PeterP  
#1 Posted : 09 June 2016 11:28:07(UTC)
Rank: Forum user
PeterP

We have a vacuum cleaner on site that is owned by a contracted cleaning company, could someone please advise on who would be responsible for have it tested. Many thanks
Invictus  
#2 Posted : 09 June 2016 11:33:13(UTC)
Rank: Super forum user
Invictus

There is no legal requirement to have it tested, you can carry out visual checks on it. If you use it have your staff check it if you don't make sutre they completed checks. http://www.hse.gov.uk/pubns/books/hsg107.htm
PeterP  
#3 Posted : 09 June 2016 11:48:03(UTC)
Rank: Forum user
PeterP

Thank you Invictus
gerrysharpe  
#4 Posted : 09 June 2016 14:09:24(UTC)
Rank: Super forum user
gerrysharpe

Although there may be no legal Requirement to have it Pat Tested, The Insurance company may see it differently and it may be a clause that all Portable electrical Equipment will need to be Pat Tested at regular intervals. Normally the HSE would expect to see a Pat Test register with regular testing done and in an office environment at least Yearly. Normally if a contractor supplies their own tools and equipment then they would be responsible for its maintenance and upkeep, and supply you with a Pat Test register of their equipment that they have on your site. The UK Health and Safety Executive along with insurance companies will expect you to perform PAT testing to ensure that you are compliant with certain regulations including: Health and Safety at Work Act of 1974 The Electricity at Work Regulations of 1989 The Provision and Use of Work Equipment Regulations of 1998 The Management of Health and Safety at Work Regulations of 1999 Not complying with the above mentioned regulations can result in fines up to £5,000 and/or six months imprisonment. Fines have been seen to go as high as £20,000 and offences heard in the Crown Court have carried sentences of more than 2 years imprisonment in additional to unlimited financial penalties. So even though PAT testing itself is not legally required, it simply helps you to protect yourself by ensuring that you are complying with these regulations. Claims that PAT testing is required by law and that the client is breaking the law by not having it done are simply not true. The law does require however that employers, including self-employed, ensure that all electrical equipment that they provide in their business is safe and properly maintained. This means that PAT testing is a critical part of your company’s health and safety and should be considered part of a solution to your safety concerns. take a peek here http://www.pat.org.uk/is...ing-a-legal-requirement/
Invictus  
#5 Posted : 09 June 2016 14:19:14(UTC)
Rank: Super forum user
Invictus

gerrysharpe wrote:
Although there may be no legal Requirement to have it Pat Tested, The Insurance company may see it differently and it may be a clause that all Portable electrical Equipment will need to be Pat Tested at regular intervals. Normally the HSE would expect to see a Pat Test register with regular testing done and in an office environment at least Yearly. Normally if a contractor supplies their own tools and equipment then they would be responsible for its maintenance and upkeep, and supply you with a Pat Test register of their equipment that they have on your site. The UK Health and Safety Executive along with insurance companies will expect you to perform PAT testing to ensure that you are compliant with certain regulations including: Health and Safety at Work Act of 1974 The Electricity at Work Regulations of 1989 The Provision and Use of Work Equipment Regulations of 1998 The Management of Health and Safety at Work Regulations of 1999 Not complying with the above mentioned regulations can result in fines up to £5,000 and/or six months imprisonment. Fines have been seen to go as high as £20,000 and offences heard in the Crown Court have carried sentences of more than 2 years imprisonment in additional to unlimited financial penalties. So even though PAT testing itself is not legally required, it simply helps you to protect yourself by ensuring that you are complying with these regulations. Claims that PAT testing is required by law and that the client is breaking the law by not having it done are simply not true. The law does require however that employers, including self-employed, ensure that all electrical equipment that they provide in their business is safe and properly maintained. This means that PAT testing is a critical part of your company’s health and safety and should be considered part of a solution to your safety concerns. take a peek here http://www.pat.org.uk/is...ing-a-legal-requirement/
It's a myth that all portable electrical appliances in a low-risk environment, such as an office, need to have a portable appliance test (PAT) every year. The law simply requires employers to ensure electrical equipment is maintained in order to prevent danger – it doesn’t state what needs to be done or how often.
Invictus  
#6 Posted : 09 June 2016 14:30:01(UTC)
Rank: Super forum user
Invictus

