Dear All, Can anyone advise on whether there is a legal requirement to provide test switches for testing the Emergency Lighting? Emergency Lighting tested today, however Manager does not want to proceed with the remedial works highlighted (test switches and a few luminaires needing replaced) Thanks MAT
NickH  
#2 Posted : 08 April 2013 17:24:10(UTC)
Rank: Super forum user
NickH

BS 5266-1:2011 Emergency lighting – Part 1: Code of Practice for the Emergency Escape Lighting of Premises will give you more accurate guidance. However, there is no 'legal' requirement to have test key switches. Indeed, some units are self testing, so there is no need (provided they are being regularly servcied/ maintained). You don't say whether the faulty units are maintained or non-maintained units. Although a slightly higher initial outlay, we have recently switched to using LED bulkhed emergency lighting units, as there are no luminaires to replace. Also, in most instances they provide a far higher Lux level when illuminated. With regard to not replacing faulty liminaires then you could potentially be in hot water here. If they have previously been deemed necessary, and no significant changes to the layout of the workplace, etc., has taken place they would still be seen as a requirement.
Zimmy  
#3 Posted : 08 April 2013 18:44:18(UTC)
Rank: Super forum user
Zimmy

A 'self testing Em light? Mmmmmmm
Zimmy  
#4 Posted : 08 April 2013 18:47:13(UTC)
Rank: Super forum user
Zimmy

Fit test switches and wire them so you can keep the main lights running when they are under test. If integral then ensure that the individual fitting can be switched (easy to do). You MUST be able to test the units (full discharge etc) so best to have switches.
bob youel  
#5 Posted : 09 April 2013 07:10:49(UTC)
Rank: Super forum user
bob youel

whilst there may not be a specific sentance in law that says that such switches must be tested etc. it is a requirement to have adequate management and by implication this means that actions to manage must be carried out and one such action is to adequately test!
MAT  
#6 Posted : 09 April 2013 09:47:28(UTC)
Rank: Forum user
MAT

Thank you all for your assistance. Nick we have a combination of maintained and non-maintained on site. No issues with replacing defective lights. I am of the opinion that we should fit test switches to allow fire wardens to carry out this function as part of their checks(trained of course). Failing that it would appear that we are expected to send the place into darkness( slight exageration) by flicking a MCB. This also goes against our own company policy that only electrically qualified persons should open a distribution cabinet/board. Thank you all again MAT
NickH  
#7 Posted : 09 April 2013 10:27:45(UTC)
Rank: Super forum user
NickH

Zimmy - just one example of a 'self testing' system: http://www.p4fastel.co.u...and-monitoring/index.htm Just to clarify, I don't use this particular one, but we do have one or two systems in some premises throughout the estate. They seem to work quite well.