I am currently working on a project which has very poor water flow rates to the site, we are looking to improve the water supply to the fire hydrants on site. One option available to us is is water extraction from the major river on the boundry to our site, has anyone previous experience and knowledge of the pro's and con's associated with this method of providing fire hydrant water. Additionaly i would be very interested in visiting other sites to view the metods which have been used.
Regards
DPK
|
|
|
|
Rank: Super forum user
|
Hi DPK
Not my area but I would have considered this a 'last resort' as it may cause unnecessary complications and extraction licence if a permanent fitting.
Considering risk how many hydrants are likely to be operating at any one time? How about adding supplementary tank(s) / booster pump.
The option of emergency top up would probably not need any arrangement as the FS would probably be doing this if normal source was exhausted.
Having capacity to do yourself is the 3rd layer of control as opposed to primary. Ist supply, 2nd tank + booster pump (fed from main) 3rd - emergency top up (from appliance or.... say a river.
Naturally keeping a mobile pump and long hose on a 'come in handy' basis adds to your peace of mind!
Steve
|
|
|
|
Rank: Forum user
|
DPK
Taking water from a river is regarded by the Environmental Agency (EA) as water extraction and to do this you would need an extraction license. If the EA visits you site they could end up prosecution your company.
A couple of IOSH colleagues in the Yorkshire reign have mentioned that the EA have carried out visits to their site to look at environmental issues on site. So there is always a risk.
Regards
Jim
|
|
|
|
Rank: Super forum user
|
If you want to remove or abstract water from a surface source (e.g. river, stream or canal) or from an underground source and take more than 20 cubic metres (approximately 4,400 gallons) a day, you will almost certainly need an abstraction licence.
Its not something I do on my site, but i know some of the other sites within our company do.
This is the environmental link http://www.environment-a.../topics/water/32020.aspx
Si
|
|
|
|
Rank: Super forum user
|
Extraction from watercourses has been used to feed sprinkler systems in the past so no reason it cannot apply to hydrants subject to abstraction license being obtained.
You do need to have an alternate supply in case the river is re-routed or dries up in drought conditions.
Secondly, the extraction point needs to be fitted with screens etc to prevent ingress of debris such as branches and weeds.
|
|
|
|
Rank: Forum user
|
You say that there are already Fire Hydrants on the site. Do you have a works Fire Brigade? If not the local Fire Brigade will have done site visits to ensure that they are familiar with the layout of the site. In the event of a fire occuring they will be able to request that the water authorities boost the incoming presssure to the site. If that is not successful, the Fire Brigade have the resources and capabilities to take unlimited amounts of water from the river, provide it is used for fire fighting purposes. Hope this helps in some way towards your project outcome.
|
|
|
|
Rank: Forum user
|
An important thing to consider believe it or not are the potential health hazards ! Spraying jets of river water around during routine testing and emergency use will carry a potential risk of infection to operatives of the system. The most significant of these is Weil's disease (leptospira sp) caused by water contamination with riverborn rat urine which can be fatal - i.e. you will need to adopt strict procedures - covering cuts or abrasions, use of gloves and thorough hand washing and general hygiene considerations and action to be taken if you feel unwell. Your local fire service will probably have a suitable procedure in place to cover these aspects when pumping from open water you can use.
|
|
|
|
Rank: Super forum user
|
I think you really need to be looking at the reasons for the low flow in the first instance. This is especially so if a fire main supply will be required for the final structure. Get your services engineer/designer involved as this should have been identified by the cdmc and designers during design meetings.
The environmental impact of surface water abstraction means that licences are hard to come by nowadays.
Bob
|
|
|
|
Rank: Super forum user
|
By the way I think it also might be cheaper to upgrade the main than undertake abstraction.
Bob
|
|
|
|
Rank: Forum user
|
Have you considered setting up EWS (Emergency Water Supply) tanks for the specificate areas of concern. If for use by emergency service then all is required is a suction eye connection. It can be linked into the main for automatic replenishing etc. Use these on the airfields as hydrants not always in the right place.
|
|
|
|
Rank: Super forum user
|
DPK - most older factories / mills still do this.
We had a "lade" which we used to divert water from the river into. We had rough screens fitted at the access to the mill to remove the bigger items, trees, sheep, bales of hay etc. finer screening to remove leaves, grit etc. The water would then be dosed to kill off any water borne nasties then charge up the system.
Pros - plentiful supplies and cheap enough. You just pay for what you use - plus the lisence fee.
Cons - screens choke regulary in autumn and when the river is in spate.
Contamination to your systems from other sites up stream
You need to ensure that nothing can get back into the river.
Also worth checking if there is a well on site you can tap into. If the river runs nearby, there is a good chance there is a water supply under your feet.
