Scrumpyman  
#1 Posted : 18 August 2010 12:31:45(UTC)
Rank: Forum user
Scrumpyman

Can I ask why, in a fairly standard size office, a requirement for two types of Fire extinguisher exists? Not by law, (at least I don't know of any) but by an appointed Fire Officer. While the previous Fire officer said something completely different. One water the other CO2. Chances are an electrical fault will be the cause of any fire either through wiring or an electrical appliance and so water would be useless. If a paper fire ignited through, I don't know, lets say sunlight through a window, would a water extinguisher be used with so many electrical appliances around? It appears to me that yes, Fire extinguishers should be provided but the one per 200sq metre rule (depending on activities in the building) and one per floor would be sufficient for most offices. Having said all that, my first instinct is to get everyone out to a safe place and not use the extinguishers (a whole different debate I know). I would be interested to hear everyone thoughts.
PhilBeale  
#2 Posted : 18 August 2010 12:55:50(UTC)
Rank: Super forum user
PhilBeale

Scrumpy when identifying the need for placing fire extinguishers you need to to account the likely hazards so given an office environment then there would be electrical hazards as well as class A hazards so what you have in place is right in my mind. You are right about one fire extinguisher per 200m2 but i seem to remember that secondary fire extinguisher should also be supplied, then as you say on per floor etc. Of cause you could look at installing a powder extinguisher but they make one hell of a mess and will destroy all electrical equipment in that room. you also need to consider travel distance to the nearest fire extinguisher as well so although you may only be <200m2 you might still need more than one to meet the travel distance. But as you say evacuating first is a priority putting out the fire if trained to do so and safe to do so is a secondary consideration. Phil
Helmsman  
#3 Posted : 18 August 2010 13:42:41(UTC)
Rank: New forum user
Helmsman

Any Fire Officer inspecting a premises is going to give his/her interpretation of the regulations. In the old fire certificate days we were told to move electrical equipment (a photocopier) just about every year at the annual inspection - one wanted it here, one wanted it there. We just moved it back and forwards between the two different places. More recently I was given some advice about creating a safe escape route which was completely reversed by the same officer in a phone call later the same day - from "you can't do that" to "yes, that's OK". They are only human and trying to do their job... but it is frustrating sometimes.
firesafety101  
#4 Posted : 18 August 2010 14:13:32(UTC)
Rank: Super forum user
firesafety101

Electrical equipment on fire - switch off and use CO2. Paper, timber etc. on fire - liquid based extinguisher i.e. water or foam. Electrical fire spreading to paper, timber etc. switch off electrics and use the CO2 on the electrical equipment and the liquid based extinguisher on everything else. I usually recommend one of each in the standard risk, i.e. office and shops as there is always electrical equipment that would be damaged by water and there is always other combustible materials that would be blown away by the force of a CO2, thus tending to spread the fire. Site all extinguishers strategically, i.e. CO2 near to electrical equipment, but near to the exit routes as you want to be on the way out when you decide whether to have a go at the fire or not. Always sound the alarm and evacuate, (all fires start small), call the brigade if necessary.
Scrumpyman  
#5 Posted : 18 August 2010 17:35:39(UTC)
Rank: Forum user
Scrumpyman

Thank you all for your responses. Is the two types of extinguisher law? Am I right that you have to provide a means of extinguishing a small fire?
firesafety101  
#6 Posted : 18 August 2010 18:02:57(UTC)
Rank: Super forum user
firesafety101

It all depends upon your fire risk assessment, however I think all fire officers like to see extinguishers in the workplace. Scrumpyman - by the nature of your questions I think you need a competent fire risk assessor to sort things out for you.
freelance safety  
#7 Posted : 18 August 2010 18:07:53(UTC)
Rank: Super forum user
freelance safety

I think that is good advice Chris, I think some assistance may be needed.
paul.skyrme  
#8 Posted : 18 August 2010 18:14:36(UTC)
Rank: Super forum user
paul.skyrme

I can put you in touch with a fire risk assessor if you want?
paul.skyrme  
#9 Posted : 18 August 2010 18:15:13(UTC)
Rank: Super forum user
paul.skyrme

p.s. NOT ME! Oh for an edit facility!
Scrumpyman  
#10 Posted : 19 August 2010 08:16:43(UTC)
Rank: Forum user
Scrumpyman

