#1 Posted : 05 June 2013 22:35:04(UTC)
Rank: Forum user
Nick-H

Hello all, Hope you are all enjoying the sunshine (short-lived though it will surely be!). I work in the HE sector and we have many chemical fume cupboards in our facility that are used to protect empoyees from being exposed to harmful chemical agents that they are using. Last week we had a report that one such cupboard had stopped working just before someone needed to use it. The person who was called to it could see that the power to the fume cupboard was off and it seemed "dead". They called the Estates guys, who sent up electricians to investigate. Their analysis showed that the trip on the cupboard had activated and they said that this was because a faulty piece of equipment had been plugged into one of the 13 amp sockets attached to the cupboard. They reset the trip and the cupboard duely started working again. They left, after telling the staff in the area that they had to check the equipment used with the cupboard to ensure it was electrically safe. I heard about this second hand and was immediately horrified that plugging in a faulty piece of electrical equipment would cause the entire cupboard to stop working. Thankfully, in this case the work had not actually started and people had simply been preparing for the work. However, if the cabinet had failed during the work, the operative and others could have been exposed to dangerous substances. I wrote an email to various people about this and insisted that this had to be investigated immediately to see if it was true that tripping the sockets would stop the entire fume cupboard, whether other cabinets were similarly affected and, if so, take action to rectify this. An independent check by a qualified electrician determined that the fume cupboard was indeed set up to stop completely if something tripped out the sockets. However, a senior Estates manager has written back to say that this behaviour is likely to be a design feature to cause "total isolation" in the event of a fault and that they would not alter such an installation because "it could risk falling foul of the Electricity at Work Act". We are still awaiting a reply from the cupboard manufacturer about this, but my question is: 1. What aspect of the EAWA exactly would we "fall foul" of if the cupboard were set up with independent trips for the sockets and fan? I cannot really think of any, but I am willing to be corrected. 2. Not withstanding any EAWA issues, I feel that the current design does reflect a very poor design principle (ie failing to danger) and does mean we are breaching our responsibility to protect employees AFAIRP under HSWA,COSHH,IRR & PUWER. I think the design might also breach the EU machinery directive. Surely it has to be safer for a fault on the sockets not to stop the entire cupboard. I think the Estates manager is looking too narrowly at one aspect of safety. What are peoples' thoughts?
paul.skyrme  
#2 Posted : 05 June 2013 23:41:21(UTC)
Rank: Super forum user
paul.skyrme

Nick, On the face of my scanning of your post then you are spot on! Safety circuits should have special consideration, LEV for a fume cupboard that has a potential to harm if it fails, IMHO is a safety circuit as much as is EM lighting TBH. Rubbish design of the install. No EAWR issue to respond to. Why sockets in the booth? Are they suitable for the environment? I could go on, but, IMHO you are on the right track.
Jane Blunt  
#3 Posted : 06 June 2013 06:22:07(UTC)
Rank: Super forum user
Jane Blunt

I also work in the HE sector, and this gives me pause for thought - I wonder if I have the same problem! I agree with you absolutely, a fault that trips the associated sockets should not trip the fume cupboard itself. I would challenge the view of Estates - this cannot be right. Paul - these sockets are usually on the panels just outside the booth, along with gas taps, water taps, air flow indicators etc. My particular problem when some of mine were installed was that ajacent cupboards were on different phases, leading to sockets less than 15cm apart on different phases! I got it changed.
paul.skyrme  
#4 Posted : 06 June 2013 07:34:37(UTC)
Rank: Super forum user
paul.skyrme

Jane, Nothing wrong with 2 phases within 150mm of each other, we put them much closer in 3ph equipment. No requirement in BS7671 to prevent this either, it is allowed. I don't see the issue to be honest. If you look at BS4163, then you will see that "safety systems" must not be affected by central emergency switching systems for example. IMHO, this should be extrapolated out to ensure that "safety systems" supplies are as robust as they can be, I'm not proposing totally separate, but I would personally never put them on the same final circuit as socket outlets, as these are prone to abuse, and are often stupidly on RCD's which in themselves are not the safest thing in the world, this results in the "safety system" being on an RCD.
Jane Blunt  
#5 Posted : 06 June 2013 14:22:02(UTC)
Rank: Super forum user
Jane Blunt

paul.skyrme wrote:
Jane, Nothing wrong with 2 phases within 150mm of each other, we put them much closer in 3ph equipment. No requirement in BS7671 to prevent this either, it is allowed. I don't see the issue to be honest. .
Obviously 3 phase equipment is, well, 3 phase, so is not relvant to the discussion. I disagree with you on the proximity of different (single) phases, particularly in a lab environment. The age of the variac is not quite over. I have discussed this with one of the specialist HSE inspectors whose verdict was that putting two phases in close proximity is extremely bad practice.
Johnmann  
#6 Posted : 06 June 2013 14:39:19(UTC)
Rank: Forum user
Johnmann

Just a thought, but what happens if there is a power cut while you are in the middle of a chemical test? Seems that the actual safety issue is the reliance on the presence of an electrical supply to ensure safety.
Paul Duell  
#7 Posted : 06 June 2013 14:41:57(UTC)
Rank: Forum user
Paul Duell

