bovovey  
#1 Posted : 10 August 2011 21:43:41(UTC)
Rank: Forum user
bovovey

I'm wondering if anyone has any experience on cast iron support columns in an old mill building please. The building is single storey and originates from the early 1900s. I know that cast iron columns are notorious for being brittle (from HSE misc 157), but I have seen a builder, who is constructing blockwork partitions, fixing the wall ties to the cast iron columns using a nail gun. The builder is insisting that it is perfectly fine. I'll admit that it does seem to hold the ties, but I have concerns that such action could damage the structural integrity of the columns. I've trawled the web but can find nothing refering to nailing into cast iron columns. Has anyone come across this type of work? Any information is most gratefully received.
firesafety101  
#2 Posted : 10 August 2011 22:14:00(UTC)
Rank: Super forum user
firesafety101

Don't know about nails into cast iron columns but I do know that when involved in fire, water will just make them collapse due to their brittle quality as you say.

Good luck, I will watch this one with interest.

boblewis  
#3 Posted : 10 August 2011 23:25:51(UTC)
Rank: Super forum user
boblewis

I am not sure that cast iron is a suitable substrate for shot fixings. This is due to its very brittle nature. I would contact the manufacturers of the gun used for advice. Both Hilti and Spit have very good advice teams. The columns may be weakened by every fixing made.

Bob

bob youel  
#4 Posted : 11 August 2011 11:24:49(UTC)
Rank: Super forum user
bob youel

Listen to Bob as I sure that such practices are not suitable and sufficient

Stress is built up in the cast iron which can manifest itself as a brittle failure / deformation at a later period especially so as impurity in the 1900's was a big problem and impurities are a prime factor in failure of cast materials. Luckily such columns were over engineered otherwise more would have collapsed but by undertaking such actions the structural strength is probably compromised

The client should have somebody in place to appraise and confirm the system of work e.g. A structures expert who specialises in mechanical - fabrication engineering [as against a civils only expert] / metallurgist or similar and I have yet to meet a day to day builder who knows about the structural integrity of metals especially exotics and casts or, in most cases, cares about the subject

Once the builder is off site and paid the problem lies with the client and this appears to be yet another case of the client being given poor advice

Is this a notifiable job? If so was the CDMC suitable for the work in hand
bovovey  
#5 Posted : 11 August 2011 11:48:49(UTC)
Rank: Forum user
bovovey

Thanks for your help so far - it is confirming my suspicions. I've called Hilti and their technical team said 'suck it and see' something I'm not happy with when it comes to structural integrity. Another builder is suprised the shot fixing has not already shattered a column.

Bob, the background to it is that the builders are spending a week putting up some partitions. It is a meduium sized factory move that has been planned for some time and a CDMC will be needed, and very likely a structural engineer. I'm afraid the client has been very secretive and busy haring off without discussing matters with anyone - until now.
m  
#6 Posted : 11 August 2011 12:49:30(UTC)
Rank: Super forum user
m

An alternative is to contact a foundry that still casts iron, there must be some left. They may be well placed to answer your question.
peter gotch  
#7 Posted : 11 August 2011 12:53:21(UTC)
Rank: Super forum user
peter gotch

I think your client needs to get a structural engineer with extensive experience of historic structures (not lot of people meet this person spec) before the builder finishes putting up the partitions! Preferably before they continue to carry out work liable to damage the columns.
Graham Bullough  
#8 Posted : 11 August 2011 19:26:12(UTC)
Rank: Super forum user
Graham Bullough

Over the years numerous redundant old textile mills incorporating cast iron columns and located in various parts of the UK have been converted with interior partitions to create domestic flats and industrial units. Thus, it should be reasonably feasible to find structural engineers and others with appropriate experience and knowledge of affixing partitions of various types to cast iron columns.

My late dad was involved with cotton mills and their machinery in his teens and twenties, and once told me that cast iron columns were extremely strong in compression (probably over-engineered in many cases with greater-than-necessary wall thickness), but pretty weak if exposed to tension or shock. Therefore, any lateral forces applied to such columns should be kept to a minimum and balanced, whether applied via fixings inserted into them or via non-invasive 'bolt around' fixings. It might be worth having a look at the nature of fixings, if any, on/into such columns if you can. Also, if you know of any industrial premises which have such columns and remain in use, their engineers might be willing to tell you about the types of fixings used and also give you a rough idea about what loadings can be imposed without incurring problems.

