#1 Posted : 24 March 2011 13:50:47(UTC)
Rank: Forum user
SDCL-Pete

Hi all, Bit of background; I work for a small design and fabrication firm (8 people) and have been asked to implement the recommendations of our H&S consultancy with a view to forging this as a career path. One of their recommendations was to supply torches at fire extinguisher points as an emergency lighting system. My own fire safety training consists of a Fire marshal certificate, knowledge of our work/premises and common sense. The main flaw I see with this idea is that if no-ones near any of the torches or extinguisher points and we have a power failure and fire; how would anyone find their way to this emergency lighting system? There is no ambient lighting in the area (street lighting or light from other buildings) so in the dead of winter it gets pitch black. To install a full emergency lighting system would be quite pricey for us but the more I think about this; the more stupid it seems to me. Does anyone else have any experience of a system like this being used? If so, how do you justify this? Training? Incorporate it into the emergency plan? Just don't see how this is a sensible suggestion myself....
martinm  
#2 Posted : 24 March 2011 14:11:52(UTC)
Rank: Forum user
martinm

"to supply torches at fire extinguisher points as an emergency lighting system" I have a rechargeable torch and when the power fails, it automatically turns itself on. This means that I can find my way to it and then detach it to use as a normal torch. This type of device may be what the consultant had in mind, it is certainly better than a plain battery powered torch, martin
chas  
#3 Posted : 24 March 2011 14:22:23(UTC)
Rank: Super forum user
chas

Is this what your after http://www.safetlight.co.../safety_lighting_faq.asp (ps I do not work for the company)....I have also seen ones with luminous handles.
Ken Slack  
#4 Posted : 24 March 2011 14:24:56(UTC)
Rank: Super forum user
Ken Slack

Looking at the topic maybe you could also install Photo Luminescent signage as a cheap backup....
PhilBeale  
#5 Posted : 24 March 2011 14:25:20(UTC)
Rank: Super forum user
PhilBeale

I think the key consideration is suitable and sufficient i don't think torches would be adequate given that it is a fabrication company. You can buy twinspot emergency lights relatively cheaply £30-£40 having a few of these wired in around the place so when the mains fails they will come on automatically. some and i could argue that you need to get them installed to the relevant BS but i think suitable and sufficient would meant that you could get them installed without the BS or at least they will be more effective than torches. However you will still need to test they are operating correctly on a monthly and yearly basis. torches may be fine in an office environment but my view not for a fabrication workshop. But as always without seeing the premises or knowing more i can only offer this as another possible consideration. Phil
Taylor  
#6 Posted : 24 March 2011 16:00:42(UTC)
Rank: Forum user
Taylor

I've no experience of such a system being used but another suggestion to put forward having read the thread. Given the small size of the firm and the small number of people, would it be practical to have people carry a small torch with them rather than install torches at fire extinguisher points. Avoids the need to find your way to the torch if the power fails. You would have to make sure people carry them at all times and have a system in place to ensure batteries are checked / changed. Might be an alternative.
PhilBeale  
#7 Posted : 24 March 2011 17:36:37(UTC)
Rank: Super forum user
PhilBeale

Taylor wrote:
I've no experience of such a system being used but another suggestion to put forward having read the thread. Given the small size of the firm and the small number of people, would it be practical to have people carry a small torch with them rather than install torches at fire extinguisher points. Avoids the need to find your way to the torch if the power fails. You would have to make sure people carry them at all times and have a system in place to ensure batteries are checked / changed. Might be an alternative.
Unless you work in a really bad area for power cuts then it would be unlikely anyone would carry the torches with them for very long if you accept the fact you only ever get a power cut maybe once every couple of years if that also i don't think it's practical or realistic to expect people to carry torches with them every day at work. At my old company the only time we carried torches where if we working is ceiling roof voids where if the lights failed you would never find your way out. phil
paul mc  
#8 Posted : 24 March 2011 19:28:08(UTC)
Rank: Forum user
paul mc

SDCL-Pete wrote:
Hi all, Bit of background; I work for a small design and fabrication firm (8 people) and have been asked to implement the recommendations of our H&S consultancy with a view to forging this as a career path. One of their recommendations was to supply torches at fire extinguisher points as an emergency lighting system. My own fire safety training consists of a Fire marshal certificate, knowledge of our work/premises and common sense. The main flaw I see with this idea is that if no-ones near any of the torches or extinguisher points and we have a power failure and fire; how would anyone find their way to this emergency lighting system? There is no ambient lighting in the area (street lighting or light from other buildings) so in the dead of winter it gets pitch black. To install a full emergency lighting system would be quite pricey for us but the more I think about this; the more stupid it seems to me. Does anyone else have any experience of a system like this being used? If so, how do you justify this? Training? Incorporate it into the emergency plan? Just don't see how this is a sensible suggestion myself....
I actually saw this system used on an american tv show today ( NCSI) and though what a good idea, but then its scripted they know where to go its not pitch black and plus walking about in the dark isnt good tv. perhaps take into consideration as previously stated luminescent signs or torches that are luminescent and have a little run through yourself in pitch black and see if that helps you. ps thanks to ken for the spelling of luminescent
jay  
#9 Posted : 25 March 2011 09:50:23(UTC)
Rank: Super forum user
jay

