firesafety101  
#1 Posted : 21 June 2011 16:37:14(UTC)
Rank: Super forum user
firesafety101

I did a fire risk assessment this morning, a detached building of three floors used as office accommodation. It is an old building with a central timber staircase - that is the only access to/from the first and second floors. Each of the landings has three of four timber doors opening inward but access is directly into the staircase (no lobby). There is also a half landing with kitchen (kettle, toaster, microwave, fridge etc.) The ground floor has three doors opening into the staircase enclose. None of the doors are FR and some do not have self closers. In my opinion, as it is the only means of escape all doors opening into the staircase enclosure should be FR30 complete with door sets etc. I would like a second opinion from you people out there and, how to go about informing the RP that he requires all those fire doors. Please bear in mind he rents out just two of the offices at present - five offices are unoccupied so not a lot of income being generated at present. I believe this is the first fire risk assessment done for this building?
Safety Smurf  
#2 Posted : 21 June 2011 16:56:58(UTC)
Rank: Super forum user
Safety Smurf

Hi Chris, If the two offices he rents out at present are on the ground floor I'd recommend he does it before he gets anymore tennants in. That way he could wait for the security of the promised extra income before having to make any outlay.
firesafety101  
#3 Posted : 21 June 2011 17:21:31(UTC)
Rank: Super forum user
firesafety101

Foiled again Smurf - one ground and one first. The RP actually uses the second floor himself. I suppose I should have mentioned the premises are owned by a pension fund. Does that make any difference as they probably have lots of money but every penny spent means less pension for all?
David Bannister  
#4 Posted : 21 June 2011 17:36:32(UTC)
Rank: Super forum user
David Bannister

Perhaps it is feasible to replace the doors from the occupied units now and do the others when and as they become occupied, on the basis that the risk of fire is greater from within the occupied areas, assuming the exposure from squatters/arsonists is not great. Keep the doors to the vacant units securely locked. That would probably be my pragmatic approach.
bleve  
#5 Posted : 21 June 2011 19:45:43(UTC)
Rank: Super forum user
bleve

I am probably precluded from answering as I am an uncaring or possibly dispassionate or hard hearted Fire Risk Assessor. However, I would deliver the bad news that in the case described, that they should be providing a protected lobby at the first floor or providing smoke control within the stair case. In the case that only the ground floor is currently occupied, I would not be too concerned, but my written recommendations within the FRA would be protected staircase throughout, protected lobby at first floor or smoke control throughout. Ability to finance compliance is not my problem and should not influence my findings. Maybe harsh but fair and keps me out of harms way. Of course, in these more enlightened times, you may well be able to demonstrate the case that the existing doors are capable of restricting smoke and fire spread beyond the time required to effect a complete evacuation based on occupancy, detection/alarm design coupled with fire load, calculated fire growth and fire effluent production versus obscuration, tenability during the required or calculated time required to reach a place of ultimate safety, but hey, as we all know FRA is not rocket science, we only have to follow guidance notes etc, etc. Regards
firesafety101  
#6 Posted : 21 June 2011 20:42:04(UTC)
Rank: Super forum user
firesafety101

bleve I would much rather have you with me than against me! Don't be so hard on yourself - you are only saying it is it should be said. You mentio the guidance notes etc. - the guide suggests that if the travel distance can be met there may be no need to protect the stairway - does anyone else see this ? You have stirred up something I was thinking about actually, that suggestion of the existing doors being capable of restricting smoke enough to enable escape. Every door is a solid timber door and they all close positively into the rebate. Some do not have closing devices and none have smoke seals. I know it is not your decision but "what if" all doors were positively self closing, the alarm is fully operational, there is smoke detection right through the building and it will be low risk once all measures have been taken?
bleve  
#7 Posted : 21 June 2011 21:23:15(UTC)
Rank: Super forum user
bleve

Self closing doors with 25 mm rebate and calculation of likely time to and degree of smoke obscuration coupled with likely time to incapacitation versus time to escape may well prove no further action is necessary. you still need to demonstrate this by calculation and ra. further detail on fire loading and may be able to advise
bleve  
#8 Posted : 21 June 2011 22:49:02(UTC)
Rank: Super forum user
bleve