Why scare people the PAT testing is not a legal requirement, I also attach the link to the nyth busters http://www.hse.gov.uk/myth/july.pdf http://www.hse.gov.uk/pubns/indg236.pdf PA having to complete PAtesting is the myth and the HSE doesn't want to office equipment tested regularly at all. You should plan accordingly, so now we test a built in fridge frezer annually, tell me were has it moved too. desk top monitors etc do not need it either if you read through the regs then you would find that they also give a guidence of what needs doing and when, most of the office equipment is double instulatted and therefore needs some sort of test but even then it is not prescptive. IT tells you at the beginning that it is not compulsory but may assist in helping you comply to the law. So if the guidence tell you that you don't need it doing for 5 years you don't need to, bvisyal inspections will suffice and then recording them annually but you don't need to have it PA tested by anyone.
Invictus  
#7 Posted : 09 June 2016 14:39:44(UTC)
Rank: Super forum user
Invictus

Sorry 'HSE doesn't want to see office equipment tested anually at all'.
gerrysharpe  
#8 Posted : 09 June 2016 14:45:35(UTC)
Rank: Super forum user
gerrysharpe

However... Under The Provision & Use of Work Equipment Regulations 1998 Covers inspection under S.6(1) Every employer shall ensure that work equipment is inspected: (a) 'after installation and before being put into service' (b) 'after assembly at a new site or location'. It can be seen that even new equipment should be inspected before use. Equipment moved to a new location should be inspected to ensure that it has been properly assembled and has not been damaged during transit. S.6(2) places a duty on every employer to ensure that work equipment subject to deterioration is inspected at: S.6(2)(a) 'suitable intervals' S.6(2)(b) 'each time that exceptional circumstances which are liable to jeopardise the safety of work equipment have occurred'. How you you satisfy The HSE when they say haw have you Inspected and Tested the Vacuum Cleaner and How have you recorded it ? Simply by doing a visual Inspection is not going to satisfy the HSE as to the equipment's electrical safety, and also its states "The inspection and testing should be carried out by a 'competent person', this being a person with the necessary skills, experience and qualifications." So simply asking the Cleaner is the hoover ok, is not the correct way. For the sake of a pat test which could cost £1 per item or less, you have a record of its electrical safety, completed by a competent and Qualified individual. Surely its better to be safe rather than sorry?
chris42  
#9 Posted : 09 June 2016 14:46:10(UTC)
Rank: Super forum user
chris42

It is just laziness to an extent, it is easier to just get everything done once a year, requires little thought or effort. But at almost £1 a time can be a little costly. Also if you are going to get someone in to visually inspect they just as well plug it in the tester. From indg236 Not every electrical item needs a portable appliance test (PAT) In some cases, a simple user check and visual inspection is enough, eg checking for loose cables or signs of fire damage and, if possible, checking inside the plug for internal damage, bare wires and the correct fuse. Other equipment, eg a floor cleaner or kettle, may need a portable appliance test, but not necessarily every year. Do you really want your employees " checking inside the plug" from the above? Even if you are happy to let them, who has the time, who will co ordinate, will they each be issued with their own screwdrivers. Laziness wins Yes I know not Friday yet.
Invictus  
#10 Posted : 09 June 2016 14:48:31(UTC)
Rank: Super forum user
Invictus

Don't like the braces and belt approach, I feel it holds safety back.
gerrysharpe  
#11 Posted : 09 June 2016 14:53:01(UTC)
Rank: Super forum user
gerrysharpe

Also the Electricity at Work Regulations do not specifically mention portable appliance testing and inspection; they simply require electrical systems to be 'maintained' in a condition so as not to cause danger. However, the only way we know if a system needs to be maintained is if it is inspected and tested, and so the need for such inspection and testing of a system is implicit in the requirement for it to be maintained. Anyone who inspects and tests and electrical system is, in law, a duty holder and must be competent to undertake such work.
Invictus  
#12 Posted : 09 June 2016 14:57:02(UTC)
Rank: Super forum user
Invictus

chris42 wrote:
It is just laziness to an extent, it is easier to just get everything done once a year, requires little thought or effort. But at almost £1 a time can be a little costly. Also if you are going to get someone in to visually inspect they just as well plug it in the tester. From indg236 Not every electrical item needs a portable appliance test (PAT) In some cases, a simple user check and visual inspection is enough, eg checking for loose cables or signs of fire damage and, if possible, checking inside the plug for internal damage, bare wires and the correct fuse. Other equipment, eg a floor cleaner or kettle, may need a portable appliance test, but not necessarily every year. Do you really want your employees " checking inside the plug" from the above? Even if you are happy to let them, who has the time, who will co ordinate, will they each be issued with their own screwdrivers. Laziness wins Yes I know not Friday yet.
Why didn'y I think of that as things only go wrong once a year, so why carry out any other inspections, visual etc. have everything tested once a year attitude is what is wrong with health and safety, it's the same with PPE don't give people who require it for a task give it to everyone, then no-one has to think.
Xavier123  
#13 Posted : 09 June 2016 15:10:38(UTC)
Rank: Super forum user
Xavier123