If invasive type fixings can be used, my inexpert guess is that drilling holes for such fixings is likely to be a far better method than any which involve single impact like a nail gun or repeated percussion as with a hammer.
paul.skyrme  
#9 Posted : 11 August 2011 19:29:49(UTC)
Rank: Super forum user
paul.skyrme

Stop the job now and kick the contractor off site for incompetence.
Historical cast iron is inhomogeneous.
It is full of stress raisers, whilst cast iron in general in good condition is excellent in compression, it is already full of stress raisers, you are adding to the static load and the stress raising points by this action.
Even historic cast iron is excellent in compression see Eifel Tower & Iron Bridge as examples, cast iron in compression & wrought iron in tension.
No material fails in compressive loading ever.
All failures come from tensile loading, in this situation you are increasing the surface tensile load of the columns above that of the original design, even though there would have been significant safety factors included in this design, and you are adding stress nucleation fracture points in the material structure to promote catastrophic failure of the surface of the columns which will be in tension due to the compressive loading by the insertion of the shot fired nails.
Get someone to do the maths then if it works out you will be fine.
If you do engage a structural engineer, even a historic specialist please ensure that they have sufficient competence in the fracture mechanics and the failure of stressed metallic materials to assess this application correctly.
Zimmy  
#10 Posted : 11 August 2011 19:35:11(UTC)
Rank: Super forum user
Zimmy

Stop work and as Paul says.. get shot of him (no punn)
Jane Blunt  
#11 Posted : 12 August 2011 08:44:25(UTC)
Rank: Super forum user
Jane Blunt

paul.skyrme wrote:

No material fails in compressive loading ever.


Not strictly correct. Materials can fail in compression by a variety of mechanisms - yielding, buckling and even brittle fracture.

You can do simple demonstrations to show this.

Compress a piece of lead shot and it comes out like a pancake - yielding
Take a drinking straw and push the ends - it bows - buckling.
Put a piece of glass in the jaws of a vice and close the jaws hard - brittle fracture
bovovey  
#12 Posted : 12 August 2011 15:01:03(UTC)
Rank: Forum user
bovovey

Thank you very much everyone, your input and knowledge has been very useful and is greatly appreciated. The client has kept the builder on site and will not consult a structural engineer citing cost. They have now ceased shot fixing, not from advice, but because some of the fixings will not enter the columns. They are now drilling and tapping.

I'll be speaking to them about the CDM Regs but fear that this will be swept aside. Naturally, I'll be keeping copies of my correspondence with the client, so on their head be it - I just hope not literally. It really makes me want to walk away, but then the workforce will be left with no-one to promote and improve safety matters.

Many thanks again. Paul.
paul.skyrme  
#13 Posted : 12 August 2011 17:47:51(UTC)
Rank: Super forum user
paul.skyrme

Jane Blunt wrote:
paul.skyrme wrote:

No material fails in compressive loading ever.


Not strictly correct. Materials can fail in compression by a variety of mechanisms - yielding, buckling and even brittle fracture.

You can do simple demonstrations to show this.

Compress a piece of lead shot and it comes out like a pancake - yielding
Take a drinking straw and push the ends - it bows - buckling.
Put a piece of glass in the jaws of a vice and close the jaws hard - brittle fracture


Sorry Jane we will have to agree to disagree on this one I suspect.
Your first example is not the failure of the material due to compression, it is the material being deformed.
Your second again is not a failure as the material has not failed it has deformed.
The glass does not fail in compression it fails in tension, check your T353 course notes! ;)
The devil is in the detail, in this case it is how you define failure I suspect, I defined it in relation to the OP as catastrophic failure.
The cast Iron in the OP is prone to brittle fracture is is not a ductile or malleable material.
paul.skyrme  
#14 Posted : 12 August 2011 17:48:55(UTC)
Rank: Super forum user
paul.skyrme

bovovey wrote:
Thank you very much everyone, your input and knowledge has been very useful and is greatly appreciated. The client has kept the builder on site and will not consult a structural engineer citing cost. They have now ceased shot fixing, not from advice, but because some of the fixings will not enter the columns. They are now drilling and tapping.

I'll be speaking to them about the CDM Regs but fear that this will be swept aside. Naturally, I'll be keeping copies of my correspondence with the client, so on their head be it - I just hope not literally. It really makes me want to walk away, but then the workforce will be left with no-one to promote and improve safety matters.

Many thanks again. Paul.



Drilling and tapping is still creating fracture nucleation points!
You may be torn between the devil and the deep blue sea here as the old saying goes!
johnld  
#15 Posted : 12 August 2011 20:02:15(UTC)
Rank: Forum user
johnld

If my memory serves me correctly HSE and Courtualds carried out research into the structural properties of Cast Iron columns in the 1970’s

This followed the failure of columns in some of the very old mill buildings.

