Clews34646  
#1 Posted : 07 March 2013 16:00:31(UTC)
Rank: New forum user
Clews34646

Good afternoon everyone I'm currently carried out work on water based cutting fluids used in our lathes and surface grinders. These machines are used about 2-3 times a month and the remaining time are left idle with the fluid being un-circulated in the holding tanks on the machines. I've checked the data sheets, Acop and COSHH for info from the HSE web site but cannot seem to find any clues has to what action I should be taking, apart from calling in a specialist company, which I think at present may be to early. So I hope someone may well be able to give me some idea has to what sort of time frame as to when we should either circulate the fluid or ever replace it. Other factors that may help are, the factory is quite a physical environment so working area temperature tends to be around 18-20 degree C but this does drop over night and at the weekends.
Palmer20061  
#2 Posted : 07 March 2013 16:29:48(UTC)
Rank: Forum user
Palmer20061

I’m told that a number of factors can lead to the risk of rapid growth of the bacteria, these include; areas of still water, presence of sludge, scale or rust which provide nutrients, and a temperature in the range of 20c – 45c, so it sounds like the circumstances you mention may lead to a risk, especially in the summer. We flush infrequently used outlets (less than weekly) on a weekly basis – or drain down fully where practical to do so to prevent any possible ‘breeding grounds’. Could you drain down the reservoirs after use each time? If needed an occupational hygienist would be able to give more detailed advice.
aland76  
#3 Posted : 07 March 2013 16:31:58(UTC)
Rank: Forum user
aland76

Hi http://www.hse.gov.uk/metalworking/legionella.htm This page looks to answer the question - "HSE guidance L8 “Legionnaires' disease. The control of legionella bacteria in water systems” recommends that the MWF storage and distribution system of lathe and machine tool coolant systems should be cleaned and disinfected every six months or more frequently if recommended by machine tool or fluid suppliers." Alan
chris.packham  
#4 Posted : 07 March 2013 20:42:40(UTC)
Rank: Super forum user
chris.packham

Two thoughts on this: 1. The presence of tramp oil is a significant factor. When the machine tool is idle this floats to the surface and interrupts the interface between the coolant and the atmosphere, encouraging the growth of anaerobic bacteria. Tramp oil is easily removed with a skimmer and this can be set up so as to be portable, i.e. can be moved from machine to machine to ensure that all tanks are 'clean'. 2. Lack of oxygen can also encourage bacterial growth. This occurs when the machines are not operating, since there is no circulation to oxygenate the fluid. There is a simple, low cost answer to this. You visit your local pet shop, one that is involved in keeping fish. You purchase the requisite number of air pumps and the small stones that are used to aerate the aquarium and use these to aerate the fluid tanks. I have used both techniques and they have worked extremely well. Chris
User is suspended until 03/02/2041 16:40:57(UTC) Ian.Blenkharn  
#5 Posted : 07 March 2013 21:55:01(UTC)
Rank: Super forum user
Ian.Blenkharn

It's like evolution, but in reverse. Despite 50+ years of research regarding the microbiology of MWFs, innumerable standards and guides, field investigations, commercial development in biocide production and use, cleaning agents, chemical, microbiological and physical test systems and protocols for regular microbiological examination, even the rather wispy washy HSE MWF pamphlet, we are advised to buy a fish tank pump and aerator from the pet shop! The available evidence - yes, there is plenty for those who want to read it - does not place Legionella anywhere near the top of the list of concerns from MWF. Nevertheless, this additional risk should not be overlooked, though it can be managed generically. Mr Packham will have us believe that lack of oxygen encourages bacterial growth, obviously without understanding of the complex ecology of MWF systems and the very high frequency of obligate aerobic species co-existing with facultative and obligate anaerobes, and sulphate-reducing species, or since the question is about Legionella, the fact that Legionella are aerobic and there is some chance that oxygenation might actually encourage and promote rather than inhibit Legionella growth. Many commercial MWF systems hold 50,000 litres of fluid managed centrally and distributed factory-wide. But if you really do want to ignore all of the knowledge and experience accumulated over the last 50 years or so, why not go ahead and make it worse, perhaps for the back street mechanic operating just a single lathe, and bubble air through the fluid in a crude attempt to increase average dissolved oxygen concentrations and simultaneously generate an aerosol that may be rich in the Legionella bacteria that are the cause of concern. I despair.
Ron Hunter  
#6 Posted : 07 March 2013 22:38:35(UTC)
Rank: Super forum user
Ron Hunter

YES you have a problem and YES you should seek the advice of specialists - first stop the suppliers of the cutting/coolant fluids. The rather excellent IOSH Course on Legionella Management covers this area in fair detail. I commend that course to you.
chris.packham  
#7 Posted : 08 March 2013 07:52:03(UTC)
Rank: Super forum user
chris.packham

