Rank: Forum user
|
Hello My Learned Friends, I have a couple of questions there may be easy answers too but i will ask anyway. In the field I have worked in the past FM times seem to have changed as to what is classed as Construction Work hence coming under the CDM banner although non notifiable.
For instance a electrician or lift engineer completed a simple service maybe an hour I am surmising is not classed as construction work and is covered under assessments and safe systems of work. However lets say these trades take a little longer and there is quoted works ie Change of panel for Electrician say 4 to 8 hours work and Lift engineer changing equipment including motor for 1 to 2 days. From what i was led to believe these are now classed as "construction Work" hence the CDM apply.
1. Is the above correct ?
2. If it is or isnt correct at what stage does something become "construction" work ? 3. If something is classed as "construction" work at what stage is a CPP Construction Phase Plan required ie is there a soecific point where it does require a CPP ? Thanks in advance Alan
|
|
|
|
Rank: Super forum user
|
|
 1 user thanked Alfasev for this useful post.
|
|
|
Rank: Forum user
|
I'm no expert in the construction field but what I do know is that construction work is quite clearly defined in the CDM Regulations and the duration of works has nothing to do with wither or not something is classed as construction works. The definition of construction work can be found here on pages 10/11 and I'd say the type of work you are describing would fall under Regulations 2(e) "the installation, commissioning, maintenance, .....".
In relation to the CPP, my understanding is that it is required for all construction projects and it's the responsibility of the Principal Contractor (or contractor where there is only one) to do this BEFORE construction works start. The level of detail within the CPP should be commensurate with the level of risk of the project so a CPP for the types of work you describe will be very different to the CPP for building a housing estate as example. I've never used it personally but for simply contruction projects I've often seen referrals to CITB's CDM Wizard App where it can take as little as five minutes to create a basic CPP.
I'm sure more informed members will comment in due course.
|
 1 user thanked fscott for this useful post.
|
|
|
Rank: Forum user
|
Thanks for that and yes reading that it is pretty much as i remember and thought it was but what about with regard the secodn part of the question at what point is a CPP Construction Phase Plan required ?
|
|
|
|
Rank: Super forum user
|
CPP must be place before you start work.
|
|
|
|
Rank: Super forum user
|
fscott, the works must firstly be considered “construction work” before you consider regulation 2 (a)-(e). If you consider (e) in isolation it does not make sense as all sort of thing fall into this category. For example it would make a gas engineer servicing a boiler, the replacement a single electrical socket and institutional of a server construction work
|
|
|
|
Rank: Forum user
|
Originally Posted by: Alfasev  fscott, the works must firstly be considered “construction work” before you consider regulation 2 (a)-(e). If you consider (e) in isolation it does not make sense as all sort of thing fall into this category. For example it would make a gas engineer servicing a boiler, the replacement a single electrical socket and institutional of a server construction work
Alfasev I had never seen the document you posted the link to and it certainly helps make defining what is and what isn't construction work a bit easier (well for me at least). Understand what you are saying. Every day is a learning day especially when dealing with law.
|
|
|
|
Rank: Super forum user
|
And therein we see the problem of the current CDM regs and the wide and generic definition of 'construction work'.
The original post describes routine maintenance on existing installations and equipment in a building now falling under CDM.
There is unlikely to be any design.
So a lift engineer turns up in his van, completes the lift service and gets off on his way.
What benefit does a CPP give?
|
|
|
|
Rank: Super forum user
|
This could be cleared up if the HSE issued an ACOP. I have been on numerous seminars where they HSE say it verbally but will not put anything on paper. If you in construction day in day out that is fine, most of the time! but for FM, infrequent clients and associated businesses it not.
|
|
|
|
Rank: Super forum user
|
I believe the confusion arises due to incorrect implementation of the parent Directive.
Directive 92/57/EEC is concerned with risks arising from construction work on temporary or mobile construction sites.
CDM makes no such distinction and applies a definition of construction work irrespective of setting.
3 goes now at attempting to implement a Directive, and the regulators still haven't got it right.
|
|
|
|
Rank: Forum user
|
My advice would be to define a list of routine maintenance activities that are done on a "business as usual" (BAU) basis. I would then define BAU works as routine and not specifically requiring CDM.
Any works that fall outside of these BAU activities I would define as construction and would expect to see a CPP etc.
As others have said ignore the times of the works and focus on what works you do that keeps the building running vs what is improvements/refurbishment/repair type activites.
|
|
|
|
Rank: Forum user
|
|
|
|
|
Rank: Super forum user
|
Alan
First, the time someone spends doing work or the size of a projet is irrelevant to CDM. In Regulation 2 there is a detailed list of what is defined as 'construction work' including repairs, maintenance... all encompassing if go by the letter of the law.
