Rank: Forum user
|
Just a quick one - this came in a sales email this morning.......
"My company provides Electrical Installation Condition Reports – this is a detailed electrical survey of your building to ensure its safety. This type of maintenance / report is a strict requirement of The Electricity at Work Regulations 1989, so it’s important for your organisation to ensure that this is arranged."
I've not come across this as a strict requirement, can anybody confirm or quote?
For information we are talking about a purpose built office dating from 2004 with absolutely no indication of any electrical issues within the supply system, a good and competent IT chap and regular (possible over regular) PAT for all electrical stuff and PUWER maintenance beyond that for small electrical tools etc.
|
|
|
|
Rank: Forum user
|
5 Yearly Fixed Wiring Testing The legal requirements are enshrined in the Electricity at Work Regulations 1989 and states that: All systems shall at all times be of such construction as to prevent, as far as is reasonably practicable, danger. All systems shall be maintained so as to prevent, so far as is reasonably practicable, such danger. Any equipment provided under these Regulations for the purpose of protecting persons at work on or near electrical equipment shall be suitable for the use which it is provided. The Health & Safety Executive (HSE) recommends that to comply with the regulations, an inspection and testing programme should be undertaken at all places of work. The requirements for fixed installation testing are contained within the Institution of Electrical Engineers 17th Edition, Wiring Regulations (BS 7671:2008).
|
|
|
|
Rank: Forum user
|
Great Thanks for that, a little searching now I know where to look and I'll have things sorted
|
|
|
|
Rank: Super forum user
|
A "condition report" or a "detailed electrical survey" isn't the same as a certificate of test and inspection in accordance with IEE Regs though!
|
|
|
|
Rank: Super forum user
|
As of Amendment 1 to BS7671:2008 which came into force on the 1/1/12, the Periodic Inspection Report (PIR) is dead! :( Its replacement is the Electrical Installation Condition Report (EICR). So what the OP's supplier email is offering are the "new" PIR's, AKA EICR the equivalent replacement. Also the time scale between inspections is NOT set in stone, those dates are a guide for the maximum time to initial inspection. They can be changed either way by the person signing the original electrical installation certificate who decides on the interval to first inspection, then by the competent person signing the subsequent PIR/EICR documents. The time-scales are not even “in” BS7671, they are contained in the IET Guidance Note 3 – Inspection & Testing (ISBN 978-1-84919-275-0), as table 3.2, page 65 of this document and they are guidance to the competent person. There are also 11 notes to this table indicating other conditions, references & guidance. It may be found that the insurer of the business (etc.) may set their own conditions on the timescale etc. for the inspection, their risk, their shout.
|
|
|
|
Rank: Super forum user
|
One last comment/question, how competent is your IT chap with regard to the maintenance of low voltage fixed electrical installations, you could well have a 3 phase incoming supply, the fault current at the origin of your building will be in the region of 25kA. Also, if any maintenance has been done to the fixed building electrical installation, how do you know that this has been done competently? If accessories have been replaced, has the earth fault loop impedance at these replaced devices been verified? Have there been "any" changes to the installation since the original Electrical Installation Certificates were completed? What was the date to the first inspection on the original EIC's? If this has "expired" then you may find that the small print in your insurance policy allows them to get out of ANY claim.
Oh and YES I do do this for a living!!!
I'm about to set out on about my 12th EICR of the year tomorrow, without the EIC's, MWC's and other electrical works that I have done.
Here is one now, who changes the failed fluorescent tubes in your office and how long after they fail? Most types of discharge lighting are a fire risk when they are fitted with a failed lamp, they can and do overheat.
So do you "still" think that it is unnecessary?...
I am open to further forum, PM or email discussions, or even by phone if you wish. You are located far enough away from me for it to be probably not financially viable for me to undertake the work for you, so there is no conflict of interest anyway.
|
|
|
|
Rank: Super forum user
|
I'm with Paul here. And, yes, I also do this for a living and for the record, I teach regs and Inspection and Testing so there! :-)
|
|
|
|
Rank: Super forum user
|
Paul/ zimmy
Just a quickie - as the 'old style' PIR's have been replaced by the EICR, does that mean that electricians should no longer be producing the resulting reports on the old style PIR documentation?
If they are, are they still valid for insurance purposes?
|
|
|
|
Rank: Super forum user
|
Not to be out done by Zimmy, I also teach the I&T & I am down as a C&G examiner for the prac! ;) ;) ;)
He knows I am teasing him, but it is true.
As of 1/1/12 a PIR is no longer a recognised form of reporting in BS7671, so IMHO they are no longer recognised by BS7671, thus they are no longer compliant with BS7671, thus you can not use them.
I had my annual NICEIC Approved Contractor assessment last week, my Area Engineer suggested that PIR's were acceptable up until June this year, he had short shrift from me and we agreed to differ. My argument is above. If you ask the IET, if you get an answer I believe it will be along these lines.
I suggest you ask your insurer, though it is doubtful they will understand the question.
|
|
|
|
Rank: Forum user
|
Lots of info - thank you all again. I think I know where I'm at now: a) Get our building chaps to hunt up the original sign off (I don't know why they are not in H&S File?) b) Check dates etc. c) Check with our insurance company for their opinion d) If cert out of date or insurance company advises - get building blokes to reply to email. As my main job I do project development for environmental programmes, wish the forums available there were as comprehensive as this. Cheers
|
|
|
|
Rank: Super forum user
|
Paul
Excellent stuff (as always). Many thanks for the info.
Nick.
|
|
|
|
Rank: Super forum user
|
Paul said..."I suggest you ask your insurer, though it is doubtful they will understand the question."
Very true.... Unfortunately insurers rarely have experts and we really do rely on you experts out there. Yep, we require inspection of fixed wiring - mainly for property protection since many fires arise from electrical faults. But consider the scenario - can we really possess all the expertise on electricity and the intricacies of which form is valid. Multiply that by all the other legal requirements - LOLER, CoSHH, PUWER, Noise Asbestos etc etc.
People need to understand that whilst we do our best we are rarely expert in any field. In the main we are "generalists". There are odd examples where an insurer has someone who has a high level of knowledge and expertise - but that is the exception in my view.
And lastly who really knows best? I would say it is someone who lives and breathes the subject every day. Someone who works in the field!
Phil
|
|
|
|
Rank: Super forum user
|
Sorry - I should have added that I used this post to do some research and make sure our internal information is up to date and that we make the correct comments when we ask policyholders for evidence of inspections.
Phil
|
|
|
|