Chris, To my mind, travel distance should be a maximum of 18 m including 3 m from stair to final exit. If typical office fire loading, then I can’t see CO2 and CO values resulting in significant smoke obscuration and detrimental effect on tenability. Similarly radiant heat flux resulting in inability in escape or anticipated incapacity should also not be an issue .i.e. I can't see exposure to 4.5 kW/m^2 (160 ° C) in excess of 60 seconds being an issue. I would review extent of rebate at the doorframes, recommend provision of self-closing devices and ensure installation of an L3 fire alarm system as a minimum. above is based on fully ambulant occupancy!!!!!!
firesafety101  
#9 Posted : 21 June 2011 23:15:17(UTC)
Rank: Super forum user
firesafety101

L3 system already in place. I agree with closers, the problem is however there is no guarantee that the doors will not be wedged open. That goes for FR doors as well. An open fire door is not a fire door!
Heather Collins  
#10 Posted : 22 June 2011 09:00:07(UTC)
Rank: Super forum user
Heather Collins

Chris - there's never a guarantee that the occupants won't in some way interfere with the fire precautions provided. What do you base your comment on in this case? Did you actually see doors wedged open (or conveniently placed wooden wedges on landings?)
Safety Smurf  
#11 Posted : 22 June 2011 09:14:47(UTC)
Rank: Super forum user
Safety Smurf

ChrisBurns wrote:
Foiled again Smurf - one ground and one first. The RP actually uses the second floor himself. I suppose I should have mentioned the premises are owned by a pension fund. Does that make any difference as they probably have lots of money but every penny spent means less pension for all?
It's quite normal for pension funds to invest in property. I wouldn't even take that into consideration, it's the rent he pays that funds the pension schemes.
PhilSmith1981  
#12 Posted : 22 June 2011 09:18:11(UTC)
Rank: Forum user
PhilSmith1981

Chris, I don't know if this will be of any use to you. http://www.communities.g...ents/fire/pdf/151543.pdf Regards, Phil
MB1  
#13 Posted : 22 June 2011 09:38:09(UTC)
Rank: Super forum user
MB1

Hi Chris, No mention of what you have discovered regarding ignition sources, fuel etc... mounds of paper files stacked anywhere... you could also mention lots of timber - non fire retardent as excelent fuel and spread of fire too!
firesafety101  
#14 Posted : 22 June 2011 10:00:47(UTC)
Rank: Super forum user
firesafety101

Morning all. MB1 everything is nice and tidy, bins emptied regularly, no stacks of rubbish anywhere. The only thing out of place was the Mantrap on the upper landing. (vacuum cleaner). That was quickly dealt with. Phil I already have and use that document, thanks. Heather, you are right. The office doors were wedged open. I believe the occupants like to feel the extra space and also to see who is coming up the stairs. Unoccupied offices are kept locked. I believe they would still be wedged open if they were fire doors. There are door retainers on the market that operate to close the door on operation of the fire alarm, I might be recommending these. Thanks all - don't stop yet as I still have the writing up to do.
Safety Smurf  
#15 Posted : 22 June 2011 10:18:05(UTC)
Rank: Super forum user
Safety Smurf

Hi Chris, What sort of building structure is it? I'm imagining a late 19th early 20th century large house? What is the rest of the structure like? If FD30's were fitted would they be the only thing left after 15 minutes?
MB1  
#16 Posted : 22 June 2011 10:28:52(UTC)
Rank: Super forum user
MB1

quote=Safety Smurf]Hi Chris, What sort of building structure is it? I'm imagining a late 19th early 20th century large house? What is the rest of the structure like? If FD30's were fitted would they be the only thing left after 15 minutes?
Had a very similar experience with a small retail property where FD30's were installed in the occupied areas and unoccupied floors were secured to detract people to use for stock or other usage, the occupiers hadn't installed detection systems to them!
messyshaw  
#17 Posted : 22 June 2011 10:40:08(UTC)
Rank: Super forum user
messyshaw

What is the travel distance from top room to final exit? If it's within 18m (or not far off), with no fire loading in the stairs and with positive self closers (assuming the doors are solid and well fitting with suitable rebates), wouldn't the L3 system be a suitable mitigating control measure? BS5839 suggests a cat M system for small office buildings. So, as a L3 system may even represent detection in every room in a single staircase building, and considering the risk associated with non sleeping occupants in a building they are familiar with - wouldn't this be enough? Of course, it's almost impossible to make any such assumptions blind, as fire loading, layout, general condition of the premises and other matters would need to be considered. But as this is a low risk environment with an OTT detection system, maybe that's enough. As far as occupiers wedging doors; seems to me that as long as the risks associated with wedging (or interfering with any FS measure) has been recorded in the FRA, then it's responsibility of the RP to maintain the measures and not the assessors
firesafety101  
#18 Posted : 22 June 2011 10:56:40(UTC)
Rank: Super forum user
firesafety101

