rickstefanetti84  
#1 Posted : 25 November 2016 09:00:10(UTC)
Rank: Forum user
rickstefanetti84

Morning!

I was having a dicussion yesterday wtih a press operator about locking out machines when unplanned maintenance or repair is required. In my opinion, I feel that if you are entering an area where you have to remove a guard to remove product that is wrapped around rollers etc, you need to use lock out to be sure the machine wont unexpctadly start.

He said that he felt opening a guarded area (interlocked) and then pressing an E-stop button also, meant that you wouldnt need to use lock out as you had two seperate systems (open guard and e-stop pressed in) that would prevent the machine starting up.

I'm no press or lock out expert, so thought id share the debate on here and get the opinions of those with far more knowledge and expertise in lock out and printing presses.

thansk in advance!

Spencer Owen  
#2 Posted : 25 November 2016 10:03:16(UTC)
Rank: Forum user
Spencer Owen

Morning Rick,

I've not worked with large plant much but I would agree with you in that the system should be locked out.
What negatives come from locking the machine out? I can think of a few negatives that could come from not locking it out and that not being sufficient...

Roundtuit  
#3 Posted : 25 November 2016 10:30:50(UTC)
Rank: Super forum user
Roundtuit

And the production supervisor walks past, sees a stopped machine closes the interlock releases the E-Stop presses start - it has happened with fatal consequence

Also are the interlock and E-stop actually two separate systems? I have seen set-ups over the years where they have been wired in to the same circuit especially where one or both devices have been retro-fitted to the machine.

MEden380  
#5 Posted : 25 November 2016 12:30:38(UTC)
Rank: Super forum user
MEden380

If you need to work on the press you need to carry a lock out procedure and not rely on an interlock and an emergency stop button.

I have seen a machime with interlocks carry on running after a guard was lifted to demonstrate how it would stop - it didn't.

I have also seen emegency stop buttons not work as they were never correctly wired up.

What about any residual energy in the system such as hydraulic preasure, E stop buttons don't always disipate this.

Kate  
#6 Posted : 25 November 2016 13:32:07(UTC)
Rank: Super forum user
Kate

Lock it out!

It's no good having two separate protections each of which can easily fail.

rickstefanetti84  
#7 Posted : 25 November 2016 14:21:29(UTC)
Rank: Forum user
rickstefanetti84

Thanks guys. I appreictae your feedback and agree, lock out is the safest possible solution, so why wouldnt you use it.

thanks again,

Rick

piobaire  
#8 Posted : 25 November 2016 14:33:33(UTC)
Rank: Forum user
piobaire

Lock it out.  Only way to ensure the machine is not started up inadvertently is by isolating it.  Interlocks and emergency stops are not robust means of isolation and are not designed to be used as such.  Having worked with machinery in the past, I would not go into the guts of a machine unless I knew it was isolated. As I'm not familiar with your particular machine, the other thing to bear in mind is whether locking it out will prevent all parts of the machine moving as some presses utilise gravity or stored energy as a motive force for operation.  Lock it out.

Hope this is useful.

Ian Bell2  
#9 Posted : 25 November 2016 15:09:58(UTC)
Rank: Super forum user
Ian Bell2

Reg 19 of PUWER is quite clear. What is there to discuss?

Bob Hansler  
#10 Posted : 25 November 2016 15:17:52(UTC)
Rank: Forum user
Bob Hansler

As above.  Lock out.

chris42  
#11 Posted : 25 November 2016 15:29:25(UTC)
Rank: Super forum user
chris42

A rare event, everyone in agreement.

rileym  
#12 Posted : 25 November 2016 15:47:52(UTC)
Rank: Forum user
rileym

Definitely lock out however I would add to ensure that the correct circuit has been locked out.  I remember reading about a case where a worker isolated one of three augers and correctly locked it out.  However during maintenance it started and caused serious injury.  Apparently the isolators were wrongly marked or wrongly wired and it had never been noticed before.  Also as has been said before ensure any stored energy is dissipated. 

djupnorth  
#13 Posted : 26 November 2016 10:01:17(UTC)
Rank: Forum user
djupnorth

Roundtuit,

That is exactly what happened in a client's factors several years ago and the operator was killed.

Regards.

DJ

paul.skyrme  
#14 Posted : 05 December 2016 21:31:47(UTC)
Rank: Super forum user
paul.skyrme

Originally Posted by: rickstefanetti84 Go to Quoted Post
Morning!
I was having a dicussion yesterday wtih a press operator about locking out machines when unplanned maintenance or repair is required. Inmy opinion, I feel that if you are entering an area where you have to remove a guard toremove product that is wrapped around rollers etc, you need to use lock out to be sure the machine wont unexpctadly start.
He said that he felt opening a guarded area (interlocked) and then pressingan E-stop button also, meant that you wouldnt need to use lock out as you had two seperate systems (open guard and e-stop pressed in) that would prevent the machine starting up.
I'm no press or lock out expert, so thought id share the debate on here and get the opinions of those with far more knowledge and expertise in lock out and printing presses.

thansk in advance!