Thanks for the advice but I don't need a Fire Risk Assessor. I have a Fire officer and that is my problem. I am trying to use common sense and realistically in the event of a fire, I want people out of there, I don't want anyone to be a hero and try to tackle the fire. Yes, I know extinguishers have to be provided but the law says to extinguish a small fire. So if thats the case why the need for two? My argument is, provide one extinguisher with training, fire drills and everyone aware of the evacuation plan. I believe that to be reasonably practicable. Any comments?
teh_boy  
#11 Posted : 19 August 2010 08:32:34(UTC)
Rank: Super forum user
teh_boy

Agree with above comments... you may find it useful to read the following guidance. There are no 'laws' only a requirement to assess. I am not sure if you know the difference between 'law' ACOPs and guidance? I am not going to go there now tho :) http://www.communities.g...ons/fire/firesafetyrisk2 I am sure reading the relevant parts of the above might help.
teh_boy  
#12 Posted : 19 August 2010 08:35:11(UTC)
Rank: Super forum user
teh_boy

Sorry that doen't read how i intended :) I also think this is an issue you could debate all day - search the forums for extinguishers and you will some huge debates on the topic.
flukey  
#13 Posted : 19 August 2010 08:54:18(UTC)
Rank: Forum user
flukey

scrumpyman wrote:
Thanks for the advice but I don't need a Fire Risk Assessor. I have a Fire officer and that is my problem. I am trying to use common sense and realistically in the event of a fire, I want people out of there, I don't want anyone to be a hero and try to tackle the fire. Yes, I know extinguishers have to be provided but the law says to extinguish a small fire. So if thats the case why the need for two? My argument is, provide one extinguisher with training, fire drills and everyone aware of the evacuation plan. I believe that to be reasonably practicable. Any comments?
To the best of my understanding the requirements come from BS 5306, whilst a 13A rated extinguisher (such as a water or AFFF) can cover up to 200m2, but there is a requirement to have an additional extinguisher per floor regardless of floor area. That means you should have at least 2 13A rated extinguishers per floor. Then you need to consider if you have differing fire loads, such as you would in an office, and provide Co2. However, in my experince the above rule is flexible. A visiting fire officer only wants to see if an extinguisher is there, they will not start calculating floor space. I have heard rumour of one very large retailer who thought of removing extinguishers from all its sites (justified by risk assessment) but didn't in the end because it would likely have spread them all over the media (you can imagine the headlines!).
Scrumpyman  
#14 Posted : 19 August 2010 10:46:09(UTC)
Rank: Forum user
Scrumpyman

Flukey - thanks, very helpful. teh boy - No problem, I took it how you intended it :) and you are right, deabte could go on forever. Is there any case law for not providing correct or sufficient amount of extinguishers?
firesafety101  
#15 Posted : 19 August 2010 11:25:19(UTC)
Rank: Super forum user
firesafety101

scrumpyman I think you are missing the main point here. There is more than one type of fire therefore there has to be more than one type of extinguisher. If you have an office premises completely made up of timber with timber furniture and paper for sending messages and writing letters then a water extinguisher is the only one you will ever need. If you have an electrical sub station made of brick/metal with nothing other than electrical equipment inside then a C02 would suffice. It is when you have more than one type of fire risk present that you have to provide the right extinguisher for each risk. I assume you have an office with timber, paper etc. also electrical equipment such as PC, printer, copier etc, maybe evan a kitchen with electrical cooking/warming equipment, toilets with paper and perhaps an electic hand dryer, I could go on and on and on. If so you will also need to cover those risks. Seeing as you have a fire officer are you not able to talk to him/her for clarification?
Scrumpyman  
#16 Posted : 19 August 2010 12:17:39(UTC)
Rank: Forum user
Scrumpyman

