stevedm  
#1 Posted : 09 May 2014 16:10:28(UTC)
Rank: Super forum user
stevedm

Sorry to ask this but we are having a bit of a barney here...

Does emergency lighting regardless of maintained or non-maintained have to be wired so that in the result of power fail they illuminate?


RayRapp  
#2 Posted : 09 May 2014 17:10:36(UTC)
Rank: Super forum user
RayRapp

I cannot see how emergency lighting can be considered 'emergency' lighting without being tested. Furthermore, an annual periodic inspection/discharge test must be undertaken by a qualified contractor.

Under the Regulatory Reform (Fire Safety) Order 2005, article 17 details the Responsible Persons duty on maintenance:

17. — (1) Where necessary in order to safeguard the safety of relevant persons the responsible person must ensure that the premises and any facilities, equipment and devices provided in respect of the premises under this Order or, subject to paragraph (6), under any other enactment, including any enactment repealed or revoked by this Order, are subject to a suitable system of maintenance and are maintained in an efficient state, in efficient working order and in good repair.

Emergency lighting falls under this article as its function is to indicate clearly a means of escape, provide illumination along such routes to allow safe egress through escape routes and exits provided and to ensure fire alarm points, extinguishers etc. provided can be readily located.

British Standard BS5266 is the official guidance document in regards to emergency lighting with Part 1, 2011 and Part 8, 2004 dealing with maintenance and servicing.

Ian A-H  
#3 Posted : 09 May 2014 18:04:49(UTC)
Rank: Forum user
Ian  A-H

Hi Steve

Surely emergency lighting that does not illuminate in a power failure is just lighting?!!

Ian
mssy  
#4 Posted : 10 May 2014 15:41:54(UTC)
Rank: Super forum user
mssy

Ian A-H wrote:
Hi Steve

Surely emergency lighting that does not illuminate in a power failure is just lighting?!!

Ian


LOL Post of the week :)

Mebo  
#5 Posted : 12 May 2014 12:23:49(UTC)
Rank: Forum user
Mebo

SteveDM wrote:

Does emergency lighting regardless of maintained or non-maintained have to be wired so that in the result of power fail they illuminate?



The answer to your question is yes. However, short of not wiring it at all, it would not be possible to wire an emergency unit in such a way that it did not come on at power fail.
Mebo  
#6 Posted : 12 May 2014 12:26:21(UTC)
Rank: Forum user
Mebo

Reflecting after I pressed "post"...

If you didn't wire the battery then it wouldn't come on. However, as Ian says, you would then have an ordinary rather than emergency light.
jay  
#7 Posted : 12 May 2014 12:39:35(UTC)
Rank: Super forum user
jay

What is the type of premises you referring to, and what are the activities being undertaken?

Extract from the Section 5 Further guidance on emergency escape lighting of the Fire Safety-Risk Assessment Guide for Offices & Shops:-
https://www.gov.uk/gover...1/fsra-offices-shops.pdf

The primary purpose of emergency escape lighting is to illuminate escape routes but it also illuminates other safety equipment.

The size and type of your premises and the risk to the occupants will determine the complexityof the emergency escape lighting required. Borrowed lighting may be suitable in small premises where the light is from a dependable source, e.g. street lamps, and it will adequately illuminate escape routes. Where borrowed lighting is not suitable, then a number of torches, in strategic positions, can be considered.

Single ‘stand-alone’ escape lighting units may be sufficient in small premises and these can sometimes be combined with exit or directional signs (Figure 54). The level of general illumination should not be significantly reduced by the sign.

In larger more complex premises a more comprehensive system of fixed automatic escape lighting is likely to be needed. This will be particularly true in premises with extensive basements or where there are significant numbers of staff or members of the public.

However, you "insurer" that covers fires may have specific requirements that are over & above the official guidance
stevedm  
#8 Posted : 12 May 2014 12:55:05(UTC)
Rank: Super forum user
stevedm

Thanks all argument finished...1 nil!!!
Zimmy  
#9 Posted : 13 May 2014 19:34:37(UTC)
Rank: Super forum user
Zimmy

Em lights best fed from local circuits and unless on a phase-fail system. Exit lighting does add something in the mix.

Never from their own circuit as they will only come on when that circuit fails...and not the local lighting
tony.  
#10 Posted : 13 May 2014 21:14:07(UTC)
Rank: Forum user
tony.

Zimmy,
Not quite true.
Maintained fittings can be ontheir own circuit, asthey are always 'on'
Jonesy73  
#11 Posted : 13 May 2014 21:43:28(UTC)
Rank: New forum user
Jonesy73

If we can go back to the original question and clear up for those that don't know -

Maintained lighting is designed to be lit continuously and will continue to work even in the event of a power failure. This allows the unit to double as a standard light fitting but still supply the necessary backup in the event of a power outage.

Non-maintained emergency lighting is designed to turn on in the event of a power failure, day-to-day it just looks like the lamp might have blown. It is linked into the building’s lighting circuitry and reacts to a power failure ensuring emergency exit routes remain illuminated.

Both types require a battery hook-up in order to work in emergency situations.

I'm not sure why anyone would pay for materials and labour to install non-maintained. If I fork out for this, then maintenance and testing, I want it to work in general, not just when I have to get out of the building in a hurry. Possibly thinking "It's so worth it".

