Welcome Guest! The IOSH forums are a free resource to both members and non-members. Login or register to use them

Postings made by forum users are personal opinions. IOSH is not responsible for the content or accuracy of any of the information contained in forum postings. Please carefully consider any advice you receive.

Notification

Icon
Error

Options
Go to last post Go to first unread
Russ1977  
#1 Posted : 30 March 2016 12:42:19(UTC)
Rank: Forum user
Russ1977

Hi all,

After some opinions if you would be so kind,

Fire exits that lead to roofs as a final destination, discuss. I have my thoughts my would welcome everyone elses.
martin1  
#2 Posted : 30 March 2016 13:11:26(UTC)
Rank: Super forum user
martin1

I'll wade in and say "no" as you don't know if there is fire underneath said roof ( presuming all part of same structure ).
jwk  
#3 Posted : 30 March 2016 13:20:05(UTC)
Rank: Super forum user
jwk

Fire exits must lead to place of safety, defined in the RR(FS)O as 'a safe place beyond the premises'. Don't think a roof meets that definition,

John
stonecold  
#4 Posted : 30 March 2016 13:45:44(UTC)
Rank: Super forum user
stonecold

Is there a safe way off the roof? Its ok in some circumstances for a fire route to cross a roof, but im not sure if you mean once your on the roof you cant actually get off it?
firesafety101  
#5 Posted : 30 March 2016 13:59:41(UTC)
Rank: Super forum user
firesafety101

No problem at all as long as there is a safe route fom the roof leading to a safe area.

If that route leads to a yard there must be a way out of the yard.

Consider the occupancy, who may need to use that means of escape, disabled, children, people who wear dresses and skirts who should not climb ladders, etc. affects of weather, ice and snow, fall protection and so on.

Can the roof take the weight of the expected load.

Be aware of glazing panels higher than your roof that may need to be fire rated.

Fire risk assessment by a competent person should sort it out for you.

Ron Hunter  
#6 Posted : 30 March 2016 14:59:19(UTC)
Rank: Super forum user
Ron Hunter

jwk wrote:
Fire exits must lead to place of safety, defined in the RR(FS)O as 'a safe place beyond the premises'. John


So by that definition, I can't have an assembly point in the ground level car park of my office complex?
jwk  
#7 Posted : 30 March 2016 15:06:01(UTC)
Rank: Super forum user
jwk

Ron, good point! By 'premises' I suspect they actually mean within the building perimeter, rather than the demesne.

I was always taught that a place of safety would be somewhere where the people evacuated could move onwards without further assistance. Of course that's a bit of a moot point in some places, but it's a reasonable definition for most circumstances. It would preclude a roof, though as st9onecold says you can use a rooftop walkway as part of an escape route,

John
Invictus  
#8 Posted : 30 March 2016 15:41:44(UTC)
Rank: Super forum user
Invictus

jwk wrote:
Ron, good point! By 'premises' I suspect they actually mean within the building perimeter, rather than the demesne.

I was always taught that a place of safety would be somewhere where the people evacuated could move onwards without further assistance. Of course that's a bit of a moot point in some places, but it's a reasonable definition for most circumstances. It would preclude a roof, though as st9onecold says you can use a rooftop walkway as part of an escape route,

John



I think leaving them on the roof is a bit tuff but hey they are out of the building. It also needs to be remembered that you cannot place your plan around the Fire Brigade getting you off the roof before you end up at ground level, through the whole the fire has made.
phargreaves04  
#9 Posted : 30 March 2016 22:03:44(UTC)
Rank: Forum user
phargreaves04

I would say yes no problem, many of ours do as they are very large and complex buildings.
godscrasher  
#10 Posted : 31 March 2016 08:41:26(UTC)
Rank: Forum user
godscrasher

Yes it's perfectly fine.

A fire escape must lead to a safe place away from the fire. Fire protection should give you at least 30 minutes minimum of fire spread.

Many places have fire escapes leading to a balcony, this is a safe place until rescue arrives. many places have a need to have a 'place of relevant safety' in the stairwell for disabled people. Again this is fire rated to give at least 30 minutes protection (or which should be 60 in a stairwell).

The important thing is that the fire protection needs to be adequate to stop the spread. Once the spread is limited then the fire is contained and everyone, even the person on the roof can be rescued.
RayRapp  
#11 Posted : 31 March 2016 09:00:54(UTC)
Rank: Super forum user
RayRapp

Godscrasher wrote:
Yes it's perfectly fine.

A fire escape must lead to a safe place away from the fire. Fire protection should give you at least 30 minutes minimum of fire spread.

