#1 Posted : 11 January 2016 15:05:48(UTC)
Rank: Forum user
scott_graeme

would really appreciate some feedback from any electrical specialists on minor works certificates.
working on a contract that is applying external wall insulation to domestic properties in scotland, prior to the insulation services are extended and we remove external lights and sockets to enable the insulation and render once the render is complete we reinstate the lights sockets etc, normal weather conditions we are completing a house a week but due to bad weather this has been prolonged and the wires are left taped up for longer than we would want
when the elec reinstates the lights/sockets would this require a minor works certificate? bs7671 says they may issue a cert but every electrician i speak to gives me a different answer from yes, no to maybe
do the other members think iam taking the wrong approach to insist we get a minor works cert for remove/replace existing external lights and power sockets?
paul.skyrme  
#2 Posted : 11 January 2016 19:58:44(UTC)
Rank: Super forum user
paul.skyrme

I take it that you are not just taping the wires up outside the property with them still connected to the supply inside surely?

That is simply unacceptable.

If you are complying with BS7671, and you are modifying the electrical circuits by extending them or re-locating accessories, then an MWC must be produced as this is required by BS7671.
If your electrician is a member of a registration body, then this will be a requirement of their membership conditions also.

If the work is being done under building control warrant etc. then the modification to the services should really be covered by this also as required and this would also require the issue of certification under BS7671.

IF, there are no modifications to the wiring in that it is just a disconnect and reconnect of the same or an equivalent item, then strictly there is no requirement for an MWC, however, the persons undertaking the work must be able to prove if necessary that the device was correctly reconnected, and the removal/replacement had no detrimental effect on the circuit.
Without an MWC, or an alternative means of recording the test results how could they prove this.

I can recall some years ago, we changed socket brands, and I fitted a socket with L-E reversed as I was so familiar with the “old” type I just connected the wiring in the same order, not checking the terminals, without my going back and inspecting & testing my work correctly that would have gone unnoticed, and could have been lethal.

I learnt my lesson that day, and I always double check, even though I always I&T any work I do anyway, even if I’m not issuing a cert, e.g. like for like maintenance, such as replacing a damaged socket outlet, I will verify the polarity & the loop impedance.
I have seen faulty new sockets in the past too, with no earth connection between the wiring terminal and the socket outlet pin.
scott_graeme  
#3 Posted : 12 January 2016 16:35:48(UTC)
Rank: Forum user
scott_graeme

hi paul,
thanks for the help/info, no we isolate all supplies from within the property the tape is just to stop water getting in but due to severe weather some jobs have been left like this for 5 weeks so we were thinking of testing/certing just to be sure the water hasn,t crept in to the wiring, on the rare occasion there is no means to isolate we put the exposed wiring in an ip rated external isolation box but as of yet this hasnt happened as in general there is a means to isolate within the property