Textile processing machinery has CO2 fire suppression activated by the plastic tube pressure system (a drop in pressure = alarm), supplemented by manual release handles. This to combat the fire risk from the inevitable build up of fly which is highly combustible.
My concern is that cleaning and maintenance ops are done whilst on automatic, exposing personel to asphyxiation. I want the system to be switched to "manual only" when any work is in the danger area.
Given that this deection system is much more reliable and robust than optical/ionisation detectors, am I being reasonable please?
|
|
|
|
Rank: Super forum user
|
Risk depends on the size of enclosure, amount of CO2, (presumably no ventilation), likely size of hole in tubing caused by maintenance activity, duration of discharge.
What size is the enclosure, is there a clear alarm on discharge? On hearing the alarm, can the maintenance techs evacuate the area.
All things considered, I would prob go for the option of switching to manual activation during maintenance
|
|
|
|
Rank: Forum user
|
Dear Stuff. we need more info.
Is the CO2 system a large bank of cylinders designed to flood the whole work room or whole machine (if it is an enclosed machine) OR a small co2 cylinder (like a fire extinguisher) with a nylon tube?.
If the first case then I would expect a 30 sec delay while the alarm sounds to allow operating staff to evacuate before the workspace / machine is flooded with CO2. I see no difference between operators and maintenance staff.
If you are flooding an enclosed machine that only maintenance go inside, the i would expect the automatic feature to be disabled along with machine isolation. Leave manual available or locked off as well, according to your fire RA.
If the second case the volume of CO2 is small and is directed only at the fire as the flames only burn the nylon tube where the fire is. No action required.
hope this helps
Peter
|
|
|
|
Rank: Super forum user
|
This forum is going to the dogs, I give up
|
|
|
|
Rank: Super forum user
|
This sounds like a very old system to me. I would think that all automatic fire supression would have a manual over ride for maintenance work. If nothing else it saves replacing anything due to accidental operation.
|
|
|
|
Rank: Super forum user
|
It would possibly be more worth while to consider the efficacy of the suppression system vs materials involved in the fire.
|
|
|
|
Rank: Super forum user
|
Fire trace is okay wrt electrical panels of small volume, questionable wrt to large equipment enclosures.
Many variables: position of tubing, size ofd enclosure, ventilation or leakage rate etc.
|
|
|
|
Rank: Super forum user
|
Thanks for your contributions.
These are medium size carding machines for man-nmade fibres, each having its own CO2 bottle bank, number depending on size of fire area. I'm not sure at the moment whether there is any alarm/delay built in to the system but that certainly is something for me to check.
This situation is not as serious as an enclosed room but I am still concerned that a machine operator could have their head and shoulders within the discharge area and be overcome if they take a lungful.
If it emerges that there is (say) a 20 sec delay after an alarm sounds, do you think that staff training would be an adequate control or should there still be a lock-off system?
|
|
|
|
Rank: Super forum user
|
I would go for the option of switching from auto to manual during maintenance activities. As Chris has stated, it prevents accidental discharge and the costs to replenish the system.
In the case of visual inspection tasks, I would suugest that damage to the activation/pressure sensing tubing would be highly unlikely, coupled with short travel distance/quick exit (head and shoulder) and so would not see the need to switch over to manual operation.
|
|
|
|