I might be missing the main point and I apologise if I am, but my point is, I want employees to evacuate the buillding, not to tackle fires. That being the case, one extinguisher is sufficient in my opinion. Is there case law to establish a sufficient number/type of extinguisher?
teh_boy  
#17 Posted : 19 August 2010 12:37:47(UTC)
Rank: Super forum user
teh_boy

scrumpyman wrote:
Is there case law to establish a sufficient number/type of extinguisher?
I doubt it as I can't think of many situations where I would sue someone for this? However take a look at fire brigade enforcement notices. http://www.dsfire.gov.uk...forcementPublicRegister/ I chose my home county but a quick *generic* search engine will give you others. My point was enforcement action will be taken on article of law, the guidance is a good way to show compliance with the law. The guidance suggests a min number of extinguishers. You would be hard pressed to risk assess out. Also IMHO a fire tackled in it's very early stages and extinguished might well save lives but it all depends on circumstance! Where's messyshaw when you need him? :)
Mick Noonan  
#18 Posted : 19 August 2010 12:56:33(UTC)
Rank: Forum user
Mick Noonan

What if the only fire extinguisher on the floor doesn't work? secondly I would point out that the extinguisher can be used to facilitate safe evacuation where the fire is blocking the egress route. There, two good reasons to have more than 1 unit.
freelance safety  
#19 Posted : 19 August 2010 13:19:15(UTC)
Rank: Super forum user
freelance safety

I’ve only just read some of the comments on this subject, as a former fire officer I can tell you the following:- There are lots of fire legislative requirements:- to name a few e.g. – Fire and Rescue Services Act 2004 – Regulatory Reform (Fire Safety) Order 2005 – Building Act 1984 – Building Regulations 2000 – Fire (Scotland) Act 2005 – Fire Safety (Scotland) Regulations 2006 – Building (Scotland) Act 2003 – Building (Scotland) Regulations 2004 – Fire Precautions Act 1971 (Northern Ireland only) – Building Regulations (Northern Ireland) 2000 – Health and Safety (Safety Signs and Signals) Regulations 1996 In terms of the commentary relating to case law, this can be both civil and criminal. Get a copy of Munkman’s and look through the masses of fire case law, including extinguishers, relating to criminal judicial precedent! I understand the sentiments of getting everyone out and not tackling fires however, there are legal requirements for providing specific fire marshal training; suitably assessing the types of extinguishers needed for the location based on a classification system e.g. 1. Class A: Solid materials. (e.g. Water) 2. Class B: Flammable liquids. (e.g. Foam) 3. Class C: Flammable gases. (e.g. Co2, also for B type fires) 4. Class D: Metals. 5. Class F: cooking oils. (e.g. wet chemical) Extinguishers should be: • Located within easy reach so that no-one has to travel more than 30m to get one • Placed in conspicuous locations such as on escape routes, stairways, corridors, exits or landings • Grouped together in fire points where practicable • Wall mounted on brackets (not more than 1m high) and sign posted • On similar positions on each floor. Worth noting that both New Look and the Co-op have both recently been prosecuted, check out Augusts SHP, for fire breaches (including fire assessments and fire marshal training). Both got six figure fines, if I remember correctly New Look was fine in the region of £400,000 and the Co-op £200,000!
Scrumpyman  
#20 Posted : 19 August 2010 13:26:58(UTC)
Rank: Forum user
Scrumpyman

Thanks for all the brilliant advice. I hold my hands up, two extinguishers is good, I wont be arguing again.
freelance safety  
#21 Posted : 19 August 2010 13:30:26(UTC)
Rank: Super forum user
freelance safety

Your Welcome. Glad to know you have a fire officer who cares.
firesafety101  
#22 Posted : 19 August 2010 15:19:50(UTC)
Rank: Super forum user
firesafety101

scrumpyman good to see you have finally seen the light. However you may now find that two extinguishers may not be adequate - what about the alternative exit, do we need to site some there? If I remember correctly New Look and the Coop, and Tesco have recently been prosecuted for - among other things - inadequate fire risk assessment, so if I were you I'd get your fire officer to have another look. Best of luck.
Alex Petrie  
#23 Posted : 21 August 2010 15:13:32(UTC)
Rank: Forum user
Alex Petrie

I know I've come to this debate late on, but let me offer an alternative thought. What if the first extinguisher fails? Your insurance company may also have something to say on the matter. In order to be covered for hot work they usually require there to be two extinguishers. Obviously this is different for your office but it's worth checking out, if only to give you a more definitive answer! A
firesafety101  
#24 Posted : 21 August 2010 17:21:39(UTC)
Rank: Super forum user
firesafety101

