#41 Posted : 06 June 2017 16:04:42(UTC)
Rank: Forum user
DanIsaacs

Originally Posted by: johnmurray Go to Quoted Post
I fail to see what you are getting at

What I'm getting at is quite simple. If the air concentration in buildings even with damaged asbestos in them is lower than 0.0003f/ml and no-one has done any tests to show what the long term exposure is from domestic scale interation with asbestos then there remains no evidence whatsoever to support the presumption that removing damaged or friable asbestos from buildings is safer than leaving it where it is. I think that would be a pretty important thing to find out for the safety of the general public considering asbestos abatement is going to increasingly become the main source of asbestos release for them.

Given that asbestos manufacturing has long been banned, the only people nowadays who would theoretically be in a position to make money from misinformation are asbestos abatement firms (whose interests are best served by promotong removal) and lawyers (whose interests might be best served either way depending on who they represent). Not to mention the deplorable way in which air fibre measurements which could be being used to help inform researchers are treated as "commercially sensitive data" by some of these firms (yes, I have personal experience of this). To my mind that gives a fairly equal proportion of potential for industries "to get rich over the bodies of its workers.... " or the public, on both sides of the debate, not just those trying to play down the risk, but those trying to inflate them. That's why I believe the only way forward is proper evidence. The whole reason why asbestos got banned in the first place (eventually) is because the asbestos firms could no longer deny the sheer weight of evidence. Same with smoking in public places, lead in petrol, etc.. Evidence is everything with these issues and I'm appalled at the complete lack of it for modern exposures and abatement practices.

descarte8  
#42 Posted : 06 June 2017 16:07:29(UTC)
Rank: Super forum user
descarte8

This is some what difficult coming in so late to a conversation, but to try and answer some outstanding questions / scenarios / hypothosis:

In an acitivity involving asbestos, the destruction of an asbestos matrix such as asbestos cement will results in a wide range of particles, most of which are abestos fibres still bound in cement.  A proportion however will be released into the air surrounding the release point and dilute according proportionally away from the source according to the inverse square law.

Figures of fibres quoted often relate to the concentration in the breathing zone typically described as being 30cm from the mouth, which would in liklihood be in a range from 10-50cm from the source.  

These fibres, assuming individual fibres, will likely remain airbourne and be re-made airbourne quite easily, due to the size >5um, the rest will settle as dust (in time according to size - Stokes law)

Where are all these fibres now?  Background world air concentrations are (I recall) in the region of 0.000001 f/ml.  If you do the math on this for the total volume of atmosphere for the planet, you get something in the region of 1.4^18m3 or 1.4^27ml3 - so dilution is one answer to the original question.  Add in agregation, washing out in rain (could be condensation nuclei for example) is where most of the fibres go.

Now, how this relates to background concentrations of asbetsos related diseases, this has to take into account both background concentrations 0.000001f/ml is the level estimated for rural countryside, levels as high as 0.0005 may be found inside buildings, and between for built up environments, but also the half-life of asbestos fibres within the lung and the body's natural defence and repair mechanisms against cancer, and the delayed onset of symptoms and the latency in the peak (still increasing - at least in the UK) of asbestos related diseases (a well known phenomena) this explains why there are relatively fwew, but also increasing unmbers of asbestos related diseases such as mesothelioma.

I think if you have any specific (and perhaps shorter) questions I am more than happy to try to answer (as well as providing refernces for any of the above)

thanks 1 user thanked descarte8 for this useful post.
jodieclark1510 on 07/06/2017(UTC)
descarte8  
#43 Posted : 06 June 2017 16:26:31(UTC)
Rank: Super forum user
descarte8

http://www.hse.gov.uk/research/rrpdf/rr696.pdf

Is one example of studies undertaken on the exposure risks from domestic and environmental mesothelioma

If asbestos materials are damaged, it can be assumed fibres are being released, during the removing process, with the exception of non-friable materials (non-freely fibre releasing), asbestos enclosures fitted with HEPA filters and correct removal techniques, would control the release of asbetsos fibres and prevent further disturbance and deterioration of the asbestos and future higher exposures from occuring.

Asbestos abatement should not increase exposure to the public to asbestos fibres.  If deteriorated asbestos is constantly releasing fibres (due to even the movement of air over the surface), removing of the material (again using propoer abatement techniques, enclosures, HEPA filters etc) should result in a decrease of asbestos fibres in the air and reduced exposure / risk to the occupants.