David
|
|
|
|
Rank: Super forum user
|
Extraction from a well is also subject to licence and charge.
|
|
|
|
Rank: Super forum user
|
Correct John but less contamination issues and cleaning requirements
David
|
|
|
|
Rank: Super forum user
|
Extraction water is also charged by the cubic metre and I really think there needs to be more thought over the cause rather than what is at best a sticking plaster solution.
Bob
|
|
|
|
Rank: Forum user
|
David H
Thanks for your reply, good point you have made regarding the well, we have no well that I am aware of but I do know the water table is very high so there may be an opportunity there, at least worth investigating.
With regard to other replies, we have a suitable large enough main to site, however the mains pressure is poor and unfortunately does not met with any standards such as BS9990 - 1500 litres per min etc etc...
We are investigating all options, tanks are possible, but we have limited space, increasing water pressure is down to the local provider and with regard to the local fire authority, we are in negotiation to agree on the most suitable method of water provision.
For those who have advised water extraction is chargeable, not if it is for fire fighting it isn't.
DPK
|
|
|
|
Rank: Forum user
|
Could a booster pump be installed for fire fighting purposes? Problem with this is that the water mains would have to be able to take the extra pressure. Or, a procedure such as having two outlets open upon activation of the booster pump.
|
|
|
|
Rank: Super forum user
|
DPK
I am aware the Fire Service is not charged when they abstract water in time of emergency BUT the creation of a formal main using such water is potentially a different matter. Can you guarantee that the fire hydrant points will only ever be used for fire. I know of many situations commercially where the main serves other functions also.
It really still sounds as though a sticking plaster is being sought. I would guess that matter of fire water run off has also been considered fully if you have surface waters close by, other than formal sewers.
Bob
|
|
|
|
Rank: Forum user
|
At this point I feel like I have more questions than answers!
The OP does not make clear how the present arrangement works - apart from unsatisfactorily. I presume that you have a number of hydrant points that are supplied directly via the water main with no tank and or boosting in place.
In addition it is not clear on what basis these hydrants are used/expected to be used. Is it simply a contingency for emergency fire-fighting purposes that one would hope to never use in anger or is it a set-up that is perhaps used for more general wash-down type activities that could also serve a fire-fighting purpose?
In a past life I have worked on emergency fire pump systems and it is not too uncommon to find such pumps fed from rivers - if I were to guess I'd suggest that in my experience such set-ups would represent fewer than 10% of emergency firepumps that I encountered. It is far more common to have a dedicated (large) tank to feed the emergency firepumps. It is also a much less complicated arrangement - regarding valves, header tanks, suction lift etc - if one uses pumps fed from a tank. As others have mentioned one of the main problems associated with drawing water from a reservoir or river is ensuring that any solids are filtered prior to reaching any non-return valves and or sensitive pumping equipment. Many such installations suffer reliability issues as a result of NRVs sticking open - relaibility issues are generally not the sort of thing that you want with a system that may be utilised for fire-fighting.
If this set is genuinely seen as a means to fight fires then, at the risk of opening a can of worms, I'd be tempted to draw on the expertise of the company insurers as they tend to have a good insight into what is feasible/practical and also, ultimately, will need to be content themselves about your provision.
|
|
|
|
Rank: Forum user
|
Also if you want some guidance on hydrant pressures then you may find the "National guidance document on the provision of water for fire fighting" of use a PDF version is available on: http://www.firesafetyengineer.com/lga-2002.pdf
|
|
|
|
Rank: Forum user
|
I have known a fire and rescue service (in Scotland) to use a nearby swimming pool for emergency water supply to fight a fire when the hydrants failed.
And I am not kidding here (even though it is close to Xmas).
Son of Skywalker
|
|
|
|
Rank: Super forum user
|
wclark1238 wrote:
If this set is genuinely seen as a means to fight fires then, at the risk of opening a can of worms, I'd be tempted to draw on the expertise of the company insurers as they tend to have a good insight into what is feasible/practical and also, ultimately, will need to be content themselves about your provision.
Good advice there. All the major commercial property insurers employ sprinkler specialists (usually recruited from the sprinkler industry) or have access to external contractors to give advice on this type of thing.
I used to do this kind of thing (in a supervised role) a few years ago but I hated all the mathematics involved and ever changing standards that had to be applied.
|
|
|
|
Rank: Forum user
|
If you have a major river on the site boundary-i.e. no chance of the river drying up- you need to consider depth - sufficient for the end of the fire suction hose about 1.2 metres- the weight of the tender - about 16 tonnes - and access to the river. Provide a railing if you can.
Obviously talk with your local fire station officer.
If hydrant supplies are poor, consider an emergency water tank. The fire officer should be able to advise how much water an appliance uses per minute. Insurers will often state what size the tank needs to be, but I believe 30 minutes supply is common.
You can also ask the brigade to test the hydrant, but be aware this will disturb sediment and local residents may get rusty water.
Good Luck
|
|
|
|