Why two extinguishers for hot work? In my opinon the person carrying out the hot work should provide the extinguisher and it should be the correct type for the potential fire. The permit procedure should ensure this. That is what I recommend. What if the second extinguisher fails? What if the person attempting to use the extinguisher fails? You could go on and on and on ........................... Just provide the right number and type, get them serviced regularly, sited correctly, and someone trained to use them - no problem.
Alex Petrie  
#25 Posted : 21 August 2010 18:10:43(UTC)
Rank: Forum user
Alex Petrie

Chris, we're both in agreement about two extinguishers of the correct type & properly serviced etc. I was merely injecting a question which hadn't been asked earlier in the disussion. As for why two for hot work, it's just standard practice, following the FPA Code of Practice for Fire Prevention on Construction Sites. A similar stance is taken by insurance companies too. A
firesafety101  
#26 Posted : 21 August 2010 19:35:16(UTC)
Rank: Super forum user
firesafety101

Alex, thanks for pointing that out. I suppose this could be a debate in itself as the number of extinguishers surely depends on the type/size of fire risk? Small and low risk - one or two, larger higher risk - many more and larger size. Don't stick to just one or two. Would you consider carrying out a fire risk assessment just for a Hot Work operation? How about hot work in a controlled environment inside a workshop? What about the general rule of thumb that if a fire is too large for more than one extinguisher it is too large to tackle therefore get out etc. The provision of two extinguishers is the provision of one too many then?
Alex Petrie  
#27 Posted : 22 August 2010 08:30:35(UTC)
Rank: Forum user
Alex Petrie

No worries Chris. You're right though, it would depend on the level of risk. I don't know if I'd prepare a specific fire risk assessment for one operation - hot work would come into your overall site fire safety plan. If the permit procedures work though, you would have a fairly low-risk environment anyway with all combustibles tidied away and a suitable number of extinguishers etc. I wouldn't apply the one extinguisher rule too rigidly. My understanding is that fire extinguishers are there to enable people to exit a building, therefore the main objective must be to evacuate and to only use extinguishers if your escape is affected by the fire. Hence why, I think, that two would be sufficient as the likelihood of them both failing is remote provided they've been looked after. Inside a workshop....this should be covered by the premises fire risk assessment, and the level of controls appropriate to the process & environment. Yeah, I think this may be a whole new debate on it's own! I think that we can say two is the minimum but it will depend on other factors present at each site. A
Shaun McKeever  
#28 Posted : 22 August 2010 10:14:39(UTC)
Rank: Forum user
Shaun McKeever

ChrisBurns wrote:
Would you consider carrying out a fire risk assessment just for a Hot Work operation?
I guess it very much depends upon the nature of the hot work process. If you use acetylene then you immediately increase the size of the risk area significantly.
PhilBeale  
#29 Posted : 22 August 2010 19:32:19(UTC)
Rank: Super forum user
PhilBeale

Shaun McKeever wrote:
ChrisBurns wrote:
Would you consider carrying out a fire risk assessment just for a Hot Work operation?
I guess it very much depends upon the nature of the hot work process. If you use acetylene then you immediately increase the size of the risk area significantly.
As part of a fire risk assessment the issue of hot work should be covered on what to do and what the procedure is if it is something new that has never been done before then you may need to amend the fire risk assessment with how you are going to control the risk. otherwise you should always carry out a basic risk assessments fro any hot work ensuring the control measures are in place that are required under the fire risk assessment or at least the procedure you should refer to (example hot work permit which should contain all the relevant measure you need to comply with) there's lots of information on control measures you should take on the internet most of them are common sense but worth having a document to follow and record the event. Phil
Bob Shillabeer  
#30 Posted : 22 August 2010 20:44:04(UTC)
Rank: Super forum user
Bob Shillabeer

I always worked on the basis of fire extinuishers are simply to comly with the legal requirement to have them. There were no staff trained in thier use so were instructed to evacuate if a fire broke out. Simple as that. But you need to have enough fire extinguishers to meet the legal minimum so I had two (one water and one CO2) at each emergency exit all of which were subject to contracted inspection and maintenance and were within the 30m travel distance. Result - No risk of people getting burned when using the kit, no need to train and referesh, better compliance with the evacuation process and everyone understood what they had to do in the event of a fire. This was an office based operation.
Shaun McKeever  
#31 Posted : 22 August 2010 21:53:46(UTC)
Rank: Forum user
Shaun McKeever

