Thomas  
#1 Posted : 12 July 2012 12:12:51(UTC)
Rank: Forum user
Thomas

One for our electrical experts, we have recently lost our Maintenance Manager and are in the process of recruiting. In the interim one of our 17th edition qualified electricians has been asked to install 2 x 415v sockets next to a distribution board. He has stated that he can install them but they cannot be used as he is not qualified to test them (which our ex-Manager was). Can you confirm if this is correct and what qualification we should be putting our electricians through to prevent this happening in future?
paul.skyrme  
#2 Posted : 12 July 2012 20:00:39(UTC)
Rank: Super forum user
paul.skyrme

If he is an electrician then he must be competent to inspect & test his own work, if he is not, then he is NOT an electrician. Either downgrade his position immediately and his pay/salary accordingly, or sack him for obtaining a post under false pretences as he has lied to get the post. ANY and ALL QUALIFIED electricians MUST be competent to inspect and test their own works, else they are not competent to undertake these works. In which case they are not electricians, they are electrical installers, see sentence number one.
TSC  
#3 Posted : 13 July 2012 07:14:38(UTC)
Rank: Forum user
TSC

Is there not part of the qualification curriculum that Electricians do on specific testing and certification i.e. a City and Guilds part? I know a lot of electricians that have done the job for many years and have done the appreticeship route who still fail on testing exams? As for the comments of sack him then by all means go ahead but what did his job description say, what did his contract state as responsibilities, what has been his role for the last so many years and then what about other employees who watch and then do work they are not fully confident in because they fear being sacked.
Thomas  
#4 Posted : 13 July 2012 08:26:15(UTC)
Rank: Forum user
Thomas

To clarify: the individual is a City & Guilds electrician and completed his 17th Edition training last year. However it appears that there is another part (BS2391) which is required for inspection & testing. I would have thought that having completed his C&G and 17th Edition (BS7671) he should be able to install additional sockets which we can then use but he insists that every new installation needs to be tested to BS2391 and he has not been through this training course. This may be a genuine requirement or a misinterpretation on his part but as I am not a qualified electrician I am not in a position to question his decision (hence the post). Perhaps this is another case of the training industry hijacking the regulations and creating as many courses as possible as I can see no logical reason why a company would put an employee through an installation course only to then have to put them through a separate inspection course in order to utilise that training?
walker  
#5 Posted : 13 July 2012 09:05:05(UTC)
Rank: Super forum user
walker

The 'lecy regs certainly state a competent person should recognise his limitations. The guy sounds competent to me if he feels its beyond his ability.
TSC  
#6 Posted : 13 July 2012 09:08:38(UTC)
Rank: Forum user
TSC

The course quoted is the course I was thinking off.
Psycho  
#7 Posted : 13 July 2012 10:49:53(UTC)
Rank: Forum user
Psycho

there is a seperate course for testing and inspecting without it he cannot authorise the work the problem is only about 5% of time served qualified sparkies have it
boblewis  
#8 Posted : 13 July 2012 11:28:59(UTC)
Rank: Super forum user
boblewis

Sounds very like a manager ensuring he has power over his junior(s). Don't train them then they have to rely on me to approve and finalise any work done!!! Bob
paul.skyrme  
#9 Posted : 13 July 2012 18:27:01(UTC)
Rank: Super forum user
paul.skyrme

thomas wrote:
To clarify: the individual is a City & Guilds electrician and completed his 17th Edition training last year. However it appears that there is another part (BS2391) which is required for inspection & testing. I would have thought that having completed his C&G and 17th Edition (BS7671) he should be able to install additional sockets which we can then use but he insists that every new installation needs to be tested to BS2391 and he has not been through this training course. This may be a genuine requirement or a misinterpretation on his part but as I am not a qualified electrician I am not in a position to question his decision (hence the post). Perhaps this is another case of the training industry hijacking the regulations and creating as many courses as possible as I can see no logical reason why a company would put an employee through an installation course only to then have to put them through a separate inspection course in order to utilise that training?
thomas, The BS2391 you refer to in this context is NOT BS2391, it is a C&G course number 2391, which is now replaced anyway. The 2391 course (was) centred on periodic inspection and testing, rather than initial verification which is what is required for new and modified installations. I am a teacher & examiner on 2391 & its replacement amongst other courses, Any competent electrician MUST be able to adequately test and inspect "his" own new installations work in accordance with BS7671, if "he" cannot then "he" is not competent to practice as an electrician. If his level of understanding is that which you report in your post, quoted here, then find another electrician, quickly before this person kills someone. I re-iterate, with regard to “a competent electrician”, to be competent “he” must be able to design, construct, inspect and test “his” own installations work in accordance with BS7671, else “he” should not be doing it. I don’t know enough about this “electricians” background to comment any more, however, it does not seem he is suitable for the work he is employed to do, as inspection and testing is part and parcel of the everyday work for a competent electrician. I don’t know where this misinformation has come from, but I suggest that you review the situation and obtain some competent advice on both the competence of the employees and the situation you find yourself in, because if this person cannot I&T then it is doubtful “he” would be classed as competent under EAWR.
paul.skyrme  
#10 Posted : 13 July 2012 18:28:11(UTC)
Rank: Super forum user
paul.skyrme

walker wrote:
The 'lecy regs certainly state a competent person should recognise his limitations. The guy sounds competent to me if he feels its beyond his ability.
In which case he is not a competent electrician.
paul.skyrme  
#11 Posted : 13 July 2012 18:29:13(UTC)
Rank: Super forum user
paul.skyrme