After such removal works are undertaken, strict clearance procedures are followed to demonstrate safe re-occupancy

thanks 1 user thanked descarte8 for this useful post.
jodieclark1510 on 07/06/2017(UTC)
DanIsaacs  
#44 Posted : 07 June 2017 08:42:10(UTC)
Rank: Forum user
DanIsaacs

Originally Posted by: descarte8 Go to Quoted Post
I think if you have any specific (and perhaps shorter) questions

Thanks ever so much for your answer, I'm having such trouble working this model out and I'm a bit like a dog with a bone when it comes to mathematical problems, so I appreciate any light at the end of the tunnel. I do have some questions, I hope they're short and simple enough for you to answer without too much effort.

1. I can see from your rough workings how there is enough capacity in the environment in general for the fibres to have ended up there, but in order to do so (and in order to get building air concentrations down to 0.0005f/ml you quote) they must have made it out of the building somehow and this is where I'm having trouble. If ordinary household cleaning is ineffective (remember I'm modelling unidentified or unknown exposure here so cleaning methods would be vacuum, duster, etc.), and air concentration rapidly falls by settling to 0.0005f/ml (by rapidly I mean in the long term, days/weeks) then after only a few weeks, most of the fibres are in the form of settled dust not being significantly entrained to the air (otherwise the air concentrations would be higher than 0.0005f/ml), so the question is; how do they get out of the building and into the wider environment?

2. I've read the HSE paper you linked in my initial research (but thanks anyway), however, all I picked up from it that might apply to modern public exposure is "This implies that of the order of 100 female cases per year, and a similar number in men, are caused either by environmental asbestos exposure, or by unsuspected occasional or ambient exposure in occupational settings that we have classified as “low risk”". Unless I'm mistaken, I get from this that the most there could possibly be have been from residential/modern domestic type exposure is 200 deaths/per year (presuming all of these are in the "unsuspected occasional" category). Taking a 40yr latency (which is probably below average from small exposures and 50 might be more appropriate) these exposures from 2008 mortalities would have been in 1968ish. So what they seem to be concluding is that in a time when asbestos was virtually ubiquitous and no precautions whatsoever were taken with it, there was only a 200:700,000(total deaths) or 3:10,000 chance of death from interacting with it outside of occupation (or spousal contact). The HSE's own guidance states that a risk of 1:10,000 is considered tolerable for the general public and no action need be taken to reduce it. Unless they're suggesting that all the work that's been done in the past 40 years to reduce the public's exposure to asbestos has achieved nothing, I can't see how the remaining risk can be greater than 1:10,000 when the risk with no precautions whatsoever was only 3:10,000, but that would advise no action need be taken at all by the general public, which is miles away from the advice the HSE are actually giving. Of course 200 deaths is still 200 too many and everything should be done to reduce this figure, which leads me to...

3."Asbestos abatement should not increase exposure to the public to asbestos fibres.". Major surgery should not kill patients, medicines designed to do good should not do harm, any job should not injure the person doing it, but they all do from time to time because the people doing it are human and despite being dedicated professionals accidents happen and the odd "cowboy" will creep their way into almost any profession. That's why we don't have surgery unless it is absolutely necessary, we don't take medicines on the off-chance and we don't do dangerous work unless it is needed. I don't quite understand why the same principle is not being applied to asbestos abatement. Yes, it shouldn't lead to an increase in fibres, but with the best will in the world, it could and so you'd want to know that the risk of this happening is less than the risk from just leaving it there, just like you would with any other risky undertaking. All I've got on the risks from asbestos abatement is a very damning report from HSE revealing that in 49% of spot inspections they did, the building should not have passed the clearance test (despite the fact that the company involved passed it). This would give a rough indication that anyone considering asbestos removal where the current problem is causing an air concentration lower than 0.01f/ml has a 50% chance of making the problem worse. Given that no buildings regardless of the condition of the ACM have yet to be found with more than 0.0005f/ml it's hard to see how any situation would arise where your risks from removing the material are lower than your risks from leaving it in place. So the question here is; do you know of any more compelling figures about the safety of the abatement industry to balance the HSE's rather damning report?