IF the machine is correctly CE marked, thus the safety systems are correctly implemented, which as the end user, you have a statute law duty to confirm, then, no, there is not necessay a need for LOTO.

I know a site, large site, where the global H&S manager has no idea about mahinery safety, as is patently obvious from the stupid wording of his email.

The site has spent over £100,000 verifying and proving their functional safety in accordane with EN 62016, & EN 13849, it is proven, working and SAFE, where operators can enter areas and get locked in, there are trappd key systems they can use etc.

The manager, who is totally incompetent to comment, has stated that the mahines must be isoltd as in LOTO.

This turns a 5 minite job that can be safely done, into 4-7 hours of work, and has put the viability of the whole plant in jeopardy it seems.

So, there is NOT ALWAYS the need to LOTO, no.

IF the machinery is correctly implemented in the first place, then it may well not need to be LOTO'd for work.
JohnW  
#15 Posted : 07 December 2016 17:09:16(UTC)
Rank: Super forum user
JohnW

But in Rick's case it is one press needing maintenance, surely LOTO is the safe system of work so no-one can start it up?
paul.skyrme  
#16 Posted : 07 December 2016 17:17:51(UTC)
Rank: Super forum user
paul.skyrme

What type of press though.

I used to work for a company that did machinery control systems, one of the biggest global OEM's of the stuff.

One of our service guys was on site, working on a press.

We had just been taken over by another global corporate and they had forced corporate computing policy onto us.

Mandatory screen savers after x minutes, with a password to de-activate.

Nick was running the whole press in test mode from his laptop.

There was no-one at risk.

An issue happened and he needed to click a button on the screen with the mouse to instigate a controlled stop.

He couldn't do this so he had to hit the e-stop, that caused a loss of several £100k's of cost to the printing company, the web tore, and the whole press had to be re-webbed which took 4 hours, so too late to print the morning papers, they had to be transferred to another press works and there was riots.

So, don't take it that ALL presses are simple machines that can be easily LOTO's/

A small say perhaps 10 or 20 tonne blanking press which has a single die for forming steel, with a single point of isloation, then fine.

A large 6 or 8 tower say newspaper printing press such as doing things like the Daily Mail, the Times, etc. this has multiple points of isolation and for it to be effectively maintained safely and economically requires zoning and functional safety.

Not every engineering problem is as clear cut as LOTO.

Simple machines, yes, complex machines one must rely on the functional safety that has been designed in, and obviously verified as working and correctly maintained there after to comply with statute law.

Don't forget all sources of energy though...

JohnW  
#17 Posted : 07 December 2016 18:58:33(UTC)
Rank: Super forum user
JohnW

Paul, in his post Rick made no mention of any significant downtime issues so in the spirit of PUWER and risk minimisarion I believe a LOTO should be enforced in his case. Not doing so might suggest to employees that shortcuts can be taken and this could lead to other LOTO procedures being ignored, with serious consequences.

John
mistyhall  
#18 Posted : 07 December 2016 19:29:24(UTC)
Rank: Forum user
mistyhall

As with many aspects of Health and Safety, competency of the person assessing comes into play!to determine what is needed! Ive worked with Directors that believe once it has a CE mark we are good to go! Engineers that order without thinking ( well CE mark is saying all ok!!!) Dont want to spend on getting a PUWER assessment done then machines stand idle! Get a PUWER done and not fit for purpose now machine stands idle waiting to have alterations done!! I have also worked with over zealous Health and Safety Managers who want to Lock Off everything in sight and nearly caused total meltdown of the factory due to their lack of understanding!

So if its complex and you know your way around ISO 13849 and IEC 62061 (good luck) can establish categories and performance level then thats great however i prefer to work in a team with the electrican and engineer to do the assessment.

Dont forget however PUWER must account for misuse of machinery

JohnW  
#19 Posted : 07 December 2016 21:06:52(UTC)
Rank: Super forum user
JohnW

Yes, what Rick's operator was suggesting is mis-use of an e-stop, so that's not right.

Anyway, Rick just said he wants the safest option, and that will be LOTO.

John
paul.skyrme  
#20 Posted : 07 December 2016 21:26:33(UTC)
Rank: Super forum user
paul.skyrme

Originally Posted by: mistyhall Go to Quoted Post

As with many aspects of Health and Safety, competency of the person assessing comes into play!to determine what is needed! Ive worked with Directors that believe once it has a CE mark we are good to go! Engineers that order without thinking ( well CE mark is saying all ok!!!) Dont want to spend on getting a PUWER assessment done then machines stand idle! Get a PUWER done and not fit for purpose now machine stands idle waiting to have alterations done!! I have also worked with over zealous Health and Safety Managers who want to Lock Off everything in sight and nearly caused total meltdown of the factory due to their lack of understanding!