Bob their is no legal minimum for extinguishers but what there is a legal requirement for is that if you provide extinguishers then you must provide training for staff to use them. As for the rest of your argument, if you really expect staff to walk away from a flicker of a flame rather than nip it in the bud before it gets too big then I personally think you are wrong. Letting a fire develop when you could have extinguished it early may actually place more people at risk than it would have done by not extinguishing it. It also places firefighters at risk or do you think because they are trained then they won't be injured?
Bob Shillabeer  
#32 Posted : 22 August 2010 23:53:26(UTC)
Rank: Super forum user
Bob Shillabeer

I always worked on anything bigger than a wate bin was to big to deal with simply by using a fire extinguisher. This is the view of many professional fire fighters as the risk is too high for an inexperienced person to deal with and the best thing was to escape and leave it for properly trained fire figters to deal with. This has proven to be sound advise over the years and is far easier to manage than trying to train people to use fire extinguisher safely. How you say not fighting a fire instead of simply escaping and leaving it to the professionals seems to go over my head, but what do you expect from someone with well over 30 years of experience in managing this issue???
PhilBeale  
#33 Posted : 23 August 2010 09:15:52(UTC)
Rank: Super forum user
PhilBeale

there is a legal requirement to train employees how to use fire extinguishers. The office that produce GLC guides was prosecuted for not providing fire extinguisher training for it's staff fire extinguishers are not difficult to operate and following a few simple rules no employee should put themselves at risk or tackle anything bigger than a waste paper bin that has already been referred to. if you supply the equipment then employees must be trained on how to use it as other have said tackling a fire in it's early stages can prevent others been put at risk. look at some of the recent fires where employees fail to react to the situation and lose their lives, not everyone responds to a fire alarm as they should. Not sure where managing a situation for 30 years comes into play when you don't do anything about the issue in terms of providing training. maybe have a word with your local enforcement officer and tell them you are not providing any training on the use of fire extinguishers even though you have them on your premises. Phil
Wizard  
#34 Posted : 23 August 2010 09:54:01(UTC)
Rank: Forum user
Wizard

Having read the posting late, I must remember in reading this all, that this is an open forum and as I have been reliably informed by Monitors, not all are safety professionals. With this in mind we therefore cannot respond to some people's perception of right and wrong and we must keep a balance of ignorance over experience. Some of us believe that the provision and training of FFE is correct, "Bravo" common sense wins again, but hang on others believe we should have FFE because government say we have to have it, to prop open doors, hang a jacket on or to look pretty and match the decor. Maybe the government decision to require this equipment was based on a 'lucky dip in the hat' will we, wont we, maybe ?? however, I dont think this was the case. It was probably made with good advice from very experienced people in the industry of saving property losses and lives. I know many who say" I have done it this way and invested in it for 30 years or more, and nothing has ever happened" fffffff goodness! I hear that daily.........I think that last notable organisation to say that was BP or was it a sub contractor this morning conducting a tandem "critical" lift without a valid permit....... Wizard Anyway does it really matter.........is it really that important that we dont follow best industry practice, legislative requirements, and bash on regardless........ Do we suggest we all pack in and leave it to "chance"
freelance safety  
#35 Posted : 23 August 2010 10:00:37(UTC)
Rank: Super forum user
freelance safety

Good posting Wizard!
firesafety101  
#36 Posted : 23 August 2010 10:54:09(UTC)
Rank: Super forum user
firesafety101

Having commented earlier I now add that you do not always need a fire extinguisher to tackle a fire. What about the chip pan where use of a wet extinguisher is more harmful, the old fashioned fire blanket is the best for that. if a fire blanket is not available then a damp, and I mean damp tea towel works just as well. The mention of a waste paper bin with a flicker of flame - depending on the type of bin a simple ring binder placed on top may suffice to prevent the air getting to the fire thus extinguishing the fire. The use of a water extinguisher may be over the top for a small fire. Many years ago I introduced a new design waste bin, metal with the top an inverted cone with a hole in the middle. The idea was that when a fire started inside the bin the smoke, (combustion gases), hit the inside of the lid and were redirected down toward the bottom. This actually worked on at least one occasion when a fire started in one of the bins and snuffed itself out. No extinguished needed.
PhilBeale  
#37 Posted : 23 August 2010 11:28:08(UTC)
Rank: Super forum user
PhilBeale

