In a primary/junior school having a refurb and creating new music booths off the library, with a degree of sound proofing, what would be the recommendations for fire alarm sounders.
|
|
|
|
Rank: Forum user
|
I would consult the fire brigade for advice and conduct a relevant fire risk assesment. There will probably be a minimum decibel requirement above the highest expected background noise level for the sounders. Also may need to consider visible indicators as well as audible.
|
|
|
|
Rank: Super forum user
|
Alan, that's exactly what I thought, but is there a set standard? This is a room that will be occupied by children up to 11 years of age.
|
|
|
|
Rank: Forum user
|
I wouldimagine there is a set standard yes but again that would probably relate to the anticipated background noise levels so not simple to specify without knowing that information. A secondary thought on this one -- surely these issues would have been considered and resolved by the architect / designer involved in the refurb??
|
|
|
|
Rank: Forum user
|
65 dB(A) or 5 dB(A) above any sound level likely to persist for longer than 30 seconds.
75 dB(A) at a bed head of sleeping risk premises
|
|
|
|
Rank: Super forum user
|
Alan, it is the architect that has specified the sounder inside the room, the concern is would it damage the hearing of a primary school age child?
FSO, thanks, that's roughly what I thought. (perhaps 10 dB(A) above the expected level? I suppose the problem is we don't know what the noise level will be as it is a music room with volume controls.
|
|
|
|
Rank: Super forum user
|
Chris I can't imagine a fire sounder going off once in a while at 5 dB(A) above the music level is going to be that much more damaging than the music itself?
In any case the volume level of the music should be limited so it can't be increased to a point where it will do hearing damage. Just set the sound level of the alarm to be 5 dB(A) above that.
|
|
|
|
Rank: New forum user
|
Chris,
A sounder with an integrated flashing beacon may be useful.
Or having a link from the fire alarm sytem to the music system to kill the music when the alarm sounds, assuming that it is listening booths, not practice booths.
Alex
|
|
|
|
Rank: Forum user
|
I had a similar situation where sound proof booths were installed.
The solution which was agreed with the Fire Brigade at the time was to install visual alarms in each of the booths ie a flashing beacon.
We choose this option as the occupant of the booth could at times be wearing earphones.
|
|
|
|
Rank: Super forum user
|
I would go along with what had been recommended above but remember for every 3dBA increase is a doubling in sound so there is quite a difference between 5 and 10 dba. also there should be a procedure for the rooms to be checked that they have been evacuated as well either by the teacher or who ever is in the library as the children might or are unlikely to respond to the fire alarm. Also if the rooms are in a inner room situation there should be fire detection in the access rooms or other measures should have been considered (i presume there would be fire detection throughout).
Phil
|
|
|
|
Rank: Super forum user
|
Thanks to all for the really positive, practical solutions.
|
|
|
|
Rank: Super forum user
|
It is not unusual for a live music venue or a club (or disco for us old-uns) to have the PA interlinked to the fire alarm system, but might this be a little OTT?
How often will the room be used? and in tha time how often will the music be so loud as to make it impossible to hear the fire alarm? It could be that this is a very low risk which could be dealt with much easier (and cheaper)
Chris - You say 11 kids will be in the room, so where's the teacher? I cannot imagine there's an 11 to 1 teacher ratio, so perhaps a teacher or teaching assistant (who is with the rest of the class) will be elsewhere in a nearby location where the sounder could be heard.
A simple management system where someone outside the room raises the alarm by entering may suffice. - Just a thought!
|
|
|
|
Rank: Super forum user
|
messey where did I say 11 kids in the room?
Chinese whispers methinks :-)
|
|
|
|
Rank: Forum user
|
Glad you cleared that up Chris!
Just to add to the previous postings that when the sounder is activated it should not permanently damage hearing and be at a minimum of 65dBA or 5dBA above any background noise lasting in excess of 30 seconds. If excessive noise is present, a visual alarm condition should also be provided (BS 5839). Visual alarms are required if ambient noise levels exceed 90db.
Sound level is reduced by approx. 20dBA by a door and by approx. 30dBA by a fire door.
Due to individual building/room characteristics, sound level checks should be carried out to ensure minimum sound levels are obtained.
Cheers
|
|
|
|
Rank: Super forum user
|
Sorry Chris.
It was you that put '11' and 'kids' in the same sentence when you mentioned their age - so it's not my fault!! :)
|
|
|
|
Rank: Super forum user
|
One word sentences in future :-)
|
|
|
|