Many places have fire escapes leading to a balcony, this is a safe place until rescue arrives. many places have a need to have a 'place of relevant safety' in the stairwell for disabled people. Again this is fire rated to give at least 30 minutes protection (or which should be 60 in a stairwell).

The important thing is that the fire protection needs to be adequate to stop the spread. Once the spread is limited then the fire is contained and everyone, even the person on the roof can be rescued.


And who will rescue these people on the roof? According to Fire and Rescue your emergency plan should not rely on the F&R to evacuate people.
Russ1977  
#12 Posted : 31 March 2016 09:21:18(UTC)
Rank: Forum user
Russ1977

I'm with Ray Rapp and the others of the same opinion, roofs are not suitable as a final place of safety.
stonecold  
#13 Posted : 31 March 2016 09:36:23(UTC)
Rank: Super forum user
stonecold

A fire exit route can cross a roof ONLY if certain critieria is met e.g

The roof should be flat and the route across it should be adequately defined and well illuminated, the route should be non-slip and guarded with a protective barrier, the escape route across the roof and its
supporting structure should be constructed as a fire-resisting floor etc etc

The exit from the roof should be in, or lead to, a place of reasonable safety where people can quickly move to a place of total safety.

Waiting for rescue on a roof from which you cannot easily exit is not acceptable in my opinion.
ttxela  
#14 Posted : 31 March 2016 09:43:14(UTC)
Rank: Forum user
ttxela

I think even if technically acceptable I'd be somewhat disappointed if I was the one escaping the fire to find myself trapped on a nearby roof!
Alfasev  
#15 Posted : 31 March 2016 10:02:13(UTC)
Rank: Super forum user
Alfasev

Russ1977, the roof option as a “final destination” seems to me to be unsafe, but I suspect you know this. However without further details I fail to see how anyone can say it is safe or not. Fire safety and particularly fire engineering can be complex.

The 30/60 minute rate in building regulations is primarily to allow for escape only unless it is part of a whole building fire strategy and there are normally other measures in place like sprinklers. You can evacuate to a safe haven within a building complex (invacuation) but this is not a simple or cheap option.

Safe havens are normally seen in places like hospitals where it is very difficult to move everyone out of the building, but ultimately they can. The hospital will have a complex fire strategy and be equipped with a host of protection measures e.g. sprinklers, zoning, multifaceted fire alarm and panel etc. and be on the emergency services high priority list.

What is bothering me with the roof options is:-
• People cannot be stranded on the roof and be left to be rescued by the emergency services!
• What about radiated heat?
• How do you know the fire will not spread quickly and affect the roof? One small hole in a fire break will allow a fire to spread and there may be no fire breaks in the structure.
• Edge protection.
• Roof loads and possibility of collapse.
• Will people actual evacuate to a roof?
RayRapp  
#16 Posted : 31 March 2016 11:24:38(UTC)
Rank: Super forum user
RayRapp

It's interesting to observe the many different responses to what is a basically simple question. Okay as some posters have pointed out, how safe the roof may be depends on a number of different factors most of which are unknown.

I am not a fire expert - but the thought of using a roof of a building on fire as a safe refuge sends shudders through me. Perhaps safety is essentially common sense after all?
jwk  
#17 Posted : 31 March 2016 11:35:40(UTC)
Rank: Super forum user
jwk

Alfasev is quite right about safe havens, and it needs to be added that even in hospitals they are very much a court of last resort. Modern hospitals should be designed to facilitate escape in the event of fire, as they should follow the design principles in HTM-05.

A roof is not a suitable place of safety unless there is really no alternative. As people have pointed out; they will need to be taken off the roof by some other agency. The fire service like to turn up and put the fire out, they wouldn't be too please about evacuating a factory/office full of people unless there is no alternative.

Why does it have to be a roof?

John
firesafety101  
#18 Posted : 31 March 2016 11:50:43(UTC)
Rank: Super forum user
firesafety101

I wouldn't design a building with fire exits leading onto a roof but there are existing buildings where an alternative exit is required and the roof is the best scenario.

in that case the most stringent requirements must be placed on its use and including those I suggested earlier.

As for Safe Havens there is a particular budget hotel chain that builds these in to their new builds, they are done properly and are for use by wheelchair users. They include fire resisting compartment, communication and a lift designed for use in fire situations.

The idea I suppose is to place the wheelchair user in the safe haven while able people exit the building then the disabled can exit.

As for rescue from roofs, best not to rely on anyone coming to the rescue but build in a means of exiting the roof without the need for assistance.

This should include evacuation for disabled persons with assistance by employees, not the fire service.

