Welcome Guest! The IOSH forums are a free resource to both members and non-members. Login or register to use them

Postings made by forum users are personal opinions. IOSH is not responsible for the content or accuracy of any of the information contained in forum postings. Please carefully consider any advice you receive.

Notification

Icon
Error

Options
Go to last post Go to first unread
RayRapp  
#1 Posted : 28 February 2012 15:40:26(UTC)
Rank: Super forum user
RayRapp

Whilst checking an asbestos survey of a few years ago I noticed it was a type 2 survey. However, the type 1,2&3 surveys have now been replaced with a management survey and refurbishment/ demolition survey. I wonder how valid the type 2 survey is now that the requirement has changed? Comments and suggestions welcome - cheers.

Ray
Ron Hunter  
#2 Posted : 28 February 2012 15:51:08(UTC)
Rank: Super forum user
Ron Hunter

If it was a good survey then, it should still be fit for purpose. Otherwise there's nothing much between an MDHS100 Type 2 then and an HSG wotsit Management Survey now.
There were some real quality issues some years back when Reg4 was new and an over-stretched market tried to meet client demand. Most common problem we had was with areas of "silence" or "access not available" (when in most cases access was readily available).
Common fault in years past was the external Surveyor not being accompanied by someone who knew the premises.
PH2  
#3 Posted : 28 February 2012 15:57:04(UTC)
Rank: Super forum user
PH2

Ray,
I have been involved in number of demolition and re-furbishment projects that had old Type 2 surveys. They were totally inadequate; they were not invasive enough and had too many caveats to be of any real use. Had to commission new refurb' / demolition surveys that were more substantial and ultimately more useful. The Clients, needless to say, were not too happy at having to pay "again", but finally persuaded them of the necessity and when they compare the new surveys with the older one's they were able to see the differences. Grudging acceptance.

PH2
ODonnell19538  
#4 Posted : 28 February 2012 16:01:37(UTC)
Rank: Forum user
ODonnell19538

Ray

I agree with the comments of the other posters. I think it all boils down to how thorough your Type 2 survey was in the first place and how competent the asbestos surveyors were who carried out the work. The new survey guide, which details the requirements for the Management and Refurbishment/Demolition surveys appears to have been issued to address shortcomings in the standards of many Type 2 surveys and the quality of information that was being presented to clients under the old MDHS 100 guidance. If the information derived from Type 2 surveys is accurate, contains a minimum of exclusion clauses and can be relied on with some degree of confidence then I cannot see the need to 'upgrade'.

Danny
RayRapp  
#5 Posted : 28 February 2012 16:21:11(UTC)
Rank: Super forum user
RayRapp

Thanks guys, you have pre-emptied my next question - how reliable are older type 2 surveys? The sample one I have viewed appears inadequate because it is not intrusive enough and full of caveats...sound familiar.

Asbestos issues, don't you just love 'em!
Canopener  
#6 Posted : 29 February 2012 13:44:36(UTC)
Rank: Super forum user
Canopener

I don’t disagree as such with most of what has been said, however; that a type 2 survey would be ‘..totally inadequate..’ for the purposes of demolition or ‘major’ refurbishment, goes without saying. This was never the intention of the type 2 survey. Under MDHS100, both type 1 (presumptive) or type 2 (sampling) surveys were management surveys and neither was intended to be full access or fully intrusive surveys; that would have been a type 3 survey.

The adequacy of ‘old’ type 2 surveys and for that matter surveys conducted under 264 is dependent on a number of factors, some of which are in the gift of the client rather than the surveyor. The results of a type 2 survey may still be adequate for the purposes of refurbishment, if the survey actually had access to the area that is being refurbished.

I think it would be incorrect/unfair to suggest that a type 2 survey is inherently ‘unreliable’ or necessarily any less reliable than a management survey under 264.

While I note the HSE’s ‘take’ on caveats in 264 on caveats, of course some caveats are perfectly reasonable and understandable. Whether we like it or not, they are an almost inevitable feature of our work.
bod212  
#7 Posted : 01 March 2012 07:47:32(UTC)
Rank: Forum user
bod212

The room/ area/ building/ premises were surveyed under MDHS100 as a 'Type 2' survey. The survey report should have recommended re-inspections (3/6/9/12 monthly?). the transition to a 'Management' survey as defined in HSG264 should in theory be relatively seamless. Yes, the Client may have to pay for the report upgrade as it were. But if the 'Type 2' survey was fit for purpose then with some tweaking, the 'Management' survey should be as well. If, however, the survey has been done 'a few years ago' and the area never revisited the duty holder is in breach of CAR2006. Similarly, if there were caveats in the 'Type 2' that can now be justifiably dispensed with under a 'Management' survey, then a fresh survey might be the way to go. So, to answer your question, the original survey is not valid, but, may inform the update/ upgrade/ revisit of any new survey.
RayRapp  
#8 Posted : 01 March 2012 09:28:17(UTC)
Rank: Super forum user
RayRapp

