Following a Fire Risk Assessment the assessor has stated that fire doors should be hung using 3 hinges. Currently most of our fire doors have only two hinges.
Is the assessor right? because most have been installed in the last five years - is this now new legislation and the assessor is telling me I have to do this?
Cheers for any info and thanks
Rich
|
|
|
|
Rank: Super forum user
|
Just checked FPA handbook and whilst there is a lot of detail on construction of various types of hinges, fire resistance and fitting to maintain the doors resistance I cant see anything that dictates the number!
Would advise you ask the assessor where they see the requirement coming from?
Jonty
|
|
|
|
Rank: Super forum user
|
I would guess the requirement is buried in a British Standard - probably for fire doors!!
But really, is it that essential - I would think is unlikely that a 2 hinged door would not have sufficient fire resistance to allow safe evacuaion of the building etc.
I would have thought the money spent on adding another hinge to the fire doors, could be spent on more beneficial fire safety issues that you might have?
Priorities!!
|
|
|
|
Rank: Super forum user
|
The reason for three hinges is to prevent warping or movement in the door leading to gaps or a poor fit afterwards. Generally 2 30 minute rated hinges, top and bottom and a control hinge in centre. This control hinge does not need to be fire rated as its disablement in a fire would not affect the functioning of the fire door. Dont know about legislation in relation to this, Ireland based, but it is common practice for some time now. Kevin
|
|
|
|
Rank: Guest
|
Thanks for all the replies - I agree it is one of priorities but I do take the point about preventing warping.
Rich
|
|
|
|
Rank: Super forum user
|
Further enquiries with my research assistant Mr Google suggests the standard you are looking for is BS EN 1935:2002
|
|
|
|
Rank: Guest
|
kevkel wrote:Further enquiries with my research assistant Mr Google suggests the standard you are looking for is BS EN 1935:2002 O that we could all afford £168 to buy this standard - it is one of the reasons why questions like mine appear on this forum. I hope to get answers from those who (or their company) can afford to buy such extortionately priced information. The charity I work for let alone SME's cannot afford such expense and you wonder why so many fall foul of H&S law. It makes H&S compliance absolutely unaffordable and practically impossible to achieve - no wonder the HSE is making millions at £126 per hour. Kevkel - do I need to fit 3 hinges to existing fire doors where at the moment I only have 2? Rich
|
|
|
|
Rank: Super forum user
|
Approved Doc B Appendix B vol 2 p 132
"Unless shown to be satisfactory when tested as part of the door assembly, the essential components of any hinge on which a fire door is hung should be made entirely from materials having a melting point of at least 800c"
|
|
|
|
Rank: Guest
|
martinw wrote:Approved Doc B Appendix B vol 2 p 132
"Unless shown to be satisfactory when tested as part of the door assembly, the essential components of any hinge on which a fire door is hung should be made entirely from materials having a melting point of at least 800c" Thanks martinw - so do I need 3 hinges? - does your reference state how many, please. Rich
|
|
|
|
Rank: Super forum user
|
wonder why so many fall foul of H&S law.
A British Standard is NOT law, unless 'called for in legislation'.
I would take much persuading that having a 3rd hinge fitted to your fire doors is a main fire safety priority.
|
|
|
|
Rank: Super forum user
|
Not sure what type of establishment you are in but if you look at page 126 of the document :- https://www.gov.uk/gover...factories-and-warehousesMay assist you and its free from the Government (for now anyway ). Refers to those nice BS noted above. So don't trust your assessor then ?
|
|
|
|
Rank: Super forum user
|
From the document quoted above: Hinges To ensure compliance with their rated fire performance, fire-resisting doors need to be hung with the correct number, size and quality of hinges. Normally a minimum of three hinges are needed, however the manufacturer’s instructions should be closely followed. BS EN 193538 including Annex B, is the appropriate standard. That's what I have always been led to believe. As stated above, the third hinge is designed to prevent warping in the doorset. The following might also prove useful (in this instance section 2 as it quotes several aspects of BS EN 1935. http://firecode.org.uk/C...ire_and_escape_doors.pdf
|
|
|
|
Rank: Super forum user
|
That document was produced in November 2012. Archived previous vesions going back to 2006 can be found by clicking the 'archive (Previous Editions)' link here: http://www.firecode.org.uk/
|
|
|
|
Rank: Forum user
|
Rich777 wrote:O that we could all afford £168 to buy this standard - it is one of the reasons why questions like mine appear on this forum. Rich
Hi Rich Get yourself down to your local library, most larger one's subscribe to BSOnline and you can view through the library's portal. Mine allows access through the internet, so I can do it from home. In these times of austerity some LAs are closing libraries or reducing services (such as BSOnline) so you may need to hunt around - most large municipals still provide this service.
|
|
|
|
Rank: Super forum user
|
If the fire doors have been manufactured by a certified manufacturer and installed by a certified installer they will almost certainly have three hinges.
Not many people are aware of the requirement for certified installers for fire doors.
They train, usually at their own expense to gain the certification and have follow up on site tests/checks to see they do the proper installation, there is more to it than just hanging a door. The door furniture has to be the right type and correctly installed with fire resistant fillers where necessary. Glazing has to be the correct type and correctly installed.
A non certified joiner may see three hinges but fit only two as they do not know any better.