Something 'does not become' construction work, it is, or is not, from the start.
A CPP is required before the construction phase begins.
|
|
|
|
Rank:: Super forum user
|
It's been dealt with before but even if construction work remit is wider than would be liked, stop freaking out about CPPs. CPPs should be proportionate to the risks and hazards involved during the work and should be focused on protecting the workers. Doesn't effective documented RA/MS cover 99% of the requirements of a CPP for the sort of FM work adjudged to be construction work being discussed here? Don't start creating additional documents and calling them CPPs when it has zero additional benefit. I don't work in construction, nor am I a construction inspector, but I can't believe that the HSE would desire such an approach.
|
|
|
|
Rank: Forum user
|
Originally Posted by: Xavier123  It's been dealt with before but even if construction work remit is wider than would be liked, stop freaking out about CPPs. CPPs should be proportionate to the risks and hazards involved during the work and should be focused on protecting the workers. Doesn't effective documented RA/MS cover 99% of the requirements of a CPP for the sort of FM work adjudged to be construction work being discussed here? Don't start creating additional documents and calling them CPPs when it has zero additional benefit. I don't work in construction, nor am I a construction inspector, but I can't believe that the HSE would desire such an approach.
While I agree with your main point, it is not actually what the law asks for. CDM is quite explicit regarding what is construction and the fact a CPP is required. The debate comes because it is not practical for FM providers to implement fully.
On your last point, my dealings so far with HSE have led me to conclude that actually it would depend on whether they were trying to make something stick or not.
|
|
|
|
Rank: Super forum user
|
There is no doubt that CDM 2015 is a nightmare for those involved with reactive repairs and maintenance. What is all the more frustrating is there are many organisations in mainstream construction who choose to ignore CDM and get away with it, including clients, while the rest of use have to deal with the consequences of a poorly drafted legislation.
To make matters worse, each organisation interprets CDM diffetently so when you throw into the mix a CPP, H&S File, PD role, Appointments, etc it becomes almost unmanageable. Only this week I reviewed a draft CPP template from a new term contractor where we as the client were down as the PD. Don't know if it was an error or they were trying a fast one, but I put them right. Meanwhile, the HSE have a lot to answer for in my opinion.
|
|
|
|
Rank: Super forum user
|
The whole gravy train of trying to pretend that things fall outside the definition of construction work is rolling again. It started in 94 and the arguments roll on. If you are excluding people from the work area in some way however minor then a temporary site is created.
Secondly any CPP or equivalent however you label it must also cover things such as First Aid, Contact names, Welfare arrangements, hours of work etc. So any decent management plan is going to define these for any particular location in addition to the various task risk assessments.
|
|
|
|
Rank: Super forum user
|
Quite agree with Ray. CDM remains a bag of worms.
Wide and generic definitions help no body.
HSE have still not adequately addressed the difference between scheduled routine maintenance and true construction.
The design side is also a nightmare when the definition of design is considered alongside routine maintenance tasks.
Where does design start (as defined) and specifying equipment replacement during maintenance work?
|
|
|
|
Rank: Super forum user
|
Originally Posted by: boblewis  The whole gravy train of trying to pretend that things fall outside the definition of construction work is rolling again. It started in 94 and the arguments roll on. If you are excluding people from the work area in some way however minor then a temporary site is created.
Secondly any CPP or equivalent however you label it must also cover things such as First Aid, Contact names, Welfare arrangements, hours of work etc. So any decent management plan is going to define these for any particular location in addition to the various task risk assessments.
Bob, always good to get your erudite input. However I cannot fully agree with your comments. Prior to the 2015 iteration CDM was generally consistent and proportionate to the work. Major projects would have been Notifiable and the extra duties like the provision of a CPP, H&S file, CDM-C (now PD) would have kicked in. Indeed, for major projects CDM 2015 is not really a problem.
If you take for example, a simple roof repair job using a sub-contractor for the erection of a standard scaffold, all the duties in CDM 2015 now apply, including the Appointment of a Principal Designer and H&S File - it's a nonsense!
I do agree a decent set of RAMS would cover most of the measures required for a CPP and therefore this aspect of CDM 2015 is not too onerous if one creates a CPP in this fashion. Just the added bureaucracy especially for client who has to ensure the PC has a CPP in place.
|
|
|
|
Rank: Super forum user
|
Ditto from me Bob. I can't subscribe to that view. The TMCSD was created with the recognition that workers on construction sites were exposed to higher risk (the Directive preambles refer).
To apply such a global interpretation as yours (in workplaces already covered by HASAWA or the Parent Directive) is in my view wholly disproprortionate and overly bureaucratic.