Your maintenance person/ team should really be doing a monthly function test, it's just to see if the lamp and battery work at all, rather than the annual full function test for 3 hours. This too should be recorded in the log book. There could be a key switch or a localised socket which just takes a 'fish key' http://uk.rs-online.com/...00490/?origin=PSF_428090|acc
to cut the lighting power in that area and do the test.

paul.skyrme  
#12 Posted : 13 May 2014 21:47:59(UTC)
Rank: Super forum user
paul.skyrme

Tony,
I would have to disagree, as maintained lights could be turned off, in the same way as normal lighting if they are so wired.
Emergency lighting MUST illuminate (stay illuminated) in the event of failure of the normal lighting however that is achieved.
Believe me when I was discussing with a consultant who was called in as an independent witness relatively recently to a public sector building contractual issue where the central battery Em lighting was wired in flat twin & cpc.
So in the event of a fire there was every chance of the wiring melting and the EM lights going out as the supplies for the EM lights could not provide withstand to the fire for the 3 hours that the EM lights would have needed to illuminate for.
There are now people in the electrical "trade" that really have no idea what they are doing, they are dangerous, incompetent, and putting their customers at risk.

However, they are cheap, and the clients don't know any different more often than not.
So, as they are cheap, they get the work, same as the high volume low cost/low volume high cost consultancy model being discussed elsewhere.

It is the old adage of pay peanuts get monkeys, however, in this case the monkeys are quite likely to kill people or damage property when (not IF) they get it wrong.
tony.  
#13 Posted : 13 May 2014 21:56:30(UTC)
Rank: Forum user
tony.

Paul, the point i was making is that maintained em lights are always on.
A supply for this could come from any permanent supply, not just a local lighting circuit as you would with non maintained fittings

Having just spent 4k on batteries on one of my central inverter units, I fully agree,thankfully mine supplying all 96 fittings are wired in white pyro.
Shall we say a proper job.
paul.skyrme  
#14 Posted : 13 May 2014 22:51:59(UTC)
Rank: Super forum user
paul.skyrme

Tony,
Not quite, they are on, when the circuit that they are connected to is switched on, to illuminate them.
They don't "HAVE" to be on all the time.
There could be two circuits one for the "normal lights" one for the "maintained lights" the normal could suffer a power failure, that results in a fire, requiring evacuation in the dark and the circuit for the maintained lights could be switched off so they are not illuminated, but, the power to them remains energised, thus in the event of the emergency they do not illuminate.
Mebo  
#15 Posted : 14 May 2014 10:36:48(UTC)
Rank: Forum user
Mebo

There seems to be some confusion about how a maintained light operates. It has two mains inputs, one is powered continuously when the supply is present, charges the battery and senses when the mains fails.
The second "maintained" input is typically wired to a light switch and turns the (mains powered) light on and off in the normal way. The emergency function will always operate on mains failure, regardless of whether the maintained input is on or off.
It is (of course) different in France where they have a thing called "rest mode" whereby a light that has automatically come on in emergency mode can be switched off.
John (engineer at Menvier before the Americans bought it)
tony.  
#16 Posted : 14 May 2014 18:23:48(UTC)
Rank: Forum user
tony.


A standard bulkhead fitting maintained- its light is always on, can be fed from any circuit and not the local lighting circuit
A standard bulkhead fitting non maintained- its light is on when the local lighting circuit power fails.
Lets not complicate things with dual supplies, sustained fittings etc.
paul.skyrme  
#17 Posted : 14 May 2014 19:29:46(UTC)
Rank: Super forum user
paul.skyrme

No tony. not quite.
As Mebo says, again ignoring France,.
A maintained light will only operate as you describe IF it is wired in that manner.
An M/3 light according to the old designations has 2 line inputs that must be from the same phase, and a single neutral conductor, thus realistically to comply with BS7671 both supplies must be fed from the same source circuit.
(The current designation would be X1***180, where the * characters provide explicit functions.
The "trade" still refer to them in general as M3 & NM3.

The point that it seems both myself and Mebo are trying to make is that never mind how they are installed and functioning, what they are called etc. they are different designs that can be wired in different ways electrically to provide different functionality.

Some right, some wrong.

I often fit maintained 3 hr emergency lights (for a public sector client) which are not fed from the local lighting circuit, and in the event of failure of the local lighting circuit, they have to be manually energised to provide illumination.
They are not always illuminated.
These lights are NOT to comply with BS5266 the FRA or any statute requirements.
However, in the event of failure of their supply circuit they illuminate, as it is the failure of the circuit from which they are supplied we need to provide "assistance" with.
tony.  
#18 Posted : 14 May 2014 22:24:15(UTC)
Rank: Forum user
tony.

Paul,

Stop,trying to be difficult.
I'm talking about emergency lights wired with a permanent feed and neutral.
Non maintained fitting - illuminates on power failure.
Maintained fitting- allways on wired from any permanent feed and neutral and not just a local lighting circuit
Nothing complicated apart from your descriptions and I was discussing basic installations.
No more posts from me on this subject
paul.skyrme  
#19 Posted : 14 May 2014 23:47:36(UTC)
Rank: Super forum user
paul.skyrme

tony.

A non-maintained fitting will have only one line supply.
A maintained fitting will have two.

It is not my descriptions that are difficult, they exactly describe the electrical design of the fittings.
IF you can't comprehend the difference in the electrical design of a maintained and non-maintained fitting, then perhaps you should not comment?
There is NOTHING basic about electrical installations, done wrong they can kill and injure people and seriously damage property.
A maintained fitting requires two line supplies to function correctly end of story.

How many designs and installations of emergency lights have you undertaken exactly?
Do you REALLY understand how they function and are designed, and should be installed.

Your comment, that you will comment no more, to me seems to admit, that you are out of your depth?

Please all, if you don't, really, understand electrical systems, then you should not be "supervising" & "influencing" them on a level that it seems many people are.