Would you like you elderly mother to wait on a roof exposed to the elements or at worst a fire situation while awaiting the arrival of an outside agency, namely the fire service, who now have extended arrival time requirements for the first appliance, 10 minutes for some, 12 minutes for others.

Gone are the days of the 5 minute arrival time for two appliances, you will be lucky to see one in ten minutes now.






Invictus  
#19 Posted : 01 April 2016 08:30:05(UTC)
Rank: Super forum user
Invictus

Godscrasher wrote:
Yes it's perfectly fine.

A fire escape must lead to a safe place away from the fire. Fire protection should give you at least 30 minutes minimum of fire spread.

Many places have fire escapes leading to a balcony, this is a safe place until rescue arrives. many places have a need to have a 'place of relevant safety' in the stairwell for disabled people. Again this is fire rated to give at least 30 minutes protection (or which should be 60 in a stairwell).

The important thing is that the fire protection needs to be adequate to stop the spread. Once the spread is limited then the fire is contained and everyone, even the person on the roof can be rescued.



I gather you mean a 'refuge' were have you seen a balcony as a safe refuge, how is it safe? who will rescue you from the balcony?

You cannot put the FRS down on an assessment and a refuge is used to allow time to move people down and out if the need arises.
Hospitals etc will normally use Horizontal so that they do not have to move everyone out for the obvious reasons.

I personally would never say a safe haven would be a roof unless this is the route to a stairwell to exit then all other factors would have to be considered, is there any windowms onto the escape stairs are they the correct standard to resist fire, disabled people etc.
phargreaves04  
#20 Posted : 01 April 2016 23:23:36(UTC)
Rank: Forum user
phargreaves04

Sounds strange I know but the roofs we use actually lead to the ground, or very nearly do, and then to a place of ultimate safety.
Messy  
#21 Posted : 06 April 2016 20:50:37(UTC)
Rank: Forum user
Messy

No it is not acceptable to have an escape route into a dead end location such as a rooftop or blind courtyard


No ifs or buts, it is not acceptable to rely on fire service as part of an evacuation plan

Messy  
#22 Posted : 06 April 2016 21:12:05(UTC)
Rank: Forum user
Messy

I should add that I was known as mssy on this forum until today and have posted many times on the forum in relation to fire safety matters

Due to IT issues, I have had to 're brand' myself as "Messy" and start here again.

Cheers
Guyzy1982  
#23 Posted : 08 April 2016 13:24:03(UTC)
Rank: Forum user
Guyzy1982

Look at the worst case; if persons evacuate to the roof and are there for a long time due to lack of response from fire and rescue, or the FRS are busy else where, what do the evacuee's do then? People have in my opinion rightly identified that we should not have the FRS as a measure to save staff, they will have a possible fire to deal with also, therefore putting their lives in more of a danager. All escape routes should be to places of TOTAL safety.

Good luck!
firesafety101  
#24 Posted : 08 April 2016 16:05:29(UTC)
Rank: Super forum user
firesafety101

Messy wrote:
I should add that I was known as mssy on this forum until today and have posted many times on the forum in relation to fire safety matters

Due to IT issues, I have had to 're brand' myself as "Messy" and start here again.

Cheers


Thanks for letting us in on that really radical name change messy, no way we would we have guessed it was still your good self ;-)
Robert J I  
#25 Posted : 13 April 2016 15:43:14(UTC)
Rank: Forum user
Robert J I

Russ1977 wrote:
Hi all,

After some opinions if you would be so kind,

Fire exits that lead to roofs as a final destination, discuss. I have my thoughts my would welcome everyone elses.


Use to have one of those at premises I worked on. Enforcing Authority came in and made us close it.

Your place would need a fire escape off the roof to floor level, with emergency lighting, anti-slip treads and such.
Jim Tassell  
#26 Posted : 15 April 2016 14:55:10(UTC)
Rank: Forum user
Jim Tassell

Sorry if I've missed it but I don't see any reference here to the official guidance.
The conditions under which a roof can form part of an escape route are well described, with a picture, at page 86 and figure 40 in the Factory and Warehouse" guide and similarly in the other guides. See https://www.gov.uk/gover...factories-warehouses.pdf
Invictus  
#27 Posted : 15 April 2016 15:01:32(UTC)
Rank: Super forum user
Invictus

Jim Tassell wrote:
Sorry if I've missed it but I don't see any reference here to the official guidance.
The conditions under which a roof can form part of an escape route are well described, with a picture, at page 86 and figure 40 in the Factory and Warehouse" guide and similarly in the other guides. See https://www.gov.uk/gover...factories-warehouses.pdf


The question was the roof as a 'final destination', not as part of the escape route, we have as part of the scape route.
Users browsing this topic
Guest
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.