I do not know what happened to the research papers but I guess they are in an HSE archive somewhere

HSE also issued some guidance note reading the columns at about that time. I think it is the note that is referred to in the postings
Jane Blunt  
#16 Posted : 13 August 2011 08:48:14(UTC)
Rank: Super forum user
Jane Blunt

paul.skyrme wrote:
Jane Blunt wrote:
paul.skyrme wrote:

No material fails in compressive loading ever.


Not strictly correct. Materials can fail in compression by a variety of mechanisms - yielding, buckling and even brittle fracture.

You can do simple demonstrations to show this.

Compress a piece of lead shot and it comes out like a pancake - yielding
Take a drinking straw and push the ends - it bows - buckling.
Put a piece of glass in the jaws of a vice and close the jaws hard - brittle fracture


Sorry Jane we will have to agree to disagree on this one I suspect.
Your first example is not the failure of the material due to compression, it is the material being deformed.
Your second again is not a failure as the material has not failed it has deformed.
The glass does not fail in compression it fails in tension, check your T353 course notes! ;)
The devil is in the detail, in this case it is how you define failure I suspect, I defined it in relation to the OP as catastrophic failure.
The cast Iron in the OP is prone to brittle fracture is is not a ductile or malleable material.


Paul, you are taking a much too narrow view of failure. In engineering, failure has a broader definition, because, for example, if a safety critical piece of material buckles, the structure fails. To analyse structural integrity you have to take this leap.

I do not dispute that yielding and buckling are simply deformation (and the latter may be purely elastic), and do not result in the material falling into pieces. However, here we are dealing with a structure, so such events can, and do, lead to collapse of a structure. Incidentally, buckling of a column in compression gives rise to tensile and compressive stresses on the surface of the column as it deforms, so is extremely important in this instance.

As for glass failing in compression - ceramics, if compressed sufficiently, will fail, by the propagation of cracks at an angle to the applied stress. This is why I suggested the simple experiment. It is evident that you can cause ceramics and other brittle materials to fail when you apply a compressive load to them. Ceramics and other brittle materials are often orders of magnitude stronger in compression than in tension, but they can and do fail. Since many of them have very little capacity to yield, the failure tends to be catastrophic (dustpan and brush job).
johnmurray  
#17 Posted : 13 August 2011 09:48:18(UTC)
Rank: Super forum user
johnmurray

In certain circumstance the bolting method will also lead to [eventual] failure.

"Another common cause of structural failure is water ingress between sections of cast iron, particularly if previous remedial work has been carried out using stainless steel bolts which have not been isolated using nylon washers. In the presence of moisture, this rapidly leads to bimetallic corrosion and subsequent corrosion and cracking in the area surrounding the bolts"

http://www.buildingconse...titch/castweldstitch.htm
firesafety101  
#18 Posted : 13 August 2011 20:53:57(UTC)
Rank: Super forum user
firesafety101

bovovey wrote:
Thank you very much everyone, your input and knowledge has been very useful and is greatly appreciated. The client has kept the builder on site and will not consult a structural engineer citing cost. They have now ceased shot fixing, not from advice, but because some of the fixings will not enter the columns. They are now drilling and tapping.

I'll be speaking to them about the CDM Regs but fear that this will be swept aside. Naturally, I'll be keeping copies of my correspondence with the client, so on their head be it - I just hope not literally. It really makes me want to walk away, but then the workforce will be left with no-one to promote and improve safety matters.

Many thanks again. Paul.


This reply makes me think about why do we keep notes in case something happens?

We are all now aware that cast iron should not be tampered with as in the thread so why not take the issue that bit further to prevent the potential accident from occurring?

I often hear lots of people say "make sure you keep the records to prove you told them ..........???????

My point is find out who or what is the next step up and take your concerns there.
achrn  
#19 Posted : 15 August 2011 08:59:58(UTC)
Rank: Super forum user
achrn

Don't use shot fixings into historic cast iron. I think the thread has established that already.

However, there were some other comments that I would like to note:

Someone suggested contacting a foundry that still casts iron. Treat that approach with caution - modern and historic cast irons can be quite different materials, due to changes in manufacturing processes and furnaces and so on. You need to distinguish between grey, white, malleable and more recently spheroidal cast irons. A modern producer of cast iron does not necessarily know about the characteristics of historic iron.

Secondly, there was a proposal to drill (or drill and tap) cast iron. It can be done, but it's something to be avoided if you possibly can. Drilling cast iron can provoke a fracture, and certainly leaves you with a stress concentration detail. If you tap the hole it's worse.

On the positive side, if it's columns the cast iron is generally pretty good in compression. While doing these things to any cast iron is a bad idea generally, it's a worse idea to do it to iron in tension than in compression. I have seen shot-fired fixings in tensile faces of historic cast iron beams, but I would not have anything to do with a scheme that involves them.