Not knowing the safety critical aspects, I presume that what is required is emergency escape lighting, based on the risks. How about having self contained "escape sign" at the exits that double up as emergency escape lighting? In my view they do provide "enough" lighting to make your way out and should serve the purpose, although they may not provide the level of actual lighting as specified in the relevant British Standard. A couple of factors that should be considered are 1) the risk of having a fire and power failure at the some time before the alarm is sounded is your fire detection & alarm system. 2) the ease or difficulty of making your way to the final exit door.
David Bannister  
#10 Posted : 25 March 2011 12:44:07(UTC)
Rank: Super forum user
David Bannister

I had a need to refer to HMG's Factories & Warehouses Fire Safety Risk Assessment Guide this morning on a non-related matter and came across their stance on emergency escape lighting, specifically use of torches. Section 3.4.4 states that for simple premises (eg open plan factories and warehouses), few staff, suitably placed torches may be acceptable. SDCL-Pete, you will know whether your circumstances fall in to that category so the real point of your question seems to be whether the particular consultant is competent to advise you on fire matters. You clearly have doubts. Is the doubt based on other perceived shortcomings or just this issue? If the latter I suggest that you speak to the individual in question and ask them to give their rationale for making this recomendation. If the former then tackle the Principal of the consulting firm. Best wishes S4B
SDCL-Pete  
#11 Posted : 01 April 2011 13:15:29(UTC)
Rank: Forum user
SDCL-Pete

Thanks for all the replies. I think that whilst a torch in someones hand is sufficient lighting to navigate their way to an emergency exit; finding your way to a torch may be an issue. Some of the above suggestions seem like pretty good ideas. Personally, I would prefer to get some kind of permanent emergency lighting system but as with all many small businesses cash flow and landlord may be an issue there. Certainly fluorescent strips on the torches will be an ideal interim solution. Thanks again for the advice peoples!
firesafety101  
#12 Posted : 02 April 2011 11:06:12(UTC)
Rank: Super forum user
firesafety101

Personally I would go back to the fire risk assessment and review the decision for torches. This is a workshop with 8 people employed and when the lights go out the place is in total darkness. No borrowed lighting at all and 8 people all lost in the dark. Emergency lighting is required in this instance. Just think about those 8 people all trying to find the torch in the dark. What if the first person locates the torch how long will they wait until all 8 persons are together to make their way out. This is design and fabrication, any chance of the occasional trip hazard that would not be seen by torchlight? How are tables and benches arranged, are they all in a nice neat straight line with walkways always clear? Imagine the flames licking at their backsides while they wait for the last person to arrive? This is a no no. You cannot use cost as the prohibitive reason for not providing the correct equipment for fire safety. How much is a life worth? IMHO.
bkjeffrey  
#13 Posted : 03 April 2011 18:36:36(UTC)
Rank: New forum user
bkjeffrey

Can you foresee the torched being used in conjunction with the extinguishers as an aid to fire-fighting, or, will they most likely be for evacuation purposes or simply finding your way around in the event of a loss of internal lighting ? If you're going to use them as an aid in fire extinguishment then people will quickly run out of hands, if they are for evacuation purposes in the event of a fire then be careful where they are positioned as you may lead people further into the risk area if you're not fitting a torch at every extinguisher. In the event of a loss of lighting you could be aware of what route people will be most likely to take to get to the torches, I'm thinking about machinery, stairwells etc, and any other risk that the retrieval of the equipment might pose to them. Training is always a key issue and making realistic fire training, putting people under pressure as they certainly will be in the event of a fire emergency is again something to think about, lots of fire training tends to be a little too nice for my liking.
Phillip Clarke  
#14 Posted : 03 April 2011 20:58:48(UTC)
Rank: Forum user
Phillip Clarke

Without seeing the actual FRA and walking around your premises it is difficult to make an assessment. However, I have never seen any fire risk assessment recommend torches at fire extinguisher points as an emergency lighting system. I have never seen torches placed by fire extinguishers either. This past year I must have assessed over 150 FRAs in a large number of organisations from 1 woman to over 400 personnel. One might have an emergency bag near the main emergency exit along with various hi viz vests with roles on them, megaphone, a torch, building plans and nominal rolls. But torches in lieu of emergency lighting? Personally I do not see this as a sensible suggestion. How large is your building? To me 'small' and 8 personnel would suggest not that large and complicated - My advice? Check the qualifications and experience of your H&S consultants in relation to FRAs!
SNS  
#15 Posted : 03 April 2011 22:49:59(UTC)
Rank: Super forum user
SNS

Was at a CPD seminar last week, Orbik Electronics and Lighting (http://www.orbik.co.uk/ [no connections to them]) had a very good presentation on lighting a signage requiments. I will ask them if I can forward it to people not attending, or if you contact Barry Williams - Tech Director he they may send it to you. Luminescent signs alone will be outside the regulations in the near future (if not already - I need to check), with more changes on pictograms coming into effect at EU level and cascading down in about 3 - 4 years. Torches 'may' be used but must be the correct type - in a charger with an indicator to show that the supply is working and as part of a proper assessment and strategy. Concur with Phillip on checking the competencies of your consultant.