IMO look for the plate on the top edge of the door, (use a mirror or take a picture with your phone), if a fire door it will be there. The plate will have the name of manufacturer, contact them and ask the question.
I would think that will take you ten minutes?
Please get back on here with the answer.
|
|
|
|
Rank: Super forum user
|
|
|
|
|
Rank: Guest
|
FireSafety101 wrote: IMO look for the plate on the top edge of the door, (use a mirror or take a picture with your phone), if a fire door it will be there. The plate will have the name of manufacturer, contact them and ask the question.
I would think that will take you ten minutes?
Please get back on here with the answer.
Will do
|
|
|
|
Rank: Super forum user
|
Rich 777- in answer to your question and as has been pointed out there is no legal requirement on the number of hinges. Older steel plated or heavier fire doors would have traditionally been fitted with 3 hinges due to the weight. There appears to have been an acceptance that two hinges sufficed. however in recent times the use of 3 hinges has become recommended again. So should you retrofit your fire doors with a control hinge? The answer is that it is probably not practical to do so at this stage unless the door sets are relatively new. In order to fit the control hinge to function effectively the doorset would most likely require some adjustment, which I dont believe any fire authority would expect as a reasonable action. I would cite that all replacements, new installations or door refurbishments would result in the installation of 3 hinges. This for me is a reasonably practicable solution. The plates on the top of the fire doors are often removed to plane the door to fit an existing frame. Not all fire doors are part of a doorset, and doorsets are not always practical to fit in certain openings. Kevin
|
|
|
|
Rank: Guest
|
kevkel wrote:Rich 777- in answer to your question and as has been pointed out there is no legal requirement on the number of hinges. Older steel plated or heavier fire doors would have traditionally been fitted with 3 hinges due to the weight. There appears to have been an acceptance that two hinges sufficed. however in recent times the use of 3 hinges has become recommended again. So should you retrofit your fire doors with a control hinge? The answer is that it is probably not practical to do so at this stage unless the door sets are relatively new. In order to fit the control hinge to function effectively the doorset would most likely require some adjustment, which I dont believe any fire authority would expect as a reasonable action. I would cite that all replacements, new installations or door refurbishments would result in the installation of 3 hinges. This for me is a reasonably practicable solution. The plates on the top of the fire doors are often removed to plane the door to fit an existing frame. Not all fire doors are part of a doorset, and doorsets are not always practical to fit in certain openings. Kevin Cheers Kevkel - thanks for the info - I'll follow your advice seeing as most of the doors were planed to fit. Rich
|
|
|
|
Rank: Super forum user
|
Rich777 wrote:Following a Fire Risk Assessment the assessor has stated that fire doors should be hung using 3 hinges. Currently most of our fire doors have only two hinges.
Is the assessor right? because most have been installed in the last five years - is this now new legislation and the assessor is telling me I have to do this?
Cheers for any info and thanks
Rich Rich, I too had a FRA conducted and this was a point raise, I too am unclear as to an answer
|
|
|
|
Rank: Guest
|
Lawlee45239 - have find the following which probably helps both of us:
Taken from: Fire Safety Advice Centre
Quote Single Axis Hinges
Hinges and latches have an important role in ensuring the integrity of the door. The fire door hinges must remain adequately screwed, in spite of the charring of wood in the vicinity. It is common to use three hinges although tests have shown that with some doors two hinges may be adequate for a 30 minute fire door (FD30). Steel and brass hinges are effective for a half-hour door, but only steel hinges will be satisfactory for a 60 minute fire door (FD60). For the latter, it may be necessary to use hinges with extended flaps (broad butts) so that fixing is maintained even when severe charring has taken place. BS EN 1935: 2002: Building Hardware Single Axis Hinges is the current European standard for single axis hinges and being able to understand the CE markings, provided when purchasing hinges, is of some importance. Guide to Interpreting Markings for Single Axis Hinges. The Building Regulations set out the circumstances in which rising butts may be used, although these are not recommended. In such a case compensation must be provided for the cut-out from the top edge of the door by increasing the depth of the stop. Unquote
Rich
|
|
|
|
Rank: Super forum user
|
Rich777 wrote:Lawlee45239 - have find the following which probably helps both of us:
Taken from: Fire Safety Advice Centre
Quote Single Axis Hinges
Hinges and latches have an important role in ensuring the integrity of the door. The fire door hinges must remain adequately screwed, in spite of the charring of wood in the vicinity. It is common to use three hinges although tests have shown that with some doors two hinges may be adequate for a 30 minute fire door (FD30). Steel and brass hinges are effective for a half-hour door, but only steel hinges will be satisfactory for a 60 minute fire door (FD60). For the latter, it may be necessary to use hinges with extended flaps (broad butts) so that fixing is maintained even when severe charring has taken place. BS EN 1935: 2002: Building Hardware Single Axis Hinges is the current European standard for single axis hinges and being able to understand the CE markings, provided when purchasing hinges, is of some importance. Guide to Interpreting Markings for Single Axis Hinges. The Building Regulations set out the circumstances in which rising butts may be used, although these are not recommended. In such a case compensation must be provided for the cut-out from the top edge of the door by increasing the depth of the stop. Unquote
Rich
Cheers for this, so my understanding is that the current 2 hinge is adequate for 30min.
|
|
|
|