By law the final exit fire door should open outwards rather than inwards. Can someone please point me to a guidance which provides conditions/criteria that are exempt from this requirement please.
Thanks for your anticipated responses.
|
|
|
|
Rank: Forum user
|
safexpert, could you clarify where you get by law should open outwards from, surely if its by law then it's a must. whilst it is much better if the doors open outwards, there are many small shops with single exits that open inwards. there is many factors that need to be considered as to if this would be suitable or acceptable in your building. Guidance can be found here for specific places of work https://www.gov.uk/workp...-safety-advice-documents
|
|
|
|
Rank: Forum user
|
I'm guessing you are referring to section 14-2(d) of the RRFSO:
'Emergency routes and exits 14.—(2) The following requirements must be complied with in respect of premises where necessary (whether due to the features of the premises, the activity carried on there, any hazard present or any other relevant circumstances) in order to safeguard the safety of relevant persons—
(d) emergency doors must open in the direction of escape'
Bit of a grey area for me this one, and note the use of the word 'where necessary'. I've risk assessed one of our final exit doors which opens inwards but opens into a narrow corridor which is part of the fire escape route, I have left the door opening inwards as I believe it creates a greater hazard in blocking the corridor fully if it opens outwards, plus the obvious risk of injury to anyone evacuating via the corridor if the door is opened into them.
My interpretation (and always happy to be proved wrong) is that it comes down to the risk assessment
Alan
|
|
|
|
Rank: Super forum user
|
I agree except that if an exit door opens into a corridor which is part of the escape route, how is it a final exit?
|
|
|
|
Rank: Super forum user
|
dennish has provided the answer To approach from a different angle the building regulations will stipulate final exit design - The approved documents provide information (they are an AcOP to the regulations and so there may be a better way of complying with the regulations in your situation) http://www.planningporta...br/BR_PDF_AD_B2_2010.pdf Note: this applies to new buildings or refurbishment work but can be used as best practice...
|
|
|
|
Rank: Super forum user
|
Prisons, they can also remain locked.
|
|
|
|
Rank: Forum user
|
Kate wrote:I agree except that if an exit door opens into a corridor which is part of the escape route, how is it a final exit? by corridor I was describing a narrow external passageway which leads directly to the muster point, hence final exit door :)
|
|
|
|
Rank: Super forum user
|
Hmmmm, even with regard to the RFSPO, I am not convinced that a final exit door MUST ALWAYS open outwards and the 'guidance' that would exempt you from doing this is down to an individual assessment of the circumstances in each case.
For instance; we operate a small business centre (administrative work only i.e. no manufacturing processes), in a rural market town, where the main entrance/exit door, which is also one of the final fire exits, opens directly onto a pavement immediately outside of the door. I aren't going to change that because 'the law' says that it must open outwards.
The 'day to day' risks of a door opening outwards directly onto a pavement numerous times a day, and clouting someone on the pavement is higher than the risk to the occupants because the door opens inwards. Other than most fire exits, convention is that doors generally open inwards for this very reason.
Use the thing between your ears, assess the overall risks according to the circumstances and record your reasoning.
|
|
|
|
Rank: Super forum user
|
I must deduce from the postings above that there are some "dodgy" or ill informed advisors still operating.
Poor parliamentary or regulatory (civil servants) drafting is common; a good safety bod should be able to cut through drafting ambiguity and deliver a confident reasoned solution.
Identify the hazard (if any) and assess the risk of harm, injury or damage arising from the hazard.
Jon
|
|
|
|
Rank: Super forum user
|
John M wrote:I must deduce from the postings above that there are some "dodgy" or ill informed advisors still operating. Jon Thanks :)
|
|
|
|
Rank: Forum user
|
John M wrote:I must deduce from the postings above that there are some "dodgy" or ill informed advisors still operating.
Poor parliamentary or regulatory (civil servants) drafting is common; a good safety bod should be able to cut through drafting ambiguity and deliver a confident reasoned solution. Good job i've never claimed to be any good then :)
|
|
|
|
Rank: Super forum user
|
teh_boy
Do not be so certain that the approved building regs documents will and must and will be complied with. I have many recently built scenarios where the structures do not comply and enforcement is impossible as no power appears to exist especially if it is the local authority Building Control that approved below par drawings etc. - Mainly because they are the enforcers also.
On the original point my view is always to look at the likely numbers using the door, level access outside for many is far more important. If there is a potential for a bottleneck then outward opening becomes essential.