There is a re-occurring issue with asbestos surveys, many of which are not sufficient and suitable in the first place. In my experience very few duty holders actually bother to re-inspect at all, never mind 3/6/12 month intervals, which of course does question the validity of the surveys if they are several years old. Despite the requirement pursuant to CDM regs for pre-construction information and Reg 4 of CAR, many clients are not fulfilling their duty which then escalates down the contractor chain.

I believe the problem stems from the fact that CDM Regs and to a lesser extent CAR, are not properly enforced, making a nonsense out of the whole process. Of course, PCs often allow clients to get away with this because industry is client driven. I find it bizarre, if that is the right word, how we practitioners discuss nebulous issues on these forums to the ength degree; yet the reality is basic h&s requirements are often ignored by duty holders - perhaps we are far too dedicated?
ODonnell19538  
#9 Posted : 01 March 2012 09:57:50(UTC)
Rank: Forum user
ODonnell19538

Gerry D

The Type 2 Survey would not normally contain recommendations for the periodicity of re-inspection of ACMs. The survey report would have included a material assessment score for each ACM, based on asbestos type and condition, etc,. However, it is generally recognised that the dutyholder organisation, with more intimate knowledge of building occupancy activities, is far better placed to carry out the subsequent priority assessment. The combined scores of the two assessments were intended to form the basis of the subsequent action plan, which should include periodic condition monitoring of ACMs which are to be left in situ.

The Duty to manage has not changed. The introduction of new survey guidance does not place any obligation on the dutyholder to ensure a ‘transition’ to the HSG264 management survey and incur the inevitable costs of doing so. If the Type 2 survey is fit for purpose and has been carried thoroughly by competent surveyors, why and how does it require to be ‘tweaked’?

Danny
jde  
#10 Posted : 01 March 2012 11:21:24(UTC)
Rank: Forum user
jde

The simple fact of the regulations are that you either have the Management survey (type2) in place or if the project involves refurbishment or demolition then you must have the Demo/Refurb survey carried out as it is an invasive survey. Do not accept the survey if it contains caveats at all. HSE inspectors do not appreciate any survey which contains caveats. It also means that a further survey of the inaccessible areas is required prior to works commencing.
bod212  
#11 Posted : 01 March 2012 12:37:48(UTC)
Rank: Forum user
bod212

O'Donnell19538

You are correct to say that a Type 2 survey does not state the periods for re-inspection. But the management plan that it should generate will. I understand fully the duty holder/ priority assessment thing too. The scenario given by the OP suggested a type 2 survey that was 'a few years old'. Survey reports should never get to being a few years old and I'm saying this making the assumption that the survey report had a management plan arising from it.
'Transition' was my word. There is nothing in the guidance instructing or obliging duty holders to upgrade or renew, but, a survey that is 'a few years old' is not an accurate survey in my opinion. If a duty holder decided to use one that is few years old, he is not exercising his duty in my opinion. My reference to 'tweaking' is easily explained. The parameters of MDHS100 are not the same as HSG264. HSG264 is much clearer and robust. Hence the need to potentially tweak what is already in place.
The duty to manage has not changed. The algorithms used for both material assessment and priority assessment have not changed either. Are you saying that having a survey report that is 'a few years old' is acceptable? The person tasked with the periodic reinspection should be generating something to embellish the original survey. This, in my opinion, would constitute 'tweaking'. The costs for doing this may be an internal thing, they may be an external thing. But the overriding concern must be that the ACM is 'managed' A survey that is 'a few years old' suggests that the management of ACMs has fallen below the standards outlined in HSG264. There is no 'overlap' period as such between MDHS100 & HSG264. But, if presented with a Type 2 survey I would be very wary indeed as it was prepared using guidance that is now over two years old.
ODonnell19538  
#12 Posted : 01 March 2012 13:35:57(UTC)
Rank: Forum user
ODonnell19538

Gerry D

I wouldn't necessarily agree with your sweeping assertion that ‘survey reports shouldn't get to being a few years old’. If you have had a thorough survey carried out, providing there has been no significant changes in terms of occupancy or building usage, ACM condition has been routinely monitored and remains unchanged, etc., then surely the information derived from that survey remains valid? Why pay for another survey to tell you what you already know? If anything, surely it will be the asbestos register rather than the survey report that gets ‘tweaked’ by regular updates?