This is quite an old tale but I tell it because it seems relevant... When we were designing and building our new radio studio (1992) we needed separate phases in each room because we wanted audio equipment to be on its own phase to reduce the possibility of line noise, for example if a cleaner plugged a vacuum cleaner into a mains socket: The electrical engineer designing the install told us we couldn't have different phases on sockets in the same room, and suggested there was a reg against it. As the engineer later married my sister I know him quite well and consider him trustworthy in knowing his stuff! Having said that I have seen in some places (public loos in the university for example) warning that there may be 415 volts between adjacent equipment, which I guess is caused by the same thing, so maybe it's become acceptable more recently? Even if so, I would support Jane's view that using specific equipment might mean that adjacent different phases cannot be allowed in certain circumstances...
Jane Blunt  
#9 Posted : 06 June 2013 21:02:49(UTC)
Rank: Super forum user
Jane Blunt

Paul, I believe that in an earlier edition of the Wiring Regulations it was stipulated that two phases were not to be placed within 6 feet of one another unless there was a physical barrier (such as a wall). Johnman - yes, if there is a power cut the fume cupboard user may have a serious problem. They may have more than one problem!
paul.skyrme  
#10 Posted : 06 June 2013 21:29:59(UTC)
Rank: Super forum user
paul.skyrme

Yes in earlier editions then this was the case, however, now, it is acceptable, so that is that. With the info we have the issue of 2 phases to 2 single phase sockets 6" apart is not an issue. I have no install certs, no PIR's, no EICR's for the install, no design details etc. so if it was installed 6 months ago then it is fine. If it was installed when the reg was in place then it did not comply & the designer and installer should be shot at dawn! ;) ;) ;) However, under current regs no issue. This can be seen in many situations. TBH I would be more concerned about the possible failure of the supply in the middle of a possibly harmful experiment! Jane, I fail to see the issue with a Variac, I'm looking for one for my arsenal at the moment and not just a 1ph one, a 3ph one too, I have a use for them regularly!
Nick-H  
#11 Posted : 06 June 2013 23:14:45(UTC)
Rank: Forum user
Nick-H

All, Thanks for the replies. Very informative. Regarding the issue of what happens if the power fails during an experiment, yes this is a problem. Users are instructed of correct procedure (stop work immediately, close sash, vacate area, report). The fume cupboards are not on UPS systems, which would be an added layer of protection, but I expect was either not considered when cabinets were being procured or it was considered and decided not necessary or would cost too much. Given the limitations of what is in place vs what would be an "ideal" setup, all your answers show that the linking of a critical safety circuit to a non-critical circuit and placing both under the same trip is not sensible to say the least. This is exactly what I thought and I thank you all again for your input. I have some very interesting discussions ahead with the manufacturer and Estates I suspect!
Paul Duell  
#12 Posted : 07 June 2013 09:07:44(UTC)
Rank: Forum user
Paul Duell

paul.skyrme wrote:
Yes in earlier editions then this was the case, however, now, it is acceptable, so that is that. With the info we have the issue of 2 phases to 2 single phase sockets 6" apart is not an issue
Jane and Paul, thanks for clearing that up. Just for interest - and apologies for drifting OT - does anyone know what's changed, to make the reg change possible? Improvements in earthing or insulation standards maybe?
imwaldra  
#13 Posted : 07 June 2013 10:19:59(UTC)
Rank: Super forum user
imwaldra

I'm aware of the following good practices that are perhaps not being followed for the fume cupboards in question. 1. Inlet and outlet air flows to the room need to be balanced to get the right face velocities for each fume cupboard, so often there's an inlet HVAC fan as well as the outlet fan on each cupboard. So tripping the outlet fan without doing anything about the inlet air doesn't make sense. 2. I would have expected the outlet fan possibly to be 3-phase as it needs a fair bit of power for a normal fume cupboard. If so, it will be separately wired from the sockets and the Estates guy is talking nonsense - though the supplier may well have wired the trip to operate like that. 3. If the fumes are significantly harmful, there should be a low air flow alarm. However, in many cases fumes are 'nuisance' rather than 'hazardous', in which case the consequences of lost air flow are not as serious as Nick-H suggests re legal duties. For such cupboards, if there's no fixed alarm, small 'tell-tale' paper strips at the bottom of the sash, and awareness by users of the purpose of these are perhaps sufficient?
Nick-H  
#14 Posted : 09 June 2013 23:04:44(UTC)
Rank: Forum user
Nick-H

Thanks imwaldra, Make-up air is via normal "leakage" and/or balanced against normal ventilation in the room. Hence, if fume hood fails, room is likely to either be a little less negative pressure or slightly positive. That is a BMS issue rather than an issue relating to the operation of trips on the fume cupboard. I agree it can be important, but was not really the main thrust of my post. Fan on roof will be 3 phase, but fan controller on fume cupboard is clearly not supplied by separate 3 phase. I think it is the killing of power to the controller at the fume cupboard that is stopping the fan. Yes, fumes could be either, but this happens to be a cabinet inside a supervised area (IRR99) and so is used for volatile radio-isotope work. There is an alarm on the cabinet and I do hope that the alarm sounded when the trip operated (ie that the alarm has a battery backup or alarm is not on the same trip). This will be one of the various questions I will be posing to the cabinet manufacturer when I have a meeting with their representative in due course. The level of protection is all about AFAIRP as usual (unless, of course, an absolute duty applies). It could be argued that the fans should be on a maintained supply so that they cannot stop if the power fails for any reason. This has not been done and I agree that this is not necessary due to the presence of an alarm to indicate low/no flow (note above caveat on that), operator procedure to adopt in case of alarm and quantity of harmful agents used. I think the overall operation of the fume cupboard is satisfactory SFAIRP, except for this issue of the trip causing the fan to stop when a fault occurs with the sockets. That is not SFAIRP in my opinion. This was the main issue I was seeking thoughts on.
Users browsing this topic