The electrical isolation, can we consider an ESD (emergency stop device/ push button) as a safe point of isolation?. It's noticed during a site audit a piece of electrical equipment was isolated with its ESD button at the control panel & there was no locking device, but its tagged.
Can we accept?
|
|
|
|
Rank: Forum user
|
This would depend on the type of equipment it was isolating and the specification of the ESD, it must isolate both the phase and neutral conductors of the circuit
|
|
|
|
Rank: Super forum user
|
There is no way that this could, in my opinion, be classed as an isolation. That is because it does not ISOLATE as I understand it - this is not just has to break the current path as was said above, but it should not be easily removed, which is the purpose of "lockoff".
|
|
|
|
Rank: Forum user
|
Even if the isolation is "correct" my view is that a label is not a secure way of ensuring it remains isolated for the required duration and a lock is essential. It is possible of course that the power source is also locked out further up the line and the E-Stop is a secondary isolation.
|
|
|
|
Rank: Super forum user
|
On the face of it, no - unacceptable, not safe isolation for maintenance purposes.
|
|
|
|
Rank: Super forum user
|
I tend to agree that this isn't likely to be a safe method of, or probably not by definition - isolation.
One of the main issues is whether the power could be restored 'intentionally' while any maintenance is still ongoing?
Some form of robust locking off system would seem appropriate.
|
|
|
|
Rank: Super forum user
|
|
|
|
|
Rank: Super forum user
|
Vinod - you need look no further!!!!
|
|
|
|
Rank: Super forum user
|
quote=vinod]The electrical isolation, can we consider an ESD (emergency stop device/ push button) as a safe point of isolation?. It's noticed during a site audit a piece of electrical equipment was isolated with its ESD button at the control panel & there was no locking device, but its tagged.
Can we accept?
No it is not isolation in terms of the supply, it maybe that it is what I call "control isolation"
Does this e stop simply isolate the control desk preventing accidental activation whilst an operator is close to the line / machine, if so it is acting similar to an electrical interlock fitted to a safety gate would do, and can be acceptable depending on the circumstances.
Steve
|
|
|
|
Rank: Super forum user
|
Emergency switch is not a short cut to isolation, Lock out tag out should be used on all machinery,
|
|
|
|
Rank: Super forum user
|
An emergency stop button is by definition NOT isolation.
Depending upon the work being done and the detail design of the control system, it can be completely safe to undertake certain tasks with the use of only the machine emergency stop button, however, this must be under control of the person undertaking the tasks at all times and a SSW with tags outs etc. must also be in place.
|
|
|
|
Rank: Super forum user
|
Pressed the wrong button! Sorry.
Oh to be able to edit...
Also the OP does not say what was being undertaken, why the isolation was required, what the tag was for etc.
As my opening line says the EM Stop is NOT isolation of anything.
It merely disables certain aspects of the machine control system.
If isolation is required then isolation must be done, and as far as electrical works go then that means disconnecting all live conductors from the source of energy.
This may not be at the first energy inlet at the machine, i.e. the main machine isolator, it could be at a downstream isolation device which as long as it meets the requirements would be OK.
This would depend on the item of equipment being maintained.
|
|
|
|
Rank: Forum user
|
|
|
|
|
IOSH forums home
»
Our public forums
»
OSH discussion forum
»
Electrical isolation- with emergency stop button
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.