In this respect, I find the HSE's attempts to further clarify their definition of "construction work" (IOSH link above) particularly unhelpful.
|
|
|
|
Rank: Super forum user
|
Worth adding in the context of this and concurrent "chair pod" threads that HSE, having tangled themselves up with their own definitions, also expect CDM to be applied to the construction of a TV set within a studio and to the stage set of a travelling theatre company.
(e.g. http://www.hse.gov.uk/entertainment/cdm-2015/production-set-studio.htm)
Aye, right. What a mess.
|
|
|
|
Rank:: Super forum user
|
Originally Posted by: fhunter  Originally Posted by: Xavier123  It's been dealt with before but even if construction work remit is wider than would be liked, stop freaking out about CPPs. CPPs should be proportionate to the risks and hazards involved during the work and should be focused on protecting the workers. Doesn't effective documented RA/MS cover 99% of the requirements of a CPP for the sort of FM work adjudged to be construction work being discussed here? Don't start creating additional documents and calling them CPPs when it has zero additional benefit. I don't work in construction, nor am I a construction inspector, but I can't believe that the HSE would desire such an approach.
While I agree with your main point, it is not actually what the law asks for. CDM is quite explicit regarding what is construction and the fact a CPP is required. The debate comes because it is not practical for FM providers to implement fully.
On your last point, my dealings so far with HSE have led me to conclude that actually it would depend on whether they were trying to make something stick or not.
I must have missed something in the legislation - CDM Reg 12 says this: The construction phase plan must set out the health and safety arrangements and site rules taking account, where necessary, of the industrial activities taking place on the construction site and, where applicable, must include specific measures concerning work which falls within one or more of the categories set out in Schedule 3.
The HSE guidance says very little more.
So I don't doubt you need one. I'm suggesting you already have one. Health and safety arrangements? Site rules? Site specific arrangements accounting for the nature of the risks to be encountered (with some particular named issues unlikely to arise in the nature of the FM work being discussed)? If a general FM h&s management system and task RAMS doesn't deal with these things anyway then they're doing it wrong. Just stick something in the policy describing how the various aspects are met re: welfare, first aid, site contacts etc. meets the requirements of being relevant parts of a CPP for the purposes of the aforementioned 'construction work'. (again inserted disclaimer here that I'm not in the construction game). As to convincing an HSE inspector. Ah. A different ball game. I'm a regulator and always happy to accept a good, well thought out answer. I'm more likely to be unhappy that someone is producing paperwork for the sake of paperwork. I recognise that your experience may differ!
|
|
|
|
Rank: Super forum user
|
Xavier
Everything is fine and dandy until a serious incident occurs, then watch them scatter when the regulators start their investiagtion and worse, lawyers pull everything apart. Do not delude yourselves.
|
|
|
|
Rank: Forum user
|
Originally Posted by: Xavier123  I must have missed something in the legislation - CDM Reg 12 says this: The construction phase plan must set out the health and safety arrangements and site rules taking account, where necessary, of the industrial activities taking place on the construction site and, where applicable, must include specific measures concerning work which falls within one or more of the categories set out in Schedule 3.
The HSE guidance says very little more.
So I don't doubt you need one. I'm suggesting you already have one. Health and safety arrangements? Site rules? Site specific arrangements accounting for the nature of the risks to be encountered (with some particular named issues unlikely to arise in the nature of the FM work being discussed)? If a general FM h&s management system and task RAMS doesn't deal with these things anyway then they're doing it wrong. Just stick something in the policy describing how the various aspects are met re: welfare, first aid, site contacts etc. meets the requirements of being relevant parts of a CPP for the purposes of the aforementioned 'construction work'. (again inserted disclaimer here that I'm not in the construction game). As to convincing an HSE inspector. Ah. A different ball game. I'm a regulator and always happy to accept a good, well thought out answer. I'm more likely to be unhappy that someone is producing paperwork for the sake of paperwork. I recognise that your experience may differ!
Reg 12 for PCs and Reg 15 for a single contractor. I don't disagree that what you describe is a balanced and fair approach and indeed I personally struggle to the benefit a CPP adds to a job that is already well controlled has the correct paperwork.
As you say a balanced and fair approach to regulating the industry is how it should be, but as ray says, when things go wrong on what is deemed to be a "construction" project a lack of CPP will see you written up for lak of management. Fundamentally it's where the CDM regs fail to properly account for how the variance of how different work activities are managed and how the regs can possibly be implemented on the ground. The way I see it that the CDM regs are trying to apply a set of rules to someone refrubishing a kitchen as well as building crossrail in less than 20 pages, not possible in my opinion
|
|
|
|
You cannot post new topics in this forum.
You cannot reply to topics in this forum.
You cannot delete your posts in this forum.
You cannot edit your posts in this forum.
You cannot create polls in this forum.
You cannot vote in polls in this forum.