4.You say "If deteriorated asbestos is constantly releasing fibres (due to even the movement of air over the surface)". This is really key to (one of) the models I'm trying to create, the key word being "if". It seems to me that the whole question of removal vs leaving it relies entirely on that "if" and yet I'm seeing no evidence to demonstrate one way or another whether this is actually happening. The key question is, do damaged or friable sections of asbestos or asbestos dust actually release a large number of fibres simply by air movement/normal disturbance; how long does such a release remain in the environment before it is cleared away by some means and is the resulting cumulative exposure a sufficient risk to outweigh the risk from removing it? I don't see any answers to these questions in the literature, if you could point me to any that you're aware of I'd be very grateful.

Thanks again for your time.

descarte8  
#45 Posted : 07 June 2017 09:45:28(UTC)
Rank: Super forum user
descarte8

1. The air inside a building, is not a closed system, windows, doors all open and close but in general the whole atmosphere inside a house (even by design = air bricks) is replaced quite frequently - based on several factors, design, temperature, age and user influences.  There are some exceptions and examples when it can be seen poor ventilation within a building requires mechanical assistance - for example basements in areas with high natural radon.

2.  Im not sure you are comparing like for like in your ratios of deaths and HSE increased risk.  200:700,000 is the ration of asbestos related deaths to total deaths.  Where as the HSE acceptable risk is based on 1 death per 10:000 persons exposed to such a risk:
"risk of death to any individual of 1 in 1000 per annum for workers and of 1 in 10 000 per annum for the public who have a risk imposed" http://www.hse.gov.uk/risk/theory/r2p2.pdf

So you would have to make a comparison by using the 200 figure in a ratio against the total number of UK residents that year

3.  Taking the statement in bold - No buildings regardless of the condition of ACM have a internal concentration greater than 0.0005f/ml. Perhaps based upon answer in 1. are you assuming the clearance level of 0.01f/ml - often the detection limit level, usually within an enclosure - so after enclosure removal there would also be significant dilution) would be ubiquitous throughout the house after asbestos removal?

4.  One recent example study I have found, which in my opinion supports the removal (if left and disturbed risks of exposure remain): https://academic.oup.com/annweh/article/60/1/27/2196148/Airborne-Asbestos-Exposures-from-Warm-Air-Heating?searchresult=1
whereby "four of the five classrooms sampled gave measurable concentrations of amosite by TEM during simulated disturbance conditions. The highest concentration of amosite fibres countable by PCM was 0.0043 f ml −1 with a pooled average of 0.0019 f ml −1" whereby the background without disturbance (which didnt involve any damage) was "below the LOQ <0.00005 f ml".  Though you could counter argue, leaving it in place would also not result in exposure (but this assumes it will not be damaged or disturbed) and all buildings at some point in time will require the asbestos to be removed regardless (depending on the age and condiiton of the building as cities are regenerated and houses rebuilt)

descarte8  
#46 Posted : 07 June 2017 10:12:16(UTC)
Rank: Super forum user
descarte8

As you seem to love the math, heres some to peak your interest!

HSE estimates breathing zone concentrations of 1f/ml generated during drilling of asbestos cement (use of other tools such as grinders, saws are much greater)
If the task lasted 30 minutes, and the individual had a breathing rate of 10 litres of air per minute, the individual would have inhaled 300 litres of air
these 300 litres of air would have contained 300,000ml aka 300,000 asbestos fibres.

In perspective to the life time risk, 0.0005f/ml (this is likely to be an over estimate as well)
An individual living until their 80 would inhale:
10 x 60 x 24 x 365 x 80 = 420,480,000 litres of air
litres/min to hours to days to years to lifetime
and 210,240 fibres (total volume x 0.0005)

Thus the risk in 30 minutes of damaging asbestos cement sheet left in place is exceeding your lifetime exposure (which assumes 0.0005f/ml) in 30 minutes

DanIsaacs  
#47 Posted : 07 June 2017 10:41:39(UTC)
Rank: Forum user
DanIsaacs

Some really helpful ideas, thanks.


1. Are you suggesting that more fibres are removed by air changes than settling rates alone would suggest? For my model I'm using settling rates for amosite of 0.3mm/sec and air change rates of 1ACH (average of domestic properties), but for an activity at about a meter high this doesn't allow the fibres enough time in the air to experience any significant losses, basically (depending on how much turbulence you add) about half the fibres could be removed by air changes before settling. Whilst this might sound like a lot, it is insignificant if the remaining half stay in the building for the next 30 years only removed at K factors for disturbance of dust of 1e-5. To get rid of these remaining fibres by air movement within a reasonable time scale we'd have to postulate much higher settling times, but that, in turn would make each interaction much less risky as the air fibre concentration would be reduced to background within hours.


