Hello All,
I am wanting some information/thoughts about office lighting, currently we have the standard 600 x 600 light fittings with the metal Louvre panels I was wondering if changing these Louvre panels to Opal diffuses would have a detrimental effect to the emergency light system. would they block out too much light?
Any help would be appreciated!
thanks
|
|
|
|
Rank: Super forum user
|
You'll need photometric data from the manufacturers, or else you will need to undertake some calculations.
There are means of verifying this information.
What does the photometric data from the existing emergency lighting design scheme say?
Are you borderline already, or do you have plenty of "leeway"?
|
|
|
|
Rank: Forum user
|
From memory we are currently at around 4 lux and I think the minimum is 2? please correct me if I am wrong.
the prismatic sheet that is Opal doesn't give any breakdown of potential light losses etc I presume this will need to be checked with a light meter?
|
|
|
|
Rank: Super forum user
|
Difficult to measure accurately because you will have shared light, the EM lighting must give adequate levels regardless of shared light, else you would be relying on the shared light in the first place would you not?
As I said you really need the photometric data from the light fitting and check what this is on your existing design, then, you can get the photometric data with the diffuser and compare the two.
It's not just the lux level but the spread of light that could be affected, hence the requirement for the photometric data giving the spread and intensity.
|
|
|
|