Smurf you are spot on re the building and a good assessment although the premises are in good condition, good decor, no damage needing repairs etc. Good solid walls, ceiling in good condition - it has been well looked after. Messey the travel distance exceeds 18 m including the distance along the two flights of stairs, Can someone describe the difference between "normal fire risk and lower fire risk" If it is the latter 25 m is acceptable. I take the point re recording wedging doors and notifying the occupiers.
Safety Smurf  
#19 Posted : 22 June 2011 11:24:38(UTC)
Rank: Super forum user
Safety Smurf

I remember being told during my training that the only thing likely to be considered low risk would be an unoccupied concrete building full of wet fish. Personally I would probably class what you have described as normal fire risk
firesafety101  
#20 Posted : 22 June 2011 12:26:33(UTC)
Rank: Super forum user
firesafety101

Unoccupied but full of wet fish? Something fishy about that all right. ha ha. i would say that would be No risk. There must be a definition of lower fire risk?
Safety Smurf  
#21 Posted : 22 June 2011 13:23:30(UTC)
Rank: Super forum user
Safety Smurf

I beleive it's a combination of fuel, sources of ignition, occupancy and complexity of the building. Basically, everything has to be the lowest risk in it's own right before the overall level of risk can be considered as low. Nearly all of mine would be low if it wasn't for a high fire loading.
bleve  
#22 Posted : 22 June 2011 13:45:14(UTC)
Rank: Super forum user
bleve

Not necessarily, you can have a high fire loading with slow growth rate and low fire loading with an ultra fast growth rate. Lower risk would apply if: 1. The occupants are awake and familiar with the building and 2. Slow fire growth rate. Current wisdom suggests that offices typically are defined as presenting a medium fire growth rate. Accepted risk profile would be A2 and a fire safety management level 2 would apply in this instance. I can't see the case that Management level 3 would be acceptable or that the building would be classed as an A1 risk profile. However, if you can demonstrate that this is the case, go for it. My advise is that A2 provides a reasonable degree of protection for you and your FRA.
bleve  
#23 Posted : 22 June 2011 14:24:33(UTC)
Rank: Super forum user
bleve

Chris, I would make the argument for the use of the accommodation stair and support this by way of risk assessment. A2 risk profile will result in a maximum travel distance of 22 metres in single direction. Also don’t forget that rooms with high ceilings are safer than rooms with lower ceilings as they have a greater capacity to hold smoke and delay the time taken to fill with smoke to a level that affects escape. For rooms with high ceilings, it is permissible to increase the travel distance, in the case of period buildings with ceiling heights >3 metres < 4 metres, travel distance can be extended by 5%.
Safety Smurf  
#24 Posted : 22 June 2011 14:30:30(UTC)
Rank: Super forum user
Safety Smurf

That's a good point. A building of that discription and from that era will probably have ceilings at 10ft.
firesafety101  
#25 Posted : 22 June 2011 14:40:14(UTC)
Rank: Super forum user
firesafety101

bleve you are a mine of information, thanks for that little gem. In reality and speaking in words of one syllable this building would be empty of people within one minute of the fire alarm sounding, especially with so few occupiers at present. What I am thinking of recommending with regard to the stairway is all doors to be fitted with self closers, no wedges to be used and all occupiers to be instructed in the reasons for protecting the stairway. On discovering fire evacuate the room/s affected and immediately sound the alarm. On hearing the alarm evacuate to the assembly point and take the roll call. On the way out anyone can pick up an extinguisher to carry with them in case they need it on the way down. Ensure someone has called the brigade. Further recommendations for fire drills with the alarm actuated to familiarise everyone with the procedure on operation of the alarm. I haven't finished yet - just awaiting some further info. Thanks again to you all. I think this has been a good little exercise.
firesafety101  
#26 Posted : 22 June 2011 18:47:30(UTC)
Rank: Super forum user
firesafety101

I've finished this assessment. Had a chat with my customer and we agreed that I should require the fire doors along with a few other issues. Thanks to all for your assistance, as I said earlier I think this has been a good little exercise and I think a few of us can learn from it. That's what I like about this forum.
Wizard  
#27 Posted : 23 June 2011 11:01:10(UTC)
Rank: Forum user
Wizard

Chris, Can I ask if this building has building regs approval from Local Authority i.e maybe change of use? Regards Wizard
firesafety101  
#28 Posted : 23 June 2011 11:33:38(UTC)
Rank: Super forum user
firesafety101

Good point wizard but the building has been offices for donkeys years.