We are having a re-shuffle in the factory and one of my supervisors wish to create space between rows of trollies (holding foam - nothing nasty) to allow them to walk between the trollies to inspect product. The widths they are suggesting is 500mm.
This space will only be used for accessing the product, it is not a walkway or thoroughfare.
Is there any guidance on the minimum distances for non emergency access routes?
Struggling to find any - Possibly because if the alarm goes off when your in this narrow route, it then becomes an emergency access route.
Any thoughts or experience on this?
|
|
|
|
Rank: Super forum user
|
If you have a walkway and then use it as an emergency escape route you need to go by the set sizes as laid down in the building regs
Current building regulations contain guidance on the widths of escape routes and exits for new-build, non-domestic properties and the communal areas in purpose built blocks of flats in “The Building Regulations 2010, Fire Safety, Approved Document B, Volume 2 – Buildings Other Than Dwellinghouses, 2006 edition, incorporating 2007 and 2010 amendments”.
The following information is extracted from page 37 of the above document:
3.18: The width of escape routes and exits depends on the number of persons needing to use them. They should not be less than the dimensions given in the following table:
3.20: Widths of escape routes and exits
Maximum Number of Persons Minimum Width (mm)
60 750
110 850
220 1050
More than 220 +5mm per person
In calculating exit capacity, the document notes the further points:
3.21: If a storey or room has two or more storey exits it has to be assumed that a fire might prevent the occupants from using one of them. The remaining exit(s) need to be wide enough to allow all the occupants to leave quickly. Therefore, when deciding on the total width of exits needed according to the above table, the largest exit should be discounted.
3.22: The total number of persons which two or more available exits (after discounting) can accommodate is found by adding the maximum number of persons that can be accommodated by each exit width. For example, 3 exits each 850mm wide will accommodate 3 x 110 = 330 persons (not the 510 persons accommodated by a single exit 2550mm wide).
Hope that helps
|
|
|
|
Rank: Super forum user
|
Difficult to comment without knowing all the facts but the absolute minimum hallway width is about750mm, scaffolding is recommended as 660mm. So 500mm is bit tight but may be acceptable if you provide other controls, one person access, lighting, induction, signage etc.
Because a person is inspecting the trolleys using the access would not make it an emergency route if an alarm goes off however, as you have hinted at, egress has to be considered. If you are worried about it ask for feedback after the next fire drill.
|
|
|
|
Rank: Super forum user
|
500mm seems rather narrow to be doing anything other than shuffle through (and that's for a slim person). If the inspection needs anything more than a cursory glance at eye height then I suggest that the suggested width is inadequate, quite regardless of any legal issues.
|
|
|
|