2. Yes, there is a presumption in my comparison that in 1968, the whole population would be exposed to some sort of asbestos incident of a similar scale to that which we might envisage nowadays in a domestic setting. I'm not sure that this is an unwarranted presumption though, especially when you consider how much of the population would have been exposed to much higher levels than that. I think, if anything the comparison is likely to over estimate exposure risk nowadays. Not only that, but it would be an exactly like for like comparison if you were to include having an asbestos survey or test done in the first place. In that scenario we would be comparing the combined risk of both encountering a piece of asbestos and being exposed to sufficient fibres to cause you harm. For this scenario the figures are indisputable because the outcome of both of those factors together is recorded in the mortality statistics and they show that in 1968(ish) that combined risk was 3:10,000. So presuming even a moderate drop in asbestos use the risk now must be less than 1:10,000 (the risk in this case being both encountering some asbestos and being exposed to enough fibres to do you harm) the HSE standards would suggest that one need take no action to counter that risk (i.e. one need not find out if a thing is asbestos at all because it is either very unlikely to be, or it is very unlikely to harm you if it is, it must be one of those two otherwise more non-occupational deaths would turn up in the mortality statistics).


3. Partly, yes. I was also considering reassurance testing which would consider the whole building but also depending on the size of the enclosure a dispersal to the whole building could involve as little as a quarter reduction (say a whole room in a four room house was enclosed), maybe a tenth at most so 0.01 becomes 0.001 presuming the clearance testers even did their job correctly, which is still double the exposure the building was in all likelihood at before the removal.


4. Thanks for the link, I'm not sure if I'm reading this right but it does seem to be saying that for AIB in the ceiling plenum, in two out of three cases there was no measurable increase from background (which in these schools was even lower at 0.00005f/ml) and in one case levels rose to 0.002f/ml average. Doesn't that mean that in neither case could removal demonstrate a lower air concentration than just leaving it and for any given l contemplating such action there is a two out of three chance of removal making matters worse? If that's the case for an entire ceiling made out of AIB with forced air being blown over it then where does that leave my model risk assessment for finding a small piece of damaged AIB in a domestic property, the chances of harm from just leaving it must be astronomically small, such that the chances of increasing exposure by some accident or poor workmanship during removal must surely be much higher. Am I reading this wrong?

DanIsaacs  
#48 Posted : 07 June 2017 11:02:21(UTC)
Rank: Forum user
DanIsaacs

Originally Posted by: descarte8 Go to Quoted Post

As you seem to love the math, heres some to peak your interest!

HSE estimates breathing zone concentrations of 1f/ml generated during drilling of asbestos cement (use of other tools such as grinders, saws are much greater)
If the task lasted 30 minutes, and the individual had a breathing rate of 10 litres of air per minute, the individual would have inhaled 300 litres of air
these 300 litres of air would have contained 300,000ml aka 300,000 asbestos fibres.

In perspective to the life time risk, 0.0005f/ml (this is likely to be an over estimate as well)
An individual living until their 80 would inhale:
10 x 60 x 24 x 365 x 80 = 420,480,000 litres of air
litres/min to hours to days to years to lifetime
and 210,240 fibres (total volume x 0.0005)

Thus the risk in 30 minutes of damaging asbestos cement sheet left in place is exceeding your lifetime exposure (which assumes 0.0005f/ml) in 30 minutes

Thanks. 30 minutes of drilling is one big hole though! It takes a power drill about a second to get through a few mm of fairly soft material so thirty minutes would be quite a project, but I do like the route you've taken to comparison, it bypasses a lot of unknowns. Still doesn't answer whether eitheir of those risks is significant in any though, doubling an insignificant risk, just gives a slightly bigger but still insignificant risk.

Bob Hansler  
#49 Posted : 07 June 2017 11:27:07(UTC)
Rank: Forum user
Bob Hansler

Well, I'm not sure where the rest went but a few found their way into my left lung.  I'm not to happy about the situation but considering that the problem was noted before 1900 I feel a little P***** off that the problem was left to run riot by various people in positions of power.  To them it's 'Thanks folks' from one 16 year old apprentice electrician back in '69!!!

johnmurray  
#50 Posted : 07 June 2017 17:40:15(UTC)
Rank: Super forum user
johnmurray

DanIsaacs  
#51 Posted : 08 June 2017 06:50:44(UTC)
Rank: Forum user
DanIsaacs

Originally Posted by: Bob Hansler Go to Quoted Post

Well, I'm not sure where the rest went but a few found their way into my left lung.  I'm not to happy about the situation but considering that the problem was noted before 1900 I feel a little P***** off that the problem was left to run riot by various people in positions of power.  To them it's 'Thanks folks' from one 16 year old apprentice electrician back in '69!!!