Bob
|
|
|
|
Rank: Forum user
|
Hey all,
I have a scenario for you, We currently have 4 temporary office blocks, 2 on top of 2 which we are due to move into. We have only one stair case leading from the right hand side of one of them, as the top 2 are connected via a doorway do we require a set of stairs for a fire exit on the other side?? (there is a door) if so can you highlight the relevant legislation.
Obviously I need these buildings to be as safe as possible and any information you can provide will be a great help
Thanks
|
|
|
|
Rank: Super forum user
|
ryan.donald wrote:Hey all,
I have a scenario for you, We currently have 4 temporary office blocks, 2 on top of 2 which we are due to move into. We have only one stair case leading from the right hand side of one of them, as the top 2 are connected via a doorway do we require a set of stairs for a fire exit on the other side?? (there is a door) if so can you highlight the relevant legislation.
Obviously I need these buildings to be as safe as possible and any information you can provide will be a great help
Thanks See links in post #2 You must ensure a suitable and sufficient fire risk assessment has been carried out by a competent person. This is a requirement placed onto the 'responsible person' either MD or Landlord by the Regulatory Reform Fire Safety Order.
|
|
|
|
Rank: Forum user
|
Thanks very much for the quick reply all sorted
Thanks
|
|
|
|
Rank: Super forum user
|
ryan.donald wrote:Hey all,
I have a scenario for you, We currently have 4 temporary office blocks, 2 on top of 2 which we are due to move into. We have only one stair case leading from the right hand side of one of them, as the top 2 are connected via a doorway do we require a set of stairs for a fire exit on the other side?? (there is a door) if so can you highlight the relevant legislation.
Obviously I need these buildings to be as safe as possible and any information you can provide will be a great help
Thanks Have a look at this some good advice and may help with your risk assessment - https://www.gov.uk/gover...1/fsra-offices-shops.pdf
|
|
|
|
Rank: Forum user
|
ryan.donald wrote:Hey all,
I have a scenario for you, We currently have 4 temporary office blocks, 2 on top of 2 which we are due to move into. We have only one stair case leading from the right hand side of one of them, as the top 2 are connected via a doorway do we require a set of stairs for a fire exit on the other side?? (there is a door) if so can you highlight the relevant legislation.
Obviously I need these buildings to be as safe as possible and any information you can provide will be a great help
Thanks Ryan As stated by Teh-boy The risk assessment must be “suitable and sufficient” and to be so must be completed with someone competent to do so (level of competence to take into account the level of risk present, so someone competent to perform a fire risk assessment in a simple single room office may not also be competent to perform a fire risk assessment on an offshore oil platform or in a chemical processing plant). Taking you scenario into account, then could someone be in the upstairs temporary block without the set of stairs, with the door to the one with the stairs closed? If so and a fire started in the upstairs temporary block with the stairs leading from it, then how quickly would they be alerted to the fact that a fire had started. i.e. do they all have fire detection installed connected to a fire alarm system, or at least linked smoke detection/sounders installed? So as you can see matters such as the determining of the number of escape routes, exits and means of protection/detection etc. all come from the fire risk assessment process, which as stated should be “suitable and sufficient” . So if you have one in place that was not performed by yourself and are not happy with it then please raise issue with it; if on the other hand, it’s been performed by yourself then with the greatest of respect you would not be asking the question unless your competence to perform the assessment was in doubt, in which case get an expert in. HTH smitch
|
|
|
|
Rank: Forum user
|
Apologies for typos, bit of a rush in replying as just getting ready to leave office (poor excuse I know)................oh for an edit button?????????????? ;-)
|
|
|
|
Rank: Forum user
|
Just to add. We should remember that the exit door that open outwards should be manufactured to meet the required safety standard. It should open fully in such a way that it comes to rest on the wall and is fixed by a hook if necessary to the wall or is a sliding door and therefore will not present an obstacle to those rushing out or "cloud anyone on the pavement". With regard to the scenario,an international experience may help: S. 46-50 and Table 4 of Third Schedule of the Botswana Building regulations use occupant capacity of the building to determine the number of exits required. Hence 1-60 persons = 1 exit; 61-600 persons= 2 exits; 601-1000 persons= 3 exits, etc. Hence I agree with the advice that you'll need to rely on the likely numbers in the building to determine your exits.
Sanyi
|
|
|
|
Rank: Super forum user
|
As far as inward or outward opening doors, have another look at Article 14 (my capitals)
2) The following requirements must be complied with in respect of premises WHERE NECESSARY (whether due to the features of the premises, the activity carried on there, any hazard present or any other relevant circumstances) in order to safeguard the safety of relevant persons—
(d)emergency doors must open in the direction of escape;
There are lots of 'where necessarys' in the order. This means if your FRA finds that doors need to open outwards, then you must do it.