Ahem. I have no problem with not having PAT tests annually for general office equipment. There are other means of proving sufficient maintenance and safety - see all the arguments already given. Signed A regulator NB. It is, of course, more complicated than that but please don't believe that its what we have to see to find an organisation legally compliant and will almost certainly be based upon the specific circumstances relevant to that organisation.
chris42  
#14 Posted : 09 June 2016 15:29:06(UTC)
Rank: Super forum user
chris42

I'm not saying people are not expected to report noted damage when they go to use something. What I'm suggesting is that for some company's who may have someone come in once a year to do 100 items in a workshop, another dozen items in the offices is no real hastle. Saying that some only need doing say every 5 years, how you going to remember. Maybe once a year is not perfect either, but it is 4 times more and you get a record that someone checked. I'm not disagreeing that some things need not be done every year, just logistically, often the easy route is taken. I admit we do it here every year, it was done like this before I started. The kettle and those wretched 2kW fan heaters are more mistreated than tools. The last place I worked we had our own maintenance team and they did it proportionally, to the environment the item was in and they controlled the retest dates. Its not a H&S decision, it is a logistics one. Any inspection is like the MOT on your car only good for a few minutes after it has left the possession of the tester. Then only good for the things actually tested.
HSSnail  
#15 Posted : 09 June 2016 15:31:08(UTC)
Rank: Super forum user
HSSnail

gerrysharpe wrote:
However... Under The Provision & Use of Work Equipment Regulations 1998 Covers inspection under S.6(1) Every employer shall ensure that work equipment is inspected: (a) 'after installation and before being put into service' (b) 'after assembly at a new site or location'. It can be seen that even new equipment should be inspected before use. Equipment moved to a new location should be inspected to ensure that it has been properly assembled and has not been damaged during transit. S.6(2) places a duty on every employer to ensure that work equipment subject to deterioration is inspected at: S.6(2)(a) 'suitable intervals' S.6(2)(b) 'each time that exceptional circumstances which are liable to jeopardise the safety of work equipment have occurred'. How you you satisfy The HSE when they say haw have you Inspected and Tested the Vacuum Cleaner and How have you recorded it ? Simply by doing a visual Inspection is not going to satisfy the HSE as to the equipment's electrical safety, and also its states "The inspection and testing should be carried out by a 'competent person', this being a person with the necessary skills, experience and qualifications." So simply asking the Cleaner is the hoover ok, is not the correct way. For the sake of a pat test which could cost £1 per item or less, you have a record of its electrical safety, completed by a competent and Qualified individual. Surely its better to be safe rather than sorry?
As the HSE are not the enforcing authority for most offices I don't think they would be bothered in the slightest. Might want to ask the local authority officer (EHO or similar) and I bet you get the same answer! better safe system than PAT once a year! I once saw a vacuum where I could see the bare metal wires in 6 places because the leed had been cut. But it had been PAT 7 months ok so everyone thought it was OK to use!
Invictus  
#16 Posted : 09 June 2016 15:35:58(UTC)
Rank: Super forum user
Invictus

We call ours a PPM and we add FLT's, pressure vessels, lifts etc to it and it is managed through the properties department who have alerts set up. Getting people use to carrying out visual insoections is important as they start to think that everything is ok for a year if you don't. You don't have to take the plug off you just check that there is no damage to the item shell, wires are not frayed or dameged, the plug is in good order with not dame, and no scorching around the socket. Once they get into this routine, you can reduce costs. It's ok for a small office but not a large one. The thing is your right it's easier so lets do it that way. Doesn't help the workforce and won't help you if for some reason it's late getting done and they refuse to use the equipment because the PAT is out of date.
chris42  
#17 Posted : 09 June 2016 15:59:18(UTC)
Rank: Super forum user
chris42