So if its complex and you know your way around ISO 13849 and IEC 62061 (good luck) can establish categories and performance level then thats great however i prefer to work in a team with the electrican and engineer to do the assessment.

Dont forget however PUWER must account for misuse of machinery


I do, it is  a big part of my business, and growing, that along with PUWER & CE assessments.

I don't know many electricians that even understand 60204 let alone 13849 unfortunately though.

I can't get to the OP now on this screen, but IIRC there is the mention of a web, now re-webbing a multi tower printing press is not a 5 minute job.

I think that this is another scenario where the rest of the posters can only comment based on their experience, and it is only the OP that has the full picture.

There are issues with the "MD" and the acceptance of machinery such as requiring the end user to confirm CE compliance, which if you read the wording is really required, but, most end users don't have that capability, and even if they did anc could prove that the machine was non-compliant the answer from the OEM would be something like, "well your wrong, we've sold hundreds of these and no one else has aver said that that is wrong, so you must be wrong".

Heard it before, and will probably hear it again, even when you quote the law and the standards, they just stonewall you and demand money to change things to be compliant with legislation.

The end user is then the one at risk from prosecution for using unsafe machinery, the OEM gets away with it.

JohnW  
#21 Posted : 08 December 2016 11:07:48(UTC)
Rank: Super forum user
JohnW

Paul, the original poster did not mention his MD or CE marking.

I think for Rick we should be sticking to his questions. He wants to know the safest option for his circumstances, and the consensus of opinion was LOTO was the safest option, so the machine cannot be switched on during repairs.

Maybe Rick can come back with more information on the press.

John

Edited by user 08 December 2016 11:08:53(UTC)  | Reason: spelling

Mr.Flibble2.0  
#22 Posted : 08 December 2016 12:01:58(UTC)
Rank: Forum user
Mr.Flibble2.0

I would ask the operator why they wouldn’t want to use a lock off system? Why so adverse to getting a padlock and attaching it to an isolator? It will probably be time - have to walk to get one, sign one out etc or and hopefully this does not happen, but it could be a case they can open an guard, circumvent the isolator and leave the machine running to clear a jam where by using a padlock on the power isolator would prevent this.

Ask the question and get them to tell you why they couldn’t simply lock off the isolator.

rickstefanetti84  
#23 Posted : 08 December 2016 15:25:25(UTC)
Rank: Forum user
rickstefanetti84

Hi guys,

Just catching up on the posts and just to clarify, tHe press is a Mark Andy P5.

I hav ebeen on discussion with Mark Andy this week ref the tasks that require LOTO and those that can be safely perofrmed without LOTO. Followingthe discussion, we are probably going to go with the follwing:

Re web the press: no LOTO, as the press is required to be inched, so on operator re webs whislt another designated "safety operator" stands by the control panel so they an inch the press and immediately hit the E-stop if there is a need to.

Blockages: LOTO required, as operators ar placing their hands in areas where guards will be removed to get access, so the safest option is LOTO and not just depressing an E-stop.

all other tasks such as repairs and breakdowns will be performed by our site engineer and not a press operator.

see the below link for a pic...

https://www.google.co.uk/search?q=MARK+ANDY+P5&biw=2133&bih=1088&tbm=isch&imgil=b-zTN6VQtBqskM%253A%253BeWfEmYmdPIUJ5M%253Bhttp%25253A%25252F%25252Fspectragraphics.com%25252Fspectragraphics-inc-adds-second-mark-andy-p5%25252F&source=iu&pf=m&fir=b-zTN6VQtBqskM%253A%252CeWfEmYmdPIUJ5M%252C_&usg=__h3b0IkaZOAkqZt9An2kZMlkYY-w%3D&dpr=0.9&ved=0ahUKEwjX1Pea8uTQAhVpIMAKHUr6A3IQyjcIMQ&ei=k3lJWJe_KunAgAbK9I-QBw#imgrc=qlwBYsyJmVH_5M%3A

JohnW  
#24 Posted : 08 December 2016 17:20:01(UTC)
Rank: Super forum user
JohnW

Rick, good that you got some expert advice, the procedures re web and blockages are sensible. For most repair jobs I expect LOTO can be implemented, but there may be some jobs that need other consideration (that press is bigger than anything I've seen).
paul.skyrme  
#25 Posted : 08 December 2016 18:55:16(UTC)
Rank: Super forum user
paul.skyrme

Now I had in my head something like this!

https://www.google.co.uk...&iact=mrc&uact=8

This is a Goss newspaper printing press similar to those I used to work with.

Limitations of the media of discussion I guess!
rickstefanetti84  
#26 Posted : 08 December 2016 21:01:46(UTC)
Rank: Forum user
rickstefanetti84

Paul, ours are not quite as big as that, thats a pretty big press!

JohnW, thansk for your comments too. The manufacturers took some time in replying, hence me puttig it out on this forum also. The press is pretty long and we have also added various other pieces of equipmetn on to it at each end.