Examples or where necessary include: where here are > 50 people likely to use the route, or escape from an area likely to have a rapid developing fire (such as a paint storage room etc)
|
|
|
|
Rank: Forum user
|
Thank you for various insightful posts on final exits and direction of opening, it's really given me a bird's eye view. Picking up from the last post here by messyshaw 'Examples or where necessary include: where there are > 50 people likely to use the route,...'
Is there a guidance or ACOP that stipulates the number 50 and could you signpost me to that please. I'm asking to know this as I can then base my FRA and decision to allow the door to open inwards as opposed to opening in the direction of escape on this.
Again many thanks
|
|
|
|
Rank: Super forum user
|
I don't recall Article 14 (2)(d) stating anything else than they 'must open in the direction of escape', it doesn't go on to say dependant upon numbers of people expected to use the door.
|
|
|
|
Rank: Super forum user
|
Have you thought about creating a "lobby" and relocating the doors back a bit so they open into the "lobby" thus not obstruction anyone walking past and achieving the "open in direction of travel".
Not rocket science but has to be reasonably practical and cost effective.
|
|
|
|
Rank: Guest
|
The legal phrase is "emergency doors" not final doors or any other sort of doors. The mere fact an exit might be used in an emergency does mean it requires emergency doors. So a shop front door does not need to comply with Article 14. Many buildings have lots of exits some of which might be deemed emergency exits but in evacuation all exits can be used.
Part (e) of of Article 14 prohibits sliding/revolvingdoors on "... exits specifically intended as emergency exits" . Clealry this shows not all exits are deemed to require doors opening in direction of travel.
Suggested example of "emergency doors". The sterile back staircase leading to final exit doors with no external fittings used to evacuate a cinema must have outward opening doors. The prime purpose of this route is for emergency use. Absolute requirement which cannot be risk assessed down.
As far as I am aware the phrase "Emergency door" does not appear in Approved Document B and is not a defined term in the RRO. Lots of info on esape routes in AD (b) which is open to risk assesment to get appropriate standard.
|
|
|
|
Rank: Super forum user
|
The Brisith Standard 9999 refer to 'Final exit doors', doors that take you outside into the fresh air.
|
|
|
|
Rank: Super forum user
|
Invictus wrote:The Brisith Standard 9999 refer to 'Final exit doors', doors that take you outside into the fresh air. Good find if thats the right one (not time to check right now). I know I was told that 'Final exit door' - the one that leads outside, to fresh air must always open outwards but I'll be damned if I can remember the detail around this. Not my area of expertise but did want to point out that the statement itself of 'final exit door =must be outward opening' is in my mind from somewhere..
|
|
|
|
Rank: Super forum user
|
Messyshaw already made it quite clear that there's no absolute requirement for final exits doors to open outwards. For those of you saying there is, read article 14 again and note Messyshaw's emphasis on "where necessary".
For the OP. If you download the guidance for the relevant type of premises from the link you have been given and go to Section 4 "further guidance on escape routes" you'll find this "All doors on escape routes should open in the direction of escape and ideally be fitted with a safety vision panel. This is particularly important if more than 60 people use them or they provide an exit from an area of high fire risk."
Note it says "should" not "must" and again this comes down to your FRA. I wouldn't quibble about 50 or 60 to be honest in this case! If you Google "maximum occupancy" and look at some of the local authority guidance for licensed premises you will also find recommendations that rooms with inward opening doors be allowed no more than 60 persons.
|
|
|
|
Rank: Super forum user
|
Invictus wrote:I don't recall Article 14 (2)(d) stating anything else than they 'must open in the direction of escape', it doesn't go on to say dependant upon numbers of people expected to use the door. Look at my post (20) above. I have highlighted the words 'where necessary'. That means where the FRA determines they should open in the direction of escape. Example 1) If four people in an office will use the door it is 'not necessary' for the door to open 'out'. Example 2) Whereas if there are four people working in a spray shop with flammable vapours which could lead to a rapid developing fire, out opening doors may well be necessary BS9999 and various guides will help define where it is and is not necessary to have 'outward' opening doors Similarly, sliding doors can be used on escape routes. We have 64 sliding doors on escape routes in one very large building due to the processes carried on there and have successfully demonstrated to enforcing authorities that there are sufficient control measures in place to protect all relevant persons So beware of the term 'where necessary' in the RRO - It pops up a lot and can trip you up. I have known many assessors to demand doors are turned around and various other unnecessary work, just for misreading the very poor wording & layout of the order
|
|
|
|
Rank: Super forum user
|
Is it a case therefore that we all know that 'shall' in the HSE world means 'you will' and people are misinterpreting what 'should' means? 'Should' to me is only a narrower definition of 'Shall' and so I take 'should' as 'you better have very very very very good reason not to'.