I'm sorry to hear of your condition. The result no doubt of a lot of private firms putting profit before their duty of care and government unwilling to look at exactly what's happening. I'd like to think we've learnt our lesson, but with the only remaining threat being the disturbance or removal of asbestos in buildings, I can't help thinking we have exactly the same situation (albeit less severe), the whole event is being handled by a collection of private firms who (I see no reason to believe) will not just put profit before their duty of care again, unless the quality of humanity has changed since the 1960s and the bosses of these firms are just "better" people. At least the government seem a bit more willing this time round, but personally, I fear not sufficiently so.



Thank you so much, the paper on drawing pins contains some data which is almost exactly what I'm looking for in my models. I'd read the summary published results of the drawing pin tests, but they were not nearly as exhaustive as this document. I will have to digest the data and put it into my models, I'm particularly intested in the experiment with the drill and cowl which they seem to imply will have picked up all the airborne fibres. Given the size of the hole (at least 100 billion potential fibres in volume) and only a few thousand airborne fibres picked up, this initially supports the theory that the discrepancy is indeed caused by a very low (0.000000001%) proportion of all possible fibres involved in any disturbance actually ending up of respirable size.

Still doesn't answer what happens to the rest though. They can't get broken up into respirable sized fibres as that would bring the building air concentration higher than the measurements taken. I can only presume they get swept/vacuumed and the tests showing that normal vacuuming doesn't work are flawed because they use artificially inoculated carpets etc, not ones resulting from real damage where most fibres are in agglomerated bundles and so more easily picked up.

The consequence of this theory though would be that the advice to remove damaged AIB that can't be encapsualted should depend heavily of the success rate of the industry. Even if we were to generously give it a 99% success rate (i.e only 1 in 100 jobs go wrong in any way, which is much better than the HSE report seems to show) you'd want to know that leaving the AIB in place was going to cause a risk 100 times greater than a botched removal job, otherwise your total risk from getting it removed exceeds your total risk from leaving it in place. I'm not sure these results support that theory as they seem to show that even drilling damage to AIB (which is quite substantial) releases a few thousand fibres of a dangerous size, which once distributed through a 10x10 office room would give air concentrations below the clearance level (which is the best even a perfect removal operation can promise, let alone a botched one), but without accurate data on the safety of the abatement industry I can't be sure.

Still, thanks again for digging those papers out for me, sometimes doing research one cannot see the wood for the trees.

johnmurray  
#52 Posted : 08 June 2017 08:03:32(UTC)
Rank: Super forum user
johnmurray

The problems are complicated, because of the massive variability of disease in those exposed.
The common assumption, that high exposure to fibres leads to a high chance of disease development, fails in many cases of low-exposure disease development.
As those exposed, occupationally, to high levels cease to be among the living, things may become clearer as to the problem of low-exposure disease...maybe.
I suspect the employee problem is less due to them not trusting the advice, as to them being lazy...in any case, it is an employers requirement to ensure they follow procedures.
Funnily enough, I clearly remember the blue asbestos used in WWII gas masks....a very pretty blue....they used to break-up the masks and throw the asbestos into the drains...
DanIsaacs  
#53 Posted : 08 June 2017 08:53:38(UTC)
Rank: Forum user
DanIsaacs

Originally Posted by: johnmurray Go to Quoted Post
I suspect the employee problem is less due to them not trusting the advice, as to them being lazy...in any case, it is an employers requirement to ensure they follow procedures.

Yes, that's basically what concerns me in my risk assessments. Conventional risk assessment procedures for asbestos in buildings seem to take into account pretty much the worst case scenario for leaving the material in place, but presumes the removal operation will be carried out perfectly with no other consequenses. If building workers can be sufficiently lazy/unaware/incompetant as to damage ACMs even if they are labelled as such, the so can the workers of asbestos abatement firms. As for the duty of care being with the employers, if the bosses of private companies cared about the safety of their workers we wouldn't be in this mess in the first place.