I disagree.
Take your example,
2 x 1.5A = 3A + 2.5A + 0.2 + 0.15A = 5.85A
Your colleague at the next desk has the same and works the same hours as you so that is now 2 x 5.85A, into the same socket outlet.
That is 11.68A, this is very close to the maximum rating for many cheap 13A twin socket outlets which are actually only rated at 13A combined, from both sockets.
Do this twice in the office and you have 23.36A
Stick another one on and you have 29.21A this is more than the current rating for 2.5mm sq flat twin & cpc cable clipped direct.
Now allow for a little more load elsewhere and you could easily top 34 perhaps 35A.
On a cable rated at 24 perhaps, with a circuit breaker perhaps rated a 32A, it will carry 34A for a very long time.
This is a valid design for a ring final circuit as you have the load shared in both "legs" of the ring.
To calculate the load balance you would need much more information than we have here and you would need to enlist the help of My Kirchhoff,.
There could be a few derating factors on the cable, grouping or something, that could easily cause issues.
You seem to be only considering the load on the extension, that was, and is not my point.
There has been a test undertaken recently under controlled conditions by one of the labs, where by single 13A rated socket outlets were put under test at 13A for 10-12 hours, typical charging current/time for an electric vehicle I gather, I've not bothered to investigate this technology yet.
The results were worrying, not one of the cheap n cheerful, or the expensive branded sockets came out unscathed IIRC, there was certainly damage on some of them, and these were items which apparently met the requirements of the relevant standard.
With many offices working 10-12 hours per day if not more with systems that were not originally designed to take such loads then there could, be issues.
I've investigated a near fire in a premises, which if the fire had gotten hold, would have been a total premises loss.
The reason, a unit which had been fiddled with by incompetent persons unknown, who had changed settings elsewhere on the system, and increased the load on the circuit to just over 14A on a 13A fused connection unit (FCU, commonly but incorrectly called a fused spur).
The unit got very hot and overheated, however, it was the same design as you would have at home, and was not really correct for the environment, but, the installation was old...
As Zimmy says, perhaps load checking is required, diversity is a wonderful thing, but, there is now a definitive requirement to avoid such small overloads that last for considerable time as they have been found to be very damaging.