quote=Invictus]if for some reason it's late getting done and they refuse to use the equipment because the PAT is out of date.
I wish :0) There are bigger fish to fry than worrying that the office fan is PAT tested more often than is strictly necessary. Yes since starting I have had to implement a number of regular employee checking systems as you say Daily Fork truck checks, Daily ( only 5 minutes), weekly and monthly fire checks, Ladder checks and a host of other checks at our sites. Systems to ensure LOLER & PUWER examinations are done and any issues resolved, Things are serviced when they should and by competent people. To name but a few thing which were all new and foreign to them. Therefore over testing of PAT was not a priority for me and the company had already got its mind around that particular concept. I'm not going to do more than instruct employees to quickly check for obvious damage before they use something, certainly no records. So yes laziness won a bit. Guilty as charged. Over PA Testing is so low down my list of things to do I would need a work at height risk assessment for the hole I'm stood next to in order to look down at it. Chris
toe  
#18 Posted : 09 June 2016 23:33:29(UTC)
Rank: Super forum user
toe

Just out of interest, when The Scottish Fire and Rescue Service are inspecting a Care Home they expect annual PAT and 5 year fixed wiring tests to be conducted. You can argue until you are blue in the face that they are not legal requirements however, they will not authorise the Care Home Licence without these being in place.
HSSnail  
#19 Posted : 10 June 2016 10:36:51(UTC)
Rank: Super forum user
HSSnail

toe wrote:
Just out of interest, when The Scottish Fire and Rescue Service are inspecting a Care Home they expect annual PAT and 5 year fixed wiring tests to be conducted. You can argue until you are blue in the face that they are not legal requirements however, they will not authorise the Care Home Licence without these being in place.
But it might be part of the license conditions, in which case they can ask for what ever they want. Just as insurance companies etc often do.
stonecold  
#20 Posted : 10 June 2016 11:43:28(UTC)
Rank: Super forum user
stonecold

gerrysharpe wrote:
Also the Electricity at Work Regulations do not specifically mention portable appliance testing and inspection; they simply require electrical systems to be 'maintained' in a condition so as not to cause danger. However, the only way we know if a system needs to be maintained is if it is inspected and tested, and so the need for such inspection and testing of a system is implicit in the requirement for it to be maintained. Anyone who inspects and tests and electrical system is, in law, a duty holder and must be competent to undertake such work.
You can quote all the regs you like, but the actual FACT is that PAT testing is NOT a legal requirement. Even the HSE clearly say so.
paul.skyrme  
#21 Posted : 10 June 2016 19:01:23(UTC)
Rank: Super forum user
paul.skyrme

OK, we all know that PAT is not required under statute law by “name”. To answer the OP, IF the vacuum cleaner requires PAT, then it is down to the employer of the user. It is also down to them to decide if it requires PAT. If your company requires that all equipment is subject to PAT, then you are legally allowed to insist upon it under your terms of contact, as long as this is within the contract. I would suggest that you check with your insurer to see what they require because I KNOW of a company that had an insurance claim for a Fork Lift Truck accident refused because there was no PAT regime in place. A PAT regime in accordance with the IET CoP was a condition of their insurance, thus they were in breach of their terms of insurance, thus un-insured. Now that brings in a whole new raft of potential issues does it not? I would hope that we all know that the requirement comes from HASAWA74, EAWR89 (primarily), PUWER98, MHSWR etc. Now take one of these, EAWR, look to reg 4, then 5, then 6, then 7, then 8, then 9, then 10, then 11. I would also suggest checking out reg 16. I’m sure that these can be checked out by those interested. In INDG107 & 236, HSE do state that PAT is not required. However, they do state that equipment must be safe. They do suggest that user checks are acceptable for some equipment. However, EAWR89 requires that those persons are competent to do these checks. So, yes rely on user checks, but, you need to ensure that the users are competent, and be able to prove this. These user checks would need to be documented, recorded & reviewed by a competent person, to ensure that you were compliant. Next, HSE suggest the following: Who should I talk to about electrical safety? In the first instance, a competent electrical contractor should be able to give advice on electrical safety and should also be able to direct you to a suitable electrical engineer for advice about specialist areas. Therefore I suggest that you would not need to look any further! ;)
gerrysharpe  
#22 Posted : 11 June 2016 09:27:43(UTC)
Rank: Super forum user
gerrysharpe