TSC wrote:
The course quoted is the course I was thinking off.
The number quoted is not a course, nor a BS.
paul.skyrme  
#12 Posted : 13 July 2012 18:32:11(UTC)
Rank: Super forum user
paul.skyrme

psycho wrote:
there is a seperate course for testing and inspecting without it he cannot authorise the work the problem is only about 5% of time served qualified sparkies have it
There is a separate course for I&T but it is NOT required to I&T ones own work, the requirement to I&T ones own work is part of being competent to undertake the works in the first place if the person undertaking the works is an electrician.
paul.skyrme  
#13 Posted : 13 July 2012 18:33:15(UTC)
Rank: Super forum user
paul.skyrme

boblewis wrote:
Sounds very like a manager ensuring he has power over his junior(s). Don't train them then they have to rely on me to approve and finalise any work done!!! Bob
Not true Bob, if the guy is an electrician then he MUST be competent to I&T his own works. There is a lot of misunderstanding of this topic it seems.
boblewis  
#14 Posted : 13 July 2012 19:49:13(UTC)
Rank: Super forum user
boblewis

Paul Do not be so ready to condemn you do NOT know what his manager has said to him about self inspection. To test your own work does not make competent necessarily to re certify the whole of a factory system - especially the 415 supply. Some sites have internal rules do not forget. Bob
paul.skyrme  
#15 Posted : 13 July 2012 19:54:48(UTC)
Rank: Super forum user
paul.skyrme

bob, NO one has mentioned re-certification of the system of a factory. Anyway, any competent electrician must also be competent on 400v supplies, 415 is no more by the way ;) ;) ;) I don't actually CARE what his manager has told him in the past, if he was a competent electrician he must KNOW the statute law and other relevant requirements related to the work he is undertaking. Also if he is a competent electrician then he must be competent to design, install, inspect and test ALL of his own works under the scope of BS7671.
boblewis  
#16 Posted : 13 July 2012 20:35:53(UTC)
Rank: Super forum user
boblewis

Paul Do not forget also that both NICEIC and ECA require embers not to inspect and certify their own work and one could argue that this is a best practice option as it can be easy to overlook omissions or errors that oneself has made. The previous MM may have believed this and instilled it in his engineers by force of character!!! Bob
paul.skyrme  
#17 Posted : 13 July 2012 20:45:10(UTC)
Rank: Super forum user
paul.skyrme

Wrong bob, they do require this. I am the PDH & QS for an NICEIC Approved Contractor. They MUST I&T their own work, this "may" be overseen by another, and, this "may" be a good idea. However, this does not detract from the fact that a competent Electrician MUST be competent to I&T their own works, it cannot be any other way if you fully understand the process. Also, the OP is NOT referring as I understand it to the QS system run by the ECA & the NICEIC, which is under significant scrutiny within the industry . Oh, please don't refer to them as Engineers because it is patently obvious from the thread that they are so far from that it is unbelievable. ;) Sorry, that is another fact that cannot be disputed.
boblewis  
#18 Posted : 13 July 2012 23:00:42(UTC)
Rank: Super forum user
boblewis

Paul What then is the purpose of form 2 with its multiple signatures, if as you say the designer, constructor tester etc have to be one person if that person is to regarded as competent? Bob
paul.skyrme  
#19 Posted : 14 July 2012 06:43:11(UTC)
Rank: Super forum user
paul.skyrme

Bob, The old Form 2 was included for commercial reasons where by large works could then legitimately be designed by different companies to the installer and the inspection & testing company. The last bit is of heavy debate in the industry as it is impossible to correctly I&T a completed installation as is often done, the installation MUST be inspected during its construction to ensure full compliance with BS7671. It also serves the purposes of large organisations whereby they may have a design team, an installation team and an I&T team. Again the latter part being of debate for the same reasons. Remember however, it is the "person responsible", i.e. take a large complex design, you may have a lead engineer with several subordinate engineers designing different sections of the installation, it would be head of the engineering design team who would sign the certificate. I say the "old" Form 2 because with the last revision this designation was removed. To turn your argument back on itself, if you refer to BS7671:2008 Amd1 2011, you will see on page 389, that it is allowed for a single person to undertake all roles? So there is no "need" or requirement under BS7671 to have different skill sets, it is recognised that a single person can be competent to undertake al roles, this person would be called an Electrician. So, BS7671 allows for the designer, constructor & I&T to be different entities, however, there is absolutely NO requirement that they are, different entities or persons. The advanced courses, the "old" 2391 & 2400 (very old) are there for competent electricians to broaden and enhance their skill set. Take them as CPD if you like, however, a qualified electrician must be able to undertake all of the requirements of BS7671. We are not talking about designing, installing & I&T'ing a new Steelworks here, this is 2 off 400V (415 is no more by the way!), 3 phase socket outlets, which sound as if they are within sight of the DB. This is a task that should be completed by a competent electrician with no problems what so ever, including any design calculations, the installation & the I&T.
tony.  
#20 Posted : 14 July 2012 07:52:36(UTC)
Rank: Forum user
tony.

2 400 volt socket outlets should be quite easy for your electrician to install and test, worringly if the manager did all the testing, what about all the electrical safe working procedures? The possibility of him working live as he doesnt want to have a shut down springs to mind. Testing a few radial circuits should be a doddle, its more likely he hanst done it for a long time and is scared to admit it. Possibly a light refresher course at the nearest tech college? Rather than pay cut etc Tony
Zimmy  
#21 Posted : 15 July 2012 20:03:54(UTC)
Rank: Super forum user
Zimmy

I teach Inspection and testing, 17th regs, H&S occ and construction. Please, please listen to Paul. Not a lot to add but an electrician should, and in my opinion, MUST be able to test his/her own work. Otherwise it is the user who has to do it the hard way. Think of it as a driving test to prove competence. How to prove competence? Pass the exam. If not please put hands in pockets! No wonder we have so many deaths in the electrical game.