I agree with you Chris a fire blanket or even as you say a ring binder over the top of a waste bin fire is a good way to deal with the fire but this does mean that the person has to get close up with the fire at least arms length. With a fire extinguisher you can stand some 5-7 metres away and deal with the fire, probably in most offices you could in fact stand in the doorway and deal with the fire. I believ evryone should be trained and then it is down to the individual if faced with a fire if they are confident and able to deal with the fire as i always say to anyone i train if in doubt get out. I'm not looking to train hero's just to train common sense. Phil
saferay  
#38 Posted : 23 August 2010 15:33:57(UTC)
Rank: Forum user
saferay

Scrumpyman We are moving away from water extinguishers in favour of AFFF. Reason? Whilst not being recomended for electrical fires, they have a conductivity rating of 35KV meaning that they resist electricity as well as being suitable for Class A + B fires. You must also remember that CO2 extinguishers are not suitable for Class A fires, so there is a need for two different extinguisher types. Hope this helps Adrian
Shaun McKeever  
#39 Posted : 23 August 2010 17:51:40(UTC)
Rank: Forum user
Shaun McKeever

Bob I can tell you what I would expect from someone who has had 30 years experience managing fire safety, the least I would expect is that they be aware of their legal responsibilities particularly with respect to training staff. Failure to provide adequate fire safety training, including use of extinguishers, is one of the principal elements of any prosecution by the ‘professional’ fire service. In your previous posting you did not refer to the size of any fire, you only stated that staff instructions are to evacuate at the first sign of fire. My argument is that there has to be an element of common sense about this. I believe people get far too emotional about fire and the risk it poses. It is a fact that the majority of fires are extinguished by first aid firefighting, this might be the use of a portable fire extinguisher or it may simply be stamping it out, but generally it is the application of common sense. I’m not sure about what part of my posting went over your head but I will have a go at trying to explain a bit better. In your posting you said that staff are instructed to evacuate; by doing so they are ensuring their own safety. However some people may remain in the building, for example fire marshalls may be carrying out a sweep, checking other rooms so will have a delayed escape. People on other floors either above or below the fire may have to pass the floor of the fire; the taller the building the greater the problem. It may be not a real problem if all your fire doors are effective and there are no leaks of toxic gases into the escape route, unlikely except in the most modern of buildings where the build quality is good. Disabled occupants may be slower moving than others and so remain at greater risk if a fire is allowed to grow. Then of there are the firefighters who will turn up 10, 15, 20 minutes or more after the call. By this time the fire may involve an entire room or an entire floor. It may be on the point of flashing over. But the RRO says we don’t need to worry about firefighters doesn’t it?.....
messyshaw  
#40 Posted : 23 August 2010 19:36:29(UTC)
Rank: Super forum user
messyshaw

Shaun McKeever wrote:
.... I believe people get far too emotional about fire and the risk it poses. It is a fact that the majority of fires are extinguished by first aid firefighting, this might be the use of a portable fire extinguisher or it may simply be stamping it out, but generally it is the application of common sense.
Quite right Shaun- That has been my view for some time and I call the reluctance to fight fires as the 'Hollywood Effect'. Most people who have experienced a serious fire do so via TV or films. In Hollywood (or Pinewood) all crashed or burning cars explode, and all room fires flashover in a huge ball of flame. I have attended many RTAs where victims have been dragged from perfectly safe cars in case it 'blows'! In the real world (away from Sun Hill and Holby), the development of a fire - especially at it's early stages (where extinguishers are invaluable)- is most likely to be slower and less dramatic. I see training as an attempt to demystify and defuse the Hollywood Effect, but without introducing complacency. It's often training people when not to use an extinguisher that is most useful. The actual nuts & blots of using one isn't rocket science, after all they are really just a glorified aerosol can aren't they? It's about time H&S grew some balls and confronted this "run away it's too dangerous" mentality. I'll get off my soapbox now as it's making me dizzy up here! :)