due to lack of knowledge).
The guidance also states
More complex premises will probably need to be assessed by a person who has comprehensive training or experience in fire risk assessment.
In addition, the guidance states that it is not to be applied to new buildings or design and is not to be applied to buildings not recently constructed.
I do not have a problem with any person carrying out a FRA but I have now seen too many examples where those carrying out this work are jeopardising the life safety of building occupants due to lack of knowledger and a failure to recognise limitations.
If that upsets people, then so be but at this stage we are about due for another fire tragedy and the current legislation or lack thereof will bring this about sooner than later.
|
|
|
|
Rank: Super forum user
|
Bleve, it is usually when the language gets emotive that people get upset, not the difference of opinion. OK on the "shopfloor" but tends to get hammered on here in virtual reality.
Good luck with the challenge and thanks for the time in debating this. p48
|
|
|
|
Rank: Guest
|
Goodness Me! I leave this forum for a week or two and then come back to this thread.
Bleve you will know that I am well and truly in your camp although I think you have been a bit more forceful with what you have said than I have been. I am not sure if that tragedy has already happened with the Penhallow hotel fire. I understand that the fire risk assessors during the inquiry were advised to not say anything for fear of incriminating themselves. Whether this will lead to a prosecution or not I do not know.
I, like Bleve, have come across many fra's where bad advice is given. For example one fire risk assessor advised a landlord to insert intumescent strips on all fire doors on the main stairwell without taking into account that the stair was pressurised.
Other fire risk assessors seem to accept that a fire alarm has had a 25% quarterly test without knowing which 25% were tested so consequently on the next 25% test they do not know if was the same as the last 25% or a new 25%.
As for the original question, replacing 200 fire doors because there is no way of proving the existing doors is a big call. Before doing so I would look at the other measures in place, for example is there an L1 system where only an L3 system would normally have been required? is there a sprinkler system in place? are there alternative means of escape available and if so what are the travel distances involved? If there are no compensating measures and, as you have said, it is a sleeping risk, then particularly with Lakanal House in mind you are probably left with no alternative.
|
|
|
|
Rank: Super forum user
|
|
|
|
|
Rank: Super forum user
|
I've made a couple of points in this topic and do not wish to take sides as I can say I agree with some of the points that both sides are making.
I do fire risk assessments, as far as I am concerned in accordance with the guidance document and do not see the need to go further, although I can understand people with deeper knowledge will apply that knowledge and sometimes be unable to see the "other side's" point of view.
The Fire Risk Management journal May 2010 has a number of articles relating to fire risk assessment and among them are the inconsistent enforcement by fire brigades, the fines/prosecutions of all sizes of businesses, an article about B&B owners not realising the high cost of fire safety measures to comply with the rrfso and small domestic premises used as holiday cottages falling within the scope. There are also concerns from fire brigades about identifying or not being able to identify the "responsible person".
There can be no doubt that debates like this one here will go on and on for a long time to come.
|
|
|
|
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.