Stonecold wrote:
gerrysharpe wrote:
Also the Electricity at Work Regulations do not specifically mention portable appliance testing and inspection; they simply require electrical systems to be 'maintained' in a condition so as not to cause danger. However, the only way we know if a system needs to be maintained is if it is inspected and tested, and so the need for such inspection and testing of a system is implicit in the requirement for it to be maintained. Anyone who inspects and tests and electrical system is, in law, a duty holder and must be competent to undertake such work.
You can quote all the regs you like, but the actual FACT is that PAT testing is NOT a legal requirement. Even the HSE clearly say so.
I understand that its not a Legal requirement. Period. But the only way we know if a system needs to be maintained is if it is inspected and tested, and so the need for such inspection and testing of a system is implicit in the requirement for it to be maintained. So whats the best way to ensure your electrical equipment is Checked for safety, By a competent person and recorded ??
Zyggy  
#23 Posted : 12 June 2016 20:21:15(UTC)
Rank: Super forum user
Zyggy

Gerry; succinctly put! For those who disagree, please remember that we represent various types of organisations & in my world I have several clients who would not be able to find employees wiling or indeed capable of carrying out inspections. For their peace of mind they are happy to pay somebody 64p an item to come in & carry out the checks for them & before anybody comments, yes I agree with the MOT analogy, but surely that is the same for any maintenance regime?
paul.skyrme  
#24 Posted : 12 June 2016 21:22:13(UTC)
Rank: Super forum user
paul.skyrme

Zyggy wrote:
Gerry; succinctly put! For those who disagree, please remember that we represent various types of organisations & in my world I have several clients who would not be able to find employees wiling or indeed capable of carrying out inspections. For their peace of mind they are happy to pay somebody 64p an item to come in & carry out the checks for them & before anybody comments, yes I agree with the MOT analogy, but surely that is the same for any maintenance regime?
For those of you who are paying 64p, or £1.00 or such stupidly low prices for full blown Combined Inspection & Test for PAT, then you are merely fooling yourselves that you are getting the job done correctly, you are not, it is not physically possible to do a full combined I&T in accordance with the published guidance for £1.00 per item, not even £1.50 per item, the real cost should be nearer £3.50 per item for it to be done correctly in accordance with published guidance from the HSE & the IET. Now two test cases spring to mind, Dancearama Footwear & Octel. Remember, one is not discharging ones statute law duty by bringing in a contractor to do PAT, and it could be looked on as worse than not doing PAT if you chose an incompetent contractor, which, if you are paying that much, you are getting, either that or you are not getting the job done correctly. Look at what is required, now even an employee on minimum wage would need to be charged out by their employer at > £10 per hour, probably realistically £15/hr. That’s £15 appliances per hour, every hour that they work, and that must include the reporting, the office staff, the uniform, vehicle, training, qualifications, test equipment, calibration, etc. etc. now they will not be 100% productive for every working hour realistically they will be 50-70% productive as they are a peripatetic worker. So, let us take the lower bound for now. 50% productive, now all of a sudden they have to do 30 appliances per hour, that’s 2 minutes per appliance, that includes, getting to the appliance / finding it, disconnecting it, doing the visual inspection, capturing the appliance data, and recording it, connecting it to the tester, running the test, disconnecting it from the tester, reconnecting it and running a functional test after re-connection, then on to the next one, and repeat. I heard first hand a tale where the PAT was undertaken at an educational establishment. What the contractor did not realise was what they taught there. They sent a guy around simply writing stickers out and sticking them on. The H&S dept, didn’t care, they had done their bit, the management didn’t care they had done their bit. The department were well annoyed. Why? They taught “electrical”, including PAT. The institution management & H&S dept, did not care, they had their stickers, and they would not listen to those who were competent to do the work, and to teach it (they were all competent to do the work as it was a vocational college). So, now was that institution acting totally legally? IMHO, no, they engaged an incompetent contractor, which is again IMHO worse than not doing the I&T at all?
John M  
#25 Posted : 13 June 2016 04:33:38(UTC)
Rank: Super forum user
John M

We should all take note of the contents of the above posting - spot on Paul. Jon
DHM  
#26 Posted : 13 June 2016 17:30:21(UTC)
Rank: Forum user
DHM

Away from the PAT issue. If it belongs to a contracted cleaning company then they should test it!
stillp  
#27 Posted : 13 June 2016 21:21:21(UTC)
Rank: Forum user
stillp