In response to Ian’s posting, his knowledge of microbiology is far superior to mine so I will not respond to his comments on this. However, my posting was based on many years involvement, firstly in the metalworking industry, where water-mixed metalworking fluid was often something that caused problems and secondly in the prevention of damage to skin due to exposure to metalworking fluids. The issue of tramp oil causing fluid degradation is well known, as is the issue of fluid degradation when machines stand idle for long periods. The concept of using aeration via a small aquarium air pump has been used successfully for a number of years to prevent the latter. It may be ‘low tech’, but it works and has saved employers who previously had to drain tanks and refill them considerable sums of money and time. Should we sneer at solutions that work and are cost effective, simply because they are low tech?
Barnaby again  
#8 Posted : 08 March 2013 08:04:45(UTC)
Rank: Forum user
Barnaby again

User is suspended until 03/02/2041 16:40:57(UTC) Ian.Blenkharn  
#9 Posted : 08 March 2013 08:24:19(UTC)
Rank: Super forum user
Ian.Blenkharn

Mr Packham seems convinced that his home-spun aeration technique "works". With "many years involvement" in this field he will know full well the importance of evidence. Though many important advances begin with anecdotal evidence, the question to Mr Packham is simple. Where is the evidence? Throughout those "many years" surely there was time to address this innovation in a systematic way and, alone or with others, provide some evidence with which to support opinion that may otherwise distract or divert others from a more meaningful management of MWFs, preventing some of the more serious complications that can include skin problems, asthma-like illnesses, and at the most extreme, extrinsic allergic alveolitis, none of which can be prevented by a trip to the pet shop.
cheifinspector  
#10 Posted : 08 March 2013 08:32:48(UTC)
Rank: Forum user
cheifinspector

In my previous employment i worked in a machine shop where there were 5 lathes working almost constantly. We had the coolant manufacturer come in every month and measure the bacteria levels at each machine to ensure they were within the safe limits. Due to the amount of coolant that was purchased, no charge was made for this service. It might be worth contacting your coolant supplier to see if they can do this for you.
Clairel  
#11 Posted : 08 March 2013 08:59:01(UTC)
Rank: Super forum user
Clairel

All this 'Mr' lark makes me feel like I'm in a courtroom!! My first thought was that legionella is not the primary concern with MWF's and that the guidance for regular bacterial checks and regular changes of MWF should also control any risk from legionella. History would not suggest incidences of legionella related illness linked to use of MWF (though I stand to be corrected). Just my thoughts but I'm no expert on sciencey based things.....Your Honour ;-)
chris.packham  
#12 Posted : 08 March 2013 09:23:12(UTC)
Rank: Super forum user
chris.packham

Clairel You are correct, legionella is not a major issue with water-mixed metalworking fluids. The effect on the skin is. With regard to the "Mr." bit, I have perhaps a somewhat jaundiced view of this insistence in the UK on "evidence". As far as I am concerned, if it works and solves a problem then let's use it. Should I say to my client: "Yes, I know how to solve your problem, but as there is no 'scientific evidence', you cannot use it?" Interestingly, I do not encounter this insistence on "evidence" in the other countries I work in. They are concerned with: "Does it work". Chris
User is suspended until 03/02/2041 16:40:57(UTC) Ian.Blenkharn  
#13 Posted : 08 March 2013 12:41:56(UTC)
Rank: Super forum user
Ian.Blenkharn

Indeed Legionella are not recognised as a problem, but it was raised in the initial posting and Mr Packham claims to have a solution - an apparently off-the-wall and unproven solution for a problem that doesn't exist? It is also worth stopping for a moment or two to consider the use of MWFs. Are they not oxygenated already, by their circulation and recirculation during use? Indeed, one of the many earlier problems now managed by close containment and the use of baffles around lathes etc if that the damn stuff sprays everywhere. And obligate aerobes grow prolifically, through due to the complex micro-ecology of MWF systems these can co-exist with sulphate-reducing genera and other obligate anaerobes. Just about the only thing you don't find are goldfish. If this normal use of MWFs doesn't oxygenate them sufficiently, you can decide whether to get yourself off to the pet shop. And if that quaint addition doesn't then solve your problem, you know where to look for an explanation.
chris.packham  
#14 Posted : 08 March 2013 13:44:00(UTC)
Rank: Super forum user
chris.packham

My original posting was intended to be a comment on the general management of metalworking fluids and not specifically legionella. It was was in response to the scenario contained in the original posting where machines are left idle for considerable periods. With regard to the comments about aeration, if my posting is read properly I was referring to those conditions mentioned in the original posting about where the fluid is left static because the machinery was not in use. Of course, when running there is adequate oxygen in the fluid. It is when the machine is switched off for a period that the aeration becomes and issue and can be dealt with using my suggestion (as has been done numerous times with success).
hilary  
#15 Posted : 11 March 2013 11:00:14(UTC)
Rank: Super forum user
hilary

I did a quick google on aerating metalworking fluid to reduce bacterial growth and it seems that artificially aerating standing fluid is a well accepted method as long as the metalworking fluid does not foam. What a result! Thanks Chris, I wouldn't have thought of it but it seems like good advice.
chris.packham  
#16 Posted : 11 March 2013 11:06:47(UTC)
Rank: Super forum user
chris.packham

Hilary Just for the record, I worked in the metalworking industry for a number of years. The processes in which I was involved (metalforming, including metal spinning, shear and flow forming) required a very technical approach to metalworking fluids as these were critical to the performance of the equipment. I was also a member of the HSE working group that produced guidance of safe use of metalworking fluids. Chris