Additionally, although the new guidance goes some way towards improving the standards of surveys and of the information presented to clients, there is still no guarantee that a management survey carried out under HSG264 will not contain omissions and mistakes. The quality of information will largely depend on the competence and experience of the surveyors and the stringency of quality control standards applied by the organisation involved.

Danny

Ron Hunter  
#13 Posted : 01 March 2012 17:08:46(UTC)
Rank: Super forum user
Ron Hunter

I think what Gerry means is that where the responsible person has done nothing with that Survey Report, i.e. not completed a Register or initiated condition monitoring etc. then we should be very wary indeed.
ODonnell19538  
#14 Posted : 02 March 2012 08:14:08(UTC)
Rank: Forum user
ODonnell19538

Ron

Accepted. However, having been recently approached by a UKAS accredited inspection body with the suggestion that I convince my client that surveys should ideally be re-done to bring them up to the standards advocated in the Survey Guide, I suspect that some may look on the new Survey Guide as another opportunity to make a killing. I know there were a lot of bad surveys carried out under the MDHS 100 guise, but I'm certainly not about to ask my client for another pot load of money to redo 300-odd Type 2 surveys which, with some exceptions, have proved to be perfectly satisfactory and fit for purpose in the first place.

Gerry

If there has been any misunderstanding on my part then I apologise. Nothing personal intended.

Danny

bwm  
#15 Posted : 02 March 2012 09:40:39(UTC)
Rank: Forum user
bwm

RayRapp wrote:
I believe the problem stems from the fact that CDM Regs and to a lesser extent CAR, are not properly enforced, making a nonsense out of the whole process.


Quite a bold statement. What changes would you suggest?
RayRapp  
#16 Posted : 02 March 2012 11:24:43(UTC)
Rank: Super forum user
RayRapp

Well now, in the first instance the HSE need to be more proactive, perhaps actively encouraging the reporting of non-compliance with regulations via a confidential reporting service. Hopefully this would lead to investigating and enforcement - without which there is no incentive for duty holders to comply. There should no be excuse for large organisations with the resources to manage projects not to comply with legislation.
HPhillips  
#17 Posted : 02 March 2012 11:53:46(UTC)
Rank: Forum user
HPhillips

Whilst I agree compliance with CDM especially is a little hit and miss - there are active methods to report companies failing to comply - granted now that HSE Infoline has shut it is really all online but HSE does have a fairly accessible complaints form online which is highlighted from the home page!!!

I personally think HSE given the current climate and their very stretched budget is enforcing as far as they can!!!1
Canopener  
#18 Posted : 02 March 2012 13:19:34(UTC)
Rank: Super forum user
Canopener

I am happy to concede that I may be missing the point, but…

Both type 1 and 2 surveys under MDHS 100 and a Management survey under 264 are essentially the same thing. That a type 2 survey may be a few years old doesn’t necessarily make that survey ‘invalid’ or necessarily any less useful than when it was first completed. That is dependant on the circumstances. If that survey concluded that an ACM was present, this should form part of the register and the subsequent management plan, a further formal survey under 264 may not be necessary, or at least, not for many years to come. You should review the management plan periodically but that doesn’t necessarily mean that you need to carry out another survey. I am therefore not entirely convinced that an old survey is necessarily an indicator that the management of ACMs has fallen below the standards of 264.

Interestingly I took and still take a slightly different stance to the recommendation of the HSE to ‘leave and manage’ ACMs. While this might in many cases be the most practical and/or cost effective way to manage an ACM, in some cases it might well not be in the longer term. It is easy to fall into the trap of assuming that the ongoing management of all ‘in situ’ ACMs is necessarily easy and/or cost effective and that it will remain effective or robust over an extended period of time.

Following our management survey we took the decision to remove some of our ACMs rather than spend the next ‘x’ years managing it. In the grand scheme we concluded that this was likely to be more cost effective than the ongoing management.

I also take Danny's point. Although as far as I am aware, we haven't been approached to 'redo' our Type 2 survey because it NEEDS to be a new 264 survey, I would guess that this kind of approach might happen. Many of us have 'been there' with the glazing, BSEN3, first aid kits etc etc.
HSSnail  
#19 Posted : 02 March 2012 13:45:28(UTC)
Rank: Super forum user
HSSnail

I am with you on this one canopener. Companies telling me their asbestos survey has run out and they need to be paid for a new one annoy me like mad. If they did not find all the ACM on the first go why should I need them back?

Agree depending on the types/conditions of acm found you may need expert help on management, but not a full survey each time. I think if a type 2 survey has been carried out effectively it should be fine until any refurbishment work is proposed.
Users browsing this topic
Guest
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.