Paul is absolutely correct. The site services manager at the office where I used to work hired the cheapest PAT company she could find. From memory, about 60 p per item, back around the year 2003. Along came a retired couple, who both looked about 70 (not that there's anything wrong with that), and their PAT tester. He plugged items in and rotated the selector for the different tests, while she wrote out stickers. Pass if the green light came on, fail if the red light came on. I asked why one item had failed: "The red light came on" was the answer. "Why" I asked: "Cos that's what it does when something fails". I kept watching, and when he passed an item with a damaged cable and broken plug, "Cos if the green light comes on, it's OK" I had them removed from the premises. The punch line - this was the marketing office of a major multinational manufacturer of electrical equipment! That site services manager didn't last very long, and we trained one of the maintenance guys to do our own inspection & test.
douglas.dick  
#28 Posted : 14 June 2016 09:12:00(UTC)
Rank: Forum user
douglas.dick

To be fair the price you pay does not mean that you get the job done properly. I know of two very reputable Electrician companies that use this as a 'lost leader' to get other work within a company. You have to ensure the job is being done regardless of paying 10p per item or £10. To answer the OP's question, you probably are best just to have the appliance tested whilst you are having your own done.
paul.skyrme  
#29 Posted : 14 June 2016 20:25:29(UTC)
Rank: Super forum user
paul.skyrme

DHM wrote:
Away from the PAT issue. If it belongs to a contracted cleaning company then they should test it!
As the opening paragraph of post #21
stillp  
#30 Posted : 14 June 2016 21:02:10(UTC)
Rank: Forum user
stillp

douglas.dick wrote:
To answer the OP's question, you probably are best just to have the appliance tested whilst you are having your own done.
What if it fails though? Even worse, what if the PAT damages the appliance - that can happen, especially if the person doing the test is not familiar with the equipment.
paul.skyrme  
#31 Posted : 14 June 2016 21:38:25(UTC)
Rank: Super forum user
paul.skyrme

What if it fails... I had an emergency call out one afternoon to a pharmaceutical manufacturer. They had been "tasked" with PAT by their insurance company. They selected their normal electrical contractor. They hammered them on price, to the extent it was not really worth doing. I know both companies well, the end user & the contractor. So, to make ends meet, the contractor sent in a newly qualified guy (C&G PAT, and partially qualified as an electrician, BS7671 wise). The "tester" had condemned one half of one of their critical production lines. Remember this is "light" industry/manufacturing. A lot of the equipment is 1ph < 3kW, so on BS1363 plug tops. This is convenient, and allowed. As they do washdown, deep cleans etc. they have the lines on plugs so that they can move them around to clean thoroughly and easily re-direct production, or combine/split lines to meet their customer demand. They have good control of their washdowns, so that is not an issue. The guy was PAT’ing the equipment and failing it because the “normal” PAT “machine” is not designed to test & check such things as VSD’s with up front LCR filters to control EMC, they are designed to be “leaky”. The BS1363 plugs were “just” in on their tolerance for leakage, but it was too much for PAT. They had various other complex systems that were not ever, designed to be subject to PAT as would be “normal”. Also, the guy was only testing up to the first NVR in the machine, so basically the supply cord up to the first contactor, and the start button circuit. Now this guy was above the level of your average PAT person. He had undertaken and passed the C&G courses. It is just that the training does not cover everything, and not everything can, nor should be subject to PAT as per the IET CoP. Some equipment is MUCH more complex, just because it has a plug, does NOT mean it HAS to be subject to PAT as per the HSE/IET CoP. I have supplied some equipment to schools, with an “appliance inlet” think caravan power inlet. I remove them and replace them with a suitable isolator. Yes our company is covered for this even if the equipment is CE marked. Yes there is a lot that goes with it, and the OEM is aware and has “rubber stamped” it. Why, because otherwise it has a plug & socket, thus people try to PAT it, and it is not designed to be PAT’ed. PAT is NOT the be all and end all. It is suitable for a LOT of electrical appliances portable and transportable, to apply it to complex fixed appliances is beyond the scope of a “normal” PAT person, because it is not taught on the C&G course, and is not covered by the IET CoP. Thus, it requires a much higher and different level of competency.
douglas.dick  
#32 Posted : 15 June 2016 10:02:54(UTC)
Rank: Forum user
douglas.dick

stillp wrote:
douglas.dick wrote:
To answer the OP's question, you probably are best just to have the appliance tested whilst you are having your own done.
What if it fails though? Even worse, what if the PAT damages the appliance - that can happen, especially if the person doing the test is not familiar with the equipment.
If it fails you simply remove the item from use, mark it accordingly and advise the contractor. Advising the client that a PAT test would be carried would be the right thing to do, you may even discover that it has been done by them and therefore not required.