'Should' to me is a higher duty than 'where necessary'.
I concur that 'Should' is not an absolute duty as 'Shall' but my interpretation is that its almost like an ACOP and if I could reasonably including spending some money, make it so (in this case door open in direction of travel) then I ought to.
Of course if my risk assessment pointed out that if doing so would cause a bigger problem then that would satisfy me of why I did not do it under 'should' and I would be happy to argue that point in court.
|
|
|
|
Rank: Super forum user
|
Just browsing the 2013 edition of Tolleys which I know many of you may have on your desk and [F5040] and bullet point 5 states 'emergency doors must open in the direction of travel'
Now I know this is not a legal doc/book nor does it mention 'final exit' but it does state the above word for word so its no wonder this thread was not put to bed in a couple of posts...
|
|
|
|
Rank: Forum user
|
Heather in post #27 quotes "All doors on escape routes should open in the direction of escape and ideally be fitted with a safety vision panel"
Doors on or across an escape route are the doors in a corridor (for example) and nothing to do with final exit doors for use in an emergency.
|
|
|
|
Rank: Super forum user
|
I am not going to post on this thread after this because the thread is going around in circles. When people ask for advice, why do so many contributors guess the answer?
My input into this thread (re opening direction of doors & 'where necessary') is not my opinion, it's fact based on intensive experience of the RRO from before the Order was launched - and during enforcement (and appeals) via the courts.
So this is a definitive answer: It is not mandatory for doors - any doors - to open in the direction of escape. Only where necessary (see my other posts)
|
|
|
|
Rank: Forum user
|
Perhaps those that challenge the statement by Messyshaw on “where necessary” may find useful information in:
Collected Perceived Insights Into and Application of The Regulatory Reform (Fire Safety) Order 2005 For the Benefit of Enforcing Authorities- Guidance Document by CFOA (Chief Fire Officers Association)
A guidance document to provide enforcing authorities with a standard approach to the articles contained within the Regulatory Reform (Fire Safety) Order 2005. See article 14
|
|
|
|
Rank: Super forum user
|
quote=messyshaw]I am not going to post on this thread after this because the thread is going around in circles. When people ask for advice, why do so many contributors guess the answer? Quote:
Stop being such a moody moo - I can't see any posts above that 'guess' the answer - I see people have given their interpretation and even quoted books and paragraphs where they have seen a 'version' of the answer to the question originally asked. No one has been deliberately misleading by trying to just guess an answer - what it does point out is that the answer is not simple and easily understood and in attempts to answer the question some information is wrong, misleading, vague, absurd, spot-on and everything in between.
|
|
|
|
Rank: Forum user
|
Try part B of the Building regulations.
|
|
|
|
Rank: Super forum user
|
If I'm honest, Messy has quite clearly demonstrated/ provided the definitive answer in numerous posts.
On a personal level, I find that his posts on aspects of fire safety are concise and accurate, and a valid source of good information - they never seem to be subjective, just clear facts.
|
|
|
|
Rank: Super forum user
|
As with many topics discussed on this forum, it seems that some people want strict edicts which apply to each and every situation.
Surely final exit doors should be assessed and designed according to what is needed with regard to various factors including foreseeable usage, type of premises and location. My understanding is that fire doors and especially final exit doors should open in the direction of travel if they are likely to be used by a significant number of people. If a throng/surge of people could occur behind such doors it is foreseeable that this will prevent or unduly hinder the opening of the doors. For the same reason such doors should have push-bar opening devices so that they can be readily opened. By contrast, for premises or parts of premises with few occupants and visitors surely there is no problem with inward opening exit doors with turnbuckle handles or other keyless devices. (Though I know basic principles and practices regarding fire precautions I can't readily think of a suitable term for the crowd surge effect on inward opening doors. Is there one?)
Another aspect which needs to be considered is what is outside the final exit door. For example, emergency exit doors of premises in a town centre tend to be located within recesses so that they don't open onto pavements or other busy pedestrian areas. However, if the recesses are liable to be used as shelters by vagrants or have rubbish piled into them, the prompt openability of the doors could be compromised.
p.s. On a jocular note, the term "moody moo" in #34 is not bad for its alliterative (rhyming) nature but surely derogatory to cows as well as messyshaw. Apparently some cows are happy beasts: A dairy farmer I know reckons his cows enjoy listening to BBC Radio 2 in the milking parlour and tend to give better milk as a result. Better not tell the Performing Rights Society just in case they cover bovine audiences as well as human ones! :-)
|
|
|
|
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.